have a carrier rooftop model 48TJE006-601GA, getting fault…

Customer Question
have a carrier rooftop model...
have a carrier rooftop model 48TJE006-601GA, getting fault code of 7 (rollout fault), this is happening without the rollout connected. Upon power up of unit indoor fan comes on and combustion motor runs also, all the time. Thought might be bleeding off power on a coil, replaced compressor contactor and heat relay, tried different board but same thing happens. Economizer is not being used. Any ideas?
Submitted: 8 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 48 minutes by:
6/29/2010
HVAC Technician: Douglas, HVAC Technician replied 8 years ago
Douglas
Douglas, HVAC Technician
Category: HVAC
Satisfied Customers: 3,089
Experience: Manufacture Rep for Major Brand, Technical Trainer, NATE
Verified
Hi, I'm Douglas and I am here to help you resolve problems with your heating and cooling equipment.

I understand the roll out is disconnected.... was it left as an open circuit? (is it bypassed)?
Ask Your Own HVAC Question
Customer reply replied 8 years ago
Installed new rollout not taking care of problem.
HVAC Technician: Douglas, HVAC Technician replied 8 years ago
do you have a volt meter?
Ask Your Own HVAC Question
Customer reply replied 8 years ago
yes
HVAC Technician: Douglas, HVAC Technician replied 8 years ago
ok, let me pull a schematic... on moment.
Ask Your Own HVAC Question
HVAC Technician: Douglas, HVAC Technician replied 8 years ago
So the circuit with the roll out... should be marked on the board as RS terminals. I believe there are blue wires connected there.... can you verify that?
Ask Your Own HVAC Question
HVAC Technician: Douglas, HVAC Technician replied 8 years ago
While I am waiting... lets assume thats what you have. Set your meter to Volts AC and measure from one blue terminal to the other terminal (the ones marked RS) with the wires attached and the power on. Do you read 24v or 0v ?

If you read 24v the circuit is open and it may or may not be the switch. It could be a broken wire or bad terminal at the switch. If you read 0 volts then it is likely the board is bad because of a broken solder terminal or trace on the back of the board.
Ask Your Own HVAC Question
Customer reply replied 8 years ago
we have replaced the board and get the same code, the tech was reading 24 to ground, 0 v across.
HVAC Technician: Douglas, HVAC Technician replied 8 years ago
interesting.... 0 across is closed...

Now Carrier says that's an auto reset rollout but the board will continue to show the fault. They suggest checking the gas valve to validate you dont have a problem with the gas valve grounding or something. If you have a small relay, you can move the wires from the gas valve to the relay coil and cycle the power to reset the fault to see if it faults.
Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Douglas Your Own Question
Douglas
Douglas
Douglas, HVAC Technician
Category: HVAC
Satisfied Customers: 3,089
3,089 Satisfied Customers
Experience: Manufacture Rep for Major Brand, Technical Trainer, NATE

Douglas is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Carrier air conditioner coils freeze. HVAC tech came.
carrier air conditioner coils freeze . HVAC tech came. Everything checked out okay. Capacitor was recently replaced. all electrical currents good. Serviced in the last month. Any suggestions. Tech cou… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
What keeps causing the 5 amp fuse to blow on the Carrier Model
What keeps causing the 5 amp fuse to blow on the Carrier Model 48HJD015---5B1QA Serial 2807U20786?… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
i had a blower cut out on a rootop package unit. motor and
i had a blower cut out on a rootop package unit. motor and capicitor are good. i know this because i pulled the 2 wires going to the fan off the board and hooked directly to the 2 poles of the contact… read more
MattR757
MattR757
HVAC Contractor / Owner
Associate Degree
14 satisfied customers
I have a commercial roof top unit, Carrier model 48TJE006---601GA
I have a commercial roof top unit, Carrier model 48TJE006---601GA S/N 4693G01396. I am having problems with the squirrel cage motor that pushes the air into the building. When i turn the power on the … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Hi, I have a Bryant Heat pump model 213ANA042-A (7 years old).
Hi, I have a Bryant Heat pump model 213ANA042-A (7 years old). Since we moved in about 16 months ago, it seems to sometimes have a hard time starting. A local company looked at it and said it was fine… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Bryant 6 ton rooftop unit model 580cpv072074 that
I have a Bryant 6 ton rooftop unit model 580cpv072074 that does not blow cold. The main blower [squirrel cage] cycles ok however no compessor. The contactor [s] seems to be ok as they move up & down. … read more
Douglas
Douglas
HVAC Technician
Vocational, Technical or Trade Scho
3,089 satisfied customers
Code 87 on my Carrier Infinity 19 seer unit. What is this?
What does code 87 mean on my Carrier Infinity 19 seer unit. It says high contactor open, have no idea what that is.… read more
Tom
Tom
HVAC Technician
Vocational, Technical or Trade Scho
770 satisfied customers
I have a Carrier Weathermaker 8000 Gas Forced Air Upward Flow
I have a Carrier Weathermaker 8000 Gas Forced Air Upward Flow Furnace. Mounted above that is a Carrier Evaporator Coil Unit for the refirigerated air (Model # XXXXX). The house did not come like this,… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
Have a Trane Voyager I have 24v volts to contactor, but no
Have a Trane Voyager: I have 24v volts to contactor, but no 24 volts from board to fan relay. Board has been replaced and also zone sensor.… read more
Bart Jay
Bart Jay
Vocational, Technical or Trade Scho
596 satisfied customers
Have a Trane Voyager WCD060 voltage to contactor is 22.6. press
Have a Trane Voyager WCD060 voltage to contactor is 22.6. press contactor compressor comes on with indoor blower evaporator fan does not relay clicks no operation,contactor good any suggestions would … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Have a Carrier 48tje006 Over the weekends or when the system
Have a Carrier 48tje006 Over the weekends or when the system is set to off we get an (8 Flash) internatl control unit fault. This can be cleared aeach time by going to the roof and powering the unit o… read more
Douglas
Douglas
HVAC Technician
Vocational, Technical or Trade Scho
3,089 satisfied customers
Have an older RUUD unit-inside fan turns on when set to cool,
Have an older RUUD unit-inside fan turns on when set to cool, but outside unit will not start. Contactor has no voltage to engage either fan or compressor; if I manually press down contactor everythin… read more
Jason  Hvac
Jason Hvac
Hvac Tec
Vocational, Technical or Trade Scho
120 satisfied customers
I have a Bryant rooftop combo unit which is missing the service
I have a Bryant rooftop combo unit which is missing the service manual and the heating section is dead. The unit has power and natural gas-- mdl # XXXXX and I am getting 9 flashes on the board. What p… read more
Heath
Heath
Vocational, Technical or Trade Scho
1,002 satisfied customers
I have a carrier model # 58pav070-12. The led light is flashing
I have a carrier model # XXXXX The led light is flashing code 33. I have tried turning the switch off and restarting it, nothing happened. The blower fan just runs constantly, the furnace doesnt even … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
model # XXXXX unit will not operate where is AFF switch
model # XXXXX unit will not operate where is AFF switch located and if it is bad will it cause F1 to blow when IDM is called for ?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My Trane XE 60 runs its blower motor nearly all the time.
My Trane XE 60 runs its blower motor nearly all the time. The thermostat controller is of the multi-function, two stage variety. I have, intermittentantly, being able to cause the blower to turn off b… read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
i have a rheem 10 ton gas pack RRGF200100. The fan contactor
i have a rheem 10 ton gas pack RRGF200100. The fan contactor is not being pulled in , but the compressor comes on and starts the cooling cycle. The switching relay and the fan relay seem to be ok.… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
i have a carrier cassette 40qkx03670340 unit that keeps blowing
i have a carrier cassette 40qkx03670340 unit that keeps blowing the control fuse on pcb,i have checked everything out and cannot find anything wrong with the system.someone suggested that the outdoor … read more
drcool299
drcool299
shop owner
Bachelor\u0027s Degree
22 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x