Turn up the thermostat and furnace turns on. Takes ten minutes or so to turn blower on, then the furnace runs for a few minutes but never runs to reach the desired temperature.

Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 minute by:
10/28/2011
Richard
Richard, Technical Manager
Category: HVAC
Satisfied Customers: 1,514
Experience: 27 years of Experience, NATE Certified, professional trainer
Verified

Richard :

Hello if you look at the furnace is there a window at the bottom with flashing light? Count ther flahes and look on the back door for the code Richard

JACUSTOMER :
It says simultaneous fast flash is normal operation
Richard :

OK if you tun up the stat and let it fire do the flames stay on? or go on and off before the blower kicks in the blower should come on 20 seconds after flame

JACUSTOMER :
I have to go look.We don't hear the blower come on at all. No flames either. The heater starts up but no blower. It keeps going into start up mode but no blower it was kicking on earlier
Richard :

Ok we may have a bad blower first turn power off take the bottom door off and spin the wheel by hand to see if it spins freely. Next turn power back on and set thermostat to fan on will it run

JACUSTOMER :
Ok it spins freely. It is running in fan on mode with heat on
Richard :

Ok next do you have a volt meter we could have a bad board that won't energize the heat speed

JACUSTOMER : We are getting heat now.Looking for volt meter. Got meter now what do we do with it.
Richard :

You probably have a failed board but if you get a meter check for voltage from the fan motor wire on the heat terminal to the white neutral

JACUSTOMER :
Can we let it run this way until someone can come fix it.Is that expensive to replace
Richard :

Yes you can. A board is around a 100 dollars or so if that is it

JACUSTOMER-e0pl3gt1- : My husband has a volt Meter. checking it now. Should it be off. We are not sure what wires
Richard :

No, if we are checking for power we need a call for heat and the burners on.

Turn the fan back to auto for this test

JACUSTOMER :
We got white neutral, where do we put the meter wires one on white neutral and the other where.
Richard :

Look for a terminal labled heat to H or H

JACUSTOMER :
As soon as we open bottom door, power goes off for saftey. Still looking for H
Richard :

You will have to hold the door switch in

JACUSTOMER :
Which board do we look at. There is a top white lennox board and two green smaller bottom boards
Richard :

Look for the fan motor. Wires are where they go

JACUSTOMER : The fan motor wires go to top board. And bottom board
Richard :

Look for a terminal lab led Heat or H on one of them

JACUSTOMER : Found it, green led says heat. There are jumpers on this green board
Richard :

Can you get the model. I will look it up

JACUSTOMER : Lennox g32v3-75-1. We found wires what do we set volt meter too. When it was running it said 25 volt meter set to 200 white neutral and heat jumper
Richard :

I see you have an ECM motor this is a bit different. There are two harness that come off this motor one is hi voltage and one is low. The one with a black white and green wires we dont want to look at right not. The other should have several wires up to 16 or less. What we need to do here is pull that arness off and blow on it to clean it then try to plug it back in. You wont have a tester for this motor it is something only an HVAC technician will have. Since th emotor runs you probaly have a bad board ( this would be the fan board the 16 pin harness plugs into

JACUSTOMER : Ok doing this. Still same result. Blower won't come on.Bad board
JACUSTOMER :
How long can we run it in fan mode if they can't get here tomorrow
Richard :

This is a link to the service break down. This may be over your head. Its up to you. Look on troubleshooting section fo reheat mode

You can run it for a long time no damage will occur past what is bad.

Lennox has a very in depth series of checks here and I would hate to see you waste money on the worng part.

JACUSTOMER :
Ok so about how much to fix this bad boy
Richard :

If its a board for this unit is could be 200 for the part. However many of these came with 5 and 10 year warranties. Look for you warranty card and the part may be covered do you know how old it is

JACUSTOMER : Blower came on just now in auto mode.
Richard :

It could have just been a loose connection it happens on these when you can get some contact cleaner from LOWES or Home depot to clean well. Itslow voltageso it won't take much moisture or dirt to cause a problem

Maybe we saved you some trouble here

JACUSTOMER : Ok still not staying on, though just went back off. But we will try that
Richard :

Keep it on auto, if it works that way to get you by. It sounds like a bad connection if the fan came on even for a momment

JACUSTOMER : Ok do you recommend we try the cleaner or call a tech
Richard :

The fan motor is the real expensive part. I would try to clean first a can of cleaner is only 5 dollars

JACUSTOMER :
Can I use a vacuum in there
Richard :

Sure just turn off power first. Pull the harness off the motor and board

JACUSTOMER : Ok we will try that then call if no luck
Richard :

Ok

JACUSTOMER : Oh actually vacuum the harness
Richard :

Cleaner will work on the harness. I dont think the vacuum will do much there

It would have to be one heck of a vacuum..Lol

JACUSTOMER : Lol, at least we narrowed it down a bit
Richard :

Yes we did.

JACUSTOMER- : You were very helpful.Thanks for your patience
Richard
Richard, Technical Manager
Category: HVAC
Satisfied Customers: 1,514
Experience: 27 years of Experience, NATE Certified, professional trainer
Verified
Richard and 87 other HVAC Specialists are ready to help you
Ask your own question now
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Richard Your Own Question
Richard
Richard
Richard, Technical Manager
Category: HVAC
Satisfied Customers: 1,514
1,514 Satisfied Customers
Experience: 27 years of Experience, NATE Certified, professional trainer

Richard is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Have a UAPC-024JAZ, getting 25AC signal from upstairs,
Have a UAPC-024JAZ, getting 25AC signal from upstairs, change relay and start cap. TS, 26AC getting through the switch attached to compressor, but not through the switch that has a coiled tube attache… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
953 satisfied customers
I replaced my failing carrier humidistat wir. With a Nest
I replaced my failing carrier humidistat wir JA: I'll do all I can to help. How long have you been dealing with this? Customer: With a Nest and have a wiring error JA: How old is the appliance? Have y… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
My Rodgers thermostat will not bring down the temp. The
My White Rodgers thermostat will not bring down the temp. The Cooling icon keeps flashing … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,870 satisfied customers
I have a Ruud ultra Super Quiet 80 2 stage unit that the
I have a Ruud ultra Super Quiet 80 2 stage unit that the blower is not working. It has a Honeywell wireless thermostat that I don't believe is the issue. With the blower door removed, and the door int… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I replaced the capacitor and fan motor, but now the
I replaced the capacitor and fan motor, but now the capacitor won't turn on. What should I look at now? … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
MY WHIRLPOOL WATER HEATER MODEL# IS L40S62-403 PURCHED 7/13
Second opinion] MY WHIRLPOOL WATER HEATER MODEL# ***** ***** PURCHED 7/13 WILL NOT LICHT. I HAVE DONE WHAT THE BOOK SAYS DO AND GET NO SPARK FROM THE IGNITER. I TRIED LIGHTING THE PILOT ( HOLDING THE … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
FFBD2406NS3A Frigidaire dishwasher: 3 years, does not dry
3 years, does not dry heating element has continuity, high limit is normally closed. No ac to either … read more
David Hanger Jr
David Hanger Jr
Appliance Repair
1 satisfied customers
Unit quit working after we changed batteries in thermostat.
Unit quit working after we changed batteries in thermostat. Green light flashing on mother board … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
My air conditioner quit the filter was stopped up I changed
My air conditioner quit the filter was stopped up I changed it but now I have nothing please help this Georgia heat is bad … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,870 satisfied customers
The head pressure slowly raises as the suction pressure
The head pressure slowly raises as the suction pressure stays steady in the cooling mode … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Switching Condensor Motors - same type, new motor has 5
Switching Condensor Motors - same type, new motor has 5 wires, existing had 3, need help connecting the wires properly… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I'm trying to make a repair or replace decision on a 7 year
I'm trying to make a repair or replace decision on a 7 year old Goodman 70,000 BTU 95% A.F.U.E rating with a burnt out blower motor. The part cost is quite high and probably approaching 40% of replace… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
My Rheem gas furnace air handler will run for 1-2 mi. then
My Rheem gas furnace air handler will run for 1-2 mi. then stop. … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
I have an old RUUD UHQA-1310s. It doesn't blow cold air. Can
I have an old RUUD UHQA-1310s. It doesn't blow cold air. Can I recharge it with freon? … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Can I get the circuit board for a Kelvinator 2.7kw reverse
Can I get the circuit board for a Kelvinator 2.7kw reverse cycle window unit? … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
My AC unit is not turning on. It has been super hot ant it
My AC unit is not turning on. It has been super hot ant it failed lsat nite … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
I have an American Standard Condensing Unit 4TTB3018-060. I
I have an American Standard Condensing Unit 4TTB3018-060. I have never messed with this unit before but I cannot afford someone to clean it this year. So I went out removed all the screws pulled off o… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,870 satisfied customers
My york ac is on and off from cooling though the compressor
my york ac is on and off from cooling though the compressor is on in the central unit … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x