HVAC

Have HVAC Questions? Ask an HVAC Expert for Answers

Ask an Expert,
Get an Answer ASAP!

HVAC

My Rudd Power Vent 40 gal hot water heater will not heat.

Customer Question
Shows a code of 2...
My Rudd Power Vent 40 gal hot water heater will not heat. Shows a code of 2 - 3. Have powered down system and went through start up procedure. Vent runs and then shuts down with same trouble code.
Submitted: 5 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 5 minutes by:
5/3/2012
HVAC Technician: Rick, HVAC Supervisor replied 5 years ago
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 22,346
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Rickheatdoc :

Welcome to Just Answer, I will do my best to help you with your problem

Rickheatdoc :

What do you mean by a code of 2-3?

JACUSTOMER-hwe5ds4s- :

the trouble code that is displayed on the control

Rickheatdoc :

Ok, so you have an LED that blinks twice, pauses then blinks 3 times then repeats? There are many different gas valve LED configurations if I don't know which one you have I'm in the dark

JACUSTOMER-hwe5ds4s- :

yes. That is correct. It says it is the LVD circuit is failed/miswired

Rickheatdoc :

Do you have a model number for the heater?

JACUSTOMER-hwe5ds4s- :

not handy. I'll get it.

Rickheatdoc :

ok

JACUSTOMER-hwe5ds4s- :

PVP 40F

Rickheatdoc :

Give me a minute to see if I can find a spec.

Rickheatdoc :

Do you have a hot surface ignitor (HSI) a glow plug? or a pilot with electronic ignition? if the latter you should hear a ticking noise when it tries to light.

JACUSTOMER-hwe5ds4s- :

I believe it is an HSI.. I do not hear clicking. I did note now that when trying to restart, it flashes 2 - 1 and then shuts down and flashes 2 - 3.

Rickheatdoc :

I'm not seeing any documentation with the code pattern you describe. How old is the heater?

JACUSTOMER-hwe5ds4s- :

It is 6 years old. Thinking back I believe this happened before. It has a gas sensor and once it is tripped there is a sequence of moving the temperature control dial back and forth that resets it.

Rickheatdoc :

That's a flammable vapor lockout

Rickheatdoc :

Does your gas valve have a dial? have there been any vapors of any kind flammable or otherwise in the area?

JACUSTOMER-hwe5ds4s- :

It has a dial. There are no kind of vapors that have been present that I am aware of, nor are there any flammable liquids present. We did have a power interruption during the night.

Rickheatdoc :

Ok, you can try this reset procedure.Turn the water temp dial to VACATION, pull the plug, wait 30 secs, rotate the temp dial from VACTION to HOT as many as 6 times

Rickheatdoc :

Plug the unit back in after 30 seconds

Rickheatdoc :

then rotate the dial

JACUSTOMER-hwe5ds4s- :

Plug the unit back in and rotate the dial to where?

Rickheatdoc :

all the way down then all the way up then back again as many as 6 times

Rickheatdoc :

from vacation to hot

JACUSTOMER-hwe5ds4s- :

Got that, you then said "plug the unit back in after 30 seconds then rotate the dial..."

Rickheatdoc :

yes

JACUSTOMER-hwe5ds4s- :

Rick, You said to pull the plug when in the vacation position wait 30 seconds. rotate the dial from vac to hot as many as 6 times. THEN plug the unit back in after 30 seconds and rotate the dial.

Rickheatdoc :

turn it to vacation, then pull the plug, wait 30 seconds then plug it back in then rotate dial all the way up then all the way down as many as 6 times

JACUSTOMER-hwe5ds4s- :

Ok I'll try, but that's not what you wrote. I'll be back.

JACUSTOMER-hwe5ds4s- :

That does not work.

Rickheatdoc :

Since none of the specs I can access shows a valve with that type of trouble code sequencing there isn't much more I can do. I have one other suspect based on the way the unit is behaving. You will have to locate the draft pressure switch on top of the heater (it's part of the fan assembly). It has a small vacuum tube attached

Rickheatdoc :

If you can find it unplug the unit then try disconnecting one of the leads to the switch then plug it back in again. If the fan keeps running reconnect the lead to the switch

Rickheatdoc :

I'm thinking the draft pressure switch may be stuck closed and the heater won't continue the sequence if it is stick closed

JACUSTOMER-hwe5ds4s- :

I'll give it a try. I know what you are saying. Be right back.

JACUSTOMER-hwe5ds4s- :

That seems to be ok. I can't hear the draft pressure switch disengage after the fan shuts off

Rickheatdoc :

If you tired what I suggested with disconnecting the switch lead then that's all I got. Not much more I can do with no spec.

JACUSTOMER-hwe5ds4s- :

ok thanks

Rickheatdoc :

I'll opt out maybe one of my colleagues has another way to approach this

Ask Your Own HVAC Question
HVAC Technician: Walt-mod,
 replied 5 years ago
Walt-mod
Category: HVAC
Satisfied Customers: 27
Verified
Hi, I'm a moderator for this topic. Your Professional has opted out and I wonder whether you're still waiting for an answer. If you are, please let me know and I will do my best to find another Professional to assist you right away. If not, feel free to let me know and I will cancel this question for you. Thank you!
Ask Your Own HVAC Question
Customer reply replied 5 years ago

Please cancel the question.

 

Ask Rick Your Own Question
Rick
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 22,346
22,346 Satisfied Customers
Experience: 40+ yrs. experience as a licensed oil & gas technician.

Rick is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,730 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
We installed a bradford water heater 1 week ago, it has a
good morning we installed a bradford white water heater 1 week ago, it has a honeywell control, and the issue: two flashes on the LED status, the pilot goes on the unit fires for 20 seconds and then g… read more
Rick
Rick
HVAC Supervisor
22,346 satisfied customers
I have a 19.9 Rheem 120 volt water heater it does not have a
I have a 19.9 Rheem 120 volt water heater it does not have a drain valve . how do I drain it ? … read more
Rick
Rick
HVAC Supervisor
22,346 satisfied customers
AO water heater model #GS650YRVIT showing code for pressure
AO water heater model #GS650YRVIT showing code for pressure switch failed open. Is this for gas or air, where is it , can it be replaced or do I need to replace the blower unit. Unit has been installe… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
If a gas water heater with an FVIR is installed in a room
If a gas water heater with an FVIR is installed in a room with a washing machine, can cleaning products such as liquid laundry detergent and chlorine bleach trip the FVIR? … read more
Rick
Rick
HVAC Supervisor
22,346 satisfied customers
My water heater won't light. Yesterday. Trying. Is there a
my water heater won't light JA: How long has this been going on? And how severe is the problem? Customer: yesterday JA: Do you plan on doing the work yourself? Customer: trying JA: Anything else we sh… read more
Rick
Rick
HVAC Supervisor
22,346 satisfied customers
Who do i contact to replace a leaking WH7z water heater? It
who do i contact to replace a leaking WH7z water heater? … read more
Rick
Rick
HVAC Supervisor
22,346 satisfied customers
My honeywell hot water heater is flashing a code of upper
My honeywell hot water heater is flashing a code of upper sensor failure, what should i do? … read more
Rick
Rick
HVAC Supervisor
22,346 satisfied customers
I was flushing my Noritz tank less water heater and I think
i was flushing my Noritz tank less water heater and I think I used too big of a pump.. I think I blew all the seals and it started leaking on the inside and I stopped the flush and at first the power … read more
Rick
Rick
HVAC Supervisor
22,346 satisfied customers
I have a takagi tankless water heater that is used for in
i have a takagi tankless water heater that is used for in floor heat. it makes a really loud noise when it starts up. no always, but often. originally it did it all the time, but we reset some dip swi… read more
Rick
Rick
HVAC Supervisor
22,346 satisfied customers
I HAVE A WHIRLPOOL HOT WATER HEATER WITH A HONEYWELL
I HAVE A WHIRLPOOL HOT WATER HEATER WITH A HONEYWELL FLAMABLE VAPOR SENSOR LOCKOUT. MY BASEMENT GOT 2 TO 4 INCHES OF WATER DUE TO RECENT HEAVY RAINS AND APPEARS TO HAVE TRIGGERED THE LOCKOUT. MY QUEST… read more
Rick
Rick
HVAC Supervisor
22,346 satisfied customers
Bradford defender power vent hot water heater. One flash
Bradford white defender power vent hot water heater. One flash every 4 seconds or so.WV4460E 2014 pilot is working but no increase in temperature as I move temperature control up.… read more
WCohn
WCohn
Journeyman Plumber
Journeyman License
1,198 satisfied customers
I have a tankless water heater and it is not warming the
I have a tankless water heater and it is not warming the water and coming up with a C7 error. I have turned it on and off a couple of times and it will warm the water for a little and then goes off ag… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
Where on the water heater is the optimal position to install
Where on the water heater is the optimal position to install the Taco recirc. timer? … read more
Rick
Rick
HVAC Supervisor
22,346 satisfied customers
Our water heater was leaking and now are heating and cooling
Our water heater was leaking and now are heating and cooling isn't working. The fan doesn't cone on at all; Are these things related? … read more
Rick
Rick
HVAC Supervisor
22,346 satisfied customers
Draining a Richmond model 54P50E-1 water heater but it will
Draining a Richmond model 54P50E-1 water heater but it will only drain slowly … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
Our water heater will not ignite. The flame goes on for very
Our water heater will not ignite. The flame goes on for very short periods of time We changed flammable vapor sensor today SP20172 … read more
Rick
Rick
HVAC Supervisor
22,346 satisfied customers
I believe we have a flap that is stuck closed on our unit.
I believe we have a flap that is stuck closed on our unit. We are having the same problems we had a few months back, with lonely a small amount of warm air blowing through out system. We tried switchi… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
I need service on my water heater. Water heater still under
I need service on my water heater. Water heater still under warranty. Who do I contact for service asap? … read more
Rick
Rick
HVAC Supervisor
22,346 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.