I have a heat pump in an older home (1971). I have replaced…

I have a heat pump...
I have a heat pump in an older home (1971). I have replaced the original thermostat with a Honeywell TH8110U1003. However, it is not cooling. The fan runs but evidently the compressor is not coming on (I am guessing).
On the old thermostat, the wiring was as follows:
red wire into R
green wire into G
yellow wire into Y
white wire into W
I wired the Honeywell thermostat exactly the same way, leaving the jumper in place on the R and RC terminals.
Where have I gone wrong?
Show More
Show Less
Ask Your Own HVAC Question
Answered in 4 minutes by:
6/25/2010
freon
freon, Licensed A/C Contractor
Category: HVAC
Satisfied Customers: 215
Experience: 22 years Licensed Contractor State of Texas
Verified
Chat Conversation Started
freon :

you did not mention the orange wire. did you put it on o/b? Also you must program your thermostat to tell it what it is... one of the programing selections will have options for you to pick the kind of system you have.

freon :

Lets take for instance you have a single stage heat, single stage cool heat pump. this would be the option you would choose for your thermostat.

freon :

Check the installers instructions that came with the stat.

Customer:

I do not have an orange wire. Only four wires as I described. I do know that I have to choose the kind of system. Perhaps I chose the wrong one. Is there an easy way for me to find out which kind of system I have?

freon :

The rest of the wiring that you have done looks great.

freon :

ok ... i have to scratch my head on this one. you have only a 4 wire system and it is a heat pump?

freon :

What is the name of your air conditioner?

Customer:

It is a heat pump. I forget the manufacturer and am not currently at the house. The compressor was replaced last year before we purchased the home but I am unsure whether the air handler was also replaced. We have two units. One for each side of the house. The other unit has 6 wires but this one only has 4.

Customer:

Given that the 4 wires I have are connected correctly, would it be reasonable to try different system configurations in the thermostat programming and see if one of the other ones works?

freon :

Ok dr bob,

freon :

in your conversation earlier you said you saw the fan running. My first thought would be that the unit is getting a signal to come on but it may be running in heat pump mode. if this were the case and it was hot out side then it will cycle off on high head pressure. This is possible if you did not program the stat properly. But i am still at a loss as to why you only have 4 wires. do you know if your unit is a brand new digital communicating system?

Customer:

The Honeywell stat is brand new. Just received it.

freon :

if it is a regular system with gas heat and standard ac condenser then you can have 4 wires

freon :

I was speaking of the system earlier not the thermostat.

freon :

How old is the system you have?

freon :

Dr. Bob,

freon :

are you recieving this chat in a timely manor?

Customer:

The compressor is new last year. Unsure about the air handler.

Customer:

Yes, receiving in a timely manner but got distracted. It is hot out here so your suggestion would make sense.

freon :

Ok, when you say compressor this is the motor inside the condenser unit. Did you get a new condenser or new compressor?

Customer:

Sorry. Condenser.

freon :

Great! are you at the unit now?

Customer:

I am not. I am at work. My wife is a the house and she is hot! (temperature-wise I mean). I am satisfied with your response given that I am not in front of the unit. I accept your answer and will go home and try different stat configurations. If I can't solve it, I have purchased unlimited questions, so I will repose my question again. Thanks for the help. At least I know I wired what I have correctly.

freon
freon, Licensed A/C Contractor
Category: HVAC
Satisfied Customers: 215
Experience: 22 years Licensed Contractor State of Texas
Verified
freon and 87 other HVAC Specialists are ready to help you
Ask your own question now

Dr. Bob,

 

Ok. Do this also. get the model and serial of the condenser unit, if not possible count the low voltage wiring conductors to the condenser unit. if it is a heat pump you must have at least 4 or 5 wires to the condenser. That is why i think you do not have a heat pump and your problem is something else. You may have a blown capacitor or refrigerant problem. Check these out and let us know!!! Thank you so much!!!

 

freon

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask freon Your Own Question
freon
freon
freon, Licensed A/C Contractor
Category: HVAC
Satisfied Customers: 215
215 Satisfied Customers
Experience: 22 years Licensed Contractor State of Texas

freon is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I am replacing a trane weathertron thermstat with a
i am replacing a trane weathertron thermstat with a honeywell programable. trane hookup is LABEL = RIRE R = RED O= ORANGE G= GREEN Y = YELLOW X2= BLACK B= BLUE W= WHITE HONERWELL' Y2 = W2= G= W= NOT U… read more
Scott
Scott
Self Employed HVAC Service Technician
Associate Degree
400 satisfied customers
I just purchased a new Honeywell RTH5100B Non-programmable
Hi--I just purchased a new Honeywell RTH5100B Non-programmable Digital Thermostat for my mother's home. While the instructions included with the thermostat were quite descriptive, I'm at a loss trying… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Taystat 350 not working and a replacement thermostat
I have a Taystat 350 not working and a replacement thermostat - Hunter. How to match up wiring? Matches are G fan, W heating, and Y compressor. What to do with R ( red) and B (blue) on Trane unit to c… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
just installed honeywell thermostat and did not label the wires
just installed honeywell thermostat and did not label the wires before disconnecting and now unit does not cool. what to do?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a trane split system and I want to replace the old weathertron
I have a trane split system and I want to replace the old weathertron mercury bulb thermostat with my new honeywell 8000. The old has 8 wires ie: O-orange, R-red, T-brown, G-green, Y-yellow, X2-black,… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
I just bought a new thermostat, Honeywell RTH6350/RTH6450 and
I just bought a new thermostat, Honeywell RTH6350/RTH6450 and the old thermostat (Carrier) has W O G R C Y connections. this does not match the honeywell model. Which of the old wires go to the connec… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Problem; I have a trane heat pump system. Model # XXXXX
Problem; I have a trane heat pump system. Model # XXXXX with auxilliary/backup. Previously I had a honeywell thermostat, I Guess T8011R 1014 (2).this is all I find on it. I fell and hit this and every… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a Bryant 574A gas pack to which I want to wire a Honeywell
I have a Bryant 574A gas pack to which I want to wire a Honeywell RTH6350 thermostat. I have a Brown wire for RC, Red for RH, White, Green and Yellow coming from the unit. The Bryant manual suggests t… read more
Jerry M.
Jerry M.
Senior HVAC Technician
High School or GED
133 satisfied customers
I am installing a Honeywell RTH7500D thermostat. The existing
I am installing a Honeywell RTH7500D thermostat. The existing Trane thermostat wiring does not match up with the wiring of the Honeywell. The trane has the following terminals with the corresponding w… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
My old thermostat has w o g r c y terminals a blue wire was
My old thermostat has w o g r c y terminals a blue wire was hooked to the c terminal, nothing to the o the rest same color as terminal. My new programable one ( Honeywell RTH230B) has Rh Rc W Y G. My … read more
ClimateCreator
ClimateCreator
28 satisfied customers
I have a Trane 4TEH3F24B1000AB heat/cool unit, manufactured
I have a Trane 4TEH3F24B1000AB heat/cool unit, manufactured in 3/09. It has a Honeywell TH8110U1003 thermostat. The unit has 4 wires: red, white, yellow, green, which are now connected to the R, W, Y,… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a honeywell older thermostat its round and has five
I have a honeywell older thermostat its round and has five wires going to it. i am trying to install a newer honeywell thermostat but not sure which wires go were.can you help… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have Rheem rbhc 24, I want to install a new thermostat, my
I have Rheem rbhc 24, I want to install a new thermostat, my wires on old thermostat as follows: W- white wire RH- Black jumper wire from RC B- no wire RC-Red wire, with black jumper to RH O- no wire … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
The day before yesterday I attempted to install a Honeywell
The day before yesterday I attempted to install a Honeywell vision Pro 8000 thermostat model TH8110U1003. I replaced another Honeywell thermostat. and used the same wires that were labeled to the new … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
[T-Stat Wiring Issue]I have a Gas Furnace in my attic and
[T-Stat Wiring Issue] I have a Gas Furnace in my attic and external AC Condensor outside, I'm trying to change my mercury thermostat for a digital one. I currently have a Honeywell T8034C1481 (origina… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Hello, i am trying to upgrade from a Baystat 239 to a Honeywell
Hello, i am trying to upgrade from a Baystat 239 to a Honeywell RTH110B and there are 10 wires coming from my wall and only 5 places to put new wires. The Baystat was connected as follows: 0(orange) X… read more
Tom
Tom
HVAC Technician
Vocational, Technical or Trade Scho
770 satisfied customers
I have a heat pump with 2-stage heat.... 1-stage cooling. The
I have a heat pump with 2-stage heat.... 1-stage cooling. The original thermostat is bad, it is a Coleman Evcon The terminals on the thermostat are as follows: E G B O Y R X L W2 The wires coming out … read more
DanielC
DanielC
Service manager
High School or GED
95 satisfied customers
I have an old Lennox thermostat that was made by ITT, serial
I have an old Lennox thermostat that was made by ITT, serial number is XXXXX It has Five terminals, G, F, C, H, V. There is no wire on the G terminal a green wire on the F, Blue on the C, Red on the H… read more
coolman1973
coolman1973
AC/Heat Tech
Vocational, Technical or Trade Scho
162 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x