What is the proper operating pressure on a 4ton ductible split Freon 410 Goodman Brand?
And how could i get some manuals for my tech on this brand new freon 410 system?
Submitted: 8 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 37 minutes by:
6/25/2010
HVAC Technician: Mr. Jeff Pearson, Mechanical Engineering Technologist replied 8 years ago
Mr. Jeff Pearson
Mr. Jeff Pearson, Mechanical Engineering Technologist
Category: HVAC
Satisfied Customers: 155
Experience: 25 years as Refrigeration Contractor,
Verified

195 psig seems a little high for the back pressure, that coresponds to a 79 deg F suction temp.

What was the superheat at that pressure?

What amount of sub-cooling did you have at 410 psig?

 

I would just be guessing without at least those two bits of info.

 

Jeff Pearson

 

Here are a few good links for R410A split system information

http://www.docs.hvacpartners.com/idc/groups/public/documents/marketing/811-20066.pdf

 

http://www.achrnews.com/Articles/Service_and_Maintenance/bd5a903260d5a010VgnVCM100000f932a8c0____

 

Here is a Pressure Temperature chart

graphic

 

 



Edited by Mr. Jeff Pearson on 6/25/2010 at 9:26 AM EST
Ask Your Own HVAC Question
HVAC Technician: Mr. Jeff Pearson, Mechanical Engineering Technologist replied 8 years ago

Also, if you could, please measure the temperature drop across the evap coil when running at these conditions. So if I had to guess, I would say it looks like the system is undersized.

 

Jeff P.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Mr. Jeff Pearson Your Own Question
Mr. Jeff Pearson
Mr. Jeff Pearson
Mr. Jeff Pearson, Mechanical Engineering Technologist
Category: HVAC
Satisfied Customers: 155
155 Satisfied Customers
Experience: 25 years as Refrigeration Contractor,

Mr. Jeff Pearson is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I just installed a brand new HVAC unit into a house and I
I just installed a brand new HVAC unit into a house and I come back to find the outside condenser frozen solid as a rock. I obviously have an issue with the Freon but I would like the assistance of a … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Trane XR13 contactor relay C147094P02 keeps tripping. When
Trane XR13 contactor relay C147094P02 keeps tripping. When holding the contactor relay down everything runs but once released it stops. Replaced contactor relay and system started fine but after 30 se… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Relativally new 410a system, condensing unit drops out of
Relativally new 410a system, condensing unit drops out of operation during the heat of the day. Not the capacitor. Could it be something in control board in the air handler. Split 4ton goodman system.… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a goodman residential split unit that has 130psi
I have a goodman residential split unit that has 130psi suction and 212 psi liquid on a 70F day. I found one of the wire at the compressor terminal burnout. I then replaced it with new connector. I ch… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
I just had a brand new Goodman 3 ton R-410 system installed.
I just had a brand new Goodman 3 ton R-410 system installed. I replaced an old R-22 system. It seems to be running constantly and not cooling well. I called back the installer to check it out. He said… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Yesterday,The HVAC company replaced my R-22 condensor unit
Yesterday,The HVAC company replaced my R-22 condensor unit with brand new 5 ton Goodman R-410a condensor. The house was built 2005, so I assume the AC unit was 9 years old. I am worried that my R-22 i… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Im having trouble with a brand new system . Installed new
I'm having trouble with a brand new system . Installed new coil and new condenser (2 ton HEIL 410-A) last year. The line set was not replaced. This year the coil froze up with a big icicle. The filter… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
We recently installed a goodman unit (410) and manhandler,
We recently installed a goodman unit (410) and manhandler, living in Texas. when the outside temp reaches 100* the unit runs constantly and doesn't get under 79*. The tech said Freon levels are good a… read more
Scott
Scott
Self Employed HVAC Service Technician
Associate Degree
400 satisfied customers
I have been working on a Coaire mini split system 2ton heat
I have been working on a Coaire mini split system 2ton heat pump. The little tank next to the compressor(accumulator) starts freezing up. ( it looks like little snowflakes) once the tank is completely… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Goodman CLT42-1B (3.5ton - 9yrs old) - AC tech says the compressor
Goodman CLT42-1B (3.5ton - 9yrs old) - AC tech says the compressor is shot & there is no freon left - thinks there is leak in the line set. Also says the AC coil is wrong size. 3.5ton condenser to 5 t… read more
Wvfan79
Wvfan79
Mecanical Designer & Estimator
High School or GED
775 satisfied customers
I have goodman split system . I just put guages on and suction
I have goodman split system . I just put guages on and suction low pressure is 55psi and high side is 225 psi . Outside ambiant is 93 f.return air temp is 73 f. Suction temp is 98f which i used laser … read more
Bart Jay
Bart Jay
Vocational, Technical or Trade Scho
596 satisfied customers
I have an split system a/c on an apartment home that is losing
I have an split system a/c on an apartment home that is losing charge, but it holds a vaccuum and has been charged with nitrogen at 400 psi for two hours?… read more
freon
freon
Owner
High School or GED
214 satisfied customers
we have a Goodman MSG split unit and the indoor unit is leaking
we have a Goodman MSG split unit and the indoor unit is leaking oil on the bottom right hand side… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Less that a pound of r410 freone was accidently put into an
Less that a pound of r410 freone was accidently put into an r22 system would that be enough to contaminate the sytem if all that freone was removed and then replaced with new r22?… read more
Mario
Mario
Owner Of At Your Service Plumbing & Heat
High School or GED
672 satisfied customers
My New Goodman A/C unit has an excess amount of water collection
My New Goodman A/C unit has an excess amount of water collection around the outside condensing unit and the smaLL HIGH PRESSURE LINE is barely warm. My old unit was hot to touch and had no water aroun… read more
ComfortZone
ComfortZone
Associate Degree
485 satisfied customers
I just moved into my new custom home in AZ 4 months ago, I
I just moved into my new custom home in AZ 4 months ago, I have a total of 4 Lennox central AC units. It seems to me that the air coming out of the vents is cool but not much of a difference between r… read more
ComfortZone
ComfortZone
Associate Degree
485 satisfied customers
We had installed 3 years ago a Carrier system, this year our
We had installed 3 years ago a Carrier system, this year our air conditioner (the compressor is Carrier 39TDB, would not come one. We were out of freon and we put in too much freon, now we are kicked … read more
drcool299
drcool299
shop owner
Bachelor\u0027s Degree
22 satisfied customers
I am replacing existing home hvac with a new unit from heil.
I am replacing existing home hvac with a new unit from heil. Contractor says it is ok to reuse the existing refrigerant line...he will "wash out" the freon and reuse the line with the R410A coolant. I… read more
HVAC DOCTOR
HVAC DOCTOR
President
Vocational, Technical or Trade Scho
74 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x