Customer Question
contactor not coming in on...
contactor not coming in on 38en carrier outside a/c unit. Transformer 115v to 24 volt fine. voltage 29.9volts good at red wire to ground in thermostat...but no voltage to coil on contactor at ofm and compressor contactor. Pressing contactor will run unit.
Submitted: 8 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 8 minutes by:
6/27/2010
HVAC Technician: Mr. Jeff Pearson, Mechanical Engineering Technologist replied 8 years ago
Mr. Jeff Pearson
Mr. Jeff Pearson, Mechanical Engineering Technologist
Category: HVAC
Satisfied Customers: 155
Experience: 25 years as Refrigeration Contractor,
Verified

Hi, I would be happy to help a customer that has and uses a voltage meter.

 

Did you open any access panels on the furnace,? like to change an air filter?,

Ask Your Own HVAC Question
HVAC Technician: Mr. Jeff Pearson, Mechanical Engineering Technologist replied 8 years ago

 

Then there must be a open section of wire between the stat and the outdoor unit, or the stat is bad.

 

Did some wires get damaged outside? Follow the wires from the condenser to the furnace inside, and check for broken wires.

 

Remove the low voltage wires from the main contactor coil. With everything else set to run check for voltage of 24 volts. Now switch your meter to OHMS and place your leads on each side of the contactor coil. What is the reading of resistance through the coil?

 

What is the measured voltage between the two wires going to the contactor coil when they are not attached to the coil?

Ask Your Own HVAC Question
Customer reply replied 8 years ago
zero volts when not conectted to coil. 18.1 ohms on coil.
HVAC Technician: Mr. Jeff Pearson, Mechanical Engineering Technologist replied 8 years ago
Did you just check between the two wires or did you check each one to ground?
Ask Your Own HVAC Question
Customer reply replied 8 years ago
btwn two wires not to ground.
HVAC Technician: Mr. Jeff Pearson, Mechanical Engineering Technologist replied 8 years ago
Check both to ground please. Do you have a furnace inside the house?
Ask Your Own HVAC Question
Customer reply replied 8 years ago
yes furnace inside. 1.6 volts to ground on each wire.
HVAC Technician: Mr. Jeff Pearson, Mechanical Engineering Technologist replied 8 years ago
Please go to the furnace and pop off the cover plate so you can have access to the control circuit board.
Ask Your Own HVAC Question
Customer reply replied 8 years ago
ok...what now?
HVAC Technician: Mr. Jeff Pearson, Mechanical Engineering Technologist replied 8 years ago
Remove the two wires that go out to the condenser. Should be one on the yellow terminal and one on the c terminal. But they are usually red and wht in color
Ask Your Own HVAC Question
HVAC Technician: Mr. Jeff Pearson, Mechanical Engineering Technologist replied 8 years ago

Did you locate the two wires? Good, now twist them together with a wire nut.

 

Now go back outside to the condenser. The two wires you just checked for voltage 10 minutes ago, check for resistance, using the Ohms settings. check ohms between two wires.?????

Ask Your Own HVAC Question
Customer reply replied 8 years ago

18.1 ohms

HVAC Technician: Mr. Jeff Pearson, Mechanical Engineering Technologist replied 8 years ago

18 ohms is too much resistance to have in those wires. How long are the wires? That set of wires needs to be replaced. There should be a max of 3 ohms in the two wires.

 

Get yourself some 18 gage solid core wire an replace the two wires that go from the furnace to the contactor.

Ask Your Own HVAC Question
Customer reply replied 8 years ago
why are wires going from furnace to contactor for A/C?
Customer reply replied 8 years ago

I have 18 guage..but not solid strand to replace wires with. I have already run wires to unit and having difficulty with hook ups. Y or yellow terminal and BC terminal to contactor from furnace???? right?

HVAC Technician: Mr. Jeff Pearson, Mechanical Engineering Technologist replied 8 years ago

Because the control board in the furnace tells the ac to turn on and off, and the furnace blows the air around in the house

 

 

 

While you have the furnace open, do you see the safety door switch that the cover presses in when the door in put on correctly?

 

Put your thermostat back together and set it so its trying to get the a/c going. Now go to the furnace and get ready to read the voltage between terminal "Y" and "C".

 

You will need to hold in the safety switch I mentioned earlier. And allow five minutes for the time delay,

Ask Your Own HVAC Question
HVAC Technician: Mr. Jeff Pearson, Mechanical Engineering Technologist replied 8 years ago

Yes from furnace "Y" terminal and "C" Terminal to the contactor.

 

 

Ask Your Own HVAC Question
Customer reply replied 8 years ago
ok
HVAC Technician: Mr. Jeff Pearson, Mechanical Engineering Technologist replied 8 years ago
let me know when done
Ask Your Own HVAC Question
Customer reply replied 8 years ago
zero volts between y terminal and BC on furnace. Transformer and controls outside of furnace. panel does not need to be opened. I know about safety switch from opening panel before. time delay not issue.....was running already.
HVAC Technician: Mr. Jeff Pearson, Mechanical Engineering Technologist replied 8 years ago

And from "R" to ground???volts???

Ask Your Own HVAC Question
Customer reply replied 8 years ago
was 30 volts yesterday at r and G. Now zero. I think I blew transformer trying to run new wires. but still was not pulling in coil on contactor yesterday before that happened today. transformer blue and yellow 24 to 30 volts and R and G 30 volts...yesterday.
Customer reply replied 8 years ago
I connected wire to R and C to run to contactor. Smelled burned wire covering a bit.
Customer reply replied 8 years ago
what do you think? Blown transformer? Thermostat damage now maybe? tired and hot?
HVAC Technician: Mr. Jeff Pearson, Mechanical Engineering Technologist replied 8 years ago

 

 

0.00751 Ohms per foot of 18 gage wire. Even if your run was 100 feet from furnace to outdoor condenser, that would be 200 x 0.0075 = 1.5 ohms.

 

The wiring was your problem, now you just need to replace the burned transformer and run the new wires, this time unplug furnace when working on the wires.

 

Sory its taking so long, if I could I would drive over to your place and fix it all up for you.

 

When you hooked the R" and "C" to the contactor, did you use the new wires?



Edited by Mr. Jeff Pearson on 6/27/2010 at 7:17 PM EST
Ask Your Own HVAC Question
HVAC Technician: Mr. Jeff Pearson, Mechanical Engineering Technologist replied 8 years ago

 

It is the "Y" and "C" that are supposed to go to the contactor.

Ask Your Own HVAC Question
HVAC Technician: Mr. Jeff Pearson, Mechanical Engineering Technologist replied 8 years ago
I will be back in60 minutes
Ask Your Own HVAC Question
Customer reply replied 8 years ago
Not what the problem is. I bought a new transformer and ran the 18 gauge wires to contactor. Still no voltage...with wires off the contactor or not. I check voltage from 24 volt side of contactor and 24 volts there. 24 Volts at wires on control panel. Wire nutted both sets of wires directly together...still no voltage. There must be a short in relay or other wire somewhere else. I give up. I also replaced thermostat prior to this. Set in cool mode at 65 degrees and 90 degrees in house. air handler fan running...not shutting off..... Relay bad....but should not keep a/c from coming on as it should.
HVAC Technician: Mr. Jeff Pearson, Mechanical Engineering Technologist replied 8 years ago

I am sorry we have not made progress fixing your ac .

 

I don't understand, you say there is power at the control board, at the "Y" and "C" terminals, but you connect the new lines to them and there is no power at the other end?

Ask Your Own HVAC Question
Customer reply replied 8 years ago
exactly, short in the other wires. Can HVAC repair today.
HVAC Technician: Mr. Jeff Pearson, Mechanical Engineering Technologist replied 8 years ago
could you please let me know what they find?
Ask Your Own HVAC Question
Customer reply replied 8 years ago
Yes, I know the relay is bad. I think some of the connections are bad. Obviously there is a short somewhere.
HVAC Technician: Mr. Jeff Pearson, Mechanical Engineering Technologist replied 8 years ago
Often the wires running to the outdoor unit get damaged by lawn mowers, weed wackers , etc. Could this be the case?
Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Mr. Jeff Pearson Your Own Question
Mr. Jeff Pearson
Mr. Jeff Pearson
Mr. Jeff Pearson, Mechanical Engineering Technologist
Category: HVAC
Satisfied Customers: 155
155 Satisfied Customers
Experience: 25 years as Refrigeration Contractor,

Mr. Jeff Pearson is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Pearl, I have replaced a transformer on an old (25+ years)
Hi Pearl, I have replaced a transformer on an old (25+ years) carrier unit after tracking down the bad one. Now, I have power at the thermostat and all connections. Blower motor comes on when in fan o… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
I have a goodman pc048-1 stand alone ac unit.Worked fine last
I have a goodman pc048-1 stand alone ac unit.Worked fine last year.This year only the evap fan comes on when you turn the tstat to ac.The compressor and the cond.fan neither one come on.I pulled the s… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a goodman gph1336h41ca that will not call for the contacts
I have a goodman gph1336h41ca that will not call for the contacts to make connection i have 24 volts coming out of the transformer and i have 24 volts at the thermostat and when i take the purple wire… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I have a trane xe80 with a trane xe1000 ac compressor. On a
I have a trane xe80 with a trane xe1000 ac compressor. On a call to cool, the compressor doesn't start. inside blower runs fine. When you manually push in the contactor, the compressor kicks in fine a… read more
Expert
Expert
Hi, I just installed a honeywell touch screen thermostat and
Hi, I just installed a honeywell touch screen thermostat and the heat runs fine and the blower ran fine but then I wired in the condenser to the Y & C and every time it switches to cool it resets or g… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
Is the circuit board bad in my Rheem RPML-048JAZ compressor?
Is the circuit board bad in my Rheem RPML-048JAZ compressor? Symptoms are as follows: air handler fan starts at proper room temperature setting; compressor 5 minute delay expires; compressor does not … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Carrier 58 RAV air handler and "had" a Honeywell Chronotherm
I have a Carrier 58 RAV air handler and "had" a Honeywell Chronotherm III t-stat. THe contactor went bad so I replaced it and the 3 amp fuse. WHen I applied power, the t-stat burned up. I replaced it … read more
mranswer
mranswer
TECHNICIAN
Bachelor's Degree
481 satisfied customers
I have heat pump condesor with 28v going to the defrost board
I have heat pump condesor with 28v going to the defrost board but the condenser will not come on in either heat or cooling mode… read more
mranswer
mranswer
TECHNICIAN
Bachelor's Degree
481 satisfied customers
Hello i am having a problem with a Mcquay spit unit. The
Hello i am having a problem with a Mcquay spit unit. The compressor is a CLJ18 and the interior unit is mwm020FkFAC. The a/c stop cooling, but the evaporator was working. I check the compressor that i… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Carrier Infinity 58MVP that started having issues
I have a Carrier Infinity 58MVP that started having issues with the 24v system today. I found a loose W wire going to my thermostadt when my AC turned off today. When I went to the furnace, I found th… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I have two Carrier heat pumps (Clipper models mfgd Apr 1984
I have two Carrier heat pumps (Clipper models mfg'd Apr 1984 - round cylinder shape) Downstair unit which is linked with a Carrier oil furnace blew a ceramite starter capacitor and triped off the indo… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Hi, I have a Rheem RGRA Series Classic Series 90 Plus Upflow
Hi, I have a Rheem RGRA Series Classic® Series 90 Plus® Upflow Gas Furnace, which is about ten years old. For about a year it would blow the fuse coming off the red wire at 24 volts of the transformer… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
have a 2ton comfort maker, contactor will not pull in, getting
have a 2ton comfort maker, contactor will not pull in, getting 24 volts to contactor, replaced contactor, getting 240 to contactor, can push contactor in, and condesor fan comes on, dont know if compr… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
Outdoor a/c unit not working Model 10 acc-024-230-02 , conductor
Outdoor a/c unit not working Model 10 acc-024-230-02 , conductor relay just clicks and there is 22 volts available. Indoor fan keeps running with thermostat connected , digital display fading disappea… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a Model #38YCC048-301, SN #2901E25036 Carrier Heat Pump.
I have a Model #38YCC048-301, SN #2901E25036 Carrier Heat Pump. I was away on business for a week and shut it off completely. When I returned I energized the entire system, ie: Breakers, etc. The ther… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
my outside fan does not come on and the air coming out of the
my outside fan does not come on and the air coming out of the vents is colder or the same as the intake air. I checked it with a thermometer.I checked a/c volts ok at fuses for outside unit. what do y… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
Amana Temp Assure Heat Pump, model RHA36C2C, mfg P1256009C.
Amana Temp Assure Heat Pump, model RHA36C2C, mfg P1256009C. AC & heat will not come on. I hear the indoor thermostat click trying to activate the unit. If I ago outside, I hear the reversing valve cli… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
How do we hook up 2007 Coleman Compressor (dog chewed wires)
How do we rewire Coleman AC outside unit (TCDG series) - dog chewed wires (blue wires)that connect to older Carrier unit wires? Only red and white wires appear to have been connected to the 2 blue wir… read more
JBM HVAC
JBM HVAC
HVAC/R Technician
Vocational, Technical or Trade Scho
50 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x