I have a Lennox heating and air conditioner that his about

Customer Question
4 yrs old. The...
I have a Lennox heating and air conditioner that his about 4 yrs old. The M/N# XXXXX XXXXX HPD-042-230-01 and the S/N is 5806m14939. The unit will not come on. My thermostat inside of the home that regulates the unit is blank. I have used a wet/dry vacuum to remove any clogs from the plastic pipe that is hanging out of the back of the house. There is no debris, grass or anything else that is around the unit. I have also replaced all filters in the home. When I take off the side panel and push the switch manually the fan comes on but you can feel nothing happening inside the home. What can I do to fix it?
Submitted: 6 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 minute by:
6/18/2011
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 6 years ago
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 22,760
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified

 

What is furnace make/model?

 

 

Ask Your Own HVAC Question
Customer reply replied 6 years ago

Lennox....model number 13 HPD-042-230-01 serial number 5806m14939

HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 6 years ago

That is the outdoor unit. The power for thermostat comes from the indoor unit. That is the number I need.

 

 

Ask Your Own HVAC Question
Customer reply replied 6 years ago
Sorry. I have a honeywell thermostat I pulled it off of the wall and the only numbers I see on is TH5220D10290706. Is that what you need? If not, where do I locate the information you need.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 6 years ago

Do you know where you change the filter?

 

 

Ask Your Own HVAC Question
Customer reply replied 6 years ago
Yes, I have three vents in the home and I replaced the filters behind each of them. There is nothing behind him that I saw when I put in the new filters? There is just an empty whole?
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 6 years ago

 

Ok..the indoor blower....usually the filter is there but yours are in the grills.....where is the unit at that blows air through the registers?

 

 

Ask Your Own HVAC Question
Customer reply replied 6 years ago
The only unit that I know of is the one that is located outside which is the Lennox. Are you saying that there is another unit some where in the home that I have never seen? Where could it be? I have a small grill that has a hose behind it while the other two just have empty whole's. I thought the unit outside blew the air through the registers but that does not seem to be the case. Help?
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 6 years ago

Your unit outside has 2 pipes that it to the indoor unit.

 

Here is what the outdoor unit looks like

 

http://www.greenwoodheating.com/products/manuals/heatpumps/13HPD.pdf

 

Follow the pipes and they will lead to the indoor unit. That is what I need the numbers from.

Ask Your Own HVAC Question
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 6 years ago

I apologize but I must go off line now.

 

I will opt to the online experts.

 

I wish you luck!

 

Billy

Ask Your Own HVAC Question
Customer reply replied 6 years ago
Ok, let me go outside and follow the pipes. This will take a few minutes. I will get right back to you.
Customer reply replied 6 years ago

Ok, Billy. Thank you for your patience. Whomever is taking over I found the inside unit under the house. What do I do now?

Customer reply replied 6 years ago

I just received a receipt that you took my $30 without someone finishing up where Billy left off. I have not gotten the answers that I need yet. Billy was in the middle of helping me, when he had to log off. Why did you process my payment before you finished servicing me?

Customer reply replied 6 years ago
I am still waiting for help. Is there anyone out there to finish helping me?
Customer reply replied 6 years ago

I am still waiting and now I am getting another request for more money when you have not not finished helping me with my first question. Can some one step up and help me?

Customer reply replied 6 years ago
Anyone?
Customer reply replied 6 years ago

Please finish helping me someone?

Customer reply replied 6 years ago

Help...

Customer reply replied 6 years ago

The inside model number is CB 26 UH 042 R 230 1

HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 6 years ago

 

Hello, I am back online. I apologize.....it appears no one picked up the question.

 

Are you still willing to proceed?

 

Ask Your Own HVAC Question
Customer reply replied 6 years ago
Thank God you are back, Billy. I have been charged two payments and no one has helped me. I got the model number from under the house it is CB 26 UH-042-R-230-1. The serial number is 600 6H 40 70 1.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 6 years ago

I am really sorry. Let me pull my files for that unit.

 

 

Ask Your Own HVAC Question
Customer reply replied 6 years ago
Ok, thank you.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 6 years ago

 

Thanks for your patience. This usually goes smoother.

 

I have the info from all pieces now. First, do you know how to change batteries in the thermostat?

 

Thermostat manual - http://www.alpinehomeair.com/related/Honeywell%20TH5220D%20Install%20Instructions.pdf

 

 

Ask Your Own HVAC Question
Customer reply replied 6 years ago
Yes, I do but it has never had batteries in it. I works through the electricity.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 6 years ago

Thanks....process of elimination.

 

Next, does the CB26 have power to it?

 

Then if you could....running with those refrigerant pipes is a thermostat wire. It connects the indoor unit to the outdoor unit. See if that wire is intact...

Ask Your Own HVAC Question
Customer reply replied 6 years ago

I could hear a little whistling sound coming from the CB26 unit and the wires looked in tact.

HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 6 years ago

But you do not believe the blower was running?

 

and where the pipes enter the blower unit from outside...is there any frost or ice present?

 

 

Ask Your Own HVAC Question
Customer reply replied 6 years ago

There is no air blowing in the home and there was no frost or ice present.

HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 6 years ago

 

While at the unit (the CB26) you said you heard whistling?

 

And do you mind a hands on test at the thermostat to bypass the thermostat for a test?

 

 

Ask Your Own HVAC Question
Customer reply replied 6 years ago
I don't mind anything at the moment. You tell me how to do it and I will do it. :-)
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 6 years ago

Remove top section of the thermostat....the sub base will still be mounted on the wall....on this sub base are wire terminals.

 

R and G are the ones we are interested in right now.....use a short wire or a paper clip shaped in a U.....touch one end to R while touching other end to G.

 

Tell me if fan inside kicks on.

 

 

Ask Your Own HVAC Question
Customer reply replied 6 years ago
Ok, took off the top section and I see the R and G ones you mentioned. Do you want me to put the paper clips on the screws located under R and G or in the little wholes located under R and G. Just want make sure before I do it. I am also assuming we need the electricity to stay on correct?
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 6 years ago

 

It can be done various ways...remove red and green wire and twist together...attach paper clip in terminals, just hold the jumper on manually...but yes...power must be on to furnace/blower.

Ask Your Own HVAC Question
Customer reply replied 6 years ago
What is the jumper?
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 6 years ago
sorry...the "jumper" is the short wire or paper clip....it is referred to as jumping power from R to G.
Ask Your Own HVAC Question
Customer reply replied 6 years ago
Ok, got it. :-) I removed the green and R and G wires, twisted them together and placed the paper clip in the terminals manually but the fan did not kick on.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 6 years ago

Thank you.

 

Now hook eveything back up as normal at thermostat.

 

Now we have eliminated the thermostat itself as being defective.

 

I know you checked breakers for ac, but did you reset for air handler?

 

 

Ask Your Own HVAC Question
Customer reply replied 6 years ago
I don't know how to reset for air handler. How do I do that?
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 6 years ago
In your breaker box (electrical panel) turn off the breakers to indoor air handler...(not outdoor ac )
Ask Your Own HVAC Question
Customer reply replied 6 years ago
Done.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 6 years ago

 

Thanks...now....does the drain (condensate drain) from the unit drain into a rectangle pump?

 

 

Ask Your Own HVAC Question
Customer reply replied 6 years ago
I have a drain pipe that runs from underneath the home outside. Is this what you are referring too? If so, I used the wet/dry vac and cleared out this pipe this morning. Is there possibly another rectangle pump I may have missed?
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 6 years ago

Maybe...

 

Go to the unit and see exactly where the drain line goes from the air handler. It could be a small transfer pump known as a condensate pump.

 

Ask Your Own HVAC Question
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 6 years ago

Will be offline again for an hour or so.

 

Respond as soon as I can.

 

 

Ask Your Own HVAC Question
Customer reply replied 6 years ago

Ok. Here is the answer to your question. There is a black rectangle box that is located on the top of the white pvc pipe that is directly beside the unit. It has wires running from it into the unit. Also from the inside unit there is a long white PVC pipe that runs from the unit and goes out the back of the home through the foundation. It has a little hook on it and this is what I vacuumed out this morning. I will talk to you again when you return. Thanks.

HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 6 years ago

Is the black box full of water?

 

 

Ask Your Own HVAC Question
Customer reply replied 6 years ago

No.

HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 6 years ago

 

Half full or empty?

 

 

Ask Your Own HVAC Question
Customer reply replied 6 years ago

empty.

HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 6 years ago

How do feel about checking for power with a volt meter?

 

 

Ask Your Own HVAC Question
Customer reply replied 6 years ago
It seems to have power because you can hear the sound. But none the less I do not have a volt meter unfortunately.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 6 years ago

 

Do you mind taking the front door off?

 

 

Ask Your Own HVAC Question
Customer reply replied 6 years ago

No, but the front door of what? The black rectangler box or the unit itself. I do not recall if there was such a thing but I can go back under the house and see if you tell me exactly what door I am to remove.

HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 6 years ago

 

The front door of the blower unit..

 

 

Ask Your Own HVAC Question
Customer reply replied 6 years ago

After that then what should I do? Since I have to leave the computer and go under the house can you give me all the steps I need to do while I am under there before I go?

HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 6 years ago

 

Find where the thermostat wires attach..

see if they are on a circuit board that has a small blade fuse like in a car.

Ask Your Own HVAC Question
Customer reply replied 6 years ago
If it does what should I do next. I need all of the steps that I need to confirm or debunk while under the house. It is a small area and I want to look for everything that you need me to look for and test while under there. Day light right now is getting slim and my flash light is not the best.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 6 years ago

the fuse we hope is present will be a 5 amp blade fuse. If blown replace.

 

After that requires a meter so this will be the last thing I have you check.

 

Billy

Ask Your Own HVAC Question
Customer reply replied 6 years ago
Ok, thanks Billy. I will check to see if there is a circuit board with the 5 amp blade fuse you mentioned. If that does not work, I guess I will have to get a professional to take a look at it. I know it is something simple, the unit is not that old. I thought there would be a simply reset button on the unit under the house but I guess that is not feasible. I hope it does have a circuit board but I am not optimistic that it did. I know exactly what you are talking about because I see that on the outside unit. Anyway, I thank you for your help today, I was hopeful that I would have my issue solved like everyone else mentioned in their feedback columns but things just don't go like that for me. I can't say it was not from a lack of trying. I appreciate it, have a good night. At least one of us will be cool.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 6 years ago

I will leave this open for you for any follow up you may need. I also appreciate knowing what the final issue was.

 

Billy

Ask Your Own HVAC Question
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 6,022
6,022 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,022 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Goodman two stage gas furnace, 3 years old, currently is
goodman two stage gas furnace, 3 years old, currently is code in system status code says LO , its firing up but not staying on? … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Which symbol on the Friedrich heating/cooling unit is for
Which symbol on the Friedrich heating/cooling unit is for heat? Thank you! … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a trane XL90 and it's not working properly. The
Hi there. I have a trane XL90 and it's not working properly. The igniter glows bright but once the gas valve opens (can hear it and smell it eventually) the glow stops and nothing happens. I have the … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have 30 year old gas furnace (no air conditioner). the
Hi, i have 30 year old bryant gas furnace (no air conditioner). the problem is that the fan doesn't stop. searched internet and learned that mostly the problem is with the fan limit switch. however, i… read more
Webb-Guy
Webb-Guy
tech.
72 satisfied customers
My thermostat is cycling on and off vert frequently, about
my thermostat is cycling on and off vert frequently, about 20 to 30 seconds each … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
My lennox heater is not heating. The thermostat is set. I
The thermostat is set. I did not check the filter, but it is only 10 months old and the fan is running, when I just trun on the fan … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Carrier furnace 58mcb080-20 gas valve will not open... i
carrier furnace 58mcb080-20 gas valve will not open... i confirmed 24 volts going to valve... replaced the valve and same problem... i jumped 24 volts from the transformer and it opens no problem... n… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
22,760 satisfied customers
I tried to install new Honeywell WiFi thermostat
Hi. I tried to install new Honeywell WiFi thermostat th9320wf5003. And it doesn't show display. In … read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
22,760 satisfied customers
We have a Weil-Mclain boiler that keeps going int lock out
Hello we have a Weil-Mclain boiler that keeps going int lock out mode. It runs for about 20 seconds and then shut off with a solid red light. We now have an amber and red solid light. Can you help? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Lady hru? I'm troubleshooting an American Standard Freedom
Good evening lady hru? I'm troubleshooting an American Standard Freedom 80 furnace that's indicated to me the thermal protection device is open. What do I need to do to fix the issue? … read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
22,760 satisfied customers
My remote doesn't communicate with my unit. Its not the
My remote doesn't communicate with my unit. Its not the remote and I tried to re sync them several times. No luck. The unit will not turn on … read more
Eddie
Eddie
Home Improvement Contractor and Repairs
High School or GED
952 satisfied customers
I have a Honeywell propane furnace and the pilot is out.
I have a Honeywell propane furnace and the pilot is out. Iwhen the propane guy came today he said it was an automatic electrical light one but it's not on … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a question about an electric tankless or on demand
hello, I have a question about an electric tankless or on demand water heater … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My furnace won't start. Furnace is in attic. I disconnected
Yes, I disconnected thermostat and read no voltage on any leads … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Im trying to add a c wire to a EB15e. I just bought this
I just bought this place and im trying to install a smart tem … read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
343 satisfied customers
I have a 19.9 Rheem 120 volt water heater it does not have a
I have a 19.9 Rheem 120 volt water heater it does not have a drain valve . how do I drain it ? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Quiteside minisplit shows E1 code when I switch it to heat.
quiteside minisplit shows E1 code when I switch it to heat … read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
343 satisfied customers
Trying to install Honeywell lyric t5 wi fi thermostat to
Trying to install Honeywell lyric t5 wi fi thermostat to control heat pump with 7 wires … read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
343 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x