Customer Question
What could cause the blower...
What could cause the blower to not have a high output,
new moter with 2x as much horsepower as the previous?
Submitted: 8 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 2 minutes by:
6/23/2010
HVAC Technician: Mark Henley, Journeyman Technician replied 8 years ago
Mark Henley
Mark Henley, Journeyman Technician
Category: HVAC
Satisfied Customers: 3,217
Experience: UA Journeyman Pipefitter , HVAC, Refrigeration, DDC controls. 26 years.Commercial & residential
Verified
Chat Conversation Started
Mark Henley :

Hi, is this a blower motor ? Horse power is relative to other conditions having a higher horse power doesn't mean that it will move air unless the previous motor was undersized and could not run up to the rated RPM for the unit, is a lack of airflow the problem you are having ?

Customer:

yes it has low velicity

Customer:

we installed a new motor, where the old one had 1/8th hp, this one has 1/4 hp, also it has a new limit switch, and we removed and cleand the squirall cage

Customer:

in changing the changing the motor, could the capasitor still think there is a 18HP motor, and not allow the motor to rotate at the proper RPM?

Customer:

i mean 1/8hp

Mark Henley :

Hi, you definitely needed to change the capacitor with the new motor, were they rated for the same micro-farads ( MFD ) ? Usually 5 or 7.5 ? , the capacitor could have been the problem

Customer: where is the capacitor located
Mark Henley :

Hi, its a silver type can with electrical terminals on it, its usually located right on the motor housing but if you follow the wires from the motor you will find the silver can that I am talking about, it looks like this picture below

Full Size Image

Customer: we found the catacitor attached to the outside AC unit, none close to or at the inside furnace section, is this the correct one?
Mark Henley :

Hi, no that one is for the outdoor unit, there has to be in indoors but if there is not then there may have not been one on the original motor but the new motor definitely needs one, can you look on the label of the motor and see the )| sign on it anywhere in the wiring of it, also it should say that it needs a 7.5 or 5 mfd right on the motor, let me know.

Customer: mfd not found anywhere on the motor, did find SFA 5.9 and s.f 1.35, it is an emerson motor
Customer: http://www.google.com/url?sa=t&source=web&cd=2&ved=0CBYQFjAB&url=http%3A%2F%2Fwww.alpinehomeair.com%2F_viewresource.cfm%2FID%2F1645%2Fp%2FEmerson%25208000%2520Dimensional%2520Print&ei=EIMiTJ3DJsP78Ab6wIC0BQ&usg=AFQjCNFKdJO-fSu8aO3T-k1tuHzf0dv61w
Mark Henley :

Hi, ok this is a 56 frame motor, the capcitor is probably internal or attaqched to it, so no need to worry about that,

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Mark Henley Your Own Question
Mark Henley
Mark Henley
Mark Henley, Journeyman Technician
Category: HVAC
Satisfied Customers: 3,217
3,217 Satisfied Customers
Experience: UA Journeyman Pipefitter , HVAC, Refrigeration, DDC controls. 26 years.Commercial & residential

Mark Henley is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I am a home owner and recently had a new frigidaire
Hello. I am a home owner and recently had a new frigidaire fg7tc installed. it's running but doesn't seem to have much air output. the house isn't cooling off as much as i had hoped. the house had bee… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,024 satisfied customers
can I set my EL296E for the fan to be working continuously
can I set my EL296E for the fan to be working continuously at low speed and change speed when heat or cool is required?… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
Im building a new home and the builder installed a Lennox
I'm building a new home and the builder installed a Lennox ML193UH gas furnace. I've noticed a loud high pitched humming sound when the blower is running. It almost sounds like a tuning fork sound so … read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Hello, have a York furnace to heath my residence, model is
Hello, have a York furnace to heath my residence, model is TG85130d20mp11a with an emerson electronic card model 4702g, The fan runs ok but the air coming from the outlet makes too much noise, I think… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I have a 80% GMT 115-5a it starts up and then it goes through
I have a 80% GMT 115-5a it starts up and then it goes through this cycle where it will shut the flame off after only 25 seconds after the blower starts. in a few seconds it will light up for a few sec… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My furnace is making a loud noise and then shuts off...could
My furnace is making a loud noise and then shuts off...could this be a problem with my Blower Motor? I have a Rheem Criterion II… read more
Jerry
Jerry
Plumber
High School or GED
1,456 satisfied customers
my ac seems to blow real slow. I have had the motor replaced
my ac seems to blow real slow. I have had the motor replaced with a unit that was suppose to be the same as the origional. my light bill has went up $50.00 per month and the unit seems to be running a… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
hello, I hvae a weatherking furnace mo# XXXXX I was
hello, I hvae a weatherking furnace mo# XXXXX I was repalcing the blower motor. Imark the wires for the computer but when I tried to start it the moter sparked. I placed the red wire on m1, back on co… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Goodman Janitrol hvac and having problems now with
I have a Goodman Janitrol hvac and having problems now with the furnace blowing enough warm air, could I have an obstuction in the cold air intake or is it the blower moter. I ordered a new capacitor … read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
I am replacing a 40 year old Chrysler Airtemp 105K BTU/84K
I am replacing a 40 year old Chrysler Airtemp 105K BTU/84K BTU furnace with a Bryant 310JAV048090. Our home has been remodeled and the resulting duct work contains restrictions which greatly reduce th… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Is it possible to decrease the heat output on a Lennox G40UH.
Is it possible to decrease the heat output on a Lennox G40UH. We live in southern california and just need the air heated a little. I would rather the system run for a longer period of time with a low… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
I have a janitrol with a model#310902ancoa serial#49712. I
I have a janitrol with a model#310902ancoa serial#49712. I have been told that the blower motor is too small for the unit. What is the reccommended size for the unit? Also are there any current blower… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Hi, my natural gas furnace cycles very frequently. Especially
Hi, my natural gas furnace cycles very frequently. Especially when its cold outside. It often cycles 2x per minute. This even occurs when its 65 in the apartment, and I set the digital thermostat to 8… read more
Tom
Tom
HVAC Technician
Vocational, Technical or Trade Scho
770 satisfied customers
I have a Ruud urka-a036jk10e option 594 built in 10/98. Basically
I have a Ruud urka-a036jk10e option 594 built in 10/98. Basically a 100,000 btu natural gas/ac outside unit. The heat quit with over temperature switch open. a few days later it happened again. I boug… read more
Bill
Bill
High School or GED
318 satisfied customers
Recently we installed in our home new heating/airconditionig
Recently we installed in our home new heating/airconditionig unit.Model MV12BN21H. Temperaturewise everything is O.K.and unit starts & stops properly but the airflow is at extremely high speed (you ca… read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
I have a Carrier Model 58STA/STX Up draft furnace. I just had
I have a Carrier Model 58STA/STX Up draft furnace. I just had a four ton air conditining system installed. My air flow is minimal on the third floor of my house. The furnace is located in the basement… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Trane airhandler unit, model TWHO42B40AO. The blower
I have a Trane airhandler unit, model TWHO42B40AO. The blower motor sounds bad. I can spin the blower and turn the breaker on, the motor will run for a short time. From a dead start, the motor hums. I… read more
tom goellner
tom goellner
owner
Vocational, Technical or Trade Scho
1,115 satisfied customers
I have an Amana GCCA090 furnace that is blinking a 4 blink
I have an Amana GCCA090 furnace that is blinking a 4 blink error code. The blower motor is running but the gas is not flowing or igniting. What is wrong and how can I fix it?… read more
JBM HVAC
JBM HVAC
HVAC/R Technician
Vocational, Technical or Trade Scho
50 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x