I have a Lennox heart pump that has a short cycling fault,

Customer Question
what could be the possible...
I have a Lennox heart pump that has a short cycling fault, what could be the possible problem with this unit. It's only 4 years old.
Submitted: 8 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 minute by:
6/25/2010
HVAC Technician: freon, Licensed A/C Contractor replied 8 years ago
freon
freon, Licensed A/C Contractor
Category: HVAC
Satisfied Customers: 215
Experience: 22 years Licensed Contractor State of Texas
Verified
Chat Conversation Started
freon :

Did you have a tech add refrigerant this past winter?

Customer:

yes, my system was serviced (I have a maintenance contract) he also checked the refrigerant yesterday

freon :

Ok, there is a good chance that the tech who added refrigerant during the winter overcharged the system and now it is cycleing on the hi pressure switch. Are you running in heating now or cooling?

freon :

Their are folks up in the northern region that are still using heat!

Customer:

cooling....The tech said on the invoice "Found unit lockout due to short cycling fault. Cleared fault. Checked unit operation, no cause found at this time". So basically the unit started up after he cleared the fault, then stopped again.

freon :

Call the company back out and have him check the system in cooling mode, using the sub cooling method and the super heat method. The unit must have documented the type of fault. Example: hi pressure fault, low pressure fault, low voltage fault ect.

freon :

You should not have to pay again.

freon :

All faults and calls must be taken seriously and checked out with proficency. Other wise time and money are wasted.

Customer:

Yes, I will do that. Thanks for your help!

freon :

The tech did not show the type of fault on the invoice.

freon
freon, Licensed A/C Contractor
Category: HVAC
Satisfied Customers: 215
Experience: 22 years Licensed Contractor State of Texas
Verified
freon and 87 other HVAC Specialists are ready to help you
Ask your own question now
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask freon Your Own Question
freon
freon
freon, Licensed A/C Contractor
Category: HVAC
Satisfied Customers: 215
215 Satisfied Customers
Experience: 22 years Licensed Contractor State of Texas

freon is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
My son has a lennox XP15-042 heat pump and has had problems
my son has a lennox XP15-042 heat pump and has had problems with a compressor lockout code of 3 yellow flashes. the problem generally appears in winter. i have spent many years in the HVAC business bu… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a lennox 4 ton unit CBX32MV-048-230-6-07 electric
I have a lennox 4 ton unit CBX32MV-048-230-6-07 electric heat not a heat pump has elec strips for heat. my question is is my thermosat wired correctly. rh red wire with a red jumper to rc, g ==green, … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a heil furnace model N8MPN100F14A1. it has a
I have a heil furnace model N8MPN100F14A1. it has a honeywell smart valve in it with intermittent pilot. The furnace wouldnt runn so some one else changed the smart valve.model SV9641M4510. He said he… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Lennox Elite Series heat pump system. The outside
I have a Lennox Elite Series heat pump system. The outside unit doesnt come on consistently, and always seems to use the "aux" heat. The outside temp is reading way off, like -22. I am wondering if th… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
We bought a unit 4 yrs ago every year Blackmon whom we
We bought a unit 4 yrs ago every year Blackmon Moore whom we purchased it from with a extended warranty has to come out and recharge the unit. Everytime they find something different wrong. This time … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a Tappan heat pump. (Model FT5BD-18K), 1.5 TON. It
I have a Tappan heat pump. (Model FT5BD-18K), 1.5 TON. It is only 4 years old, and it's short cycling. It runs for about two minutes, then it shuts down. A few minutes later it starts up again and the… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
lennox pge12 gaspac induction motor runs all the time. unit
lennox pge12 gaspac induction motor runs all the time. unit will light and heat thru one cycle until house is brought up to tstat set temp. then unit will not come back on until power is disconnected … read more
mranswer
mranswer
TECHNICIAN
Bachelor's Degree
481 satisfied customers
G61MPV-60C-110-07 when i get a power interuption or just switch
G61MPV-60C-110-07 when i get a power interuption or just switch the main furnace breaker off then back on, the furnace will not start again (the red LED light will not light up (pulse of heart beat)) … read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
Lennox Heat Pump xp 15 060 Heat Pump Installed July 2006
Lennox Heat Pump: xp 15 060 Heat Pump Installed July 2006 replaced R22 system with gas heat Problem: was not cooling enough.. blew some cold air but not enough to reduce temperature of air more than 5… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
Have a Goodman GSH130361A Heat pump that trips 20 amp condenser
Have a Goodman GSH130361A Heat pump that trips 20 amp condenser unit breaker but only during heat cycle. Unit is 2 years old and has never tripped during cooling cycle but at times during hearting sea… read more
MagiicAir
MagiicAir
HVAC Service Supervisor
Vocational, Technical or Trade Scho
110 satisfied customers
i have a lennox pulse furnance, it doesnt heat the house very
i have a lennox pulse furnance, it doesnt heat the house very well with it always kicking on and then off in short spurts! is there a way to make it just run like a normal furnance? the furnance is pr… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Lennox heat pump- HP21-411-4P - run capicator shorted out -
Lennox heat pump- HP21-411-4P - run capicator shorted out - replaced it. compresser won't start when thermostat calls -contactors pull in but compresser only humms. Push main contactor in and it start… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a 4 year old Lennox air handler model C33-43 c -2f-2.
I have a 4 year old Lennox air handler model C33-43 c -2f-2. It only comes on intermittently when required by the thermostat. If I go and hit my hand on the side of the cabinet near the controls, it t… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I have a Lennox Pulse 21, its brand new out of the original
I have a Lennox Pulse 21, its brand new out of the original box, built in 1994, I've used and changed both a single and a double stage thermosatat, it seems to run well off either one for about 4 or 5… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have lennox HPX-A19-038 heat pump with an indoor electric
I have lennox HPX-A19-038 heat pump with an indoor electric backup blower coil. When the stat calls for hest the outside unit does not come on and the emergency heat designation comes on the stat. We … read more
DuWayne
DuWayne
Sales/ Service
Vocational, Technical or Trade Scho
126 satisfied customers
I have a Lennox Elite Model CB29M Blower Coil, Heatpump Lennox
I have a Lennox Elite Model CB29M Blower Coil, Heatpump Lennox model HP29, TStat Lennox 21J7201. We noticed when we cut over to heat this fall that the blower began running almost non-stop, even thoug… read more
Bill
Bill
High School or GED
318 satisfied customers
Hello Tech, I have a few questions and really need an unbiased
Hello Tech, I have a few questions and really need an unbiased opinion. My house has two LENNOX Pulse 21 furnaces (G21/5-100-3Q, G21Q3-60-3) one for upper level and one for lower level (each is tied w… read more
Dan Linger
Dan Linger
Lead Technician / Energy Consultant
Bachelor's Degree
62 satisfied customers
Lennox Model HP18-261V-10P mfg.date of 9/88. This unit is iced
Lennox Model HP18-261V-10P mfg.date of 9/88. This unit is iced on the external condenser that wraps around the unit, It is solid ice. It looks to me that some water started to ice on the bottom and ha… read more
Charles
Charles
HVAC Technician
Associate Degree
91 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x