I just replaced 36C03 gas valve on my furnace after a flood

and cleaned out pilot light...
I just replaced 36C03 gas valve on my furnace after a flood and cleaned out pilot light tube. I get a nice blue pilot light but I can't get it to stay lit after I release pilot knob. I already replaced thermocouple and it didn't help. What else can cause the valve to shut down pilot light?
Lenny
Show More
Show Less
Ask Your Own HVAC Question
Answered in 7 minutes by:
11/3/2012
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 22,368
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified
Welcome,
I will do my best to help you with your issue

Since you've replaced both the thermocouple and the gas valve the only other causes for the pilot to go out when you release the pilot light button are a pilot flame that's too small to heat up the thermocouple. A thermocouple that's not properly positioned so only the top 1/3 is in the flame or a bad thermocouple connection at the gas valve (did you use pipe dope on the threads?)
Ask Your Own HVAC Question
Customer reply replied 5 years ago

Thermocouple heats up to a red color. Flame covers about 90% of its length I didn't use pipe dope on the threads. I also measured voltage on my old thermocouple and it went up to 32mV. Didn't measuse it on new one, figured it wasn't the problem.

If the flame covers 90% of the length of the thermocouple then that's probably your problem. Thermocouples must maintain a cold junction in order for them to work. This means the bottom 2/3's of the tip should not see any flame.
Ask Your Own HVAC Question
Customer reply replied 5 years ago

I pulled it out so the flame was covering only 1/3 of the tip and tried going through start up process several times. It still doesn't stay lit.


 


Is it too much moisture in the air or gas line needs to be purged?


 

If you have a flame then air is not an issue. If you read 32 mV on the old thermocouple then it wasn't bad. I've listed all the possibilities. You said you didn't use pipe dope on the threads but is the connection at the gas valve tight? If so then we've covered all the bases; new gas valve, new thermo, 1/3 of the tip only in flame, strong pilot, thermo is hot, tight connection at the gas valve. There isn't anything else that I can think of. If you've done all this all I can do at this point is to opt out and see if one of my colleagues has any ideas
Ask Your Own HVAC Question
One other thing, it's a reach but; is this a typical thermocouple? No terminal block in the thermo? just a straight bare copper wire?
Ask Your Own HVAC Question
Customer reply replied 5 years ago

It's plain thermocouple labeled:


 


18" Universal Thermocouple

Opting out. Please do not respond until you get a response from another expert
Ask Your Own HVAC Question
Jerry
Jerry, Service Technician
Category: HVAC
Satisfied Customers: 3,362
Experience: HVAC Technician. Hearth Products Specialty
Verified

Please check the millivoltage on the new thermocouple, or put the old one back in. This sounds like the new thermocouple may have either been bad from the start, or is now bad. Rick has covered all the bases. Your new t couple should produce at least 20 millivolts.

Ask Your Own HVAC Question
Customer reply replied 5 years ago

I assume by "thermopile" you are refering to thermocouple. I disconected it and hooked it up to multimeter. Turned on the pilot and it went up to 28mV and was still slowly climbing up.

Yes, I had edited my post just soon after I proof read it.

Did you replace the gas valve with the exact same model? It sounds as though there is no connection being made at the valve from the couple. Also check to make certain, none of the control wires are accidentally being ground out. This will prevent the pilot from staying on.

Ask Your Own HVAC Question
Customer reply replied 5 years ago


Just checked TH and TR and they are not connected to the ground.

My old gas valve was 36CO3 Type 221.

The replacement is 36C03-300. I used 1/3" to 1/2" adapter on the outlet line. The box was labeled with adater included, but it wasn't in the box, I had to buy it at Home Depot.

Try removing all wires from the terminals on the control valve and only leave the thermocouple connected, see if this will allow the pilot to stay on. Do not over tighten the thermocouple, this is a simple wire connection and not a gas tight connection.
Ask Your Own HVAC Question
Customer reply replied 5 years ago


Do you want me to remove E.C.O. jumper as well?

No, you must leave the eco jumper in.
Ask Your Own HVAC Question
Customer reply replied 5 years ago


Disconected TH and TR wires and made sure thermocoupler connection is not overly tight. Did'nt help.

Ok, I will have to opt out. It sounds as though your new gas control valve is bad, I cannot think of any other tests that you can do, or any other problems that may cause this.
Ask Your Own HVAC Question
Customer reply replied 5 years ago


Thanks for your help. Hope someone else has the answer.

mranswer
mranswer, HVAC Mechanic
Category: HVAC
Satisfied Customers: 6,160
Experience: 20 years experience running my own business
Verified
The pilot holding coil on your new gas valve is bad. You need another valve. There is nothing complex here as you measured the right voltage from the t/cpl so the only reason the valve will not allow pilot flow is because the holding coil is not operating. Rare to get a bad valve, but there is no doubt in my mind that this is what is wrong.
Ask Your Own HVAC Question
Customer reply replied 5 years ago


I am coming to the same conclusion. I will order another valve by express shipping and if that's the case I will give you satisfied answer. Will have to wait a few days and see

OK- this issue is as simple as a light bulb and a socket- power to the socket means the bulb is bad if it does not lite up. Nothing mysterious here.
mranswer
mranswer, HVAC Mechanic
Category: HVAC
Satisfied Customers: 6,160
Experience: 20 years experience running my own business
Verified
mranswer and 87 other HVAC Specialists are ready to help you
Ask your own question now
Ask mranswer Your Own Question
mranswer
mranswer
mranswer, HVAC Mechanic
Category: HVAC
Satisfied Customers: 6,160
6,160 Satisfied Customers
Experience: 20 years experience running my own business

mranswer is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,730 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
The red emergency on/off switch was accidentally turned off.
The red emergency on/off switch was accidentally turned off. After turning it back on, checking the breakers, and turning the thermostat off, then on and resetting it, I still have no heat. What else … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I changed my thermostat and then put the original back nd
I changed my thermostat and then put the original back nd not it will not light up at all … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,086 satisfied customers
Thermostat keeps returning to 70 degrees even tho I cancel
Thermostat keeps returning to 70 degrees even tho I cancel present temp by pressing run and put a new lower temperature in and it still returns to apparently a programmed 70 which comes in during the … read more
D.E. Anderson
D.E. Anderson
Industrial Refrigeration Service Manager
198 satisfied customers
I have 4 honeywell rlv4305 thermostats. they are all hot on
Hello, I have 4 honeywell rlv4305 thermostats. they are all hot on the top right corner. they are all in standby mode. Is this an issue, or are they hot, because they are not calling for heat right no… read more
D.E. Anderson
D.E. Anderson
Industrial Refrigeration Service Manager
198 satisfied customers
I recently had a bosch geothermal CE035 installed in my
i recently had a bosch geothermal CE035 installed in my home. i am wondering how do I change the setting to keep the auxiliary heat off longer ? … read more
D.E. Anderson
D.E. Anderson
Industrial Refrigeration Service Manager
198 satisfied customers
Furnace will automatically restart when tempers urethane
Furnace will nut automatically restart when tempers urethane drops? … read more
Chad DeYoung
Chad DeYoung
8 satisfied customers
How to change cycles on Honeywell Thermostat?
I have a Honeywell thermostat model RTH63500, how do I change the cycles per hour or the temperature swing, I do not need my heat or my AC cycling in within 1 degree. With all the energy star stuff ou… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
How can I wire an existing power vent to a therm performance
Hi. How can I wire an existing power vent to a therm performance water heater? … read more
Rick
Rick
HVAC Supervisor
22,368 satisfied customers
Furnace fan won't stop running after the heating cycle is done
My furnace fan won't stop running after the heating cycle is done. The only way to shut it down is to turn off the main power switch located near the furnace. I replaced the limit switch a while back … read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I have an TACO SR502 that controls 2 pumps one for zone1 for
Hello, I have an TACO SR502 that controls 2 pumps one for zone1 for Hot water loop and the other for zone2 for baseboard heat and I also have a new TACO ZVC406 that control one other pump that supply … read more
Rick
Rick
HVAC Supervisor
22,368 satisfied customers
My Carrier 98% efficient warm air heater does not reach
My Carrier 98% efficient warm air heater does not reach maximum fan speed in the heating mode. There is an dd - on "A" cooling coil (by Trans) added above the bonnet and the same fan turns fast enough… read more
travis webb
travis webb
tech.
2,153 satisfied customers
How do i reset the filter thingy on my thermostat?
how do i reset the filter thingy on my thermostat? … read more
travis webb
travis webb
tech.
2,153 satisfied customers
Pressure switch error on my trane xl14c unit. Looking for a
Pressure switch error on my trane xl14c unit. Looking for a reset button but can't locate it … read more
travis webb
travis webb
tech.
2,153 satisfied customers
Having a issue with my early rudd gas pack. I can hear lift
Having a issue with my early rudd gas pack. I can hear lift motor come on and burner lights .burner gos out in under a min. … read more
Chad DeYoung
Chad DeYoung
8 satisfied customers
One week. Any parts I'll need will require being shipped in
hello, my name is dean JA: I'll do all I can to help. How long have you been dealing with this? Customer: One week JA: Do you plan on doing the work yourself? Customer: Yes JA: Anything else we should… read more
Rick
Rick
HVAC Supervisor
22,368 satisfied customers
I am having problems with my humidifier. An Aprilaire Model
I am having problems with my humidifier. An Aprilaire Model 700.Every time it starts, some water leaks out of the valve as shown in the picture. Not much, would say about an ounce or two. Then the lea… read more
Chad DeYoung
Chad DeYoung
8 satisfied customers
My Gibson furnace stopped working. Could you advise how I
My Gibson furnace stopped working. Could you advise how I can turn it back on? … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My 3am fuse blows up every time when I start heating my
My 3am fuse blows up every time when I start heating my house. … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x