I am trying to install a in duct smoke detector a Air products

I am trying to install...
I am trying to install a in duct smoke detector a Air products sl 2000, 24 v. system where on the furnace do I get the low 24 v. feed terminal and which terminals shuts down the unite or turns the fan off Thanks Ed.
Show More
Show Less
Ask Your Own HVAC Question
Answered in 9 minutes by:
9/10/2011
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,168
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Phil :

All work to be done by licensed professional. WE KEEP GOING UNTIL YOU ARE HAPPY . . . I come and go, be patient.

Phil :

you get the 24v from the control transformer, its the size of your fist and heavy. find it on the wiring diagram first.. then trace wires to find it

Phil :

the red thermostat wire goes directly to one side of the transformer... run that through the contacts on your smoke detector to kill the ac unit if there is smoke detected.

Phil :

read that over a few times, let me know if it makes sense on your end.

Phil :

we can go from there as necessary. phil

JACUSTOMER-q8iv5mip- :

I have no A.C. and no visable transformer, only a panel .but I will take anouther look. the three wires (thermostat ) White - com, red - - f an on manualy no heat -- black-- heat controled by thermostat. Ed.

Phil :

The furnace is fit with a 24v transformer.. and the controls are the same as with a unit with ac... the transformer is INSIDE the furnace, behind the cover that llifts up 2" then out, to expose the gas valve..

Phil :

the gas valve area can be located by noticing where the gas line enters the furnace.

Phil :

Look that over, tell me if it makes any sense on your end. Phil

JACUSTOMER-q8iv5mip- :

Sorry You Are Right, I found it on the wireing diag.

JACUSTOMER-q8iv5mip- :

Thanks Phil . So I can get my 24 v .to feed the smoke dect. from the trans , and switch on the red thermostat wire ? Ed.

Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,168
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified
Phil and 87 other HVAC Specialists are ready to help you
Ask your own question now
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 22,893
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified

 

Keep in mind if breaking 24 the fan will still run for 90 seconds. Most duct detectors are designed to stop the air flow asap as to not help spreads smoke.

 

If you want warning only then breaking 24 is sufficient...but for instant shut down as code requires breaking 24 does not cause instant shut down.

 

Just a bit of additional info on this unit.

 

 

Ask Your Own HVAC Question
Customer reply replied 6 years ago
The smoke dect. requires a pos. and neg. would the black therm.wire be the pos.and the white be neg. ? yes it requires a instant shut down,so there is no transfer of smoke.
Hello again, Billy is correct ! if the smoke detector goes off when the furnace is in the heating mode and you break the the red thermostat wire. the gas valve and the fan relay will go off,,, but the fan will keep running on its timer or furnace fan control intended to run the fan until the furnace cools down.


You will have to run line 1 from the 110v supply to the furnace through your smoke detector contacts in order to shut the fan off instantly'

Picking up the 24v to run the smoke detector from the furnace 24v transformer

regarding the positive and negative.... those are direct current voltage terms,

AC , alternating current is supplied by the utility the furnace transformer not DC power'

however with components coming from china lately many items are marked positive and negative when they are intended for AC use

look on the smoke detector wiring diagram for references to AC power

if ac is OK... then the red wire coming off the transformer to the thermostat marks
'positive'.. the other terminal will be called 'negative' even though its AC and there is no actual positive or negative


its a bit trickier than that but no need confuse the issue more than it is


verify the voltage spec on the detector is marked as AC

let me know

we can go from there

Phil
Ask Your Own HVAC Question
Customer reply replied 6 years ago
Yes it has a AC. contact Ed.
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,168
9,168 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,168 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Help me validate my plan to connect two EcoBee 3 Smart
Please help me validate my plan to connect two EcoBee 3 Smart Thermostats to a Honeywell EMM-3 Zone Controller.… read more
Phil
Phil
Mechanical Engineer
9,168 satisfied customers
I have replaced my old thermostat which was 2 wires. With a
I have replaced my old thermostat which was 2 wires. With a wifi Honeywell t5. I ran a separate transformer to power the new thermostat and I have that part working. My problem is in my overhead furna… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Looking at a W-M boiler and need some info, lol..... started
Hi!..... Looking at a W-M boiler and need some info … read more
Phil
Phil
Mechanical Engineer
9,168 satisfied customers
Model rhsl-hm3617ja, the drain pan fill with water and
the drain pan fill with water and leaked through the ceiling. do i need to replace the float switch? … read more
Iohn Keffer
Iohn Keffer
HVAC Tech
Associate Degree
41 satisfied customers
Added a basement zone to an existing American standard
Added a basement zone to an existing American standard furnace with a coil. Now that i have a basement thermostat and a basement zone damper i bought a honeywell hz311 zone board to wire it all. I hav… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
953 satisfied customers
My humidifier failed and was leaking. I shut the switch off
My humidifier failed and was leaking. I shut the switch off and unplugged the humidifier. The furnace is not fitting back up … read more
Phil
Phil
Mechanical Engineer
9,168 satisfied customers
I am putting in a Honeywell focuspro 5000 and the display
I am putting in a Honeywell focuspro 5000 and the display screen shows nothing trying to set it up what do you think I did wrong?… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Trane xr80 that is not kicking on the heat. Blower
I have a Trane xr80 that is not kicking on the heat. Blower comes on fine. The light on the circuit board does not ever come on. The ignitor does not glow and tests with some resistance on the ohm met… read more
Phil
Phil
Mechanical Engineer
9,168 satisfied customers
Replaced non programmable with programmable. Turned furnace
Replaced non programmable with programmable. Turned furnace power back on but furnace soesnt run. Replaced old thermostat to original wiring but furnace still doesn't run? … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a "heat pump" (I think) heating system in my home.
I have a "heat pump" (I think) heating system in my home. There is an outside unit that runs when the A/C is engaged and an inside unit that is the fan and heater (it has a gas line running into it). … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have an intertherm Nordyne E2EB-015ha. And would like to
I have an intertherm Nordyne E2EB-015ha. And would like to install a honeywell wifi thermostat. But a "c" wire doesn't exist. Can something be done to add one? … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My Goodman GMT070-3a furnace keeps blowing fusses after
my Goodman GMT070-3a furnace keeps blowing fusses after running for 5 minutes or so? … read more
travis webb
travis webb
tech.
2,416 satisfied customers
I have a Ruud (installed in 99) furnace with a whole house
I have a Ruud (installed in 99) furnace with a whole house humidifier installed. I'm replacing my existing wall programmable thermostat and humidistat with a 3rd generation Nest. I know how to read sc… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Trying to figure out where to connect the blue thermostat
Trying to figure out where to connect the blue thermostat wire to a Vexar furnace. There is no circuit board that I can find. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Intertherm furnace does not lite ac comes on when turned to
intertherm furnace does not lite ac comes on when turned to heat … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
We have e23 error on Nest .what to do? 24 month,no, I will
I powered nest. For more than 1h, animation came up and message was asking to attach nest to the base. It was displaying "heat set to 63". I set heat to 70. In several minutes nest displayed that there is no power attached to RC adapter an error 23… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I am trying to install a Honeywell thermostat replacing a
I am trying to install a Honeywell thermostat replacing a Lennox one. I have mapped all the wires to their respective terminals but one has me stumped. One wire goes to a terminal labeled "4". The sup… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have this furnace m1mb077abw bw. If I want to add AC how
I have this furnace m1mb077abw bw. If I want to add AC how do I wire for AC … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x