i have a trane xe 1100 central air cond system. when you turn on the ac, only the fan comes on. the compressor and condensor fan do not come on. when I push the button in on the relay at the compressor unit they both come on. I also have replaced the thermostat. Is this an issue with the lvtb.
Show More
Show Less
Ask Your Own HVAC Question
Answered in 2 minutes by:
6/29/2010
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 23,151
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified
Chat Conversation Started
Billy :

this could be a item stopping the signal to the outdoor switch....

wire off
water switch tripped from slow drain inside
backed up condensate pump

In the outdoor unit....
low pressure switch from lack of freon
high pressure switch from over heating
switch that gets 24v is bad

Customer:

Is this something I should have a technician come out to the house and look at since I dont have the right equipment for checking pressures.

Billy :

That is the problem with checking air conditioners. In the event it is a pressure issue, the homeowner cannot do anything about it due to special tools and regulations. You can check some of the basics.....but for a full check I would have a tech pay a visit and check everything.

Customer:

can you give me a list of the basics to check before I call for a tech.

Billy :

wire off
water switch tripped from slow drain inside
backed up condensate pump

Ask Your Own HVAC Question
freon
freon, Licensed A/C Contractor
Category: HVAC
Satisfied Customers: 215
Experience: 22 years Licensed Contractor State of Texas
Verified

Do you have another question?

freon

Ask Your Own HVAC Question
Customer reply replied 8 years ago
billy are those 3 things fairly easy to test. and how do you test them.

wire off...... check for disconnected 24 volt wires at unit outside. Also in the control box
water switch tripped from slow drain inside....a lot of units have float switches check yours.
backed up condensate pump.... if you have a condensate pump check to see if clogged.

In the outdoor unit....
low pressure switch from lack of freon... Look inside your unit. if you have a low pressure switch, it is a small cylinder looking gizmo with two wires comming out of it. If you have a loss of pressure this may be keeping the unit off.
high pressure switch from over heating... look and see if you have a hi pressure switch, this is the same look as the low but it may also have a red push button switch in it. now press really hard to reset.
switch that gets 24v is bad... the contacter may be bad. check and see if you have 24 volts at the contacter, follow the low voltage wires into the control box and end up at the contacter. if you put a volt meter on the two terminals and you see 24 volts and the contacter is not pulled in then it may be bad.

 

I hope this helps you figure out what is going on!

 

freon

Ask Your Own HVAC Question
Customer reply replied 8 years ago
hi freon I checked for 24 volts at the 2 wires at the contacter and it is 0 volts. And if I push the contacter in by hand compressor and fan come on

great!

 

you are not getting the 24 volts to the contacter. You must trace the low voltage wiring back and see if their is a break in the line or if there is a low voltage control that is stopping it. Like the pressure switches or possibly a time delay relay. Check the LV wires that come into the unit and look for the wire nuts. Remove the wire nuts and check for the voltage here... if it is not there then follow the wiring inside looking for breaks. if you dont find any stop hear and we will check the thermostat.

 

freon

Ask Your Own HVAC Question
Customer reply replied 8 years ago
freon where does the 24 volts come from to activate the compressor so i know where to trace the wires back to.

it ties together at the furnace control board on the y terminal screw. the other wire here on this screw goes to the y in the thermostat.

 

freon

Ask Your Own HVAC Question
Customer reply replied 8 years ago
freon , so there should be 24 volts at the Y termial at the furnace control board and if so when should there be 24 volts. And where do I put the volt meter leads to test Y terminal.

you will find that when you put the tstat in cooling mode and lower the setting that there should be 24 volts between Y and C or Y and C/B . check this.

 

freon

Ask Your Own HVAC Question
Customer reply replied 8 years ago
freon do I check this at the furnace control board or at t-stat

the furnace control board.

 

Ask Your Own HVAC Question
Customer reply replied 8 years ago
freon I checked the voltage at terminal Y and C and there is no voltage reading. Is the control board bad.

no. the problem is likely at your thermostat. Pull the tstat top half off the wall to get to the wire terminals... take the red one loose and touch it to the wire on the Y terminal... usually this is also a yellow wire. have a friend go out side and listen for any noise or the unit comming on. if it does come on then this will show that all the wiring and unit are ok but the thermostat is not working.

 

freon.

Ask Your Own HVAC Question

also some tstats require that you program the type of system that it is so that you would tell it that it is a 1 stage heat and cool system... also look for a jumper wire from RH to RC and make sure it is there at the wire terminals.

 

freon

Ask Your Own HVAC Question
Customer reply replied 8 years ago
freon I tried touching the red wire to the Y terminal and nothing happened. what else could it be?

ok ... look closely to the terminals, what color wire did you put under the y terminal?

also look closely to that wire and make sure it did not break.

 

if you did put the wires back on properly after installing the new tsat then there must be a break in the cooling wire (which is usually yellow from the tstat). To test this all you need to do is go back to the furnace and jump from the R terminal to the Y terminal with all wires still on and have someone stand next to the outdoor unit to see if it comes on.

by the way do you have a float switch on your evaporator coil or in a drain pump?

Ask Your Own HVAC Question
Customer reply replied 8 years ago
what does the float switch look like.
a float switch is a small mechanism that is clamped to the side of the drain pan or is inside a pvc fitting in the drain line it has two wires to it.
Ask Your Own HVAC Question

Dear JA Customer,

 

Please realize that i have stayed with you all day waiting to hear from you but only getting responses once in a while. I want to help you but i cant with out knowing where you are in the process. Please write back or if you have decided to do something else or have found the problem then close out this session by clicking on the ACCEPT link. Doing this pays me for my time and advice, which is only part of the deposit. Thank you for contacting Just Answers we appreciate you. If you feel i have gone above and beyond, please consider a bonus!

 

freon

Ask Your Own HVAC Question
Customer reply replied 8 years ago
freon sorry for taking so long to respond, when you would give me a test to run I would have to run to my house each time to do the test and then drive back to work to get back on the computer to respond. but I finally found the problem with your help. It was the wire on terminal Y that had a break in it. thank you for your help and patience with me sometimes these things may take all day to figure outsince I am a rookie at this. I of course will accept your answer thanks again.

Great! Success! Thank you for reporting back to me! I am very happy for you!

 

Please consider a small bonus if you can afford one. it helps balance out the ones that dont pay at all! We are very appreciative of you! If you have any other questions please ask! And come back soon!

 

freon

freon
freon, Licensed A/C Contractor
Category: HVAC
Satisfied Customers: 215
Experience: 22 years Licensed Contractor State of Texas
Verified
freon and 87 other HVAC Specialists are ready to help you
Ask your own question now
Customer reply replied 8 years ago
freon where do I add the bonus will it tell me when I click the accept answer button.
yes! just browse around the boxes to find it. Thank you so much.
Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask freon Your Own Question
freon
freon
freon, Licensed A/C Contractor
Category: HVAC
Satisfied Customers: 215
215 Satisfied Customers
Experience: 22 years Licensed Contractor State of Texas

freon is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a trane xe 1100. not starting. ac breaker tested and
hi i have a trane xe 1100. not starting. ac breaker tested and not tripped. what to check? … read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
23,151 satisfied customers
Like would like you opinion. I have an estimate 3.5 ton
Like would like you opinion. I have an estimate for a 3.5 ton Carrier Comfort 14 Central Air Cond (24ACC4) and a Carrier Performace 16 Central Air Cond (24ACC6) and the furnace estimated for both is C… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Central Air - Trane XE 1000 Model # ***** 124B100A0
I have a Central Air - Trane XE 1000 Model # ***** 124B100A0 mfr 7/91 that the condensor fan no longer is spinning. The compressor is running, and I attempted to spin the fan with a stick, but while t… read more
Douglas Feldt
Douglas Feldt
HVAC
27 satisfied customers
My central air conditioner quit cooling last night. The air
My central air conditioner quit cooling last night. The air handler quit cooling but still blows air. I checked the air handler it was not iced over and or the drain was not blocked. Any suggestions o… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Trane technician has serviced my A/C system including replacing
Trane technician has serviced my A/C system including replacing the thermostat and the circuit control board. However, the compressor continues to either "stick" on or off. If on, the compressor runs … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
When I call for ac on my upstairs thermostat it clicks but
When I call for ac on my upstairs thermostat it clicks but doesn't come on. When I call for it on the downstairs thermostat it turns on the outside unit but the clod air only blows downstairs. A very … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
A/C system cooling fine until last night when condenser starting
A/C system cooling fine until last night when condenser starting sounding strange (excessive vibration then abnormal discharge sound) so I shut the AC off. Tried to start it later and there was hum co… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
We are now required to replace both heat pump and air handler
We are now "required" to replace both heat pump and air handler on our residential system because of another change in freon. Furthermore, residential HVACs appear to be designed for obsolescence; for… read more
Heath
Heath
Vocational, Technical or Trade Scho
1,002 satisfied customers
I have a heat pump and it seems the low voltage is wired incorrectly.
I have a heat pump and it seems the low voltage is wired incorrectly. The condensing unit is a HP 26-048-9P and the evap unit is a CB 29M-51-1 (no heat strips in unit, just a heat pump) The red light … read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
ac is cycling off and on about every 20 minutes. the house
ac is cycling off and on about every 20 minutes. the house is not getting cooled down. The outside temp is about 75 degrees. the small line coming out of the condensor unit is ice cold and the larger … read more
Heath
Heath
Vocational, Technical or Trade Scho
1,002 satisfied customers
I replaced my thermostat. It is wired correctly. I have a
I replaced my thermostat. It is wired correctly. I have a trane xe 900. However now it only blows warm air and the compressor outside will not turn on. Is there a reset button I need to push? Reinstal… read more
Tom
Tom
HVAC Technician
Vocational, Technical or Trade Scho
770 satisfied customers
Have a Trane Voyager WCD060 voltage to contactor is 22.6. press
Have a Trane Voyager WCD060 voltage to contactor is 22.6. press contactor compressor comes on with indoor blower evaporator fan does not relay clicks no operation,contactor good any suggestions would … read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
23,151 satisfied customers
I have a Trane Weatherton XE 1100 Heat Pump. Went to turn
I have a Trane Weatherton XE 1100 Heat Pump. Went to turn on the air conditioner this season and the fan on the inside unit comes on and moves air but the outside unit doesn't do anything. I have chec… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a Trane XE 1100. The compressor will not work but the
I have a Trane XE 1100. The compressor will not work but the circulation fan works fine. If I trip the breaker outside I get a "click" and the fan rotates a bit. Please dont tell me I need a new compr… read more
ComfortZone
ComfortZone
Associate Degree
485 satisfied customers
I have a Trane XE 1100 A/C system that is ten years old. The
I have a Trane XE 1100 A/C system that is ten years old. The system works fine but I have noticed lately that after the system achieves the desired temp, the air handler shuts off but the compressor c… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
23,151 satisfied customers
I have a Trane XL split system that is three years old and
I have a Trane XL split system that is three years old and was installed by a reputable HVAC dealer in Tucson. Recently the AC stopped blowing cold air, I had the installer check the coolant pressure … read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
I have a Trane XE 1000 heat pump. Though its about 14-15 years
I have a Trane XE 1000 heat pump. Though it's about 14-15 years old, it's at a vacation home with only a few months use a year (air con mostly). For the last two years when I've opened the house, I've… read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
I have two Trane Weathertron XE 1200 HVAC systems (electric)
I have two Trane Weathertron XE 1200 HVAC systems (electric) - one to heat/cool upstairs, one to heat/cool downstairs. Both units were made in '95 and installed a year later. Upstairs works fine. Down… read more
tom goellner
tom goellner
owner
Vocational, Technical or Trade Scho
1,115 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x