HVAC

Have HVAC questions? Ask an HVAC Expert for answers

Ask an Expert,
Get an Answer ASAP!

carrier 38tkbo300 a coil freezes up checked for leaks

Customer Question
carrier 38tkbo300...
carrier 38tkbo300 a coil freezes up checked for leaks found one at service port on low side added 8 oz of 22 lasted a week worked for 5 days know when i hook gauges up and start unit low side goes to 35 psi after 20 min started to add freon stopped and gauge pegged at 150 on low side after i shut valve and never went back down.

inside temp was 72 degrees when check a coil still freezes up changed furnance filter .

lost i do small 134a system on vending machine
Submitted: 8 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 13 minutes by:
6/21/2010
HVAC Technician: gotoman for ac, HVAC Technician replied 8 years ago
gotoman for ac
gotoman for ac, HVAC Technician
Category: HVAC
Satisfied Customers: 5,358
Experience: 51 years of experience install design and repair of all makes and models of AC
Verified
Chat Conversation Started
gotoman for ac :

You still have a leak. The pressure should be about 65 to 70 psi on low side. You may also have a restriction. The way you describe if you were adding gas to low side and not watching high side it probably open internal relief valve. Russ

Customer:

ok unit doesn't have a drier either and internal relief valve is that like a txv

gotoman for ac :

The internal relief valve is inside compressor. It opens when pressure is to high. Russ

gotoman for ac :

If you have further questions please get back with me. Russ

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask gotoman for ac Your Own Question
gotoman for ac
gotoman for ac
gotoman for ac, HVAC Technician
Category: HVAC
Satisfied Customers: 5,358
5,358 Satisfied Customers
Experience: 51 years of experience install design and repair of all makes and models of AC

gotoman for ac is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I am an auto mechanic and work on a/c all the time. I own a
Hello, I am an auto mechanic and work on a/c all the time. I own a True Manufacturing double door cooler model GDM-35. It's an older unit and we've had to ad Freon to it every few years. It's that tim… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
I have an antique True double glass door cooler made in
Hello, I have an antique True double glass door cooler made in 1995. The spec sticker inside has been damaged so I can't read the high and low pressures. I had a local HVAC guy come over and put his g… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Billy. 1. AT customer's found suction line iced up from a-coil to compressor and c
Hi Billy. 1. AT customer's found suction line iced up from a-coil to compressor and compressor and receiver tank also iced up. 2. Found fan motor burnt up in air handler-replaced with new. Found a-coi… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
enviro air 12000 btu mini split evap freezing up . filter is
enviro air 12000 btu mini split evap freezing up . filter is clear fan is running. .The condencer only has a 5 foot line set seporating it fm evap coil. can this be the root of my problem. It cools a … read more
gotoman for ac
gotoman for ac
HVAC Technician
Associate Degree
5,358 satisfied customers
I replaced my line set 3/8 and 7/8 50ft which had a leak in
I replaced my line set 3/8 and 7/8 50ft which had a leak in the suction which caused the evaporator and condenser to freeze over several times. I replaced the line set and added a dryer on the liquid … read more
gotoman for ac
gotoman for ac
HVAC Technician
Associate Degree
5,358 satisfied customers
I have a laboratory refrigerator that I am troubleshooting,
I have a laboratory refrigerator that I am troubleshooting, but the manufacturer specs on the nameplate do not seem to be reasonable. The unit is a two door upright with a volume of 40 ft^3. It has a … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
The a/c gauge pressure on the low side was 40 psi and on the
The a/c gauge pressure on the low side was 40 psi and on the high side was 350 psi. What should I do? I just refilled with 134a after replacing high and low valves. Temperature outside is about 80 deg… read more
spivco
spivco
153 satisfied customers
My home ac system is not cooling effectively. It is an r-22
My home ac system is not cooling effectively. It is an r-22 system and I am certified in auto ac. I installed a set of manifold gauges and my low side pressure is 50 psi but high side is only 80 to 85… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Have a comfortmaker A/C unit that may need recharging. Model
Have a comfortmaker A/C unit that may need recharging. Model number is XXXXX The chart inside the panel that shows ambient outdoor temperature, refrigerant temperatures and pressures, is water damaged… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I use Atlas Frost-top with granite on top of the unit. It normally
I use Atlas Frost-top with granite on top of the unit. It normally takes about 45 minutes to freeze the granite (frost on granite) . Lately only 50% of the granite freeze up. There is water between th… read more
drcool299
drcool299
shop owner
Bachelor\u0027s Degree
22 satisfied customers
What type of pressures would you have if there was a restriction
What type of pressures would you have if there was a restriction at the metering device on a residential air conditioner?… read more
drcool299
drcool299
shop owner
Bachelor\u0027s Degree
22 satisfied customers
I HAVE A COLEMAN ROOF AIR ON AN RV MODEL 6759A707. WHAT IS
I HAVE A COLEMAN ROOF AIR ON AN RV MODEL 6759A707. WHAT IS THE OPERATING PRESSURE OF THE LOW SIDE WHEN AC IS RUNNING. REPLACED THE BLOWER AND CAP. WHEN I REPLACED THE CONDENSOR.. THE TAG SAYS LOW SIDE… read more
Tom
Tom
HVAC Technician
Vocational, Technical or Trade Scho
770 satisfied customers
I HAVE A HEAT PUMP THAT IS FREEZING UP FROM THE LINE OUT AT
I HAVE A HEAT PUMP THAT IS FREEZING UP FROM THE LINE OUT AT THE PUMP ALL THE WAY BACK INTO THE COILS. I CONTACTED A TECH ON HERE YESTERDAY AND HE TOLD ME SOME OF THE CAUSES. I CHECKED THE COIL AND IT … read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
Hi, Im working on a Carrier Roomtop- 50AH060500, was working
Hi, I'm working on a Carrier Roomtop- 50AH060500, was working fine up until last week, when the outside temp dropped to 45, the evaporator coil started icing up after about 8 hours of use, I defrosted… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My unit only runs for a couple of seconds when I start it.
My unit only runs for a couple of seconds when I start it. Could it be low on freon? The low pressure line reads 150 psi while idle. The Model number is XXXXX… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Trane residential ac unit it not cooling low 35 / high side
Trane residential ac unit it not cooling low 35 / high side 185. model #TTB 018C100AO SERIAL # XXXXX Desine LOW 300 PSI, H 300PSI ,IT R-22. My question is what is the presure low and high side ? tempr… read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
what is wrong if my coil freezes up my hi side is 300 and low
what is wrong if my coil freezes up my hi side is 300 and low side is 40 psi it has a txv and units are clean… read more
Electrifier
Electrifier
Owner - Contractor
Bachelor's Degree
147 satisfied customers
4 ton hp. spilt system. Found bad txv & replaced. When valve
4 ton hp. spilt system. Found bad txv & replaced. When valve was off, notice very small droplets of either water or oil, not sure which (to small & not enough to tell) on inside of entrance to coil ju… read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.