I recently returned from vacation and had turned the a/c down…

Customer Question
I recently returned from vacation...
I recently returned from vacation and had turned the a/c down to 80 degrees while gone. When I returned, I set the thermostat to 72 degrees. The temperature would not go below 83 last night. Is there anything that I should check before calling for repair?
Submitted: 8 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 minute by:
6/24/2010
HVAC Technician: ComfortZone, HVAC Technician replied 8 years ago
ComfortZone
ComfortZone, HVAC Technician
Category: HVAC
Satisfied Customers: 516
Experience: 10 years in the HVAC industry.
Verified
Chat Conversation Started
ComfortZone :

Is the outdoor unit running?

Customer:

I turned it off 30 mins ago.

Customer:

when it was turned on it just blew warm air

Customer:

unit is approx 5 years old and it is about 100 degrees outside today

ComfortZone :

You have an indoor unit and an outdoor unit. When you turn the system the indoor fan should come on. I need to know if the outdoor fan comes on as well.

Customer:

it does

Customer:

when it is on, it is not blowing warm air...which is what i expected

ComfortZone :

It could be that you have a blown capacitor in the outdoor unit. You will have to open the access panel and check to see if it is bulging from the top.

ComfortZone :

Full Size Image

Customer:

thanks...checking now

ComfortZone :

Bulging capacitor.

Full Size Image

Customer:

I have an upstairs unit and a downstairs unit. I turned both off and looked at each and do not see any difference, other than the one that is operating correctly is wet

ComfortZone :

You have 2 AC systems, is that correct?

Customer:

yes

ComfortZone :

From what you tell me, it sounds as if the one that is not cooling has a problem with either the compressor not starting or you are low on refrigerant. The only sure way to know is with a set of gages or an multimeter.

Customer:

ok. I guess there is no way to fix it myself? I called a repairman but will not be able to make it out til Monday.

ComfortZone :

You could try to replace the capacitor. Just get the numbers off the one that is in there and go to a supply house and see if they will sell you one. It costs about 20 dollars and that may fix your problem. Or you can wait on the repairman.

Customer:

ok. thanks

ComfortZone :

Sorry I could not get it working today. Thanks for using the site.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask ComfortZone Your Own Question
ComfortZone
ComfortZone
ComfortZone, HVAC Technician
Category: HVAC
Satisfied Customers: 516
516 Satisfied Customers
Experience: 10 years in the HVAC industry.

ComfortZone is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a Rudd Air Conditioner installed last September
I have a Rudd Air Conditioner installed last September 27,2017. This is the first summer for it, and it is miserable. HVAC company that installed it has been her multiple times trying to fix the probl… read more
canuck the pro
canuck the pro
282 satisfied customers
My ac is not blowing cool air. I think the coil might be
My ac is not blowing cool air. I think the coil might be frozen but just checked the line and it doesn't seem to be frozen. Any suggestions on how to fix this? I've turned the system off at circuit br… read more
oilburn62
oilburn62
27 satisfied customers
We have a 5-ton Goodman packaged AC/heat-pump unit which is
We have a 5-ton Goodman packaged AC/heat-pump unit which is 8 years old. It sits outside the house on a slab. It is very cold today: 0 degrees F. Last night I set the digital thermostat down to 69 F a… read more
DennisMooreAC
DennisMooreAC
Service Engineer
Associate Degree
76 satisfied customers
my question is that i have a honeywell focus pro 6000 thermostat
my question is that i have a honeywell focus pro 6000 thermostat recently installed in my home. the thermiostat seems to be working fine, but i noticed that the room temperature has not changed from 7… read more
HVAC Applications
HVAC Applications
11 satisfied customers
Have a Lennox C33-38A-2F-2 A/C unit. Compressor was running
Have a Lennox C33-38A-2F-2 A/C unit. Compressor was running and so was fan but only blowing hot Air. Set @77 indoor temp was 83. I looked at the attic unit and noticed a build up of Ice around the com… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
We are at a hotel and bought 50 units PTCO94E35AxxxAB about
We are at a hotel and bought 50 units PTCO94E35AxxxAB about 15 months ago. This summer we had trouble with 48 of them short cycling while cooling. The warrenty guy gave me new thermomisters to put on … read more
hvacexpertjoe
hvacexpertjoe
Electronics Technician
Vocational, Technical or Trade Scho
80 satisfied customers
I have a Rheem RCHA-36A2GG17 central air conditioning unit.
I have a Rheem RCHA-36A2GG17 central air conditioning unit. It wiil run for a few minutes and turne off. it is no longer cooling the house. Any suggestions on how to fix it?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Just had a complete Goodman Unit installed (Condensing Unit
Just had a complete Goodman Unit installed (Condensing Unit (SSX140481A), Gas Furnace (GMVC951155DX), Evaporator Coil (CAPF4860D6) and a Thermostatic Expansion Valve (TX5N4)). After installed the A/C … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Our A/C condenser outside is running but is not cooling properly.
Our A/C condenser outside is running but is not cooling properly. Minimal air is coming through the vents. The inside temperature has been at 81-84 degrees the last 3 days. I thought it was just extre… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My A/C is on but not blowing very much air through the vents
My A/C is on but not blowing very much air through the vents and the temperature in the house just won't come down. I've read this might be the unit's filter, could this be the case? If so, how do I r… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a Rheem heat pump that I purchased in June 2009 (Model
I have a Rheem heat pump that I purchased in June 2009 (Model # XXXXX; Serial # XXXXX). This unit heats and cools the second story. Last week the upstairs unit stopped cooling. The technician said the… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
We live in Florida, and when we go north for the summer were
We live in Florida, and when we go north for the summer were told to set the dehumidistat at 60* and the thermostat at auto, cool and 70 degrees. If it is set at higher than 70 we may have mildew. My … read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
My tempstar thermostat has the A/C temp set at 72. The AC
My tempstar thermostat has the A/C temp set at 72. The AC came on last night around 9pm and ran constantly until 10:45 this morning when I finally just turned it off. The temperature that shows on the… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
I had a Carrier Infinity Heat Pump and air handler (4 ton)
I had a Carrier Infinity Heat Pump and air handler (4 ton) installed a couple of years ago and my electric bills are going up in the winter, not down. I don't know if it's because of colder weather re… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
I have a 5 ton Trane air conditioning unit. My house is 2200
I have a 5 ton Trane air conditioning unit. My house is 2200 sq. feet. I live in Phoenix Az. It is currently very hot. My problem is this: Even though I have set my temp on auto and cooling and indoor… read more
Heath
Heath
Vocational, Technical or Trade Scho
1,002 satisfied customers
The honeywell AC control always shows as 72 F regardless hold
The honeywell AC control always shows as 72 F regardless hold to reduce the temperature although the temperature is 80 F… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
We are a HVAC contractor in the Tampa Bay area and we have
We are a HVAC contractor in the Tampa Bay area and we have had an ongoing problem with a customer that insist he had a problem with the location of his thermostat. The stat was in the same location fo… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I had a new totaline thermostat installed, However we are having
I had a new totaline thermostat installed, However we are having prolems with it. The tempeature fluctuates and the HVAC runs constantly. We just had a new unit installed and went from a 3 ton to 3.5 … read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x