The blower motor stopped working on my Lennox AC unit B24Q3.5-1P.

I am electric savy an...
The blower motor stopped working on my Lennox AC unit B24Q3.5-1P. I am electric savy an prefer to do this myself. Trying to get some tips on specifics to look at before I start digging. I have pictures of wiring diagrams off the blower itself.
Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 minute by:
6/19/2010
Richard
Richard, Technical Manager
Category: HVAC
Satisfied Customers: 1,514
Experience: 27 years of Experience, NATE Certified, professional trainer
Verified
Chat Conversation Started
Richard :

Hello

Customer:

hello

Richard :

I am assuming your talking about the outdoor condensor fan motor? If so, this is pressty straight forward. however before you replace the motor you might want to check the capacitor. Do you know how to do this?

Richard :

Hello

Customer:

The motor I am taling about is the one that forces the air though the ducting. Is that the condensor fan motor?

Richard :

Alright this will be a little different

Richard :

Do you have a volt meter you can use?

Customer:

Yes

Richard :

Alright will the fan run if you set the thermostat to fan ON?

Customer:

No, I have alternated between auto and on, with no change. fan does not kick on at all.

Richard :

There must be a little problem with the site I had sent you another message. however, locate the blower section ( gas furnace?) find the fan motor there will be several wires coming from it. the white is the nuetral and the otheres a various speeds. Typically black the cool but not always. the board may be marked. Set it to cool and check for power. This typically a PSC motro so there might be a capacitor on there as well. Do you know how to check that? Next if no power make a jumper wire from R to G on the low voltage thermostat connections and tell me if the motor comes on then

Customer:

I know how to check the cap. This will take a moment.

Richard :

ok

Customer:

The capacitor is bad. I will recap, so you can let me know if there is something that I may have misstepped. I securred power to the unit.

Customer:

Then shorted the leads on the capacitor. should have brought its potential to 0.0 I set my multimeter to 2M ohms and checked it and it stayed at 0 ohms.

Customer:

I am going to check one more time, because I did not disconnect it from the rest of the gear.

Customer:

The capacitor is working fine. I isolated it and grows to infinite the way it should.

Customer:

I reconnected the capacitor, applied power, set the unit to kick on. I felt the coils start to cool and put a jumper between R and G, but nothing happened.

Richard :

hello

Customer:

I am on

Richard :

Check for voltage between cool and neutral on the board you should have power if not check for power between Y and C on the low voltage wires and G and C

Richard :

if you try to spin the motor by hand will it spin freely?

Richard :

you can try another speed but if you have power the motor has probably failed

Customer:

I had 0 at cool and neutral. 0 at Y and C. 26.6 v at G and C. I will go check motor freeplay.

Customer:

The motor spins easily

Richard :

Hello

Customer:

hello

Richard :

This might be your problem if you had no voltage between Y and C either the thermostat failed or was not set to cool and temp lowered or a broken wire. R is the 24 volts to the stat on a call for cool it energizes the Y terminal

Richard :

put a jumper from R to Y on the board nd tell me what happens.

Richard :

Thank you

Customer:

So when I set the AC on, and the fan should be blowing, I should see 0 volts at Y and R.

Customer:

I set the power on, motor should have been on. I had 0 at y and r. 26 at y and c. 26 at y and neutral, and 26 at g and c.

Richard :

Yes 0 at Y and R and 24 at Y and C

Richard :

If no power at the motor your board may have failed or a loose wire. Can you put power direct to motor?

Customer:

I am not sure how to do that.

Customer:

JUmper?

Richard :

See if you can take the motor leads and hook them to direct power. if there are open terminals on L1 and Neutral or and extention cord. Only do this if you feel comfortable. i just want to make sure the motor will run beofre I tell you , you have a bad board.

Richard :

If you had power to Y and C there should have been power at Cool and neutral

Customer:

Now I am not sure if I had neutral right or not. My diagram is showing Y1 (yellow) is cool. R (red) is power. G (green) is blower. w1 (white) is heat, C (blue) is common. I have been checking as if w1 is neutral. Nothing is labled neutral so I went with white as neutral, but now I believe that is wrong.

Customer:

Is C (blue) also my neutral?

Customer:

I have access to the leads to the motor. So potentially if I have the motor power applied at the board leads and the motor is not on it should be the motor. If there is no power at the leads to bring the motor on when there should be, then it is the board?

Customer:

With AC on and fan set to on, I checked at the fan motor. At the motor, Blue (Low), then Red(med), and then Black (high) to Ground and all showed 120VAC. I would think that there should be something there to limit which one the power is coming from (low, medium, or high). Diagram shows the other orange lead, but that is taking back to the transformer.

Customer:

I have some good pictures of the board and the diagram, but I don't know how to post it, in this chat room. Is there an email I can send the picture to.

Richard :

Hello

Richard :

You can not send email through here. However you have 120 volts from all of the motor speeds to neutral at the same time?

Customer:

Yes

Richard :

To be sure you were not measuring feedback take the motor leads off the board and measure voltage at the board.

Customer:

I will try that

Richard :

Ok let me know what you find.

Customer:

I pulled the motor connections off the board, turned ac and fan to on and got nothing at the board. Then just to double check witht the connections removed, I got 120V at the motor again, so it was feedback of the transformer.

Richard :

Hello

Richard :

i am not exaclty sure why you have voltage there but the low voltage transformer should not influence the readings on the motor terminals. With the leads off are you able to hook up power to the motor to see if it will run. it is sounding like a failed board but i just want to be sure.

Customer:

I tried to figure out the way to check the blower motor, but with the confined spacing and lack of experience, I am not that comfortable with it.

Richard :

Use your ohm meter to check the motor. One side to the White then check to the remaining leads.

Customer:

From the looks of the board, I did see a resistor that looked burnt. It did not show infinite, but it did show a lot of resistance. About 1.4 megohms, if I remember correctly, that is pretty close to being an open.

Richard
Richard, Technical Manager
Category: HVAC
Satisfied Customers: 1,514
Experience: 27 years of Experience, NATE Certified, professional trainer
Verified
Richard and 87 other HVAC Specialists are ready to help you
Ask your own question now
Ask Richard Your Own Question
Richard
Richard
Richard, Technical Manager
Category: HVAC
Satisfied Customers: 1,514
1,514 Satisfied Customers
Experience: 27 years of Experience, NATE Certified, professional trainer

Richard is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,730 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I am looking for a gas valve for my Duo Therm Model 708001-2
I am looking for a gas valve for my Duo Therm Model 708001-2 mobile home furnace. The numbers on the valve are TF-555 TM-6 … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,058 satisfied customers
I would like to install a new thermostat with my new hvac
Hi I would like to install a new thermostat with my new hvac and I need some documentation please … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Rheem RGDE 07NNMAGR what does a ingniter moduel look like.
rheem RGDE 07NNMAGR what does a ingniter moduel look like … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Jotul GZ 550 DVII Acadia. The pilot light lights
Hello I have a Jotul GZ 550 DVII Acadia. The pilot light lights and burns but it will not flame up. I had my local fireplace dealer come look at it and they said it was the thermocouple but they did n… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a Honeywell thrmosttat RTH221B1021 no instructions.
I have a Honeywell thrmosttat RTH221B1021 no instructions. How do I set it. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Home heat pump if the low side gas got 10 degrees warmer
home heat pumpif the low side gas got 10 degrees warmer after it left the evaporator and the high side gas got 10 degrees cooler in the condenser at the same time, what effect would that have on the e… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Looking for 2 filters RAC-45BE3AS. Just started. Where i can
Looking for 2 filters RAC-45BE3AS JA: I'll do all I can to help. How long have you been dealing with this? Customer: Just started JA: Do you plan on doing the work yourself? Customer: Yes JA: Anything… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
In 2003, we had a new high-end Carrier Infinity Weathermaker
In 2003, we had a new high-end Carrier Infinity Weathermaker furnace installed - Model 58MVP-100-20 (run on propane). 8 years later, in 2011 - while still under warranty (parts and labor) the main hea… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Riello 40 series mectron oil burner has issues on cold
Riello 40 series mectron oil burner has issues on cold start … read more
Brian
Brian
Plumbing & Heating Engineer
115 satisfied customers
I just bought an older manufactured home with a Honeywell
I just bought an older manufactured home with a Honeywell Chromo therm thermostat. I cannot get the fan to turn off. It's set to auto and off but continues to run. Help … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
If a gas water heater with an FVIR is installed in a room
If a gas water heater with an FVIR is installed in a room with a washing machine, can cleaning products such as liquid laundry detergent and chlorine bleach trip the FVIR? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have an un identified heating control valve on my boiler.
I have an un identified heating control valve on my boiler. I have anamtrol tank on the side of my unit so I am hoping that the valves are also amtrol product. If I send you a picture can you identify… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Roll out switch keeps tripping on my heil furnace replaced
Roll out switch keeps tripping on my heil furnace replaced both them also high limit switch and air inducer … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Hunter 44860 thermostat, manual mode, the heat icon does not
Hunter 44860 thermostat, manual mode, the heat icon does not appear on the screen.. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have and I comfort thermostat and a brand new heat pump.
I have and I comfort thermostat and a brand new heat pump. The technician set it up so that the emergency heat strips kick on at 35° I would like to change that setting down closer to 10 or 15°F I hav… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Trane model tud080c936a1 (XE78) furnace. Sometimes
I have a Trane model tud080c936a1 (XE78) furnace. Sometimes the furnace fails to light and I get the two blinking lights error code. In watching the furnace I can see that ignitor kicks on, but the bu… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a thermostat model # TSTATBBPRF01 under that is
I have a Bryant thermostat model # TSTATBBPRF01 under that is###-##-#### Can I get a users manual telling me how too hook it up to a second zone heating system … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have an oil burner question, One week, Yes, Please connect
Please connect me with someone who deals with oil burner questions… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x