I have a Carrier Outdoor AC unit. It came with the house which…

Customer Question
I have a Carrier Outdoor...
I have a Carrier Outdoor AC unit. It came with the house which was built in 1993. The Fan on the AC unit stopped working. When I looked at it it looked like 2 of the wires that come of it arced on the fan blades. I have a yellow wire, black and white, 2 black wires and 2 white wires. A black wire and a white wire are capped together and the other black wire and other white wire are just hanging there. There is an orange wire cap lying on the ground. I assume it belongs to the two wire that are just hanging from the fan motor. Should I cap those two wires together and see if it'll run again? If i do and it still doesn't work what else should I look at? Also the power box on my house by the AC unit has a T bare looking thing that pulls out and has two sets of two brass flat pins, what it is?
Submitted: 8 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 5 minutes by:
6/25/2010
HVAC Technician: ComfortZone, HVAC Technician replied 8 years ago
ComfortZone
ComfortZone, HVAC Technician
Category: HVAC
Satisfied Customers: 516
Experience: 10 years in the HVAC industry.
Verified
Chat Conversation Started
ComfortZone :

It should work if you wire nut those 2 wires back together. From what you are describing it sounds as if those are the rotation wires for that motor. Make sure you use zip ties to keep them out of the way of the fan blade.

ComfortZone :

The t-bar is the disconnect for that outdoor unit, you pull it out to disconnect 230 volt power from that outdoor unit.

Customer:

Ok, I re-capped and the unit does not turn on.

ComfortZone :

Make sure you have power to the disconnect box. Do you own a voltmeter? If not check the breaker box

Customer:

breakers are on, don't have a voltmeter, when i discovered the AC not working there were sparks flying from the fan blades, i am assuming from the two wires that had lost the wire cap.

ComfortZone :

Does that disconnect box say "contains no fuses" on the inside?

Customer:

yes

Customer:

is it possible for the t-bar disconnect to fail?

ComfortZone :

No.

ComfortZone :

that simply makes a circuit. No moving parts involved. Plug it in and it should be hot to the outdoor unit

ComfortZone :

If you open the access panel where the power wires go into that unit, there should be a contactor. Make sure the contactor is pulled in. If it is not use a pencil and depress the center of it. Picture to follow

ComfortZone :

Full Size Image

Customer:

ok I'll try that, is the panel under the t-bar and just pull off or down?

ComfortZone :

It is on the outdoor unit. Follow the wires to the unit and it will lead you there

Customer:

ok

ComfortZone :

You should see the low voltage wires going there as well

ComfortZone :

They run with the copper pipe coming out of the house to the outdoor unit

Customer:

ok i removed the access panel and saw wires going into the terminals, i did not see a contactor.

Customer:

also earleir when i did apply power the blower fan kicked on an then off and there was a clicking noise comming from the area of the fan motor on teh outside unit

ComfortZone :

Where do the black and the white wire from the motor attach to get their power?

Customer:

I'll have a look they go from the motor thru a plastic wire run to the side and then down.

Customer:

there are two pairs of black and white wires capped together, the black and white wire are capped again 2/3 they down teh side of the unit and then those wires leave the unit and go to the power box on teh side of the house

ComfortZone :

Does the yellow wire go to a silver cylinder in the unit?

Customer:

no, it too goes 2/3 the way down is capped to another yellow wire that leaves the nuit and goes through the conduit that goes to the power box

Customer:

sorry, leaves the unit and goes through the conduit

ComfortZone :

And this power box is attached to the house?

Customer:

yes

Customer:

ok, so should I just hang in here til soemone else joins?

ComfortZone :

yes

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask ComfortZone Your Own Question
ComfortZone
ComfortZone
ComfortZone, HVAC Technician
Category: HVAC
Satisfied Customers: 516
516 Satisfied Customers
Experience: 10 years in the HVAC industry.

ComfortZone is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Switching Condensor Motors - same type, new motor has 5
Switching Condensor Motors - same type, new motor has 5 wires, existing had 3, need help connecting the wires properly… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
The fan on my 4 ton unit keeps over heating then shutting
The fan on my 4 ton unit keeps over heating then shutting off. I just put a new motor on. Does the fan blow up or down? … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
I have a Lennox AC that won't start. There's a buzzing noise
Hi, I have a Lennox AC that won't start. There's a buzzing noise produced by the unit, but the fan won't turn. The furnace fan works fine. When pulled out the switch (?) (it's 2 copper blades screwed … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Purchased a Protech fan motor 1/2 HP, 208-230hp. 5 wire,
Hi, purchased a Protech fan motor 1/2 HP, 208-230hp. 5 wire, reversible. For my Corsaire (Rheam) AC. Model FADC 036JAS. Motor went in fine. Electrical hook up is another matter. The old motor had 3 wi… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
MY GE 5KCP39EG BLOWER MOTOR WENT OUT DUE TO A BAD BEARING.MY
MY GE 5KCP39EG BLOWER MOTOR WENT OUT DUE TO A BAD BEARING.MY REPLACEMENT MOTOR IS A GE 5KCP39LG BLOWER MOTOR.CAN YOU PLEASE SHOW ME HOW TO WIRE UP MY NEW MOTOR TO MY FURNACE?… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I replaced my old fan motor today. It had 3 wires and the new
I replaced my old fan motor today. It had 3 wires and the new fan has 5 wires. I don't understand the wire chart where to hook up the wires.… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I am replacing my Rheem RHE51-23055-11 1/5 condenser fan motor.
I am replacing my Rheem RHE51-23055-11 1/5 condenser fan motor. I am also replacing the run capacitor with a RHE 43-25133-03 is a 35/3 mfd 370V The old motor was a 3 wire, Black, Brown, Orange. The ne… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Hello! I accidentally cut the thermostat wires to my ac only
Hello! I accidentally cut the thermostat wires to my ac only outdoor unit. The thermostat wires coming from inside have 3 wires (red, green and white) but they somehow connected to only 2 wires going … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
REEPLACED FAN MOTOR WITH NEW ONE BUT THE WIRES R DIFFERENT
REEPLACED FAN MOTOR WITH NEW ONE BUT THE WIRES R DIFFERENT COLORS. NEW MOTOR BLACK RED YELLOW BROWN BROWN/WHITE OLD MOTOR BLACK RED BROWN ORANGE PURPLE THE CAPACITOR IS DUAL CAP WITH 3 POSTS. HOW DO I… read more
cmcdonald51206
cmcdonald51206
MANAGER
High School or GED
14 satisfied customers
I have a Trane XE 1000 (model TWR036C100A) from 1998. I noticed
I have a Trane XE 1000 (model TWR036C100A) from 1998. I noticed that my AC was no longer blowing cold air a couple of days ago. I went to investigate, and I saw the fan on the unit outside stopped spi… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Trying to wire a Honeywell 6450 thermostat. The wiring for
Trying to wire a Honeywell 6450 thermostat. The wiring for the old thermostat is: orange to O, white to W2 with a jumper to E, green to G, red to R, blue to X, black to L, and yellow to Y. It's a heat… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Quantum plus 522a air conditioning unit stopped working. The
Quantum plus 522a air conditioning unit stopped working. The outside unit makes a noise, borderline siren but not shrill and the fan blades don't rotate. No cool air coming out of vents inside but fur… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Im replacing the fan motor on my furnace. The original motor
I'm replacing the fan motor on my furnace. The original motor had just 2 wires that attached to 2 wires coming out of the heater. The replacement motor is a 4/speed motor with a black (high), white (c… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Hi, can you talk me thru a condenser fan wiring job, from a
Hi, can you talk me thru a condenser fan wiring job, from a 3 wire motor to a 5? I did not purchase a new capacitor as mine was updated along with a Kick start sys less than a year ago.… read more
Heath
Heath
Vocational, Technical or Trade Scho
1,002 satisfied customers
Need help installing Honeywell thermostat RTH2510.
Trying to install a Honeywell thermostat model RTH2510. We have a Janitrol Heat/AC - central heat and air with a heat pump. The air conditioner is not kicking on and all the wires are connected. It wo… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a Carrier central Air unit - Model 38EH024300DL The
I have a Carrier central Air unit - Model: 38EH024300DL The dual capacitor (25/5uf 440VAC #97F5360) was bulged/bad. I was replacing both the capacitors (25/5uf 440VAC #97F5360 and 53-64uf 250VAC #HC95… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
Help! I am going on 3 days with no air conditioning.
Help! I am going on 3 days with no air conditioning. I have a Trane XE1000 made in 1997. The outside fan quit working so I bought a replacement motor. The wiring is the problem. The motor I had has 3 … read more
Heath
Heath
Vocational, Technical or Trade Scho
1,002 satisfied customers
I chatted with a Tech earlier and he deferred to someone with
I chatted with a Tech earlier and he deferred to someone with more experience. I have a Carrier unit which stopped working yesterday. When i tried lowering the temp in the house, my father was by the … read more
Jason  Hvac
Jason Hvac
Hvac Tec
Vocational, Technical or Trade Scho
120 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x