Customer Question
JACustomer: My AC (Trane...

JACustomer:

My AC (Trane XB13) outside fan not running, something else out there is, (humming noise), but no serious cooling in the house. Fans in house is running. Breakers reset etc. Fan outside spins freely. Some circuit board in house shows a bright green light.  Is there something to reset?

Submitted: 8 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 5 minutes by:
6/26/2010
HVAC Technician: gotoman for ac, HVAC Technician replied 8 years ago
gotoman for ac
gotoman for ac, HVAC Technician
Category: HVAC
Satisfied Customers: 5,358
Experience: 51 years of experience install design and repair of all makes and models of AC
Verified

Expert:

Check your inside unit and see if you have a float switch in drain line. This switch opens circuit to outside unit when drain stops up (keeps from flooding house). If float switch is OK, go outside and open panel to unit. It will be on corner of unit. You will see an open relay that is contactor. See if that is energized.

JACustomer:

Is the outside loud hum normal? A lot of heat through the top of unit at that point. Inside float area appeared fine.

Expert:

Open up outside panel and check capacitor. This a large silver cannister. See if top is puffy or bulged.

JACustomer:

Out here now, does not appear bulged. Some circuit board in there, blinking green.

Is there anything that might have tripped in our high heat (100f)? To make sure I'm clear, if AC is set on inside, fans run, some cool comes through vent. Outside unit fan doesn't turn but there's a loud hum and a lot of heat coming up through unit.

Expert:

OK, you will need to take top off unit. There are four 1/4-inch screws that hold on top. We need to check to see if fan is stuck or not.

JACustomer:

I have the big fuse outside currently pulled for this, is that correct?

Screws removed.

Expert:

Yes, that will kill power to unit. Just remove the plastic top and try to spin fan. Feel fan and see if it is hot.

JACustomer:

Fan seems to move freely. Fan housing isn't hot currently, but then again hasn't been powered for a while now.

Expert:

OK, turn on unit and see if fan tries to run.

JACustomer:

Nope no fan. Loud hum, cool air through vents inside, and heat out here from unit, but no fan outside.

Expert:

See if fan tries to start. Let it run Try spinning fan. Compressor does run correct?

JACustomer:

Motor housing a bit warmed after that.

Reach in a powered-on AC unit?

Not sure I'd know compressor noise. Something is cooling enough for cool air to flow somewhat inside the house. There is a clear temp drop on air coming out of vents, just not as much of one as normal. But I know the fan out here should turn.

Expert:

You still may have bad capacitor. Time to call service tech.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask gotoman for ac Your Own Question
gotoman for ac
gotoman for ac
gotoman for ac, HVAC Technician
Category: HVAC
Satisfied Customers: 5,358
5,358 Satisfied Customers
Experience: 51 years of experience install design and repair of all makes and models of AC

gotoman for ac is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
My Trane XR11 is making a loud screeching noise - sounds
My Trane XR11 is making a loud screeching noise - sounds like the fan is failing. Any suggestions?… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
We have a Weatherking heat pump AC, The pump is outside the
We have a Weatherking heat pump AC, The pump is outside the furnace and AC in the attic. Last night the AC went out. It is 108+ here in AZ The fan still blows. I did do a rest on the thermostat, no so… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
we have a trane xb 10 and it keeps causing the circuit breaker
we have a trane xb 10 and it keeps causing the circuit breaker to shut off. We changed the circuit breaker and it didn't help. Even with the circuit breaker off there is a green light flashing in the … read more
gotoman for ac
gotoman for ac
HVAC Technician
Associate Degree
5,358 satisfied customers
Hi, I have a trane 2twb0030. The compressor has a flashing
Hi, I have a trane 2twb0030. The compressor has a flashing green light. It's has power but won't turn on. handler is working fine. Any suggestions ? Thanks.… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
The air in my house was running just fine today but I come
The air in my house was running just fine today but I come home from work and the temp in the house is 82 right now, there is no air coming out the vents....I did some reading and turned cool to off a… read more
gotoman for ac
gotoman for ac
HVAC Technician
Associate Degree
5,358 satisfied customers
I have an American Standard air handler, model number: TWE031EBFB1.
I have an American Standard air handler, model number: TWE031EBFB1. I have read the illustrated manuals telling me that my circuit breaker location is behind a "Air Tite" circuit breaker door but ther… read more
gotoman for ac
gotoman for ac
HVAC Technician
Associate Degree
5,358 satisfied customers
My unit is still working inside but I heard a noise coming
My unit is still working inside but I heard a noise coming from the outside unit so I turned it off, now the outside fan will not come on and there is only a humming noise coming from the unit now. Sh… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
If I turn on the AC - the unit outside clicks on as expected
If I turn on the AC - the unit outside clicks on as expected and the fan in the house kicks on as expected, but it does not cool. Changed the filter (sad to say it was long overdue) but to no avail. T… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
I have a Trane xr 14 and on of the units quit blowing cold
I have a Trane xr 14 and on of the units quit blowing cold air. I giggled the wires outside and it worked. It quit I did it again. Today it would not work. and there is a green wire coming from the ho… read more
gotoman for ac
gotoman for ac
HVAC Technician
Associate Degree
5,358 satisfied customers
I have a trane xr90 about 3 years old, getting a trouble code
I have a trane xr90 about 3 years old, getting a trouble code 4 "open temperature limit circuit". I have reset it and it goes through its start up process fine, except the blower motor will not start,… read more
gotoman for ac
gotoman for ac
HVAC Technician
Associate Degree
5,358 satisfied customers
I have a XT302 C deluxe Programmable Heat Cool Thermostat.
I have a XT302 C deluxe Programmable Heat Cool Thermostat. The system and thermostat were working, but now the sytem is off and the thermostat display will not come on. I checked the circuit breaker a… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Hi. I am replacing drywall and disconnectEd the trane thermostat.
Hi. I am replacing drywall and disconnectEd the trane thermostat. I reinstalled but now the ac will not kick on. Do I need to re-sync or something?… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
I have a trane XB13 that will not start. It was running and
I have a trane XB13 that will not start. It was running and then the power went out. Since then, I can't get it to work. I checked the fuse in the basement box. It is fine. Turn the fuse on and off. T… read more
gotoman for ac
gotoman for ac
HVAC Technician
Associate Degree
5,358 satisfied customers
My Ac is not working properly. The unit is a 2.5 ton Janitrol
My Ac is not working properly. The unit is a 2.5 ton Janitrol and has been working fine the last month. I am in SE VA and it has been around 100 for several days now. The thermostat says its cooling b… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I have a Trane XL 1200, who knows how old. The fan outside
I have a Trane XL 1200, who knows how old. The fan outside is not running and makes a loud squealing noise. I stuck a long screw driver to try and turn the fan, it felt stiff. I turned off the breaker… read more
ComfortZone
ComfortZone
Associate Degree
485 satisfied customers
My outdoor fan is not working for my ac. all is working inside
My outdoor fan is not working for my ac. all is working inside the house. i checked the fuses and breaker to the outside unit. the ac makes noise outside, but the outdoor fan does not move. the indoor… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
I have a Trane XE 90 gas furnance in my house. Model#TXCO36C4HPB1
I have a Trane XE 90 gas furnance in my house. Model#TXCO36C4HPB1 SERIAL#m434pua5g 1997. I have a AC only unit outside. AC unit is working fine. But, the fan is not working on my furnance. For some un… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Hello-- My HVAC fan just stopped working. Outside Compressor
Hello-- My HVAC fan just stopped working. Outside Compressor working with thermostat set to cool. White-Rogers circuit board has flashing LED. 3 amp fuse on board fuse checks OK. With furnace switch o… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x