i had a repairman change my contactors and capacator inside…

Customer Question
i had a repairman change...
i had a repairman change my contactors and capacator inside my ac unit because he said the contacts were burnt and the capacator was old. After he changed them my compressor began kicking on and off. It takes all day to cool off my house because the compressor don't run long enough to cool good. He said its because the compressor is getting old but it never did this before he changed the parts. It was running good and could cool off my house very rapidly. Could he have put the wrong contacts or capacator in to make it do this? I asked this question earlier and forgot to but my email address in so i hope i am not charged twice. The unit is about 18 years old but still was working very good. The voltage on the compressor says 270 / 208 but on the capacator it says 370 volts. These should be the same correct?
Submitted: 8 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 5 minutes by:
6/27/2010
HVAC Technician: Mr. Jeff Pearson, Mechanical Engineering Technologist replied 8 years ago
Mr. Jeff Pearson
Mr. Jeff Pearson, Mechanical Engineering Technologist
Category: HVAC
Satisfied Customers: 155
Experience: 25 years as Refrigeration Contractor,
Verified
Chat Conversation Started
Ask Your Own HVAC Question
HVAC Technician: Mr. Jeff Pearson, Mechanical Engineering Technologist replied 8 years ago

The voltages are referring to different types of voltages and do not need to be the same. Each compressor however needs to have it correct capacitor in order to work properly. The type and size of the capacitor is described by the numbers that are in this form,;

45uf-370volt or 470volt what does the one in there now say? And what is the model number of the compressor? Look for this form, "AV123RT-029-17" OR "55528-EXN"

also get the condensing unit make and model number. Then I will tell you what size cap should be in there.

Jeff P

Ask Your Own HVAC Question
Customer reply replied 8 years ago

Dont think i can get make and model cause its old and hard to read also i have to get inside outdoor unit to see the info plate. The voltages were marked on the top so i just looked through the fan housing. I will try.

HVAC Technician: Mr. Jeff Pearson, Mechanical Engineering Technologist replied 8 years ago
It is very important that you get at least the numbers off the compressor. You should only have to take a few screws out to get the cover off. The compressor numbers are usually on the top of the compressor and stamped in or on a plate. If you can do that I'll do the rest. The wrong cap in your compressor could cause it permanent damage.
Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Mr. Jeff Pearson Your Own Question
Mr. Jeff Pearson
Mr. Jeff Pearson
Mr. Jeff Pearson, Mechanical Engineering Technologist
Category: HVAC
Satisfied Customers: 155
155 Satisfied Customers
Experience: 25 years as Refrigeration Contractor,

Mr. Jeff Pearson is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Rheem RAKA-048JAZ won't kick on after main power was turned
Rheem RAKA-048JAZ won't kick on after main power was turned off. No reset button on condenser unit. Tried raising temperature and turning breaker off, waited 30 min, still won't come back on. Any idea… read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
463 satisfied customers
Kenmore Heil-tempstar heatpump #867.801121.... changed
Kenmore Heil-tempstar heatpump #867.801121.... changed contactor (1 pole 208-230v,,, house stat is in off postion....disconnected low voltage wiring from the heat pump period (from house stat to heat … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Hello what would be a replacement unit for an old York RTU
Hello what would be a replacement unit for an old York RTU Model # XXXXX Specs as follows: Gas Heating Capacity: 275 MBH Cooling Capacity: 127 MBH Electrical: 208/3/60… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
Hi. I have a 2007 Rheem 13 SEER R 22 Heat pump / AC unit.
Hi. I have a 2007 Rheem 13 SEER R 22 Heat pump / AC unit. Last year (2001) it wasn't keeping up with cooling when we turned on in the spring. We called a contractor who came out and re-charged the sys… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Goodman CK49-18 HVAC. Is about 9 years old. ABout
I have a Goodman CK49-18 HVAC. Is about 9 years old. ABout 2 years ago the capacitor blew. The serviceman came out, replaced the capacitor, said that the compressor was taking a lot or energy to fire … read more
Wvfan79
Wvfan79
Mecanical Designer & Estimator
High School or GED
775 satisfied customers
So, now we need to address the burnt contacts, etc. Do you
So, now we need to address the burnt contacts, etc. Do you have any recommendation, or is this a normal condition. Also, as long as we have you, one of our registers has a lot of dust/dirt on the ceil… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
i need for a fujitsu general 24000 btu air conditioner model
i need for a fujitsu general 24000 btu air conditioner model a0g24aba serial # XXXXX 024099 the contractor and the capacitor please advise what i have to buy and where and if i can not acquire the ori… read more
drcool299
drcool299
shop owner
Bachelor\u0027s Degree
22 satisfied customers
Air conditioner quit working overnight. Compressor on outside
Air conditioner quit working overnight. Compressor on outside unit is not running. Cooling fan on unit is running. Contactor was replaced last year and a small charge was given to the unit. Where do I… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
I have a RUUD Achiever, 2006 model UAND 042JBZ. I cleaned it
I have a RUUD Achiever, 2006 model UAND 042JBZ. I cleaned it up today since it's been working hard with the 100 degree plus temps. here in Oklahoma City. After I got everything put back together, the … read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
how would i know the tech is telling the truth that the contactor
how would i know the tech is telling the truth that the contactor needs to be replaced. the compressor was not coming on and he had replaced the condensor 4 weeks ago. now he says the condensor blew a… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
My air handler is running and the fans is blowing inside, but
My air handler is running and the fans is blowing inside, but the compressor and fan outside are not. I can hear the power trying to engage the compressor but it is not kicking on… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
i had a repairman replace the contacts and capacator on my
i had a repairman replace the contacts and capacator on my ac unit and now the compressor keeps kicking on and off which it never did before he changed the parts. It takes all day to keep my house coo… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
My compressor wont stay on and we have replaced the kickstart
My compressor wont stay on and we have replaced the kickstart and the start capacitor. Do you have any idea as to whats the matter it?… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
compressor contactor burnt out. Purchased contactor 30amp 24v
compressor contactor burnt out. Purchased contactor 30amp 24v coil compressor fan will not start. What size contactor do i need. Service to compressor 208/230 control circuit from thermostat 24v… read more
Jason  Hvac
Jason Hvac
Hvac Tec
Vocational, Technical or Trade Scho
120 satisfied customers
Trane XL 1200 WCX024G does not cool, fan rans all the time,
Trane XL 1200 WCX024G: does not cool, fan rans all the time, the LED blinks once a second. I checked capacitors, cleaned electrical braker's contacts from oxides and checked the braker's coils. The do… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a Trane heat pump that is almost 22 years old. Have
I have a Trane heat pump that is almost 22 years old. Have never had a problem until recently when the compressor started running even though turned off at the thermostat. Once running, the unit would… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
I have a Rheem Central Air Conditioner purchased in 1994-model
I have a Rheem Central Air Conditioner purchased in 1994-model RAKA-036JAZ. Yesterday, I had a repairman come and clean it-it has been working for the past two months with no problems. He said contact… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
I have a Ruud condensing unit manufactured in 1/95 model UAKA-037JAZ.
I have a Ruud condensing unit manufactured in 1/95 model UAKA-037JAZ. The system sopped cooling the other day after being turned off for several days. Blower was running but no cooling. Called local t… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x