Welcome, I will do my best to help you with your issue

The first thing to do is to try a reset. Turn the power switch on the side of the furnace off, wait a minute or so then turn it back on and tell me what happens.
JACUSTOMER: I did it already several times - nothing happens.
Rickheatdoc : Also when you "checked the fuse" which fuse did you check?
JACUSTOMER: Fuse that is same as auto fuse, I think 3 amp
Rickheatdoc : Have you flipped the breaker in the electrical panel off then on again?
JACUSTOMER: I did it once, all of them one by one.
Rickheatdoc : Ok, I'm going to need a model number for your furnace
JACUSTOMER: The red light that is on circuit is on - does it mean that electrical part is ok?
JACUSTOMER: PG8UAA048111
Rickheatdoc : If you see a lit LED then the unit has power
Is the LED blinking?
JACUSTOMER: No, it stays. Also there is no clicking sound that should be when furnace trying to ignite.
Rickheatdoc : Do you have a multi-meter?
JACUSTOMER: Yes, what should I check?
Rickheatdoc : Hang on, checking something Are you sure you have a PG8U not a PG8J? You mention a clicking noise and my spec shows no pilot only hot surface ignition. I have no spec for a PG8U.
JACUSTOMER: Let me recheck. It is PG8U and also label says: this device has no pilot and equipped with ignition device.
Rickheatdoc : Ok your clicking description sounded like a pilot burner electrode.

Is the blower access panel in place?

JACUSTOMER: There is no clicking noise and I think it was earlier when furnace was operated normally. Yes.
Rickheatdoc : Ok the should be a switch on the blower with a red lead remove the red lead and wait for the LED to go out then reconnect it and tell me what the blinking LED sequence is. Sorry I meant to say on the draft induction fan not the main blower. keep the blower door in place.
JACUSTOMER: Could you please give me more description or link to picture to understand where it is located. Is it upper door?
Rickheatdoc : Do you mean the draft fan?
JACUSTOMER: Where should I look for the LED?
Rickheatdoc : The LED is on the circuit board. The exhaust vent starts at the draft fan.
JACUSTOMER: Same that is currently is on when door is closed?
Rickheatdoc : Yes there's only one
JACUSTOMER: I should remove it and put it back?
Rickheatdoc : There is no viewing port? You should be able to see it with the blower door in place.
JACUSTOMER: I mean what should I do to make this test? There is a small round window to see Led. Remove red wire?
Rickheatdoc : There is a safety switch on the on the draft fan. You want to remove the red lead until the LED goes out then reconnect it and tell me the blinking sequence.
JACUSTOMER: Draft fan is behind upper door, correct?
Rickheatdoc : Yes. I have to leave and I don't want to leave you hanging so I'm going to opt out and open this question back up for my colleagues to help you. One should pick up your question shortly.
JACUSTOMER: OK, I have found a page with “bad starting capacitor” and looks like it’s my case. Here is the link:http://www.fixya.com/support/t2796330-blower_motor_stopped. After turned on for 2 hours, blower fan started for the first time and stopped. After about 10 attempts it’s finally started and not stopped and furnace currently working.
Ask Your Own HVAC Question
Customer reply replied 5 years ago

I have already resolved this issue and here is the info: I have found a page with “bad starting capacitor” and looks like it’s my case.

Here is the link:

http://www.fixya.com/support/t2796330-blower_motor_stopped

After turned on for 2 hours, blower fan started for the first time and stopped. After about 10 attempts it’s finally started and not stopped and furnace currently working.

Comfort Specialist
Comfort Specialist, HVAC Technician
Category: HVAC
Satisfied Customers: 1,368
Experience: Master Lic. holder for HVAC & Gas, Contractor, Estimator, Designer, Air Balance Certified, LG Master Commissioner, UNC Cert. holder for Industrial Ventilation
Verified

Yeah, you can usually eliminate the other furnace components by watching the furnace fire up. You can remove the door and set the thermostat for heat with the temperature set up higher than the room temp. At that point go to the furnace and sit in front of it while holding in the door switch (button). You will see the furnace try to fire. If it ignites and then shuts down after a minute or so it pretty much eliminates a few of the major components and narrows it down. One good way to visually inspect a bad fan capacitor is by looking at the top cap where the two terminals are and the wires connect.

In some cases the top cap will swell and cause the cap to bulge upwards. A standard fan capacitor can be as cheap at around 5-10 dollars depending on size and can be purchased at any HVAC supply house. Brand does not matter, just be sure you buy the exact size replacement and voltage. You can power the furnace down completely at the electrical panel and disconnect and use a screwdriver to bridge the two capacitor terminals while holding the insulated handle of the screwdriver. This will discharge any electricity stored in the capacitor and make for safe removal. You can then take the capacitor to a supply house for testing or replacement. The supply house will have to use a special capacitance tester to tell if it is within range. If the capacitor test good you will want to get back into the furnace and go further with diagnostics. I can also help with that as long as you own or borrow a volt-meter.

Also, if you are not in a hurry and the current capacitor seems to be holding up you can also purchase one online. If you need help doing so and you can wait let me know and I'll be glad to point you in the right direction.

It may help for you to have a copy of the actual furnace SERVICE GUIDE. It's not just some manual. It has valuable information that may help you if this problem returns. I have pasted the link to the guide below. Simply copy and paste it into your browser address bar then save a copy to your computer for future reference: http://www.docs.hvacpartners.com/idc/groups/public/documents/techlit/sg-pg8d-04.pdf

Ask Your Own HVAC Question
Customer reply replied 5 years ago

I am not in a hurry. Could you please point me where I can buy capacitor for my furnace online?

Sure thing. Your furnace blower takes a 10mfd @ 370v capacitor. I have pasted the address below to a $5.99 replacement with free shipping.

http://www.amazon.com/Universal-Capacitor-10-MFD-370V/dp/B0002YTKAK/ref=sr_1_2?ie=UTF8&qid=1351904992&sr=8-2&keywords=10+mfd+370

Can't beat such a good deal!

Thank you for using Just Answer.

Comfort Specialist
Comfort Specialist, HVAC Technician
Category: HVAC
Satisfied Customers: 1,368
Experience: Master Lic. holder for HVAC & Gas, Contractor, Estimator, Designer, Air Balance Certified, LG Master Commissioner, UNC Cert. holder for Industrial Ventilation
Verified
Comfort Specialist and 87 other HVAC Specialists are ready to help you
Ask your own question now
Ask Comfort Specialist Your Own Question
Comfort Specialist
Comfort Specialist
Comfort Specialist, HVAC Technician
Category: HVAC
Satisfied Customers: 1,368
1,368 Satisfied Customers
Experience: Master Lic. holder for HVAC & Gas, Contractor, Estimator, Designer, Air Balance Certified, LG Master Commissioner, UNC Cert. holder for Industrial Ventilation

Comfort Specialist is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Goodman GVC9 furnace: blower will turn on, but no heat.
Goodman GVC9 furnace: blower will turn on, but no heat. Checked intake and exhaust, they look ok. Flashing code 4 so replaced the filter which needed replacing. Limit switch in middle of unit shows no… read more
Rick
Rick
HVAC Supervisor
23,072 satisfied customers
Concord 90 furnace blower runs wont stay lit. I blew out
concord 90 furnace blower runs wont stay lit JA: Did you check the furnace's filters? Customer: yes JA: Do you plan on doing the work yourself? Customer: yes JA: Anything else we should know to help y… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
My RUUD furnace blower is not turning on. The circuit board
My RUUD furnace blower is not turning on. The circuit board says its a "Limit Switch Open" error. How can I fix this?… read more
Rick
Rick
HVAC Supervisor
23,072 satisfied customers
My 59SC2b furnace blower running time and blow cold air
My 59SC2b furnace blower running long time and blow cold air after heating cycle. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Luxaire9v serires furnace Blower won't go into second stage.
Luxaire9v serires furnace Blower won't go into second stage. I replaced pressure switch and still no working. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Carrier furnace blower fan comes on without heat set point
Carrier furnace blower fan comes on without heat set point being triggered … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
My furnace blower stopped suddenly. I live in about 2,000sq
My furnace blower stopped suddenly. I live in about 2,000sq feet single family home. I called an HVAC technician. They arrived and installed a new motor. However, after they left I run the furnace and… read more
Rick
Rick
HVAC Supervisor
23,072 satisfied customers
Have an older luxaire commerical furnace blower motor runs
have an older luxaire commerical furnace blower motor runs all the time … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
My furnace blower wiil not start. Hopefully. Furnace tries
my furnace blower wiil not start JA: Did you check the furnace's filters? Customer: no JA: Do you plan on doing the work yourself? Customer: hopefully JA: Anything else we should know to help you best… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My evcon furnace blower fan cycles every day at 8:20 with no
My coleman evcon furnace blower fan cycles every day at 8:20 with no demand and no exhaust fan operation. It just co es on runs for 2 minutes then shuts down, and there was no previous heat dema d … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
My Nordyne furnace blower starts immediately when I turn on
My Nordyne furnace blower starts immediately when I turn on the switch. The LED light on the control board flashes 5 times. There is no flame. … read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
My '92 Carrier model 58ssc furnace blower motor has finally
Hi! My '92 Carrier model 58ssc furnace blower motor has finally quit. I wonder what I can replace it with … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
We have a question about a furnace blower that is not
We have a question about a Bryant furnace blower that is not working. The model number is ***** We have noticed a blinking light error that has two short and four long blinks. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a loud noise coming from furnace blower motor. Do i
I have a loud noise coming from furnace blower motor. Do i need to oil up the motor? Its a lennox g40uh (x) … read more
Rick
Rick
HVAC Supervisor
23,072 satisfied customers
I'm replacing a furnace blower motor and assumed it would be
I'm replacing a furnace blower motor and assumed it would be plug and play. Old motor had 5 wires; white, brown, black, red and blue. The brown and white went to the cap, with another white wire comin… read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
387 satisfied customers
My furnace blower won't shut off. Have confirmed it's not
My furnace blower won't shut off. Have confirmed it's not the thermostat (by disconnecting same). Could the fan relay cause this? … read more
derekh1966
derekh1966
0 satisfied customers
Our lenox furnace blower doesn't come on when on auto
Our lenox furnace blower doesn't come on when on auto setting. Still comes on when set to on. Ideas of what maybe going on? … read more
Tim Ohms
Tim Ohms
HVAC Journeyman
31 satisfied customers
Furnace blower cycle on and off even when thermostat is in
furnace blower cycle on and off even when thermostat is in the off position. … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x