My compressor wont stay on and we have replaced the kickstart…

Customer Question
My compressor wont stay on...
My compressor wont stay on and we have replaced the kickstart and the start capacitor. Do you have any idea as to whats the matter it?
Submitted: 8 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 28 minutes by:
6/26/2010
HVAC Technician: Douglas, HVAC Technician replied 8 years ago
Douglas
Douglas, HVAC Technician
Category: HVAC
Satisfied Customers: 3,089
Experience: Manufacture Rep for Major Brand, Technical Trainer, NATE
Verified
Hi, I'm Douglas and I am here to help you resolve problems with your heating and cooling equipment.

The kickstart is only for the actual start of the compressor and it is taken out of the ciruciut in less than a second so that's not your problem. The run capacitor could be but you would have to compare the microfarad rating of the capacitor agaist the rating plate of the compressor to be sure.

The question then becomes whether the compressor is shutting off as a result of the thermal overload or if the contactor is opening. If the contactor is opening it wouldnt be the compressor neccesarily but more likely a control such as a high or low pressure switch or something like that.

How long does your compressor run? Do you know if the outdoor fan stays running when the compressor shuts off?
Ask Your Own HVAC Question
Customer reply replied 8 years ago
We replaced the run capasitor when we replaced the kickstart the compressor kicks on for a few seconds and then shuts off. It is a geothermal unit closed loop geothermal system so we don't have an outdoor fan unit.
HVAC Technician: Douglas, HVAC Technician replied 8 years ago
OK... yeah I guess I missed that....

Can you see if the contactor opens (the relay that drives the compressor)? Or does it stay in and the compressor pops off by itself?
Ask Your Own HVAC Question
Customer reply replied 8 years ago

We are waiting for it to do something! We had the breaker turned off to the unit and I had to turn it back on. It still hasn't done anything. It just tried to come on! It appears the low capacity starter pulled in and stayed in and the start is off now and the compressor is now off.

HVAC Technician: Douglas, HVAC Technician replied 8 years ago
ok so the contactor pulled in, but the compressor didnt start? IS the compressor warm to the touch?
Ask Your Own HVAC Question
Customer reply replied 8 years ago
yes it is hot
HVAC Technician: Douglas, HVAC Technician replied 8 years ago
OK.... the first thing we need to do is let it cool and this will take several hours. Just because the shell cools down doesnt mean the compressor is cool enough internally to reset the overload.

Check the rating plate of the compressor for the microfarad requirements and make sure the capacitor you have matches it. It will be identified either as mfd or uF. You may also have a tight compressor in which even the right capacitor may not fix it. Be sure it's wired correctly.

Have you had a tech look at it?

Do you have a volt ohm meter?

Ask Your Own HVAC Question
Customer reply replied 8 years ago
We have a volt ohm meter and we haven't had anyone look at it.
HVAC Technician: Douglas, HVAC Technician replied 8 years ago
does your meter have a setting for mfd or uF? Most dont but some modern ones do.

Do you know how to measure resistance (ohm setting)?
Ask Your Own HVAC Question
Customer reply replied 8 years ago
Yes, the meter has a mfd setting. Yes, he knows how to measure the ohm setting.
HVAC Technician: Douglas, HVAC Technician replied 8 years ago
Ok... first thing. Set it to mfd and have him disconnect the run capacitor and measure the capacitor from one terminal to the other. It should measure within 10% of the rating on the capacitor.

Next remove the wires from the compressor and make sure he notes where they went. There are 3. The terminals should be marked R S C (run, start, common). Put the meter in Ohms and measure from R to C then S to C and then R to S and make a note.

Please be sure the power is off before doing any of this!
Ask Your Own HVAC Question
Customer reply replied 8 years ago
from r to c is: 1 ohms from s to c is: 2 ohms from r to s is: 2.5 ohms The capacitor is: He thinks his meter isn't measuring the capacitor. It says zero for the rating. This is the new capacitor that we just bought. We had the old one checked and it measured o.k. but we went ahead and bought a new one and put it on.
HVAC Technician: Douglas, HVAC Technician replied 8 years ago
Hmmm your measurements for the compressor windings say the overload is closed.

so nothing happens when he tries to read the capacitor? Do you have the old one still so we can see how it measures?
Ask Your Own HVAC Question
Customer reply replied 8 years ago
He gets the same reading off of the old one. The points on the contactors look a little bit burnt.
HVAC Technician: Douglas, HVAC Technician replied 8 years ago
as in black?
Ask Your Own HVAC Question
Customer reply replied 8 years ago
They are black and little rough but not completely burnt away.
HVAC Technician: Douglas, HVAC Technician replied 8 years ago
well, hard to tell from here, but a pitted contactor can certainly offer a voltage drop.

I would reconnect everything, remove the kickstart and see how it does right now if you attempt to start it.
Ask Your Own HVAC Question
HVAC Technician: Douglas, HVAC Technician replied 8 years ago
Is your husbands meter alalog (with a needle) or digital?
Ask Your Own HVAC Question
Customer reply replied 8 years ago

The compressor ran briefly without the kickstart it didn't make any loud noise like it has been when it tries to start. It growled a little bit before when it tried to start. The compressor isn't vibrating or anything so we assume it isn't running.

 

It is a digital meter.

Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have just installed a new copeland compressor ( model
I have just installed a new copeland compressor ( model zr48k53-pfv-7me)and it won' start. Looks like it is wired right. … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Rudd unit stopssed working. opened cover and looked at main
rudd unit stopssed working . opened cover and looked at main control board . fault code... high pres. ol trip , shut off power to unit. tried again after 1/2 hour wait. 3 unsuccesful start attemp, shu… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a Rheem RAFD-036JAS AC unit. Recently, the outdoor
I have a Rheem RAFD-036JAS AC unit. Recently, the outdoor fan has been acting up and needed kickstarted about 50% of the time...yesterday, even kickstarting it wouldn't make it run. I realized that it… read more
WCohn
WCohn
Journeyman Plumber
Journeyman License
1,749 satisfied customers
Breaker trips on my 2twr3042a1000A. It tripped once about a
hi breaker trips on my 2twr3042a1000A. It tripped once about a week ago and I reset it and it worked. Now it won't reset. i suspect the start capacitor on the compressor (or a bad compressor). Any ide… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,024 satisfied customers
Outside fan is working fine but I hear the compressor try to
outside fan is working fine but I hear the compressor try to turn on for a few seconds then stops and fan stays on… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
HAVE A RAFD-060JES A/C unit that is having some troubles.
HAVE A RAFD-060JES A/C unit that is having some troubles. When the thermostat, the blower fan in the heater unit comes on, the compressor unit fan comes on, but it appears that the compressor is not s… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,024 satisfied customers
My condensor unit is a copeland 2.5 ton scroll compressor.
My condensor unit is a copeland 2.5 ton scroll compressor. Replaced the bad dual run capacitor on it this moring. The old one I removed was a p/n 97f9834 marked 36uf 6uf 370vac. Replaced it with a 35u… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,024 satisfied customers
We have a unit, model number RRKAA060JK10E. The unit when
We have a unit, model number RRKAA060JK10E. The unit when it starts the amps surge up to around 160 amps and then Comes back down to around 33 amps. Why is there such a large starting surge? We have h… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,024 satisfied customers
I have a Rheem RAKA-060JAZ unit and its been having problems
I have a Rheem RAKA-060JAZ unit and its been having problems starting and blowing the 50amp breaker. In looking at my unit, it doesnt have a starter capacitor. What would be the best option here. Shou… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Problem with AC. Wife called to say that the house was 88
Problem with AC. Wife called to say that the house was 88 but the thermostat was calling for 70. I was able to get home a few hours later to find the outside fan not turning. I disassembled it to find… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Trane XR12 and the fan stopped working. Upon opening
I have a Trane XR12 and the fan stopped working. Upon opening up the panel on the side I noticed that the starter (part # XXXXX) had fallen apart. I have changed this part and the fan is still not wor… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Carrier central Air unit - Model 38EH024300DL The
I have a Carrier central Air unit - Model: 38EH024300DL The dual capacitor (25/5uf 440VAC #97F5360) was bulged/bad. I was replacing both the capacitors (25/5uf 440VAC #97F5360 and 53-64uf 250VAC #HC95… read more
Douglas
Douglas
HVAC Technician
3,089 satisfied customers
Ive had my Payne Ac Unit for five years. Recently Ive had
I've had my Payne Ac Unit for five years. Recently I've had issues with it blowing the breaker on start up? We replaced the breaker but it continues to trip - we also replaced the capacitor thinking t… read more
Douglas
Douglas
HVAC Technician
3,089 satisfied customers
I need help on a Coleman DRHS0301MD we have placed a new compressor
I need help on a Coleman DRHS0301MD we have placed a new compressor new defrost board and new contactor , we can get the fan to work but the compressor wont kick in.… read more
Douglas
Douglas
HVAC Technician
3,089 satisfied customers
I have a AC unit that the fan runs off and on but the compressor
I have a AC unit that the fan runs off and on but the compressor is always running. Fan motor is really hot. It has a kickstart on it. What do I need to do???… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
heat pump- compressor starts but wont stay on, replaced capacitor
heat pump- compressor starts but wont stay on, replaced capacitor and have hard start on. turned unit off for two days, tryed again still wont stay on.is compressor out for good?… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
my lennox hvac 13ACD-036 is 2 years old and keeps tripping
my lennox hvac 13ACD-036 is 2 years old and keeps tripping the circuit. The service guys looked at it today and told we the capacitor was shot (round shaped 45-5 ) and they replaced it with an oval sh… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My home AC works OK, but I worry about outside compressor.
My home AC works OK, but I worry about outside compressor. It starts not synchronously with both fans (cooling fan on the compressor and on the evaporator). Sometime compressor starts before fans or c… read more
Rick or Nick in Texas
Rick or Nick in Texas
General Manager-Lead Tech
Own and run HVAC business 29yrs
44 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x