Customer Question
I will like to know...
I will like to know how to wire the 24 volts from the secondary side of the transformer to the normally open and Normally closed relay. I know that the 120 volts is staged down to 24 volts for control. And I know that 120 volts is conducted from the door switch to one of the normally open terminals on the relay. Would the common on the 120 go to the door switch also?
Submitted: 8 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 58 minutes by:
6/25/2010
HVAC Technician: Tim H., HVAC Professional replied 8 years ago
Tim H.
Tim H., HVAC Professional
Category: HVAC
Satisfied Customers: 3,972
Experience: Experienced in all aspects of HVAC, both residential and commercial.
Verified
Thanks for giving me the opportunity to help! Let me see if I can try to help you. First of all, which relay were you trying to replace? Is this the fan relay (the one that controls the fan?)
Ask Your Own HVAC Question
Customer reply replied 8 years ago
This relay is the control relay. The terminals are numbered from 1 to 6. The first two switches are NO., and the other two switches have to be energised to open then, the fan will come on. However, I had the black hot wire that is pigy backed coming from the door switch to one of the terminals on the relay, but the terminal does not show , according to the diagram on the relay, if it is NO or NC. Then, I had the common wire hooked up to the white wire that goes to the heat. May be I shouldn't have done that cause, I am thinking that is why the heat came on with the fan at the same time when I fliped the power switch to "ON", even though the door was open. This is all I could tell you.
HVAC Technician: Tim H., HVAC Professional replied 8 years ago
Are you trying to control the fan only with this relay?
Ask Your Own HVAC Question
Customer reply replied 8 years ago
I am trying to wire this relay according to how it is supposed to be wired, so that, it can control the flow of the 24 volts to control when the fan comes on and when it shouldn't. What I am not sure of is that, I don't know if I have to just send 120 volts to the fan motor or through the relay. For your information, this is a furnace with a control board.
HVAC Technician: Tim H., HVAC Professional replied 8 years ago
On a fan relay, you only control the hot side of the 120 volts. In other words, one side comes from the hot side of the 120 volts and the other side goes to high speed hot lead of the blower.
Ask Your Own HVAC Question
HVAC Technician: Tim H., HVAC Professional replied 8 years ago

on a fan relay, you only control the hot side of the 120 volts. in other words, one side comes from the hot side of the 120 volts and the other side goes to high speed hot lead of the blower.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Tim H. Your Own Question
Tim H.
Tim H.
Tim H., HVAC Professional
Category: HVAC
Satisfied Customers: 3,972
3,972 Satisfied Customers
Experience: Experienced in all aspects of HVAC, both residential and commercial.

Tim H. is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I need to setup a simulator to operate a thermostat. What
I need to setup a simulator to operate a thermostat. What parts do I need? Transformer? and ?… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,024 satisfied customers
My Lennox Thermostat is not working, even after I changed the old one.
I have a Lennox cb25uh. Thermostat not working. Changed thermostat, still not working. 220 volt to unit. Breakers ok. There seems to be a problem internally which will not light up the thermostat.… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,024 satisfied customers
I have a Lennox G61MPV series gas unit with Hard Lockout
I have a Lennox G61MPV series gas unit with Hard Lockout code 5+6. Can I repair it? If so how? Thanks… read more
Tim H.
Tim H.
HVAC Professional
Vocational, Technical or Trade Scho
3,972 satisfied customers
I have an American Standard Freedom 90 single stage furnace.
I have an American Standard Freedom 90 single stage furnace. I have power to the furnace both at the switch and going into the card. But nothing happens when I turn the heat on. No light indicator eit… read more
Tim H.
Tim H.
HVAC Professional
Vocational, Technical or Trade Scho
3,972 satisfied customers
Replacing a Fed Pacific Mechanical 28v low voltage thermostat with a Honeywell programmabl
Replacing a Fed Pacific Mechanical 28v low voltage thermostat with a Honeywell programmable 24 low voltage v unit. The old thermo has just 2 wires, red & white. When it was wired from the Fed Pacific … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
How do I install a Venstar t5800 to control a swamp cooler
How do I install a Venstar t5800 to control a swamp cooler and a gas furnace? I currently have 2 thermostats to control them seperately.… read more
V12Tech
V12Tech
252 satisfied customers
How do I wire a two 24vac transformer system on a gas fired
How do I wire a two 24vac transformer system on a gas fired hot water system with 6 white rogers 1311-102 zone valves.tried to replace 1 zone valve and must of mis phased my transformers cause I let t… read more
warmneighbor
warmneighbor
owner
Vocational, Technical or Trade Scho
9 satisfied customers
I working on a arcoaire furnace. The ignitor wont glow. I
I working on a arcoaire furnace. The ignitor won't glow. I checked there isn't 120 volts going to ignitor. I also noticed on the White rodger control module the red light is not on. but there is 120 v… read more
Heath
Heath
Vocational, Technical or Trade Scho
1,002 satisfied customers
Furnace wont turn on at all: Furnace WAS very dirty. Not
Furnace won't turn on at all: Furnace WAS very dirty. Not used much in 10 years. I had closed most vents when it stopped working. I changed filter, and it worked one more time for a few minutes, and h… read more
Tim H.
Tim H.
HVAC Professional
Vocational, Technical or Trade Scho
3,972 satisfied customers
My Lennox HS8 home air conditioner is dead. I have checked
My Lennox HS8 home air conditioner is dead. I have checked all breaker with no results. I have opened the outside box and see no loose wires or other breakers/fuses. What do I need to do next… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Our air conditioner as well as heater will not come on. I have
Our air conditioner as well as heater will not come on. I have checked the disconnect outside, the breakers and still nothing. I had someone helping me earlier but he opted out. Can anyone else help?… read more
Tim H.
Tim H.
HVAC Professional
Vocational, Technical or Trade Scho
3,972 satisfied customers
Okay I have a small issue with understanding all this and am
Okay I have a small issue with understanding all this and am probably over thinking it. Will describe as best I can what I want to do is this I have an induction blower motor and snap disc sensor to l… read more
servtech50
servtech50
HVAC/R service tech
216 satisfied customers
I have a problem with a oil furance the step down transformer
I have a problem with a oil furance the step down transformer burnout on the 120 volt coil put in a new one and that burned out the 120 volt again. Checked with a volt meter have 120 volts.… read more
hvacmonster
hvacmonster
6 satisfied customers
I have a 3 year old Lennox hi efficency gas furnance and a
I have a 3 year old Lennox hi efficency gas furnance and a Honewell HE 265 humidifer. How can I wire the humidisat so that the humidifer runs when the blower is on, not just when the furnance is on?… read more
Bill P.
Bill P.
Installer/ Troubleshooter/Technician
286 satisfied customers
genaire1137 humidifer-set point at 7-complaint dry air in the
genaire1137 humidifer-set point at 7-complaint dry air in the house-house new-test mode works fine.works when call for heat and blower fan on unit works… read more
Mike
Mike
Service Tech/ Installer
High School or GED
149 satisfied customers
I have a Trane Air Handler that the 24 volt transformer is
I have a Trane Air Handler that the 24 volt transformer is not working. Both primary and secondary coils are good. when the power is turned on there is 120 VAC on both sides of the primary coil (no vo… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
Hi I have benn having a problem with my furnace turning off.
Hi I have benn having a problem with my furnace turning off. I am somewhat confued on how to test and wire thr r8184g to the thermostat.I bought a rebuilt unit but still i am having problems.I replace… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
i have a carrier heat pump. the sytem went down on tuesday.
i have a carrier heat pump. the sytem went down on tuesday. i checked filter and all breakers for indoor and outdoor units and the outside power bar. everything was good. I threw the power for the ind… read more
coolman1973
coolman1973
AC/Heat Tech
Vocational, Technical or Trade Scho
162 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x