I have a T7300A1062 and a Q7300B1040 I am replacing it with…

Customer Question
I have a T7300A1062 and...
I have a T7300A1062 and a Q7300B1040 I am replacing it with a Pro 6000. Do I hook up th A1 and A2 wires? and where do I connect them>
Submitted: 8 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 7 minutes by:
6/28/2010
HVAC Technician: Rick Mather, HVAC Technician replied 8 years ago
Rick Mather
Rick Mather, HVAC Technician
Category: HVAC
Satisfied Customers: 3,634
Experience: 35 years experience, HVAC
Verified
Chat Conversation Started
Rick Mather :

That A1 ans A2 is for an economizer control most likely you don't have one that still works

Ask Your Own HVAC Question
HVAC Technician: Rick Mather, HVAC Technician replied 8 years ago
Chat Conversation Ended

If you are still working with your Expert on this question, you can post additional replies and receive additional information on this page.  If you received a satisfactory answer in Chat, you can accept the chat conversation above.
Ask Your Own HVAC Question
HVAC Technician: Rick Mather, HVAC Technician replied 8 years ago

Here is manual for sub base

 

http://customer.honeywell.com/techlit/pdf/62-0000s/62-0098.pdf

Ask Your Own HVAC Question
Customer reply replied 8 years ago

what do i do with the wires that connect to A1 and A2 terminals?

HVAC Technician: Rick Mather, HVAC Technician replied 8 years ago
Well you could make it work with a ice cube relay and use Y1 for the econ, and then bring on cooling with y2 but only if the econ still works other wise cap the wires
Rick Mather
Rick Mather, HVAC Technician
Category: HVAC
Satisfied Customers: 3,634
Experience: 35 years experience, HVAC
Verified
Rick Mather and 87 other HVAC Specialists are ready to help you
Ask your own question now
Customer reply replied 8 years ago
we did cap the wires but the cooling did not come on. The tstat timed out on the delay but did not energize the contactor. I think there must be something else wrong the wiring or the programing with the new tstat. Thanks for your help.
HVAC Technician: Rick Mather, HVAC Technician replied 8 years ago
Well the old wiring was in the link for the a1 and a2 but just be sure your wiring is correct and the program for the correct system
Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Rick Mather Your Own Question
Rick Mather
Rick Mather
Rick Mather, HVAC Technician
Category: HVAC
Satisfied Customers: 3,634
3,634 Satisfied Customers
Experience: 35 years experience, HVAC

Rick Mather is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,634 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Im trying to replace a t7300d2007 thermostat with honeywell
im trying to replace a t7300d2007 thermostat with honeywell rht7560e but the wire codes on the terminals dont match can you help? … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Can I replace a Honeywell T7300F2010 thermostat with a
Can I replace a Honeywell T7300F2010 thermostat with a Honeywell RTH2300? … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My name is ***** *****. I am replacing a rheem contactor
Hi, my name is ***** *****. I am replacing a rheem contactor 42-420044-02 with 42-25101-01. all the connections are straightforward except for the low voltage wires. Do I connect the same color (yello… read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
463 satisfied customers
I have a new honeywell focuspro 6000 thermostat, I hooked up
I hooked up the R, Y, C, W, G wires... only wire not plugged in is orange. Schematic doesn't show it needing to be hooked up. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Rick. I have an EK1 with an old Rodgers 1145-42. My blower
Customer: Hi Rick. I have an EK1 with an old white Rodgers 1145-42. My blower does not work in 'auto' mode so I was looking for a fan limit switch. The WR doesn't look like it, so I checked the voltag… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
Replacing a rheem contactor 42-42728-02 with 42-25101-01. moved all connections in strai
replacing a rheem contactor 42-42728-02 with 42-25101-01. moved all connections in straight order, and A1, A2 with yellow and Tan respectively. but only turns on if I hold down the button in the cente… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Hear-N-Glo 6000 fireplace where the pilot stays on
I have a Hear-N-Glo 6000 fireplace where the pilot stays on but the burner will not come on. I measured 425 mv at the theropile unconnected and connected to the valve. I have tapped the valve assembly… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I HAVE A HONEYWELL FOCUS PRO 6000 TH6220D1002 . WANT TO HOOK
I HAVE A HONEYWELL FOCUS PRO 6000 TH6220D1002 . WANT TO HOOK IT UP A GOODMAN GMVC950704CX 2 STAGE FURNACE SINGLE STAGE AIR 4 WIRES WHERE DO I PUT THE WIRES ON BOTH WIRE COLORS ARE BLUE, RED, WHITE, GR… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
hey have a TH 6000 series thermostat on a heat pump. What terminal
hey have a TH 6000 series thermostat on a heat pump. What terminal to hook up for defrost control… read more
ComfortZone
ComfortZone
Associate Degree
485 satisfied customers
I bought a Honeywell Focus Pro 6000 thermostat (2 heat, 2 cool
I bought a Honeywell Focus Pro 6000 thermostat (2 heat, 2 cool conventional). I want to hook it to my RV which has hi and low switch for the fan. The blue wire was to the hi fan and the orange wire wa… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I aslo have a 3AAT82B32A2 Thermostat and like to convert it
I aslo have a 3AAT82B32A2 Thermostat and like to convert it to a honneywell PRO 6000 Thermo but dont know about the wiring connections thanks Joe… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
My church has a Honeywell T7300F series 2000 thermostat with
My church has a Honeywell T7300F series 2000 thermostat with a Q7300A Subbase. The thermostat is used only in a hot water heating system. The primary heat source is hot water circulated through radiat… read more
Bart Jay
Bart Jay
Vocational, Technical or Trade Scho
596 satisfied customers
Frozen condensate.Worcester- bosch greenstar 24Ri.Wish to fit
Frozen condensate.Worcester- bosch greenstar 24Ri.Wish to fit Sauermann SI1820 condensate pump.Need advice where best to connect electrics (including blockage cut out switch)on pump to boiler.… read more
Rick Ridley
Rick Ridley
UK Heating Engineer
30 years on the tools
871 satisfied customers
What is difference between RHEEM RCHJ-48A1G and RHEEM RCHJ-48A2G
What is difference between RHEEM RCHJ-48A1G and RHEEM RCHJ-48A2G ? I cannot seem to find any information on internet and Rheem has not contact information, we have to go through their distributors who… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
What are the functions of the A2 and RH wires on an Intertherm
What are the functions of the A2 and RH wires on an Intertherm thermostat and where would they connect on a Honeywell RTH 7600 thermostat?… read more
Mike
Mike
Service Tech/ Installer
High School or GED
149 satisfied customers
Have purchased a RTH3100c thermostat. Am replacing a Robertshaw
Have purchased a RTH3100c thermostat. Am replacing a Robertshaw thermostat. I have one wire idetified as "A1" with no reference to on new Honeywell- please advise- This wire was associated with "Heat-… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I just moved a thermostat......it is a Vision Pro TH 8000 series,
I just moved a thermostat......it is a Vision Pro TH 8000 series, TH8320U1008......0636 I messed up the wires.....can you give me the correct sequence and colors to hook up the wires correctly. Also m… read more
Jack Pearce
Jack Pearce
Vocational, Technical or Trade Scho
9 satisfied customers
Can I use a Honeywell pro 6000 to replace a Trane BAYSENSOO6B
Can I use a Honeywell pro 6000 to replace a Trane BAYSENSOO6B T-STAT and if I can,t what do the 1,2,3,4 trmanals on the Trane T-STAT go to (R,W,Y,G)?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x