I have central AC sysyem - Spacepak airhandler, York

Customer Question
affinity 3s outside unit and...
I have central AC sysyem - Spacepak airhandler, York affinity 3s outside unit and a Honeywell TH8100U1003 thermostat. The outdoor unit has been intermittently cooling but seemed to start working again if i turn off the breakers and reboot and then the thermostat display stopped working (changed batteries no luck). I then purchased the same thermostat as a replacement and when I connected the wires exactly as they were the system now heats when you set it to cool. The only thing I can think of that could be different is that the factory installed jumper between RC a R does appear to be slightly different in that the old one has a black section on the jumper ( to small to tell what it is) and the new one is just a wire jumper. I hope someone has experience with this and can help. Thank you
Submitted: 6 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 7 minutes by:
8/28/2011
HVAC Technician: Phil, Mechanical Engineer replied 6 years ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,702
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified
Phil :

All work to be done by licensed professional. WE KEEP GOING UNTIL YOU ARE HAPPY . . . I come and go, be patient.

Phil :

I need the make and model number of the outside unit please.. that will tell me if its a heat pump or not. The jumper is likely OK, but you may have to change one of the wire locations on the thermostat.

Phil :

Blue and Orange operate the 4 way reversing valve that puts the system into heat or cool mode. that connection is likely just reversed.

Phil :

tell me what color the wires that attach to the thermostat are, and what wire goes to each terminal.

Phil :

the easiest way to do that is to find where the thermostat wires attach at the inside unit.

Phil :

Phil

Customer:

Phil,

Customer:

sorry for the delay - I had to find the heatpump manual - it is a York Affinity R-410A outdoor split system airconditioning or heat pump 5 ton

Customer:

checking wires now

Customer:

red to RC which is jumpered to R

Customer:

white to OB

Customer:

Black to Y

Customer:

Blue to G

Customer:

C not used

Phil :

Thanks. I need the model number of the heat pump, thats not in the manual.. it is stamped on the units name plate outside.

Customer:

checking now

Customer:

model YZB06011A

Phil :

the white to OB is likely the problem.. that sends voltage to the reversing valve to change from heating to cooling. its operating backwards.. or the wire is broken or some such

Customer:

i will check connection now

Phil :

remove white from OB as a test. tell me if it stays in heat mode or switches to cooling.

Phil :

we can go from there.

Phil :

Phil

Customer:

doing now

Customer:

removed thermostat, disconnected and taped white wire, replaced thermostat and waiting for startup

Customer:

unit started - thermostat says cooling - airhandler is blowing, but york affinity outdoor heat pump unit is not

Phil :

Is the outside unit running?

Phil :

or running but not cooling?

Phil :

Phil

Phil :

\

Customer:

it wasn't running, then it started up and is heating

Phil :

turn it off

Customer:

done

Phil :

I suppose it is supposed to be cooling now, not heating

Customer:

at thermostat - should I throw the breakers?

Phil :

this indicates that it was not the thermostat that was bad, but that the reversing valve is not operating properly to put the system into cooling mode.

Phil :

breakers are ok

Phil :

the control coil on the 4 way valve should be energized to put the unit into cooling... either the coil in the valve is bad, or the valve is stuck. or the control card is bad

Phil :

thats easy to checl

Phil :

check

Phil :

remove the outside service panel on the outside unit that exposes the compressor and a valve with 4 fat tubes and two wires attached.

Phil :

reconnect the white wire on the thermostat

Phil :

turn the thermostat to cooling mode

Phil :

hold the metal blade of a small screw driver next to the end of the coil with the two wires attached

Phil :

you should feel a magnetic pull

Phil :

if not, find where the two wires attach and check for 24v

Phil :

if you have 24v... then remove the wires and use your ohm meter to check ohms through the coil.

Phil :

if it reads infinity, the coil is bad

Phil :

Phil

Customer:

I have not yet gone outside, but i reconnected the white wire and rebooted and the same happened - heat came on. I then tried and experiment - I switched it to heat and set the temperature to 5 degrees higher and the system turned off

Phil :

It sounds like the 4 way valve (the reversing valve we have been discussing) is malfunctioning. do the tests mentioned earlier.. we can track it down to a stuck valve or a bad control coil on the valve)

Phil :

Phil

Customer:

it is now dark here so I will need to try and do this in the morning or early evening

Phil :

Just post a detailed remark when you can, I will be notified and we can pick it up and go from there.

Phil :

Phil

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,702
9,702 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,702 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Just bought a new honeywell smart wifi thermostat rh9585 - i
just bought a new honeywell smart wifi thermostat rh9585 - i have the wiring as follows from the furnace. Y to y - G to g - R to r - W to w. I have removed the jumper because I have a C and RC wire co… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I am switching my thermostat from an iComfort and to a
I am switching my thermostat from an iComfort and to a Honeywell. I've switched the four wire wiring to a five wire and have been able to get the heat to work and the fan to work but not the compresso… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I am replacing a Honeywell T8112D1005 thermostat. The
I am replacing a Honeywell T8112D1005 thermostat. The bettery terminals are corroded and the display stopped working. I tried cleaning up the terminals, but they are eaten through. I found a newT8131C… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a honeywell t8085a with q682b subbase controlling an
hello, i have a honeywell t8085a with q682b subbase controlling an electric air handler and separate gas boiler heat circuit. I have 6 wires, one is r/w/g/y and the other is r/w. they landed on c/c/r/… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
we have 3 Honeywell T87 manual dial thermostats. The one on
we have 3 Honeywell T87 manual dial thermostats. The one on the first floor was replaced with a Honeywell RTH7600 wired via the "heat pump" diagram per honeywell's recommendation (York Affinity 9.C He… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
What terminals should I be using for Electric Heat and Central
What terminals should I be using for Electric Heat and Central Air with a fully programmable auto switching thermostat?… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Bryant Heat Pump 652AJ036-A and am installing a Honeywell
I have a Bryant Heat Pump 652AJ036-A and am installing a Honeywell RTH6350 thermostat. Old thermostat had O, G, C, W2, Y/W same wire, Rc, Rh, Rc-Rh jumper wire. There's no Aux wire. I was going to pla… read more
joeydelia
joeydelia
HVAC-R Tech
High School or GED
81 satisfied customers
York affinity 3s AC with York furnace, intermittent cooling.
York affinity 3s AC with York furnace, intermittent cooling. Sometimes air discharge is cool, sometimes not. Outside compressor/fan are sometimes off when I go outside to check on it, even though the … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Replacing 2 wire Mercury thermostat with Honeywell digital
I am replacing a 2 wire mercury thermostat with a Honeywell digital programable RTH2300B thermostat. I have only two wires connected on the old thermastat (black and red). The new thermostat has conne… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I just purchased a Honeywell RTHL 2310B Programmable Thermostat.
I just purchased a Honeywell RTHL 2310B Programmable Thermostat. My old thremostat has a place for RC and RH. RC and RH had a jumper wire to them,with one red wire to the RH spot also. Do I leave the … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have replaced an oil fired hot air heater with a Heil hot
I have replaced an oil fired hot air heater with a Heil hot air propane fired heater that has an A/C coil on top, there is an outside A/C compressor. I would like to wire this all up using a Honeywell… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I just bought a Honeywell Thermostat RTH221B. I am replacing
I just bought a Honeywell Thermostat RTH221B. I am replacing a 16 year old White-Rogers Heat/Air condition thermostat with a mecury switch located inside. The installation guide on page 6 said that if… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
I am trying to install a Honeywell thermostat model #RTH7400/RTH7500
I am trying to install a Honeywell thermostat model #RTH7400/RTH7500 for a heat pump. My old thermostat has a W2 connection and I want to make sure that this connection goes to the Aux and I was also … read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
I have a Honeywell TH8320U thermostat that Im trying to install
I have a Honeywell TH8320U thermostat that I'm trying to install and a Carrier Tech 2000SS heat pump and need some help with the wiring color codes. I have wired the thermostat as instructed in the ma… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
I am replacing a carrier thermostat (TSTATCCPB501) with a Honeywell
I am replacing a carrier thermostat (TSTATCCPB501) with a Honeywell (RTH 230B). The wiring went to terminals on the Carrier marked R(red), G(green), Y1(yellow), W1(white) and C(blue). The Honeywell ha… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I am attempting to replace a York thermostat with the Honeywell
I am attempting to replace a York thermostat with the Honeywell RTH2310B. I have attached the wires as directed I get the heat no matter where my selector in heat or cool. Do I need to remove the jump… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
HI there. I need to install a new Honeywell thermostat (RTH
HI there. I need to install a new Honeywell thermostat (RTH 6400D). The contractor left the wire ready but took off (filed for bankrupcy). I have 6 cables coming out the wall: green, red, blue, white,… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I am replacing an existing thermostat which is not programmable
I am replacing an existing thermostat which is not programmable to one which is. In the current existing thermostat, there are 4 wires apart from the red one which comes factory connected to two ports… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x