Honeywell Chronotherm III problem

I have a Honeywell Chronotherm...
I have a Honeywell Chronotherm III. I replaced the batteries and now when I turn on the heat the furnace turns on and then stops about 1 minute later. The fan never comes on. On the front of the panel it shows the time and the "AC". Why is my system doing this ? Why won't the fan come on and blow heat in the house? Why does the Panel display "AC" ?
Show More
Show Less
Ask Your Own HVAC Question
Answered in 8 minutes by:
12/1/2010
Tom
Tom, HVAC Technician
Category: HVAC
Satisfied Customers: 770
Experience: 16+yrs HVAC/R service. Residential Commerical Industrial
Verified

The AC display means that the thermostat is not getting ac power from your furnace...

I would try removing the thermostat from the sub-base (plate that is attached to the wall)...try cleaning the connections between the thermostat and base and also check the thermostat wires for loose or dirty connections...

The wiring is 24 volts...so you can carefully remove it with power on...or shut the power off at the furnace if you like..
<br/Customer:
What should I use to clean it with? Alcohol?

Tom :
I'm trying to remember how it connects...brass pins perhaps..? I would use a pencil eraser on any surface you can...alcohol might work ...I would shut power off if you do that..Shouldn't matter..but you cannot be too careful.
<br/Customer:
It is brass pins. I will try the eraser

Tom :
That should take any tarnish off...even if you don't get inside the plugs..getting one surface clean and replugging it often times takes care of the problem..

Check the stat wires..I think the Chronotherm uses little screw terminals..make sure they are snug..
<br/Customer:
Still getting the same thing - AC. Also, when I turn the Fan to "on" nothing happens.

Tom :
Do you own a voltmeter?
<br/Customer:
No volt meter

Tom :
Ok...is this a gas furnace? And it was trying to run earlier?
<br/Customer:
Yes and Yes

Tom :
Ok..if you take the wire from the W terminal of the sub base and connect it with the R terminal...that will by pass the thermostat and we'll at least see if your furnace runs...If it does..you probably need a thermostat..if it doesn't we have a problem in the furnace.

I would shut the power off before moving the wire.
<br/Customer:
The furnace fires up but shuts off in about a minute.

Tom :
I would try moving the W wire and see if it will stay running.
<br/Customer:
What do you mean move?

Tom :
Unscrew the terminal screw...remove the wire under the W terminal and connect it under the R terminal..... you don't need to put the front of the thermostat back on for this test...just turn the furnace back on...you are bypassing the internals of your thermostat... Essentially 'hot wiring' your furnace to see if it will stay running...
<br/Customer:
There is already a wire on the R terminal.

Tom :
That's the 24 volt power from the furnace...that's ok..I want you to connect the W wire with the R wire....that should make your furnace run and hopefully stay running...

If the furnace is ok..it will run until you unhook it..

If that is the case you have a bad thermostat.

If it still quits...you have a furnace problem..
<br/Customer:
Get the same result. Looks like it is a furnace problem. Fan never turns on.

Tom :
Did it light?
<br/Customer:
Yes

Tom :
What kind of furnace do you have/

I'm not sure what to make of this...the AC means the thermostat isn't seeing power...and now it lights but the fan won't come on...It's almost like you have problems on both ends..

If you need to get heat...... you could unhook the G terminal wire and add it to the R and W...that would give you fan..
<br/Customer:
Bdp508. Looks like it is a Carrier

Tom :
Strictly manual control...but at least you'd have heat..

I would get someone with a volt meter over there to do some testing...I'd hate to tell you to buy a thermostat...and it be something else...but the blower should have started in the heat mode...

If the fan doesn't run by connecting G ... then you probably have a control board issue or a bad blower motor..
<br/Customer:
It is a bdp model 518A060. Do you think it is time to call in an expert?

Tom :
If you can get by without the heat for the night..I probably would. ... It will be difficult to go much further without taking some volt readings to find out what's really going on..
<br/Customer:
Ok. Thanks very much!

Tom :
You're welcome...I'm sorry it wasn't something we could diagnose easily over this venue. Good luck..I hope it's nothing expensive.
<br/Customer:
Me too.....

Tom
Tom, HVAC Technician
Category: HVAC
Satisfied Customers: 770
Experience: 16+yrs HVAC/R service. Residential Commerical Industrial
Verified
Tom and 87 other HVAC Specialists are ready to help you
Ask your own question now
Ask Tom Your Own Question
Tom
Tom
Tom, HVAC Technician
Category: HVAC
Satisfied Customers: 770
770 Satisfied Customers
Experience: 16+yrs HVAC/R service. Residential Commerical Industrial

Tom is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Our carrier infinity says "system malfunction". The fan is
our carrier infinity says "system malfunction". The fan is working but it is not cool. I went to the attic and changed the filter but code is still there. What does this mean? … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
My carrier furnace is not turning on. Thermidistat is blank.
My carrier furnace is not turning on. Thermidistat is blank. Error codes is 33. … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Our carrier infinity thermostat says system malfunction.
our carrier infinity thermostat says system malfunction. When I press and hold the right button it says ignition lockout. 53 events active. What the what is that? … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
The supplemntal heat is not working in my carrier air
The supplemntal heat is not working in my carrier air handler … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Carrier 2500a keeps saying it's low on fuel and shuts
Carrier reefer 2500a keeps saying it's low on fuel and shuts down.but is full of fuel … read more
Michael Ferryman
Michael Ferryman
88 satisfied customers
Phil, we have a Carrier Infinity Weathermaer natgas
Phil, we have a Carrier Infinity Weathermaer natgas furnacethis week the limit switch had to reset at lest 4 ties. We replaced the limit switch,ever since then the furnace runs but the top of the plen… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Cost to replace a expansion valve on a carrier infinity.
cost to replace a expansion valve on a carrier infinity … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Need an interconnect schematic for my carrier furnance. Need
Need an interconnect schematic for my carrier furnance … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
I Have a Carrier gas furnace model PG9MAB060120A. The
I Have a Carrier gas furnace model PG9MAB060120A. The burners blow but the air from the heat exchange at the furnace is luke warm. Is there a problem with the heat exchange? … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,142 satisfied customers
Have a Carrier Weather Maker 8000 ts and the light on the
Have a Carrier Weather Maker 8000 ts and the light on the front panel is blinking … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
We have a Carrier Infinity System Thermostat Model #
We have a Carrier Infinity System Thermostat Model # SYSTXCCUIZ01-A and the plastic "heat" and "zone" buttons are broken. We are looking for a new unit with this model number to replace our current un… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
We would like to purchase a Carrier Infinity System
We would like to purchase a Carrier Infinity System Thermostat model SYSTXCCUIZ01-A. Searching for this but haven't had much luck. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Im changing my thermostat from a carrier to honeywell
Im changing my thermostat from a carrier to honeywell rth6580wf. The orange wire, not sure where to connect it on the honeywell … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Airheatman, Trying to source a control board for a Carrier
Hi airheatman, Trying to source a control board for a Carrier forced air furnace that a technician said was no longer available. The number is ***** obscured, looks like 3057?5 702 working with a 3012… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I'm on service with a commercial Carrier heat pump, It wont
I'm on service with a commercial Carrier heat pump … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My high efficiency condensing furnace (Carrier) emits a
My high efficiency condensing furnace (Carrier) emits a terrible eye-stinging odor when heating. The furnace runs quiet and otherwise appears to be trouble free, however I see (and smell) a fresh (wet… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Have Carrier fan coil unit model FV4CNB003. Have Carrier Fan
Have Carrier Fan Coil unit # FV4CNB003. Seemed to run and change speed during operation. Is this normal? … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
We have a Carrier A/C with Carrier TP-PRH01 thermostat. Set
We have a Carrier A/C with Carrier TP-PRH01 thermostat. Set on hold, auto, cooling.75 dgr. A/C will run for a while and go dark.Cooling stops. eventually it will light up and cooling will begin and wi… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x