HVAC

Have HVAC Questions? Ask an HVAC Expert for Answers

Ask an Expert,
Get an Answer ASAP!

HVAC
This answer was rated:

Goodman Heat Pump Not Shutting After Reaching Desired Temperature

Goodman heat pump does not...

Goodman heat pump does not click off when thermostat reaches desired temp. I have an Amana model #  ASZC16 heat pump and a Honeywell programmable thermostat. I have it set for 69 at night and 67 during the day. The temp stays constant at night at 69 but the air keeps pumping out. Then when it resets in the morning to 67 degrees, as soon as the inside temp reaches 67 degrees, it clicks back on until the temp rises above 67. Do I have a bad thermostat or is this normal?

Show More
Show Less
Ask Your Own HVAC Question
Answered in 29 minutes by:
3/6/2012
Bart Jay
Bart Jay, HVAC Technician
Category: HVAC
Satisfied Customers: 655
Experience: 35 years in HVAC. NATE Certified EPA certified
Verified

Bart Jay :

Sounds like it is working correctly. You say when it hits 67 it comes back on, as it should. You say the fan switch is set to auto correct? If it is in the ON position the indoor fan will always run

JACUSTOMER-xu48wmgn- :

Yes, the fan switch is set to auto. I guess I'm wondering how energy efficient this unit is when it blows air all night. Shouldn't the blower stop blowing air when the temp I have set it for is reached? Seems to me once it reaches the desired temp it continues to cycle air all night, the temp stays constant but its always running using my electricity. I have a furnace on the first level of my home and when the temp reaches what I have it set for it stops running for a while until it starts to cool down. Shouldn't the same happen with a heat pump system?

Bart Jay :

Yes the fan and system should shut off it the temperature gets above the setting of 69. Does the temperature get higher than 69

JACUSTOMER-xu48wmgn- :

The temp never gets higher than 69 so it just keeps running.

I thought once it hits my desired temp it would shut down until it falls below it again

Bart Jay :

Could the unit be too small for the space and it has to keep running to maintain the temperature

JACUSTOMER-xu48wmgn- :

That is a good question, its a nice size home so I just assumed what the sales person offered matched what I would need for the house. Its a 16SEER Amana ASZC16. Looks like a fairly large unit. What's the unit called in the attic? Is that the blower?

Bart Jay :

In the attic is the sir handler which has the blower in it

Why did you replace it three times?

Does it cool the house okay in summer

JACUSTOMER-xu48wmgn- :

The first unit failed because the compressor went bad within a year. The second unit just kept failing. The T-valve? Went back, the refrigerant got contaminated and the unit was blowing cool air in winter and not enough cool air upstairs. The temp would climb to 95 degrees with the unit running full blast. Then it failed 3 times this winter for various reasons. Amana guy came to check it out and he said the whole thing needed to be replaced again. Its been a nightmare. So I got another unit installed this week. 3 units in 3 years

Bart Jay :

Something is not right

Either it is not piped correctly or maybe undersized.

It only does the upstairs?

Do you know the full model number and what is the square footage

JACUSTOMER-xu48wmgn- :

I can't agree with you more, the only saving grace is I haven't had to pay for the new units or all of the repairs. Yes, the HP is only for the 2nd level of my home where I have 4 bedrooms and 3 bathrooms

Its about 1500 square feet upstairs with a big 2 storey entry foyer. I'll have to get the full model number tonight when I get home. But if I understand as long as the temp is at where I set it then the air handler will keep running? Is it possible I have a bad thermostat? Its a Honeywell programmable unit

Bart Jay :

If the temperature does not get ABOVE 69 then the fan and system will continue to run

Try this whole - while it is running and set for 69, lower it to 68 then 67 and see if everything shuts down. It should and if it does the thermostat is working correctly

Let me know tomorrow and get the full model number. Should be numbers after the aszc16
JACUSTOMER-xu48wmgn- :

I did that and it does shut down. Do you know the air temp that it should be blowing on average. Sometimes it feels like cool air is coming out of the vents and then it gets warm and cools again

Bart Jay :

Hard to say. 90-100 is all a heat will generate. Do you have an emergency heat selection on the thermostat

JACUSTOMER-xu48wmgn- :

I do have an emergency heat setting and when I used it the last 3 weeks, because I was told not to use the heat pump, it was clicking on and off all day and night.

Bart Jay :

So the electric heat would keep the space warm and satisfy the thermostat, correct?

JACUSTOMER-xu48wmgn- :

That is correct...

Bart Jay :

Was the indoor unit replaced 3 years ago also

JACUSTOMER-xu48wmgn- :

Yes it was. I guess I was expecting the heat pump to act the same way in that it would shut off every once in a while.

Bart Jay :

Get me the model numbers of both indoor and outdoor units

JACUSTOMER-xu48wmgn- :

OK

Ask Your Own HVAC Question
Customer reply replied 5 years ago

The model number of my unit is ASCZ160241AC and it reads AMANA on the side. I noticed last night that the fan wasn't running outside but inside it was blowing air and the thermostat read Heat On. I thought if the thermostat read Heat On the fan outside should have been also running. I checked it this morning and it was.

It is possible that you caught it during a defrost cycle. The outdoor fan will shut off during defrost.

Did you get the indoor numbers?

Where do you live?

Bart Jay
Bart Jay, HVAC Technician
Category: HVAC
Satisfied Customers: 655
Experience: 35 years in HVAC. NATE Certified EPA certified
Verified
Bart Jay and 87 other HVAC Specialists are ready to help you
Ask your own question now
Customer reply replied 5 years ago

For three years I've been having all this trouble and now the crew realized that my dampers we closed in the attic was creating all this back pressure. The new unit they just installed works great now and my vents don't whistle with air flow any more. Thanks for your help. Not sure if it was the dampers causing all of the problems but I'm sure it couldn't be helping.

Ask Bart Jay Your Own Question
Bart Jay
Bart Jay
Bart Jay, HVAC Technician
Category: HVAC
Satisfied Customers: 655
655 Satisfied Customers
Experience: 35 years in HVAC. NATE Certified EPA certified

Bart Jay is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
My goodman heat pump was working then it just stop blowing
my goodman heat pump was working then it just stop blowing air. … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Connected new programmable thermostat and now furnace does
Connected new programmable thermostat and now furnace does not turn on. Put back on the old thermostat and furnace still still does not come on … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Installed a new programmable thermostat, but it wouldn't
Installed a new programmable thermostat, but it wouldn't work with the system So I uninstalled it (thinking it was not compatible)/ Installed the old one again Now the old one won't work either … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My goodman heat pump model ssz14361 keeps blowing fuses.
my goodman heat pump model ssz14361 keeps blowing fuses … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I am installing an Emerson programmable thermostat for a 14
Hi. I am installing an Emerson programmable thermostat for a 14 year old Ruud furnace. Assuming it is a single stage system but thermostat has a "power stealing switch". Will it ork on the Ruud? … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I removed my programmable thermostat to correct an air
I removed my programmable thermostat to correct an air infiltration problem in the wall it was mounted to. After reinstalling it I can't get power to the device. … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My Rodgers programmable thermostat us not working, current
My White Rodgers programmable thermostat us not working, current temp and time are flashing. Heat runs for a minute when turned on and off then cuts off. Temp inside is 58. … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Our honeywell programmable thermostats ( two of them) are
hello our honeywell programmable thermostats ( two of them) are not allowing the heat to get higher than 62 degrees even though they are set for 70 degrees … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My Honeywell non programmable thermostat is showing that
My Honeywell non programmable thermostat is showing that it's showing that it is running auxiliary heat I got on 70 but it won't go over 65 I try to set back to just heat but it goes back to auxiliary… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Will the honeywell Focus 5000 non programmable thermostat
Will the honeywell Focus 5000 non programmable thermostat work with central Air system and baseboard heat for one room … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I'm trying to install a 7560e programmable thermostat to
I'm trying to install a 7560e programmable thermostat to replace an old (mercury) unit. I wired up everything based on current configuration, but the heat (electric) won'the come on. … read more
Scott
Scott
Self Employed HVAC Service Technician
Associate Degree
400 satisfied customers
Have installed a Honeywell programmable thermostat.
Have installed a Honeywell programmable thermostat. Connected the red and white wires. When the thermo was set the valve to my boiler opened but when I reset the thermo to a lower temp it does not clo… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a Honeywell MagicStat/3355 programmable thermostats.
I have a Honeywell MagicStat/3355 programmable thermostats. Pilot light is on, I switched to heat and checked time and day and presses run program. Furnace does not start. … read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
Have a Goodman heat pump with aux heat banks and have added
Have a Goodman heat pump with aux heat banks and have added a Honeywell programmable thermostat. Something doesn't feel right since changing. I talked to Honeywell and told them the old thermostat wir… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Goodman Heat pump heats but does not cool. Thermostat ok.
Had simular problem about a year ago. Repairman replaced, a relay… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My sister has a Goodman Heat Pump. Does it have any audible
My sister has a Goodman Heat Pump. Does it have any audible alarms for malfunctioning or safety shutoffs for disabling unit? Recently she had water in the ceiling below the unit and it also warped the… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Goodman heat pump /ac will not come on. Replace oustide
Goodman heat pump /ac will not come on. Replace oustide fuses, themostat seems ok. fan will not come on. pushed reset button on outside unit and fan ran until I released button then quit. Thermostat d… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Goodman heat pump question. 3-ton unit model
I have a Goodman heat pump question. 3-ton unit model gsz140361kc. There is power to the unit. I have 25.4 volts coming to the unit. I read 25.4 volts between red and blue, between white and blue, and… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x