Customer Question
Where's the reset button on...

Where's the reset button on my furnace?

Submitted: 6 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 3 minutes by:
10/16/2011
HVAC Technician: Richard, Technical Manager replied 6 years ago
Richard
Richard, Technical Manager
Category: HVAC
Satisfied Customers: 1,514
Experience: 27 years of Experience, NATE Certified, professional trainer
Verified

Hello, there is typically not a reset button on furnaces. Turning the power on and off, resets the control. If you have no heat, you may have another issue. Without a model number, I am only guessing here; but if the fan will run, we have power. Is the fan running non stop? Is there a draft motor running as well?

Ask Your Own HVAC Question
Customer reply replied 6 years ago

Model #:M3RL060A BW!

No, the fan isn't running at all; only when I flip that switch. I don't know what a draft motor is.

HVAC Technician: Richard, Technical Manager replied 6 years ago

Hello!

If you take the doors off, look for a circuit board that may have flashing lights. The draft motor is connected to the vent system. It is the motor that blows the exhaust out.

Ask Your Own HVAC Question
Customer reply replied 6 years ago

The door is off. There is a circuit board. It has a red light that flashes while the blower is on. Right now, nothing is running. Can you find this model on line for troubleshooting?

HVAC Technician: Richard, Technical Manager replied 6 years ago

Hello!

While I try to locate a spec, can you look on the back of the door? There should be something that tells you the flash code. Count the flashes.

Ask Your Own HVAC Question
Customer reply replied 6 years ago

Undecided Do you mean count the flashes that happen after I flip that light switch and the blower kicks on?

HVAC Technician: Richard, Technical Manager replied 6 years ago

Yes! I found the spec. We just need to know how many times the red light flashes, then pause and do it all over again.

Ask Your Own HVAC Question
Customer reply replied 6 years ago

I turned the switch on, the red light came on for a while, then off, on, off, on, off, on. When I reached a count of 9, I figured the answer you're looking for is ONE. It was flashing only once, as opposed to blink, blink or blink, blink, blink. Is that what you mean?

HVAC Technician: Richard, Technical Manager replied 6 years ago

Hello!

If you have 1 blink, it means there is an open limit switch. Look for small switches near the burner area ( it showed 2 in the diagram). They should have a button in the middle. Push to reset, then make sure the filters are clean. However, if you have a continuing flash, this means there is a short on the flame sensor or a shorted gas valve relay (this is on the board). For the Flame sensor, take off the cover hiding the burners. There will be a small metal rod with 1 wire going to it. Make sure it is clean (use a scotch brite pad ) and it is not touching anything. Then, re-apply power and test. Let me know how it goes.

Richard
Richard, Technical Manager
Category: HVAC
Satisfied Customers: 1,514
Experience: 27 years of Experience, NATE Certified, professional trainer
Verified
Richard and 87 other HVAC Specialists are ready to help you
Ask your own question now
Customer reply replied 6 years ago

I found a set of small, rectangular plugs with a tiny red and black button-looking thing between them. The first one I tried, did nothing, but the other one, closest to what I think is the draft motor, made a clicking sound when I pressed it. Then I flipped the white switch, the blower came on, and the red light stayed on. Should I be able to see a flame in that small, glass window? I don't. Should that white switch always be in the "On" position?

HVAC Technician: Richard, Technical Manager replied 6 years ago

Hello!

It looks like a limit tripped; so now we need to find out why. If it was near the draft motor, check the outside vent for an obstruction (someone may have shoved something down it). Next, you may have to take the draft motor off to see if a mouse or bird went in there. After that, it may get tricky, the heat exchanger may be cracked but let's not condemn it yet.

Ask Your Own HVAC Question
Customer reply replied 6 years ago

How do I find the outside vent? Take the draft motor off??? Surprised It's time for bed. I'll turn our oven off now and put another blanket on my bed. Will I still be able to review your answers once I've clicked ACCEPT ANSWER ??? Thanks for your help. Pretty sure there's a visit from a face to face technician in our near future.

HVAC Technician: Richard, Technical Manager replied 6 years ago

Hello!

The vent is the exhaust pipe coming off the furnace to the outside. You will want to make sure this is clear. The draft motor is a small motor the vent is connected to in the furnace.

And yes, even after you accept, you can come back to this question.

Ask Your Own HVAC Question
HVAC Technician: Richard, Technical Manager replied 6 years ago
Hello No you don't and even after you lclick accept you can always copme back to this question for further help. The site charges your card but I don't get paid until you click accept. Let me know if you need more help Richard
Ask Your Own HVAC Question
Ask Richard Your Own Question
Richard
Richard
Richard, Technical Manager
Category: HVAC
Satisfied Customers: 1,514
1,514 Satisfied Customers
Experience: 27 years of Experience, NATE Certified, professional trainer

Richard is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,730 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Need a heat exchanger for model GIN 80bu-1000 14B-3A; ser. #
need a heat exchanger for model GIN 80bu-1000 14B-3A; ser. # 1607K 03798 … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
In 2003, we had a new high-end Carrier Infinity Weathermaker
In 2003, we had a new high-end Carrier Infinity Weathermaker furnace installed - Model 58MVP-100-20 (run on propane). 8 years later, in 2011 - while still under warranty (parts and labor) the main hea… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Comfortmaker RPJ II furnace. It won't heat. The
I have a Comfortmaker RPJ II furnace. It won't heat. The induction motor runs and runs. I don't see the ignitor light. But, I don't hear the click before the ignitor should light. Does that mean the p… read more
Tim H.
Tim H.
Lead building engineer
Vocational, Technical or Trade Scho
3,961 satisfied customers
I have a furnace 17 years old. renters say are experincing
I have a bryant furnace 17 years old. renters say are experincing maybe a co2 leak. any advice.… read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
I have a Carrier furnace 58MCA080-13112. Got home from
I have a Carrier furnace 58MCA080-13112. Got home from vacation and my furnace won't work. The inducer motor comes on and you can see the flame thru the window, so it heats heats up but the blower nev… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Is it unsafe to have a cracked heat exchange on your
Is it unsafe to have a cracked heat exchange on your furnace? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I need a heat exchanger kit for a weil-mclain ultra 105, no
i need a heat exchanger kit for a weil-mclain ultra 105 … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
How do I check heat exchanger for blockage. Today. Sounds
how do I check heat exchanger for blockage JA: I'll do all I can to help. How long have you been dealing with this? Customer: today JA: Do you plan on doing the work yourself? Customer: yes JA: Anythi… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
When were stainless steel heat exchangers required for
When were stainless steel heat exchangers required for residential usage and/or what HVAC company was the first to provide them. And are they as effective as touted.… read more
D.E. Anderson
D.E. Anderson
Industrial Refrigeration Service Manager
198 satisfied customers
Funky smell coming from heat exchanger outside...... repair
funky smell coming from heat exchanger outside...... repair guy said the gas not m ixing with the air properly..true? said probably just clogged … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Heat exchanger is a month old and heat stopped working.
Heat exchanger is a month old and heat stopped working. Three lights are blinking saying it is a limit or rollout switch … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,080 satisfied customers
I have a property with a Keeprite heat exchanger installed.
I have a property with a Keeprite heat exchanger installed. I believe the filter is clogged but I don't know where it's located. The model is PGF018K040E … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
The condensation water leaks from heat exchanger near the
The condensation water leaks from heat exchanger near the filter and comes on the ground tray. There is no blockage of any sort. What needs to be done for auxiliary condensation tray if it is cracked.… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,080 satisfied customers
How can I clean the inside of the heat exchanger on my
how can I clean the inside of the heat exchanger on my furnace? … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My carrier heating heat exchanger is plugged. I understand
My carrier heating heat exchanger is plugged. I understand it is civered under a recall action. if bI purchase a new systeem 59mn7a080-20 what price drduction do I receive? … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
How much time should be allowed to change a heat exchanger
How much time should be allowed to change a heat exchanger for a 48tjf016 series 580ba and 2 men?… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,080 satisfied customers
I have Yorx High efficiency tubular heat exchanger, im not
Hi, my name is***** have Yorx High efficiency tubular heat exchanger, im not sure wich model though GY9S , GM9S, or GF9S. There is water leaking from the white PVC pipes, can I just cut them out and r… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,080 satisfied customers
I was looking into a trane tud060 heat exchanger and noticed
I was looking into a trane tud060 heat exchanger and noticed a buildup of white powder at one of the factory seams and need to know what is causing this. I attached a pic. Thanks… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x