GLOWWORM 18SXI PUMP STOPS AFTER BOILER REACHES TEMP. PUMP STAYS…

Customer Question
GLOWWORM 18SXI PUMP STOPS AFTER...
GLOWWORM 18SXI PUMP STOPS AFTER BOILER REACHES TEMP. PUMP STAYS OFF BOILER FIRES AND OVERHEATS.PHONE GLOWWORM TEC LINE, FITTED MAIN PCB & SMALLER PCB.STILL HAVE SAME FAULT
Submitted: 8 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 4 hours by:
6/27/2010
HVAC Technician: Phil, Mechanical Engineer replied 8 years ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,798
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified
Chat Conversation Started
Phil :

Hello

Phil :

Thats tricky... those were worthy tries with the PCB board etc. Next item on the suspect list is the flow switch... the boiler should no come on unless there is water flow either DHW or the space heating section. Locate the flow switch, let me know if you have a multi meter to check it with, or are handy around electricity... we have several options regardless you skill set etc ...

Customer:

TWO PORT VALVE STILL OPEN ,STILL CALLING,PUMP SHOULD NOT BE OFF,WHAT WOULD SWITCH PUMP OFF. 230VOLTS STILL AT PUMP TERMINALS,I UNDERSTAND GLOWWORM SWITCH NEUTRAL SUPPLY TO STOP PUMP IF SYSTEM SATISFIED,BUT IT IS NOT. CAN RESTART BOILER BY RESETTING OVERHEAT STAT AND PUMP WILL RUN,BUT WILL HEAT TO TEMP,PUMP WILL RUN AS IF ON PUMP OVER RUN THEN STOP.BOILER WILL FIRE (TWO PORT STILL CALLING PUMP SHOULD BE ON BUT NOT, WILL THEN OVER HEAT)WOULD FLOW SWITCH TURN OFF PUMP WITH TWO PORT OPEN AND STILL CALLING.

Customer:

TWO PORT VALVE STILL OPEN,STILL CALLING, PUMP SHOULD NOT BE OFF,WHAT WOULD SWITCH PUMP OFF. 230VOLTS STILL AT PUMP TERMINALS, I UNDERSTAND GLOWWORM SWITCH NEUTRAL SUPPLY TO STOP PUMP IF SYSTEM SATISFIED, BUT IT IS NOT DHW STILL CALLING. CAN RESTART BOILER BY RESETTING OVERHEAT STAT PUMP WILL RUN AND BOILER FIRE.BOILER WILL RUN UNTILL TEMP SATISFIED GAS SHUTS DOWN, PUMP WILL RUN AS IF ON PUMP OVER RUN THEN WILL STOP, TWO VALVE STILL OPEN & CALLING PUMP SHOULD BE ON BUT NOT,BOILER WILL FIRE AND GO OFF VIA OVERHEAT STAT.WOULD FLOW SWITCH TURN OFF PUMP WITH TWO PORT OPEN AND STILL CALLING

Phil :

Hello again, if there is 230 volts at the pump terminals, and its a 230volt pump, the pump would be running uniess it or its capacitor arragement were defective...

Phil :

have you checked the capacitor and start winding switch on the pump motor?

Customer:

SORRY BOILER DOES NOT HAVE FLOW SWITCH. THE PUMP IS OK,GLOWWORM SWITCH NEUTRAL TO STOP PUMP. I HAVE BEEN IN TRADE SINCE 1963. WILL BE GOING BACK TO BOILER TO CHECK CONSUMER INTERFACE

Phil :

Hello again. I will opt out, please do not click the accept button. hopefully another expert here will pick this up, or you will figure it out youself.

Customer:

THANK U ANYWAY ALL THE BEST

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,798
9,798 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,798 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I Have a Potterton 28i combi Boiler about 12 years old When
Hi I Have a Potterton 28i combi Boiler about 12 years old When I switch on the blr I get a red fault light indicating no flow or pump faulty,The water pressure is reading 1.5 bar Although there is pow… read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
463 satisfied customers
We have an older oil burner. Just recently, it began to run
We have an older oil burner. Just recently, it began to run until thermostat reaches the proper temp and then shuts off as normal. In order to start it again, it needs to be bled. Then it will cycle u… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Buderus GB 142/60 seems to overheat in DHW mode. When activated
Buderus GB 142/60 seems to overheat in DHW mode. When activated boiler temp will quickly increase to OY code before heating stops. It will refire when the reading is in the 140-150 range and keep repe… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I am working on a 199M R2 10/15/2007 after servicing the combustion
I am working on a 199M R2 10/15/2007 after servicing the combustion chamber and burner it fired once and ran through a full operation cycle. Today it will not call for heat. The burner fan starts when… read more
Nathan Marshall, MP
Nathan Marshall, MP
Master Plumber,HVAC Tech,Tradesman
Vocational, Technical or Trade School
275 satisfied customers
i have GLOWWORM MICRON 60FF BOILER THAT KEEPS GOING TO RESET
i have GLOWWORM MICRON 60FF BOILER THAT KEEPS GOING TO RESET AND I HAVE TO REFIRE IT UP MANUALLY RATHER THROUGH THE WIRELESS SIGNAL SYSTEM WHICH APPEARS TO BE WORKING OK. I HAVE EVEN REPACED THE BATTE… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
9,798 satisfied customers
our ecotec 838402_06 fires up and is supplying hot water perfectly
our ecotec 838402_06 fires up and is supplying hot water perfectly well but I have tried to get the radiators working this weekend but without success. I have gone through the programme modification v… read more
Plumbers_Mate
Plumbers_Mate
General Manager
Vocational, Technical or Trade Scho
3 satisfied customers
I am working on a Baxi duo tech combi he 24 lpg. the heating
I am working on a Baxi duo tech combi he 24 lpg. the heating side of the boiler works fine but as soon as you turn on a hot water tap the flame goes out. not error codes are flashing. i have replaced … read more
Plumbers_Mate
Plumbers_Mate
General Manager
Vocational, Technical or Trade Scho
3 satisfied customers
Hi We have a potterton promax 24he have had a new pcb ignition
Hi We have a potterton promax 24he have had a new pcb ignition board fitted, boiler lights then cuts out, it lights again then cuts out,just keeps doing this… read more
Plumbers_Mate
Plumbers_Mate
General Manager
Vocational, Technical or Trade Scho
3 satisfied customers
We have had some problems with the (GlowWorm) boiler in the
We have had some problems with the (GlowWorm) boiler in the flat. Danny's wife (Sheva) had informed us that the boiler was flashing red light a couple of days ago and stopped working. We have had a Gl… read more
Rick Ridley
Rick Ridley
UK Heating Engineer
30 years on the tools
871 satisfied customers
I have a oil fired boiler and a seprate oil fired hot water
I have a oil fired boiler and a seprate oil fired hot water heater they share the same oil feed line.The oil line has a T fitting and oil goes off the T fitting to the water heater and then on to the … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
HI, my Glowworm Fuelsaver 100F has stopped working a few hours
HI, my Glowworm Fuelsaver 100F has stopped working a few hours ago, can you help. The pilot lights up but goes out after 20-30 seconds.… read more
Rick Ridley
Rick Ridley
UK Heating Engineer
30 years on the tools
871 satisfied customers
Hi my son has a main condensing boiler its a main 24 he.
Hi my son has a main condensing boiler its a main 24 he. the boiler wont light the red light keeps flashing . he has changed the pcb and its still the same any idears.thanks… read more
Rick Ridley
Rick Ridley
UK Heating Engineer
30 years on the tools
871 satisfied customers
hi,I have a glowworm 100e combi boiler on which the circulation
hi,I have a glowworm 100e combi boiler on which the circulation pump has started to run constantly when the boiler is switched on and is firing up also,this is happening when the roomstat is turned to… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
Baxi 105HE 4years old - flame failure light flashing - boiler
Baxi 105HE 4years old - flame failure light flashing - boiler not working on ch/hw setting (boiler fires up for a couple of seconds then goes out)-turn knob to hw setting and boiler functions (hw only… read more
Rick Ridley
Rick Ridley
UK Heating Engineer
30 years on the tools
871 satisfied customers
We have had a new pump fitted, and now the boiler fires up
We have had a new pump fitted, and now the boiler fires up even when all the controls on the timer say it should be off. Could it have been incorrectly wired up. Also despite new pump and deep flush o… read more
Heath
Heath
Vocational, Technical or Trade Scho
1,002 satisfied customers
Baxi Duo-tec 24 HE pcb The mains fuses keep blowing, any
Baxi Duo-tec 24 HE pcb The mains fuses keep blowing, any basic checks I can do? If I need to replace the pcb, where can I get one? Thanks Mike… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
hi we have a c24 heatline boiler 4 years old, which has intermitent
hi we have a c24 heatline boiler 4 years old, which has intermitent hot water (20 sec intervals) The engineer has left central heating sensor out to allow us to have water (works fine but at lower lev… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
sometimes starts ok and goes faulty after a minute, sometimes
sometimes starts ok and goes faulty after a minute, sometimes 30 minutes, sometimes ok all day. To get out of fault condition turning of water temp rotary control on and off several times on boiler so… read more
coolman1973
coolman1973
AC/Heat Tech
Vocational, Technical or Trade Scho
162 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x