I have a lifebreath unit,connected to it a 5 ton a/c condenser…

Customer Question
I have a lifebreath unit,connected...
I have a lifebreath unit,connected to it a 5 ton a/c condenser and coil.A/c unit is properly charged but coil keeps freezing up.I was told that you need 400cfm per ton,but it seems like theres not enough air flow.How can I increace the flow of air?
Submitted: 8 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 29 minutes by:
6/17/2010
HVAC Technician: Tim H., HVAC Professional replied 8 years ago
Tim H.
Tim H., HVAC Professional
Category: HVAC
Satisfied Customers: 3,972
Experience: Experienced in all aspects of HVAC, both residential and commercial.
Verified
Chat Conversation Started
Ask Your Own HVAC Question
HVAC Technician: Tim H., HVAC Professional replied 8 years ago
Check your furnace or air handler blower. If it's multispeed, you may have to switch leads to a faster blower speed. I'm assuming you've already checked furnace or air handler filter and it's clean?
Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Tim H. Your Own Question
Tim H.
Tim H.
Tim H., HVAC Professional
Category: HVAC
Satisfied Customers: 3,972
3,972 Satisfied Customers
Experience: Experienced in all aspects of HVAC, both residential and commercial.

Tim H. is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I installed a 5 ton goodman a/c unit.Now I have to replace
I installed a 5 ton goodman a/c unit.Now I have to replace thr air handling unit for cooling and heating.i would like to replace the furnace with high efficient nuiy.anty recommendations. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I am working on a Rheem system that has two Rheem furnaces
I am working on a Rheem system that has two Rheem furnaces twin together in the basement, with a 5 ton A coil in each furnace and two 5 ton condensing units outside. The building has a basement and fi… read more
Michael Ferryman
Michael Ferryman
110 satisfied customers
We just had the TXV replaced on our new XC17 A/C - this apparently
We just had the TXV replaced on our new XC17 A/C - this apparently came up as a problem in testing a complaint we had of "hard starting." During the repair, they lowered the blower speed. When I quest… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
I have a snyder general furnace model # XXXXX and a
I have a snyder general furnace model # XXXXX and a confortmaker condensing unit model # XXXXX Now and then I have to get the unit recharged as I apparently have a slow leak. The tech added about 4 an… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
Can an oversized heat pump (5 ton) with undersized ducts (3-3.5
Can an oversized heat pump (5 ton) with undersized ducts (3-3.5 ton) cause pressure build up to cause a rigid air vent duct connection to come apart? Can this senario also cause excessive condensation… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
Error lights on Lennox Harmony III Zone Control System
I have a Lennox Harmony III Zone Control System, controlling A/C distribution between the 1st floor and 2nd floor. Today we noticed the upstairs was too warm and the air flow seemed very slow. I looke… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Central A/C Ton size of condenser and air handling units
Central A/C: "Ton" size of condenser and air handling units - matching to duct size. I was informed that the ton size of the condenser (such as 3 ton = 36,000 BTUs) is matched to a particular size of … read more
freon
freon
Owner
High School or GED
214 satisfied customers
I just had a bryant 3.5 ton installed with a 5 ton condenser
I just had a bryant 3.5 ton installed with a 5 ton condenser? I have approximately 2000sq ft in my house. The units doesnt seem to be working very well. Is it trur the unit is spec's so it wont go bel… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
have a gmv950905dx with a goodman heat pump outdoor unit,coil
have a gmv950905dx with a goodman heat pump outdoor unit,coil is freezing up ,appears it is not moving enough air in cooling mode???????… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have an 850 square foot apartment. The ac is freezing up.
I have an 850 square foot apartment. The ac is freezing up. The a/c repairman says it is because of a mismatched system. I have a 2 ton 10 seer outside unit with a 1.5 ton inside coil. I have about 15… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
MY coil unit keeps frosting up and not blowing cool air. What
MY coil unit keeps frosting up and not blowing cool air. What can I do to fix this, and is it something I can do my self? Also can I buy and install the refrigerant R22 my self?… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
My husband was persuaded to replace our still functioning HVAC
My husband was persuaded to replace our still functioning HVAC system by someone he knows. This man has been in this business for several years. My husband contacted an acquaintance in the business fo… read more
Jerry M.
Jerry M.
Senior HVAC Technician
High School or GED
133 satisfied customers
We own a 25-year old center hall colonial. Upper floors have
We own a 25-year old center hall colonial. Upper floors have a total of 2300 sqft & basement has two finished rooms adding about 500 sqft. The furnace replaced 1997 by previous owner. It is a Lenox G2… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
my a/c unit freezes after about 3 hours of use. Any ideas why
my a/c unit freezes after about 3 hours of use. Any ideas why? I had the freon checked. I cleaned the condenser coil. what next?… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
Hi I am hoping to replace my 5 ton, 10yo Rheem (which I am
Hi I am hoping to replace my 5 ton, 10yo Rheem (which I am told is too large for my 2100 sf house) with a 4 ton Carrier. I have talked with 5 Carrier dealers and remain confused. I was thinking about … read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
hi, good morning! we just lived in ths new house for 2 weeks,
hi, good morning! we just lived in ths new house for 2 weeks, they have installed the Carrier AC unit and Compressor unit outside. We noticed that the air flow from the AC vent is so loud, like wind s… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
I had a 4 ton Lennox heat pump installed three weeks ago. It
I had a 4 ton Lennox heat pump installed three weeks ago. It worked fine the first two weeks and has since started freezing up. I have a three story house and there is a air return on the third floor … read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
I think i have the same problem. I have a carrier weathermaker
I think i have the same problem. I have a carrier weathermaker 8000, and i just cleaned up a large puddle of water. its still leaking. So, just call an HVAC to see if its copper?… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x