Why is the oil furnace not staying lit?

Customer Question
Why is the oil furnace...

Why is the oil furnace not staying lit? It will fire up instantly and stay lit for 30 seconds. After pressing the reset it will light up again but won't stay lit.

Submitted: 5 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 13 minutes by:
4/26/2012
HVAC Technician: Comfort Specialist, HVAC Technician replied 5 years ago
Comfort Specialist
Comfort Specialist, HVAC Technician
Category: HVAC
Satisfied Customers: 1,368
Experience: Master Lic. holder for HVAC & Gas, Contractor, Estimator, Designer, Air Balance Certified, LG Master Commissioner, UNC Cert. holder for Industrial Ventilation
Verified

Hello there! I'm Norman but you can call me Norm. Let's see what I can do to get you some answers today. Can we start by you telling me a little more about your oil furnace, such as the model number, the age, the location, etc.?

JACUSTOMER : It's a mo HTL 100 series 55 about 30yrs in the basement. The vents and the furnace have just been cleaned and vacuumed as well.
Wvfan79 : Wow she's old! I'm fairly certain I will not be able to find information on that baby.
JACUSTOMER: I'm wondering if it would have a heat limit switch on it?
Wvfan79 : Without an exploded service view this may be difficult for me to instruct you. Lets start here. Are you familiar with the flame-rod, if so, does this furnace have one, if so, have you cleaned it? When you reset are you resetting a limit or just the furnace itself? The flame rod senses the consistency and quality of the flame at the burners or pilot.
JACUSTOMER: There two electrodes beside the nozzle, i',m guessing one is a flame sense and the other is the igniter. I think the reset just restarts the furnace. And yes it was cleaned.
Wvfan79 : The flame sensor should look like a steel rod. You can ensure that is clean by using a fine grit sandpaper or steel wool. How did you clean it when you serviced the unit? The question about the heat limit switch is a good one, however most furnaces have a resettable limit near the burner box. Most of the time they are manual. You can check yours to see if it has a manual reset button in the middle. If it is not tripped that is probably not your problem. You can test for voltage on both sides of the switch to be certain when the furnace goes through start up procedure.
JACUSTOMER: It had a lot of soot when I cleaned it. I don't think the furnace had ever been cleaned before. I used a de-greaser and a coarse paper towel on it.
Wvfan79 : Use something a little harsher on it like I recommended above. This may be part of your problem. Have you replaced any oil filters and nozzles?
Wvfan79 : Also are your air filters cleaned.
JACUSTOMER-ebzey0tq- : There is one grey Honeywell box that the T-Stat wires go to with a reset button and another box above it with a cream colored Auto/man. dial on it. The oil filter is new, the air filter about 6mos.
Wvfan79 : I'm not sure how dusty your home is but you may want to consider changing the air filter after 6 months.
JACUSTOMER: The air filter still looked fairly clean.
Wvfan79 :Does your furnace have oil nozzles? You might want to change that filter anyway a lot of times debris is not visible on the exterior of the filter but is trapped inside the fibers.
JACUSTOMER: When it fires up, the flame looks good, How would a new nozzle affect the duration of burn? I have cleaned the orifice and the little filter inside the nozzle as well.
Wvfan79 : It probably wouldn't. How does the flame look? What color is it? Does the base of the flame tend to lift?
JACUSTOMER: It is a strong yellow flame, with a good roar to it, a little louder than before the vents were cleaned. I can't see the start of the flame as there is a ccollar over it leading to the ceramic fire pot.
Wvfan79 : Does the flame ever tend to surge?
JACUSTOMER: No, it lights and stays steady, then cuts out.
Wvfan79 : As for your remark about the flame color the flame of some oil burners may be light yellow in color. More often it should have a blue - white or chrome colored flame. A dark yellow flame is an indication of a lack of air in the mixture. If is the case you may have problems on that end tripping the limit. Adjustments should be made by a professional with the correct tools.

A proper air to fuel ratio is required for a effective flame on an oil burning unit. It will take a combustion analyzer or a smoke tester to make any air adjustment. You can also tell if your burner is not receiving enough air by checking the amount of soot. A low air mixture will produce more soot and will also produce higher levels of dangerous carbon monoxide.

JACUSTOMER: I guess I'll have to phone around to find an old furnace tech. Living on an island does have a few drawbacks. Thanks for your time.
Wvfan79 : You are very welcome. Have I answered all of your questions today?
JACUSTOMER: Yes thanks, ***** ***** of any more.
Comfort Specialist
Comfort Specialist, HVAC Technician
Category: HVAC
Satisfied Customers: 1,368
Experience: Master Lic. holder for HVAC & Gas, Contractor, Estimator, Designer, Air Balance Certified, LG Master Commissioner, UNC Cert. holder for Industrial Ventilation
Verified
Comfort Specialist and 87 other HVAC Specialists are ready to help you
Ask your own question now
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 5 years ago
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 22,888
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified
Hello,You will not have a flame rod. Follow the 2 yellow wires from your reset box...they go to an eye under the transformer. Clean this eye first. If it still faults there are other things we can do.Billy
Ask Your Own HVAC Question
Ask Comfort Specialist Your Own Question
Comfort Specialist
Comfort Specialist
Comfort Specialist, HVAC Technician
Category: HVAC
Satisfied Customers: 1,368
1,368 Satisfied Customers
Experience: Master Lic. holder for HVAC & Gas, Contractor, Estimator, Designer, Air Balance Certified, LG Master Commissioner, UNC Cert. holder for Industrial Ventilation

Comfort Specialist is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
My oil furnace will not start. Making a humming noise.
My oil furnace will not start. All I hear is a humming noise. I have pressed the reset button and it seems to crank up but within a few seconds it shuts off and a red light comes on. I ran out of oil … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
my oil furnace ignights then runs a few seconds then goes out
my oil furnace ignights then runs a few seconds then goes out changed the filters and nozel still no difrent… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
22,888 satisfied customers
I have a Buderus G115WS/5 boiler with a Riello oil burner.
I have a Buderus G115WS/5 boiler with a Riello oil burner. Direct vent. I am wondering whether I can successfully convert this system to natural gas by installing a new burner designed for the purpose… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
When I run out of oil in my Lenox oil burner, the reset
HI when I run out of oil in my Lenox oil burner, the reset button turns red. One quick push and the burner fires up. This morning, no heat. I have oil and the reset button is blinking green, which I'v… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a beckett oil burner in a floor furnace. It is A-AF.
I have a beckett oil burner in a floor furnace. It is A-AF . I installed it in Oct. 2017 . It got low of oil in the tank and sucked air. I bled it and put a new nozzle in it . I also washed up the ele… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a wei-mclain gold oil burner that stopped firing up.
I have a wei-mclain gold oil burner that stopped firing up. the blinking green indicator light is flashing. the blinking green light goes off while I press the reset button for 45 seconds until I get … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Trane XV90 Oil Furnace. My furnace made some extra noise and
My furnace made some extra noise and then cut off... the red light on the oiled burner unit is flashing … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have an oil furnace... after running out of oil, then oil
I have an oil furnace... after running out of oil, then oil delivery today, I need to restart it. I have a Riello 40 burner. I've hit reset twice... sounds like it fires up but still blowing cold air.… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Oil furnace will not turn on message says standby but it
Oil furnace will not turn on message says standby but it doesn't do anything can anyone help… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Oil furnace will run if reset but will on run to degree,
oil furnace will run if reset but will on run to 69 degree, even if you have is set thermostat set on 80 degrees. Nozzle has been replaced, oil filter was changed.… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have one zone of an oil burner/forced hot air system that
I have one zone of an oil burner/forced hot air system that is not working. I replaced the zone valve which had a burned out motor. But it appears that no water is circulating through that zone (upsta… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My reillo burner on my oil furnace wont fire it wont do
Hi, my reillo burner on my oil furnace wont fire it wont do anything when you push the reset button any advice … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Oil burner Aquastat possible problems. Two days. I have in
The stat is fairly new I think the igniter transformer might be bad or going bad. Which may have led to my problem.… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My patriot 80 fuel oil furnace ran out of fuel and now it
My patriot 80 fuel oil furnace ran out of fuel and now it wont blow hot air … read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
22,888 satisfied customers
Flashing light on Beckett oil furnace. The pump was seized,
Flashing light on Beckett oil furnace JA: Did you check the furnace's filters? Customer: Yes JA: Do you plan on doing the work yourself? Customer: The pump was seized , I installed a new one JA: Anyth… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,142 satisfied customers
I have a oil burner assembly off a Shenandoah waste oil
I have a oil burner assembly off a Shenandoah waste oil furnace I have no spark I do have 120 volts at board for the transformer assembly that sits a top the spark electrodes is there a way to test th… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have an oil burner question, One week, Yes, Please connect
Please connect me with someone who deals with oil burner questions… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
22,888 satisfied customers
My oil furnace keeps shutting off. The red light comes on,
My oil furnace keeps shutting off. The red light comes on, and we have to push the red button to turn it on again. I have half a tank of oil so that is not the issue. This morning, when it shut down, … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x