cool on code on carrier thermostat flashing after storm pa…

Customer Question
cool on code on carrier...
cool on code on carrier thermostat flashing after storm passed
Submitted: 8 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 3 minutes by:
6/24/2010
HVAC Technician: Phil, Mechanical Engineer replied 8 years ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,823
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified
Chat Conversation Started
Phil :

Hello, .lightening storms can damage electronics controls. Does the stat still work to operate your system in cooling and heating mode.?

Customer:

yes i think so. i can turn on fan and air conditioning seems like compressor not functioing as usual. cool air comig from the fan outside the compressor.

Customer:

an airconditiong service can come tomorrow but it will probably cost me.

Customer:

is there a way to reset the system

Phil :

The compressor is off, could be an electronics control card issue.. due to the electrical storm. or a burnt out compressor etc. If you have a multi meter we can check a few things before the tech arrives... that will help you in dealing with him.

Customer:

no multimeter

Phil :

in that case wait for the tech.. hope he is sharp...if he whips out a multi meter right off to verify power to the unit, then kills power to the unit and uses the meter to look for a short..he is on the ball and his diagnosis is probably pretty good.... if he fumbles around that will be a sign he is short a clue or two.

Phil :

tell me how old your unit is and i can provide some more insight on what may be wrong with it.

Customer:

house built in 2002 air bear filter changed every four months. never needed service.

Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,823
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified
Phil and 87 other HVAC Specialists are ready to help you
Ask your own question now
HVAC Technician: Phil, Mechanical Engineer replied 8 years ago

Thanks for the accept AND the tip! the unit is 8 years old, over due for fan motor failure, lets hope its that, and close to the end of the compressor life as well, if the repair cost is over $200, stay in touch I will give you recommendations on how to get a good deal on a new unit.

 

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,823
9,823 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,823 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
My old Reznor ft100 keeps going into lockout, goes through
My old Reznor ft100 keeps going into lockout, goes through heating cycle ok but after reaching temperature set point and going through the cool down blower time the unit goes into lockout. Not sure wh… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a gas furnace model # 383kav036070 and the error code
I have a Bryant gas furnace model # 383kav036070 and the error code is 12 … read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,024 satisfied customers
Carrier Heat Pump shows System Malfunction when hit 90. Why?
My Carrier Heat Pump says "System Malfunction" when it hits the mid 90's outside. At that time the outside unit shuts down. 3 or 4 hours later , after it's cooled down, the message goes away and the o… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
We had a storm surge and the "cool on" is flashing and we do
We had a storm surge and the "cool on" is flashing and we do not have air conditioning. How do I reset this?… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Have a Carrier heat pump system. Outdoor unit is model 25HNA624A003
Have a Carrier heat pump system. Outdoor unit is model 25HNA624A003 and indoor coil is model FE4AF002000. Unit would not cool. While waiting several days for technician to come, thermostat (Carrier In… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Have a Carrier Model# ***** furnace flashing code 12 Blower
Have a Carrier Model# ***** furnace flashing code 12 Blower on after power up - Blower runs for 90 seconds if unit is powered up during a call for heat. (R-W closed) I replaced the control board in th… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Hello I have a 40QNC012 Carrier Puron cooling system. Did start
Hello I have a 40QNC012 Carrier Puron cooling system. Did start yesterday but stop after 10 minutes. Red light is flashing 3 times. Code seem to be 4-way valve fault. What should I do not Carrier Tech… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
9,823 satisfied customers
I have a Carrier Synergy 2000 SS Heat pump with a Carrier Thermidistat.
I have a Carrier Synergy 2000 SS Heat pump with a Carrier Thermidistat. In heat mode the compressor & Outside fan do not run. When I put in cool mode, both the compressor & outside fan come on. Lookin… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
9,823 satisfied customers
Hello-I have two carrier units (one upstairs, one down) and
Hello- I have two carrier units (one upstairs, one down) and Carrier thermostats. Yesterday we had a power surge and the downstairs unit is no responding. I get a code HP when I turn it to Auto mode a… read more
hvacexpertjoe
hvacexpertjoe
Electronics Technician
Vocational, Technical or Trade Scho
80 satisfied customers
i have a 1989 carrier weathermaster that is heating but the
i have a 1989 carrier weathermaster that is heating but the blower fan will not shut off. I think it happened after the Sandy storm. Gas flames cycle on and off with the thermostat but the blower stay… read more
ComfortZone
ComfortZone
Associate Degree
485 satisfied customers
I have a split type room air conditioner model R24AWN-NC9,
I have a split type room air conditioner model R24AWN-NC9, serial No 909KADT02162. This afternoon before a storm the units' saftey switch cut the units' power off. After the storm passed I turned the … read more
gmac2905
gmac2905
hvac tech
Vocational, Technical or Trade Scho
18 satisfied customers
I have a carrier Crusader 58SSC075 gas furnace. Unit was running
I have a carrier Crusader 58SSC075 gas furnace. Unit was running at the end of the heating season but failed at recent start up. The control board had a number of resistors burned and the primary wind… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My Carrier Comforts Zone 2 system will only work for cooling
My Carrier Comforts Zone 2 system will only work for cooling not heating. Obviously this means the fan is working but when I switch the thermostat to heat it stops. Any suggestions?… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Im working on a carrier 58DHC 095JC Furnace that is flashing
I'm working on a carrier 58DHC 095JC Furnace that is flashing a code 12, but the code guide is gone. What does the flash code 12 indicate?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
my fan coil is not communicating is what my infinity heat pump
my fan coil is not communicating is what my infinity heat pump says. I am trying to get the last cool air out of it before we run out of electicity. We are in Virginia beach and Hurricane Irene's oute… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
Hi, Our power to the house went out last evening due to an
Hi, Our power to the house went out last evening due to an electrical storm. It came back on a couple hours ago, but our Carrier Weathermaker 8000 has not come back on. It's 54 degrees in the house an… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Carrier system with one outside unit the house is
I have a Carrier system with one outside unit the house is two story the thermostat started flashing filter yesterday I changed the filter and hit the filter reset but it is now only cooling the lower… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
For Gotoman for AC This is Roger again - Im back looking
For Gotoman for AC: This is Roger again - I'm back looking at that Carrier Comfort Zone II AC system that comes on full bore and freezes us out till we shut it off. In looking at the programming in th… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x