My amana 90 furnace is not working, I tried turning it on and it sounds like it wants to start but just cant do it. Where should I start?
Show More
Show Less
Ask Your Own HVAC Question
Answered in 2 minutes by:
9/24/2012
Tom
Tom, HVAC Technician
Category: HVAC
Satisfied Customers: 770
Experience: 16+yrs HVAC/R service. Residential Commerical Industrial
Verified

Tom :

Hi...Tom here..Sorry you're having trouble.


 

Tom :

I'll do my best to help and opt out if I cannot.


 

Tom :

What does it do on a call for heat? And have you checked the control board to see if it's giving you a fault code?


 

Tom :

Specifically........does the exhaust blower start? Then (assuming hot surface ignition) does the ignitor glow?


 

Customer:

I am not going to lie to you tom im not exactly a professional and no nothing about furnaces so here goes nothing. Im not sure what fan it is on my thermostat i have an auto and on on my fan switch when i turn it to on it works and blows air.


 

Tom :

Ok...fair enough! If you were a professional furnace guy you wouldn't be here...


 

Tom :

The fan 'on' switch on your furnace is for the 'main blower'... the one that moves air through the furnace to your ducts.


 

Tom :

Leave it on auto for now.


 

Tom :

Is your furnace in the basement / attic?


 

Customer:

ok


 

Customer:

basement

Tom :

Ok......now if you go down there and remove the top service cover....you'll see a small blower unit attached to the exhaust pipe. A 90% will have plastic exhaust...on a call for heat the first thing that has to happen is the exhaust blower has to start...check that first.


 

Tom :

If it's in 'lockout' you'll need to cycle the power off then on to reset...you might as well do that just in case.


 

Tom :

Generally they'll try to light 3 times and if they don't the control board goes into lockout requiring reset.


 

Customer:

k so turn the power off and try a reset?


 

Tom :

Yes..sorry for the delay...


 

Tom :

Any luck?


 

Customer:

no i cant get it to do anything now

Tom :

Do you have only the top service panel off or do you have the lower one off as well?


 

Customer:

just the top, ok i did a reset and when i turned the power back on an orange light started to glow.. and then it tried to go and now nothing

Tom :

Ok the orange glow is the ignitor...


 

Customer:

the exhaust fan is going

Tom :

After that it will delay for a couple of minutes and retry...after 3 it locks out.


 

Tom :

Is this the first time you've tried the heat this fall?


 

Customer:

yes and its on its third attempt


 

Tom :

ok..it will lock out after that. This may sound dumb.......has the gas been turned off to the furnace for any reason?


 

Tom :

Check the gas shut off valve near the furnace.


 

Customer:

i looked at that i believe it is on the hose is running vertical and the lever is also up and down with the hose


 

Tom :

OK good......


 

Tom :

Now locate the gas valve....may look similar..but not exactly like the one in the pic


 

Tom :

It will have the gas pipe and a couple of wires attached.


 

Tom :

Reset the power.........let it try to start again....when the ignitor has warmed up for a few seconds..you should hear the valve click if it opens to let gas in the furnace3


 

Tom :

furnace.


 

Tom :

See if it clicks and let me know.


 

Customer:

got it and yes it clicked

Tom :

but absolutely no flame?


 

Tom :

Or does it light and go right out?


 

Customer:

i cant see a flame the ignitor turns bright orange and then goes out and it tries three times and shuts down

Tom :

Ok....take a look at the gas valve....it should have either a knob to turn it on/off or possibly a little switch....make sure it's on.


 

Customer:

its on


 

Tom :

Ok...thanks for checking that. You never know.


 

Customer:

should i turn it off then on

Tom :

No..on is good.


 

Tom :

Ok..from my end...it sounds like the gas valve may be defective. If your gas is on...and the valve clicks.......it should light.


 

Tom :

The only other thing...and it's a little hard since I'm not there.....is if the air pressure switch is opening during the ignition cycle and making it start over.


 

Customer:

so i have to call the professionals not type to them ha

Tom :

possibly! You're doing great though!


 

Tom :

Is there a small window in the lower panel to see the control board light?


 

Tom :

IF not...you may have to remove the lower panel to get a look at it. There will be a door switch you'll have to hold down to power it back up. Try that and see if you get a fault code. There should be a light on the control board that will flash a series of flashes for different faults.


 

Tom :

It's probably going to be a single flash indicating excessive tries for ignition..but just thought I'd check.


 

Customer:

k there is not light on down there i opened the lower one and held the switch.. but when i did a reset there was flames for a brief moment on the first start up after that nothing on the second and third

Tom :

Ok....very good. I would try this ....last test....... Get a tool...wrench...pliers..small hammer....etc..try lighting it.......when it clicks.. tap on the valve ...anywhere you can get the tool on it......don't beat it..but firm taps....see if it lights.....sounds like the valve is sticking.


 

Customer:

now i cant get a flame again sounds like i better call in the big guns

Tom :

Yeah...sorry it wasn't something simple....you did great.....and we eliminated all of the obvious stuff. You never know.......often times it's something simple.


 

Tom :

I'm guessing a defective gas valve though.


 

Tom :

Anything else I can do for you tonite?


 

Customer:

i appreciate your help how do i pay you for your time


 

Tom :

The problem is easily verified by hooking up a gas pressure gauge.


 

Tom :

Something service guys will carry.


 

Tom :

By rating my answer (as long as you don't rate it poor....) I'll receive credit for assisting.


 

Tom
Tom, HVAC Technician
Category: HVAC
Satisfied Customers: 770
Experience: 16+yrs HVAC/R service. Residential Commerical Industrial
Verified
Tom and 87 other HVAC Specialists are ready to help you
Ask your own question now
Ask Tom Your Own Question
Tom
Tom
Tom, HVAC Technician
Category: HVAC
Satisfied Customers: 770
770 Satisfied Customers
Experience: 16+yrs HVAC/R service. Residential Commerical Industrial

Tom is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
My 26000 btu heater began with it cutting off ocasionally
Second opinion] my 26000 btu heater began with it cutting off ocasionally now it wont light at all but the pilot will light @ when u release the button it goes out what is my problem. thanks … read more
Rick
Rick
Supervisor
22,874 satisfied customers
Electric heated floors in bathroom not working. Replaced
Electric heated floors in bathroom not working. Replaced Tstat and although the Tstat is working it's not heating floor. Checked ohms on temp sensor and also ohms on heating cable. Not sure what to te… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,142 satisfied customers
Battery died in thermostat, replaced batteries but
Battery died in thermostat, replaced batteries but thermostat does not come on and furnace won't kick on … read more
Appliance Guru
Appliance Guru
17,062 satisfied customers
My boiler in on but is not working. The lights on the screen
my boiler in on but is not working. The lights on the screen is on but not heat. … read more
Rick
Rick
Supervisor
22,874 satisfied customers
I'm not very good at these things. My Ultra 80 forced air
Hi. I'm not very good at these things. My Ultra 80 forced air heater/cooler has suddenly stopped working. The air blows, but no heat. Can't reach my repair guy as it's a holiday. Is there something ea… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I'm wondering if humidistat for my he120 can be tapped onto
Hi I'm wondering if humidistat for my he120 can be tapped onto hum terminal on my furnace … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,142 satisfied customers
Wow, I hope so. I gave a Tempstar Gas furnace, Model
Wow, I hope so. I gave a Tempstar Gas furnace, Model NTC5050BFB2, the gas will not kick on. My buddy is an A/C guy, but cannot find the legend for the LED indicators. Do you know where I cab check? … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Well im trying to see if there is a way to light my Furnace
Well im trying to see if there is a way to light my Furnace light … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Baxi heater and live in Maine. I am wondering
I have a Baxi heater and live in Maine. I am wondering approximately how much of my gas is used for heat and how much for hot water? … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,142 satisfied customers
I have an old intertherm propane furnace in my mobile home.
Hi. I have an old intertherm propane furnace in my mobile home. The blowe motor model 497540 has recently been making chirping noise on start up lasting bout 1 minute. Goes away. Doesn't happen again … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
FocusPro6000. What drives the Emergency Heat function? Heat,
FocusPro6000. What drives the Emergency Heat function? … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Carrier WeatherMaker 9200. The flame will light for
I have a Carrier WeatherMaker 9200. The flame will light for about 3 minutes with blower on. Then the flame will be off with an error code 33. The blower continues to run for a while until the error c… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
We have a Lennox I comfort system installed in 2012- we live
we have a Lennox I comfort system installed in 2012- we live in Indiana and temps have been from 20 to below zero- we have had 5 visits from a technician- replaced the pressure valve for heat- what ha… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I called 855 # and waited half hour then gave up; Just had
Just had new furnace installed plus the Honeywell therm a stat. I just want to be able to read the temp in my home from my smart phone. I am not good at WI Fi stuff. I pulled therm from wall , waited 15 seconds and replaced. Message is: Register at total connect; I can not find "total connect" to register at. … read more
Richard
Richard
IT Manager
IT Manager, Consultant
3,275 satisfied customers
Have a Nordyne G6RC100C-16, getting code that the Limit
Have a Nordyne G6RC100C-16, getting code that the Limit Circuit is open. I have tested the thermostat, it is good. Possible Control Board failure? Where would I get one? Northville Michigan … read more
Rick
Rick
Supervisor
22,874 satisfied customers
I have a nordyne package unit model R6GD-X36K072C Serial
i have a nordyne package unit model R6GD-X36K072C Serial R6F100302127 just replaced furnace board oem the igniter came on got red and popped and came apart any help or what to look for? … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,142 satisfied customers
Help me validate my plan to connect two EcoBee 3 Smart
Please help me validate my plan to connect two EcoBee 3 Smart Thermostats to a Honeywell EMM-3 Zone Controller.… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
I have a Trane heat pump. Two Trane tech. from the closest
I have a Trane heat pump. Two Trane tech. from the closest dealer have been here twice and I have two different answers but the same problem. My unit once the thermostat is at the desired setting the … read more
Michael Ferryman
Michael Ferryman
87 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x