I have a question about my air conditioner. We have a 2 story…

Customer Question
I have a question about...
I have a question about my air conditioner. We have a 2 story house and the upstairs got very hot today. The unit is running and it blows air. The thermostat is set on 78 and shows 92. What could be wrong ??
Submitted: 8 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 3 hours by:
6/30/2010
HVAC Technician: freon, Licensed A/C Contractor replied 8 years ago
freon
freon, Licensed A/C Contractor
Category: HVAC
Satisfied Customers: 215
Experience: 22 years Licensed Contractor State of Texas
Verified

Good evening,

 

thank you for contacting Just Answers!

 

First you should check the breaker for the outdoor unit. It may have tripped while you were away. If you find the double pole breaker in the tripped position (this is neither on nor off but just slightly to the middle from on) then be careful. You will have to snap it off aggressively and then back on keeping your face away from the front of the breaker panel. This is just a safe way to reset breakers.

Next, if you see that the outside unit is running, put your hand over the fan. it should be warm to almost hot. if it feels cool or just like ambient temperature then more than likely the compressor motor is not running and can be either overheated. This can happen if your condenser is dirty, the capacitor is out, or if the condenser fan is going out. If the condenser fan is going out...it could also be due to the fan capacitor. More than likely you would only need to replace the capacitor. If you feel bolden, you may open the control box of the unit and peer inside. be careful to pull the disconnect first or turn off the breaker. When looking in side see if you notice any burnt wires or a bloated or puffy capacitor. This capacitor is usually silver metal and round or oval. Most times it is a dual capacitor that services the compressor and fan in the same unit. You can tell because it will have three separate terminal posts with multiple terminals on each post.

Some times the yard man gets too close with the weed eater and cuts the low voltage wiring at the unit. Just twist the wires back together and tape em up... now splice them back color to color.

Try doing the work above to see if you can save your self some $$$. However if you dont feel comfortable dont worry. A good technician will do it for you and teach you if you want to watch.

 

freon

Ask Your Own HVAC Question
HVAC Technician: freon, Licensed A/C Contractor replied 8 years ago

Dear JACustomer,

 

I hope you found my information helpful! Please if you are finished asking questions will you please click on the ACCEPT link? If you are unhappy with my answers then by all means dont accept and click on refund. We appreciate you very much and hope the best for you!

 

freon

Ask Your Own HVAC Question
Customer reply replied 8 years ago
I had to call somebody to fix my unit. Thank you anyway
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask freon Your Own Question
freon
freon
freon, Licensed A/C Contractor
Category: HVAC
Satisfied Customers: 215
215 Satisfied Customers
Experience: 22 years Licensed Contractor State of Texas

freon is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a Honeywell Portable AC unit. The air is blowing into
Second opinion] I have a Honeywell Portable AC unit. The air is blowing into the room cool but the room keeps getting warmer especially during hot day. At night it works a bit betterr. I have a 15 x 2… read more
oilburn62
oilburn62
27 satisfied customers
Is there a way to reset or adjust the damper on a Honeywell
Is there a way to reset or adjust the damper on a Honeywell HZ221 … read more
Michael Ferryman
Michael Ferryman
110 satisfied customers
When I set my air conditioning at 68 degrees, the house temp
Hi. When I set my air conditioning at 68 degrees, the house temp will not drop below 72 degrees. I called to have a repairman come and they said it sounds like a thermostat issue. I have a Honeywell F… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
We just bought and had installed a merit series 13acx air
We just bought and had installed a merit series 13acx air conditioner. We ran it for 2 days and it froze up inside and out without cooling our house at all. The installer thinks they forgot to open se… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I had a zoned heat & air heat pump installed in my house.
I had a zoned heat & air heat pump installed in my house. One thermostat is upstairs, the other is downstairs. There is only one return in the house in the bedroom upstairs so that I can't shut off th… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
We have a new home that was just built and we have a single
We have a new home that was just built and we have a single unit with 2 thermostats(one upstairs and one downstairs). I know heat rises. However, with both set on 75, it stays 75 upstairs and like 68/… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My thermostat is set to cool, but is blowing hot air. When
My Honeywell thermostat is set to cool, but is blowing hot air. When I go into the attic, my downstairs unit is working properly (red/green lights blink simultaneously slow for cool), but the upstair … read more
Expert
Expert
I have a Rheem Gas Heat and A/C unitmodel RGH-07EAUER. The
I have a Rheem Gas Heat and A/C unitmodel RGH-07EAUER. The termostat was set for cooling and it was cooling properly, but after a time the furnace went from cooling to heating and the gas heat came on… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I think I have the downstairs unit wired wrong. I think I
I think I have the downstairs unit wired wrong. I think I am making heat instead of cool when the A/C is on. The upstairs unit is working correctly. Any thoughts/… read more
HotWired
HotWired
Industrial Electrician
Associate Degree
75 satisfied customers
I have my thermostat set on 70 , the air conditioner has been
I have my thermostat set on 70 , the air conditioner has been running constantly for 3 days now and the temperature never goes below 77, just checked again, is at 78 now.The air conditioner is working… read more
Bart Jay
Bart Jay
Vocational, Technical or Trade Scho
596 satisfied customers
If I have a HVAC unit that is operating just fine but its
If I have a HVAC unit that is operating just fine but it's too small to keep the upstairs cooled in the heat of the summer can I have an additional small unit installed to cool the upstairs separately… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
We have a 2 story house with 2 separate AC units, one for each
We have a 2 story house with 2 separate AC units, one for each floor. On Saturday we discovered that the 2nd floor wasn't cooling. We called our AC guy and he came over within an hour. When he arrived… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
how can we get the upstairs to cool better. We just bought
how can we get the upstairs to cool better. We just bought a new home. The old home was about 1800 sqft and we could run the units at 78 during the day. The new home is about 3100 sqft and when we set… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
We live in Western Massachusetts. We moved from Illinois and
We live in Western Massachusetts. We moved from Illinois and bought a new 2600 square foot 2 story home in December 2008. I'm just wondering if it is normal for the air conditioner to take 1-2 hours t… read more
Heath
Heath
Vocational, Technical or Trade Scho
1,002 satisfied customers
My thermostat is showing 81 degrees and it is hot upstairs
My thermostat is showing 81 degrees and it is hot upstairs and modestly cool downstairs. It shows "Cool On" and temperature set at 66 degrees. What do you think could be wrong with my air conditioning… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
Three weeks ago, we had a Lennox air conditioner and furnace
Three weeks ago, we had a Lennox air conditioner and furnace installed in my home in Santa Clarita, CA. It's a 2-story, 2150 square foot house. The forced-air unit (CX34-50/60C-6F-1), which is located… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
I have 2 AC Zones. The bedrooms are on the second floor and
I have 2 AC Zones. The bedrooms are on the second floor and use zone 1. The kitchen and living room are on the third floor and use zone 2. Can I just run zone 1 and leave the windows open on the third… read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
The central heating unit is turned off but sometimes continues
The central heating unit is turned off but sometimes continues to blow hot air. We have one unit with two thermostats. One for upstairs and one for downstairs. If we have the stat on downstairs and th… read more
Unavailable
Unavailable
Vocational, Technical or Trade Scho
18 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x