Newly installed Goodman 2 1/2 ton split heat pump. Air handler…

Customer Question
Newly installed Goodman 2 1/2...
Newly installed Goodman 2 1/2 ton split heat pump. Air handler is in attic 20" vertical above outside unit, 47' total line set footage run on a 45 degree slope up the side of the house into the attic. 2.1 ounces of freon added to system to compensate for extra line set footage. high side pressure will no go above 185, low side pressure is 85. outside temp is 95 degrees, return air temp at unit is 80 degrees, supply temp at ceiling registers is 65 degrees Orfice is in correct position as shown on sticker on front of unit with nozzle and teflon ring facing away from air handler. What is my proble?
Submitted: 8 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 4 minutes by:
6/27/2010
HVAC Technician: Richard, Technical Manager replied 8 years ago
Richard
Richard, Technical Manager
Category: HVAC
Satisfied Customers: 1,514
Experience: 27 years of Experience, NATE Certified, professional trainer
Verified
Chat Conversation Started
Richard :

Hello well at first glance it would seem the orifice might be bleeding by ( low high side and hi low side) but take the temperature of the lines at the coil and at the unit. This way we can look at super heat and sub cool. We will probably find that your low on charge with a high load. Also, air flow is critical. Do you know or can you measure the CFM you need 1000 or close for the charging charts to be accurate.

Customer:

cannot measure cfm @ return air grill. return is supplied with a 20x25 filter grill with 12 ' of 16" flex going into a 5' piece of 18X8 rectangle duct on intake of airt handler. suction line temp 60 degrees high side temp 89 degrees both taken @ condensing unit

Richard :

R22?

Richard :

If this is a 22 unit you have 10 degrees of SH and 6 degrees of SC. A few things your going to need to consider. I am assuming this has a PSC motor. 16inch flex will give you 1100 cfm @ a .1 friction rate this is to high for return supply you can design at a .1 but return you need to .05 today in the old days it was a .08. @ a .05 your only going to move about 750 CFM and at a .08 about 800. This is not to far off but it all adds up. You have to keep in mind what we did before 2006 is different that coil has a .3 to .35 drop on it now. The SH, with a 95 outdoor and a 80 indoor I am going to guess here but you probably have around a 73 wet bulb indoor which would put you SH around 25 degrees to be normal. so your low. This really doesn't add up, from this infor you have a low load and under charge. So next step what is the temp of the hot gas line coming off the compressor ? also, verify the temp of the liquid line if it is lower than the outdoor temp you have a restricted condensing coil or non condensables in the coil. Did you use a pump to pump it down?

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Richard Your Own Question
Richard
Richard
Richard, Technical Manager
Category: HVAC
Satisfied Customers: 1,514
1,514 Satisfied Customers
Experience: 27 years of Experience, NATE Certified, professional trainer

Richard is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a Carrier model # 38TKB024300 App 19 years old. My
HI I have a Carrier model # 38TKB024300 App 19 years old. My problem is the air conditioner works fine form 10 PM until 12- 1 pm in the afternoon the temperature out of the registers are about 59- 65 … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Lennox XC-16 makes loud momentary noise that sings through
Lennox XC-16 makes loud momentary noise that sings through line set on start up, almost like water hammer. A new air handler installed with unit. Air handler in attic, unit outside on ground floor. Li… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have Goodman Heat pump that was recently installed. There
I have Goodman Heat pump that was recently installed. There was a leak that was fixed, and in the process of adding refrigerant. The suction psi was around 214 & the liquid pressure was around 255 psi… read more
joeydelia
joeydelia
HVAC-R Tech
High School or GED
81 satisfied customers
What should the high side and low side psi be on my split
What should the high side and low side psi be on my split system? I have two separate units for two separate zones and one appears 120 psi on both hi and low gauges. Am I reading it correct? This unit… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a trane package unit suction 85 psi and line temp 65
I have a trane package unit suction 85 psi and line temp 65 degree. High side 370 psi and 175 degree on r22, what happened?… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Hello, I'd like some expert advise on the installation of a new line set. I have a s
Hello, I'd like some expert advise on the installation of a new line set. I have a split system 3 Ton 18 Seer Goodman Heat Pump System DSZC180361 - AVPTC31371, and the line set is 3/8 inch and 7/8 inc… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I was working on a Temp Star 2 ton heat pump/ Air Handler.
I was working on a Temp Star 2 ton heat pump/ Air Handler. No TXV, is was a piston coil. The Temp. of the coil was 85 degrees. I went outside to the heat pump and fan motor was running. So I unplugged… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I installed a new Grand Aire (Baker Dist.) 3 1/2 split system
I installed a new Grand Aire (Baker Dist.) 3 1/2 split system that had the condenser pre-charged with 410a. But we had to add an additional 29 feet of line set to relocate the condenser (per the custo… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I also have a Goodman ARUF024 unit and live in an Efficiency
I also have a Goodman ARUF024 unit and live in an Efficiency Condo on the Top floor. The unit cools at night very well but after 1pm on a 85 or higher degree day it only can reach 85 degrees inside. I… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a ultra 5 tech 80 air handler, an older carrier unit
I have a ultra 5 tech 80 air handler, an older carrier unit outside, guages reading "r-22" 50 deg on the low side and 275lbs on the high side, the condensor line is "cold" on the low side all the way … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
Had the large insulated line freeze up and tech came to add
Had the large insulated line freeze up and tech came to add r22 freon. I'm not sure if the tech purged the air from the lines (the blue and red ones,I'm pretty sure he bled the freon line) when he add… read more
Appliance Tech Larry
Appliance Tech Larry
Outside inhome service tech
High School or GED
19,156 satisfied customers
I am fixing up a foreclosure. Bought a new Lennox XP14 1 1/2
I am fixing up a foreclosure. Bought a new Lennox XP14 1 1/2 ton heat pump scratch & dent. Also bought new line set and Goodman air handler 1 1/2 ton. I had to have it installed on a Sunday, so my ins… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
13 seer gsx13024a r 401a coolint installed july 2011 from frist
13 seer gsx13024a r 401a coolint installed july 2011 from frist day unit works great but in high temp outside 85 degrees and above unit made a noise every 20 secounds lo temps outside below 80-85 no n… read more
Richard
Richard
Technical Manager
Vocational, Technical or Trade Scho
1,514 satisfied customers
I installed a 2 ton 13 seer R-410 goodman heatpump condenser
I installed a 2 ton 13 seer R-410 goodman heatpump condenser on a 2.5 ton air handler. Used original lineset but flushed and cleaned lines very good. Square footage is a little under 1200. System is n… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have just installed a 2.5 ton rheem condenser and air handler,
I have just installed a 2.5 ton rheem condenser and air handler, pressure checked the refrigerant lines for leaks, vacuumed the lines and cracked the valves on the high and low side for the refrigeran… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
Hi,I am doing a start up on a unit i installed in the winter
Hi,I am doing a start up on a unit i installed in the winter time.It is a 2 ton goodman condenser.put 150 pounds of nitrogen ,vaccumed it to 500 microns,and then started it up.pressure's i read where … read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
HVAC SYSTEM OVERWHELMED BY AUSTIN TX HEAT OR A STICKING REVERSING
HVAC SYSTEM OVERWHELMED BY AUSTIN TX HEAT OR A "STICKING" REVERSING VALVE ON HEAT PUMP? My return air vent and the closest insulated supply vent do not go thru the attic and are 7 feet apart. Attic's … read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
hello, its 74 degrees outside, what should the low side pressure
hello, it's 74 degrees outside, what should the low side pressure be on my rheem central a/c unit ?… read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x