I have a -Rodgers programmable thermostat 1F82-261,

Customer Question
I have a White-Rodgers programmable...
I have a White-Rodgers programmable thermostat 1F82-261, purchased last year. I also had the electric pump serviced at that time, which needed some new parts. I have been using the heat, programmed, and everything's been fine. The thermostat was put in the off position a couple days ago, and when I turned it back to the on position, the electric heat pump would not activate. I reset the circuit breakers, which didn't seem to be tripped and reset the thermostat with the help of a White-Rodgers technician. Still nothing. This has happened in the past with two different thermostats--this is the third thermostat in 3 years--that is, they are turned off and suddenly won't turn back on. Any suggestions before I call a guy out? I do not know the make and model of the heat pump.
Submitted: 7 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 9 hours by:
12/17/2010
HVAC Technician: gotoman for ac, HVAC Technician replied 7 years ago
gotoman for ac
gotoman for ac, HVAC Technician
Category: HVAC
Satisfied Customers: 5,344
Experience: 51 years of experience install design and repair of all makes and models of AC
Verified
Does anything work. Fan to on position emergecy heat anything. Russ
Ask Your Own HVAC Question
Customer reply replied 7 years ago
No, the led lights are on and the programming still shows. No fan, nothing.
HVAC Technician: gotoman for ac, HVAC Technician replied 7 years ago
If you have a voltmeter we need to check for 24 volts on thernostat. If you do not have voltmeter go to air handler pull door and you will see a terminal board with R C G W Y C. Take a small paiece of wire and jumper from R to G , If it does not run check for a blown 5 amp auto type fuse on the fan baord, Russ
Ask Your Own HVAC Question
Customer reply replied 7 years ago
Sorry, didn't see your reply. OK, you've lost me. No voltmeter. What is the air handler pull door?
HVAC Technician: gotoman for ac, HVAC Technician replied 7 years ago
Pull door off air handler(top door) You should see a terminal board with letters R Y C W G. Look on the board and see if you see a 5 amp yellow auto type fuse. Russ
Ask Your Own HVAC Question
Customer reply replied 7 years ago
What do you mean air handler. Is this the thermostat we're talking about here?
HVAC Technician: gotoman for ac, HVAC Technician replied 7 years ago
The inside unit that blows the air. Take off top panel. Russ
Ask Your Own HVAC Question
Customer reply replied 7 years ago
There is no inside unit. The huge blower unit is outside. What top panel? There's a door that warns against electric shock.
HVAC Technician: gotoman for ac, HVAC Technician replied 7 years ago
You have package unit. It would be better to call a service tech on this unit. If you open the door there is mass of wires and hard to trace. If you want to test and see if thermostat is bad . Pull front cover off and use a piece of wire to jump between R and Y to see if unit comes on.If it comes on bad thermostat , If not you will need call service tech. Russ
Ask Your Own HVAC Question
Customer reply replied 7 years ago
What kind of wire? A bare wire or plastic covered?
HVAC Technician: gotoman for ac, HVAC Technician replied 7 years ago
Does not matter it is only 24 volts will not hurt you. Russ
gotoman for ac
gotoman for ac, HVAC Technician
Category: HVAC
Satisfied Customers: 5,344
Experience: 51 years of experience install design and repair of all makes and models of AC
Verified
gotoman for ac and 87 other HVAC Specialists are ready to help you
Ask your own question now
Customer reply replied 7 years ago
I see the R but not the Y
Customer reply replied 7 years ago
OK I found the Y. I put one end on R and the other on Y. Is that right? How do I know if I touched the wires correctly.
HVAC Technician: gotoman for ac, HVAC Technician replied 7 years ago

Sorry just got back. That is correct just touch R to Y the outside unit should come on. We are checking thermostat. Russ

Ask Your Own HVAC Question
Customer reply replied 7 years ago
Do you have any idea why the blower seems to go out when the thermostat is turned off, or is that a huge coincidence? Not every time of course but it has happened that way at least three times and then the heat is down again. Do I just touch the screws holding the wires R and Y or do I have to touch the actual wires? Is there a fuse or something I could check on the blower? Just want to make sure I've done all I can.
HVAC Technician: gotoman for ac, HVAC Technician replied 7 years ago
just touch screws and let me know if it runs. Russ
Ask Your Own HVAC Question
Customer reply replied 7 years ago
OK, I tried everything again: resetting circuit breaker, new batteries, resetting thermostat, and jumping wires. Nothing.
HVAC Technician: gotoman for ac, HVAC Technician replied 7 years ago

Does fan run in on position. Do you have a volt meter. Russ

Ask Your Own HVAC Question
Customer reply replied 7 years ago
No fan. I have an old volt meter. Not sure it works anymore.
HVAC Technician: gotoman for ac, HVAC Technician replied 7 years ago
We need to check voltage on unit outside.. Before you take panel off shut off power. Take off panel and locate where high voltage wires come into contactor. Turn power on and check for 220 volts at contactor. Russ
Ask Your Own HVAC Question
Customer reply replied 7 years ago
You talk as if I know what you are talking about. I just don't think I'm getting anywhere. Panal?? Do you mean the main switch powern switch to turn off power?? If so, it's inside the panel door? Contactor? I told you I'm not sure if volt meter even works. This all sounds too dangerous, and it's wet and rainy outside. Maybe someone more comfortable with electricity could do what you're suggesting. I better just give it up. What about my question regarding turning thermostat off messing up the system?
HVAC Technician: gotoman for ac, HVAC Technician replied 7 years ago
You need to call service tech. It gets tricky when trying get a voltage reading. I am going to opt out. Russ
Ask Your Own HVAC Question
Customer reply replied 7 years ago
Please answer the question I've asked 3 times about turning off thermostat. Coincidence??
HVAC Technician: gotoman for ac, HVAC Technician replied 7 years ago

Turning off thermostat would not have anyting to do with unit not working when you turned it back on. You have jumped thermostat,turned power off and on to reset faults. Something is wrong in outside unit and I do not want to get you hurrt trying to trouble shoot the electrical system. Double check on thermostat and make sure you have the two R terminals jumper in place for heat/cool operation. Russ

Ask Your Own HVAC Question
Customer reply replied 7 years ago
I'm not sure about your last statement--two R terminals jumper in place for heat/cool operation???
HVAC Technician: gotoman for ac, HVAC Technician replied 7 years ago
There are two terminals on thermostats. One is RC for cooling and one is RH for heating. They are for systems with two transformers. To get thermostat to operate properly they must have a small jumper wire between them. Russ
Ask Your Own HVAC Question
Customer reply replied 7 years ago
Been out and about. Thanks for trying to help. I appreciate it. At least I learned how to test if the thermostat is bad. Good to know:)
Was this answer helpful?
Ask gotoman for ac Your Own Question
gotoman for ac
gotoman for ac
gotoman for ac, HVAC Technician
Category: HVAC
Satisfied Customers: 5,344
5,344 Satisfied Customers
Experience: 51 years of experience install design and repair of all makes and models of AC

gotoman for ac is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Honeywell thermostat is not turning on any heat, why?
My Honeywell Thermostat is not turning on any heat. However, the fan is working but not the Auto. Also, when I went to change the batteries, I forgot to switch it to the OFF position. Now it displays … read more
Robert
Robert
Associate Degree
161 satisfied customers
I have a Honeywell Chronotherm III programmable thermostat
I have a Honeywell Chronotherm III programmable thermostat and my a/c won't turn on. I have replaced the batteries and attached it to the wall. when i slide it to the cool position all I get is a blan… read more
Tom
Tom
HVAC Technician
Vocational, Technical or Trade Scho
770 satisfied customers
Hot water quit. Reset circuit breaker. What now? About a
About a week. On occasion water got hot. Sometimes, as now is cold. When I have reset circuit breaker it wasn't tripped, but still the aforementioned happens … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Installing a programmable thermostat and the wires do not
installing a programmable thermostat and the wires do not match the directions … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
We have a Honeywell wi-fi 7-day programmable thermostat with
we have a Honeywell wi-fi 7-day programmable thermostat with an app on my phone. Since we changed our wi-fi router (some time ago) the app does not work. There is a message on the thermostat that says… read more
Plumbers_Mate
Plumbers_Mate
General Manager
Vocational, Technical or Trade Scho
3 satisfied customers
I have a HUNTER programmable thermostat. When I went to turn
I have a HUNTER programmable thermostat. When I went to turn on my central air for the first time this season, nothing happen. The temperature in the house says 84 degrees. … read more
hvacdave84
hvacdave84
53 satisfied customers
My circuit breaker is popping and i think it may caused by
my circuit breaker is popping and i think it may caused by my intertherm thermostat. can i disconnect the thermostat and would that allow me to reset the circuit breaker? … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,862 satisfied customers
This house is missing the circuit breaker for the disconnect
This house is missing the circuit breaker for the disconnect for the outside ac unit. What do I need to get to repair this?… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Just installed a RTH6360 series programmable thermostat,
Just installed a RTH6360 series programmable thermostat, only getting heat despite setting on cool. … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a programmable thermostats. Always used it manually.
I have a programmable thermostats. Always used it manually. Somehow it is asking for programming. How do I get back to manual? … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Is a British Gas PT Plus programmable thermostat the main
Is a British Gas PT Plus programmable thermostat the main unit only or dies it also have a receiver … read more
Plumbers_Mate
Plumbers_Mate
General Manager
Vocational, Technical or Trade Scho
3 satisfied customers
I have a programmable thermostat but want to turn it off and
I have a programmable thermostat but want to turn it off and go manual. I do not have a manual and cannot figure out how to turn off. … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,862 satisfied customers
The compressor trips the circuit breaker in the house, not
the compressor trips the circuit breaker in the house, not immediately, about after 5 minutes. what are my options? can i replace only the compressor? It is a frigidare model FS3BC-042KA … read more
Chris Wagner
Chris Wagner
None
27 satisfied customers
Was changing to a programmable thermostat and furnace will
was changing to a programmable thermostat and furnace will nor kick on... tried putting old back on and it does not work either … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,862 satisfied customers
Which smart or programmable thermostats work with a reznor
hi! which smart or programmable thermostats work with a reznor v3 tcore2 … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,862 satisfied customers
Air Handler # NFCX3600C2 what causes the circuit breaker
Air Handler # NFCX3600C2 what causes the circuit breaker panel to fry? I replaced it once and the heat worked OK but when I tryed to run A C the board fryed again … read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
454 satisfied customers
I have a Honeywell programmable thermostat that is
I have a Honeywell programmable thermostat that is programmed already but I find it to be set too high for certain times of the day and night!! And my furnace seems to run constantly---how do I reset … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Installed a new programmable thermostat, but it wouldn't
Installed a new programmable thermostat, but it wouldn't work with the system So I uninstalled it (thinking it was not compatible)/ Installed the old one again Now the old one won't work either … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x