Hello i just moved into a new home with an old honeywell round…

Customer Question
Hello i just moved into...
Hello i just moved into a new home with an old honeywell round thermostat with 4 wires, red, black and what looks like 2 copper with no shielding? i purchased a lux tx1500 automatic thermostat. i have both heat and central air, so i need to connect it accordingly, my problem is that the wires were really short, i had to unscrew the wire holding screws before i could remove it from the wall, i dont know which wire R, R(something unreadable) but next to the G, the G wire and the Y wire? Can U assist?
Submitted: 7 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 18 minutes by:
5/8/2011
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 7 years ago
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 23,154
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified

 

Hello,

 

Odds are you had a R and a Rc but they were connected with a short jumper wire.

 

On your new thermostat do you have just an R or an Rc or Rh also?

Ask Your Own HVAC Question
Customer reply replied 7 years ago
i have 4 wires and to get it off the wall i had to remove 4 little screws inside the round unit. those had little tiny letters which i couldn't see until it was off and the wires had been removed, thus the problem. it looks to me that the ones on this unit were connected to the R, R with something little, G, and Y, they were connected separately to the 4 screws. the new unit has G, RH, RC, Y, W, O, B, C. The RH and RC on the new unit are jumper-ed together
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 7 years ago

Thank you,

 

so the issue is we dont know whic wire went where?

 

Hold the red wire in one hand...one at a time touch the other wires to the red.

 

Red is going to go to the rc/rh...but we need to know the others.

Touch the black to the red and tell me what turns on...blower, heat or outdoor unit.

 

 

Ask Your Own HVAC Question
Customer reply replied 7 years ago
i have touched and held the red to each of the other 3 wires and nothing happens, the heat and ac both worked with the old round thermostat. now i am really worried that i screwed it up totally!
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 7 years ago

Is the furnace turned on?

 

 

Ask Your Own HVAC Question
Customer reply replied 7 years ago
Yes i had shut off the circuit breaker but turned it on after you last request. the old round one had simply and off, cool or heat setting along with fan on or auto switches thats it.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 7 years ago

 

What is make/model of furnace?

 

 

Ask Your Own HVAC Question
Customer reply replied 7 years ago
hold on i have to look and it now appears that further inside the wall was a 5th wire which also if i touch the red to nothing happens. Furnace is Power Oil/Power Gas Furnace, Model CMF2
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 7 years ago

Thank you,

 

Did the old thermostat have a "C" terminal that could have been hooked up?

 

 

Ask Your Own HVAC Question
Customer reply replied 7 years ago
No C that i can find. there are two sets of numbers inside the old if that helps. under the upper section under the plastic knob to set the temp, there is a little placard with T87F 2873 3 and below that 0025. on the top of the underside there is Q539A1147 something unreadable tiny, and under that 0018 thats all the writing aside from the letters at the screws
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 7 years ago

 

 

Ok,...oil or gas version for furnace?

Ask Your Own HVAC Question
Customer reply replied 7 years ago
gas
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 7 years ago

 

 

The only other option is to open the furnace and check thermostat connections there. If nothing at all happens when wires touched together is a sign of a bad transformer.

 

To check would require a meter to see if unit is making 24 volts.

 

I apologize but it is now time for hands on checking with a meter.

 

Billy

Ask Your Own HVAC Question
Customer reply replied 7 years ago
the furnace is brand new, and was running fine until i removed the thermostat from the wall. if i knew where the wires where i could just put that one back on the wall
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 7 years ago

If the wiring were shorted it can burnout the transformer.

 

The method of bypassing the thermostat did not activate any function thus I am concerned about the thermostat power.

 

Something should have happened when we touching wires together...the fact that nothing happened means our control power is missing.

 

I will opt out to let the others have a look for you and see if there are any suggestions.

 

 

Ask Your Own HVAC Question
Customer reply replied 7 years ago
It seems i have 5 wires, the colors are very difficult to see, there is one red, the others ? however if i touch the red to one the heater starts, if i touch the two others the ac systems starts, the fifth wire i dont think was hooked up but i am not sure? please advise. i have a new lux tx1500E which wires to use and connect to which connections please advise. i was told by billy from your group that if i touched the red to other wires things would happen that isn't the case, 2 wires start the heat, 2 start the ac system, the 5th? Please advise!
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask BillyHvac Your Own Question
BillyHvac
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 23,154
23,154 Satisfied Customers
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics

BillyHvac is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
OK so I am replacing a Trane Baystat 239 with a Lux TX9600TSa
OK so I am replacing a Trane Baystat 239 with a Lux TX9600TSa and am not sure how to wire it. In this effort, I discovered there must be a heat pump in this house we just moved into. UGH!… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
I have a forced air oil furnace, and Im trying to replace
I have a forced air oil furnace, and I'm trying to replace the Lux tx1500 with an insteon 2441th. The wiring at the furnace (becket honeywell control) white=3/t black=T transformer green=G orange=Y re… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
State Licensed Mechanical Contractor
23,154 satisfied customers
I am trying to replace a LUX TX1500 thermostat with a Honeywell
I am trying to replace a LUX TX1500 thermostat with a Honeywell RTH7600. I have a system that is one stage, with central ac and gas heat. I do NOT have a heat pump, but there WERE wires attached to th… read more
Wvfan79
Wvfan79
Mecanical Designer & Estimator
High School or GED
775 satisfied customers
replacing Janitrol hpt18-60 with an old Lux TX1500. 7 wires,
replacing Janitrol hpt18-60 with an old Lux TX1500. 7 wires, yellow to yellow, green to green, red to red, orange to orange, white to w2, brown to e, blue to c. How do I wire to the new (old) lux tx15… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
State Licensed Mechanical Contractor
23,154 satisfied customers
I have just replaced an old mercury Honeywell analog thermostat
I have just replaced an old mercury Honeywell analog thermostat with a digital programmable thermostat from Lux Products (Ace) ATX500E. I followed the instructions but it is not working so I guess the… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
I have a Chrysler Furnace Model # XXXXX which uses a
I have a Chrysler Furnace Model # XXXXX which uses a Honeywell V810A1012 natural gas solenoid and a Honeywell R8405B1009 Controller. The Furnace also has a central air unit installed and a Hunter 4410… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
State Licensed Mechanical Contractor
23,154 satisfied customers
im trying to replace my old honeywell thermostat and can not
im trying to replace my old honeywell thermostat and can not get the wall unit to turn, seems i might have mixed up wires.... any help please?… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a Honeywell RTH3100 thermostat with wires the following
I have a Honeywell RTH3100 thermostat with wires the following wiring configuration: BLK to E, Wh to AUX, Yel to Y, Grn to G, Org to O, Red to R and the 2 heat pump connections are B is no wire and th… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Hi...I recently moved into an apartment complex in Phoenix
Hi...I recently moved into an apartment complex in Phoenix with individual ac units/heatpumps on the roof. I have not personally seen them but there are no central systems for this building. My questi… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
I have a Trane Baystat 239 thermostat, Im replacing it with
I have a Trane Baystat 239 thermostat, I'm replacing it with a Honeywell th8320u1008. this is for a heat pump application. My Baystat connection were x2=black, o=orange, g=green, y=yellow, t=tan, r=re… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have central air with an old, round Honeywell stat. My
I have central air with an old, round Honeywell stat. My boiler is connected to a White-Rodgers stat, model 1F78. It has un-used terminals labeled G, O and Y. On the Honeywell, there is a black wire o… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
State Licensed Mechanical Contractor
23,154 satisfied customers
I have a forced air system with oil heat and ac. My honeywell
I have a forced air system with oil heat and ac. My honeywell electronic thermostat started acting funny (the room temp displayed was not correct at times), so i bought a Lux TX9000TS thermostat. Said… read more
Bart Jay
Bart Jay
Vocational, Technical or Trade Scho
596 satisfied customers
I am replacing a Lux thermostat with a honeywell. There were
I am replacing a Lux thermostat with a honeywell. There were 5 wire connected to the Lux in the following order. O to O ,Y to Y ,W to W,R to RC, G to G. The issue seems to be where the G wire and R wi… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
I purchased a Honeywell RTH7500 series programmable thermostat
I purchased a Honeywell RTH7500 series programmable thermostat to replace my manual Trane thermostat. I have a heat pump with backup heat. of course the wires colors don't match. The wires installed o… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Replacing a thermostat. I am replacing the original, non-programmable,
Replacing a thermostat. I am replacing the original, non-programmable, thermostat that came with a (2002 +/-) Trane XL13 series heat pump (Trane thermostat pt no BAYSTAT240A 3AAT82B1B1) with a Honeywe… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
I have installed a new board hh84aa020 on my carrier furnace
I have installed a new board hh84aa020 on my carrier furnace and the thermostat terminals are different than the old board. I have an A/C and need to hook them up to the new board hh84aa020 . the "new… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
State Licensed Mechanical Contractor
23,154 satisfied customers
I am trying to replace a Trane Weathertorn 2 stage heatpump
I am trying to replace a Trane Weathertorn 2 stage heatpump T-stat with a Honeywell RTH7500 T-stat. As I am sure you are aware there are wiring differences.… read more
coolman1973
coolman1973
AC/Heat Tech
Vocational, Technical or Trade Scho
162 satisfied customers
Hello, I am installing a Honeywell Focuspro TH6100 on a 2 line,
Hello, I am installing a Honeywell Focuspro TH6100 on a 2 line, apartment baseboard hot water system, replacing the old "yo-yo". I am a but confused about the wiring and the many teminal choices. Both… read more
coolman1973
coolman1973
AC/Heat Tech
Vocational, Technical or Trade Scho
162 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x