Customer Question
Hello ,  I sent Mark a...
Hello ,  I sent Mark a question the other day about a 5ton ac unit. The high side was getting cold and he told me there was probably a restriction somewhere in the line, he was correct, I followed the line until it got hot and found the filter/drier was clogged. I removed it to and tried the unit to see if it would work. It did take a charge 65psi on the suction side. The compressor was kicking out before, now its not. The compressor runs and you can hear the freon flowing but the suciton side now is not getting cold. What would cause this?
Submitted: 8 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 29 minutes by:
6/17/2010
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 8 years ago
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 23,151
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified
Chat Conversation Started
Billy :

what are your high and low pressures now? I assume this is R22?

Customer:

Yes it is r22, i am not sure now, i am not at the unit, the low side was 67

Customer:

great feedback btw

Customer:

If it was undercharged wouldn't it start to get cold though?

Billy :

sorry computer issues.....that is why I need the high side reading.....a unit can be low and actually start to freeze...and it can be low with a warm suction pipe....The head pressure and super heat would give me better direction

Billy :

If head is 300 or 200 would tell more of the story

Customer:

yeah i have seen them freeze when low. i am not a hvac tech but know a little about it, both suction and high side feel the same temp. i can hear the freon flowing but neither line is changing temp.

Customer:

could it be possible for a restriction in the line still?

Customer:

before the high side was getting cold and kicking out the compressor now the compress is running normal but no temp. change

Billy :

Thanks....the reason I ask is if the valves are compromised it will run...but there is no compression...or little compression....this leads to somewhat equal pressures and a warm suction

Billy :

I would reclaim...and then run a reverse nitrogen blast through to clear the system...then vac and recharge. Air in the system with refigerant also gives warm line

Customer:

can you explain abou the valves being compromised?

Customer:

you mean blast through the high side?

Customer:

ok i got you, i understand. if the readings are say 300 then what?

Customer:

there is no isolation valve on the high side

Billy :

Then we are looking at obstruction still or bad metering device

Customer:

the reading should be?

Ask Your Own HVAC Question
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 8 years ago
Chat Conversation Ended

Your expert is gathering additional information and will be back with you shortly.
Ask Your Own HVAC Question
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 8 years ago

No king valve or anything at condenser for high side?

9:18 AM

If the valves were compromised by high head....then we could be leaking refrigerant back around the valves...this would cause low head

9:19 AM

I apologize but I must take care of some issues and will be offline for 30 min...I will respond asap.

Ask Your Own HVAC Question
Customer reply replied 8 years ago
This unit was damaged by thieves, and the tech removed the valve in order to repair it and couldn't get the isolation vavle so he just installed a tee with a schrader valve
Customer reply replied 8 years ago
This unit was damaged by thieves, and the tech removed the valve in order to repair it and couldn't get the isolation vavle so he just installed a tee with a schrader valve
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 8 years ago

I understand....well here is where you must decide on how much to put into the unit...In my opinion, the system needs to purged out with nitrogen and vacuumed and recharged...it would be best if a valve were there....but....if you evacuate...remove liquid line from condenser, then you can purge through the evaporator and blow right out the liquid line.

 

I know you do not want extra work...but you are in a situation requiring replacement or adequate repair. To achieve adequate repair means starting with a system that is known to be clear. This sets the stage for all other testing and or work.

Ask Your Own HVAC Question
Customer reply replied 8 years ago
I will take the extra work if I can get this unit running. Do you thinkg a kink in the line would cause this? BOth lines are going in the roof and can't be seen for about a foot. Is it possible that one of the lines is kinked causing this problem?
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 8 years ago

That is a great question...if I see high head pressure..that leads me towards blockage..or overcharge. If I see med to low head it sends me a different direction

 

Ask Your Own HVAC Question
Customer reply replied 8 years ago

ok if its low then where are we?

 

HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 8 years ago

Then we are at a point of seeing if the metering device (txv, cap tube, orifice etc) is damaged, stuck etc. or if the valves have been damaged by pushing against the high head pressure

 

Ask Your Own HVAC Question
Customer reply replied 8 years ago
ok thanks for your help I am going to go try out this and see what happens. Thanks again.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 8 years ago
You are very welcome. I will leave this open for you to respond to in case you have any issues. I wish you luck!
Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask BillyHvac Your Own Question
BillyHvac
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 23,151
23,151 Satisfied Customers
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics

BillyHvac is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
What be the time required for the high and low pressure side
What be the time required for the high and low pressure side to equalize right after you turn off a Lennox X-13 central air conditioner… read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
463 satisfied customers
My rheem model either pka, pla, pmb, pmc, pnj, ppa is tripping
My rheem model either pka, pla, pmb, pmc, pnj, ppa is tripping on high head pressure. on the r-22 side its reading 60, and on the hot side when the unit starts up its reading 250. the 250 goes up to 4… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I need to diagnose a pressure switch lockout issue on a heatpump.
I need to diagnose a pressure switch lockout issue on a heatpump. For the last 2 seasons during summer I got the issue sporadic (3-4 times during the season). But now it is also happening during heati… read more
D.E. Anderson
D.E. Anderson
Industrial Refrigeration Service Manager
200 satisfied customers
have a/c only 1year old unit froze up filter ok coil clean
have a/c only 1year old unit froze up filter ok coil clean unit freeze at compressor on suction side first is compressor bad or is txv bad? Freon was reclaimed & reinstalled by scale r22 system tec. s… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
State Licensed Mechanical Contractor
23,151 satisfied customers
I have an older trane XE 1200 split system that I recently
I have an older trane XE 1200 split system that I recently changed a compressor for the unit. As a rule I usually change the liquid line filter when I change a compressor but on this one I had trouble… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
State Licensed Mechanical Contractor
23,151 satisfied customers
I have a 5 ton heat pump package unit.I replaced the
I have a 5 ton heat pump package unit.I replaced the compressor and unit ran then next day head pressures are rising unit cuts out then restarts cuts out again. Now blowing cold in the morning ?… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Hi, I have a 10 year old Carrier commercial heat pump - running
Hi, I have a 10 year old Carrier commercial heat pump - running in heating mode. Works fine, but the high pressure switch kicks off after some time, because the pressure starts to jump up and down - w… read more
V12Tech
V12Tech
252 satisfied customers
GRANDAIRE, MODEL# XXXXX HEAT PUMP IS SHORT CYCLING IN
GRANDAIRE, MODEL# XXXXX HEAT PUMP IS SHORT CYCLING IN THE HEAT MODE ONLY, WHEN IN COOL MODE, IT RUNS PERFECT. THE FREON CHARGE IS GOOD, I CHANGED OUT THE THERMOSTAT, STILL SAME PROBLEM. WHEN I CALL FO… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Rheem R22 condensor. I cannot get the suction pressure
I have a Rheem R22 condensor. I cannot get the suction pressure to go above 30psi. I did a solvent flush on the lines and evap coil and the nitrogen flows through with no restrictions (at various pres… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
just installed a heat pump...not that familiar with heat pumps.
just installed a heat pump...not that familiar with heat pumps. well i'm not getting any pressure to my suction side except 5 psi's and i know i had enough freon in the system. when i purge the suctio… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a 4 1/2 ton ac system that is running at 20lb back pressure
I have a 4 1/2 ton ac system that is running at 20lb back pressure and 225 head pressure. I add freon and it seems to not make a difference. coils are clean, orfice is clear, filter is clean, ducts ar… read more
Heath
Heath
Vocational, Technical or Trade Scho
1,002 satisfied customers
Hello, I have an Arcoaire NAC036AKC3 which I believe is a 2.5
Hello, I have an Arcoaire NAC036AKC3 which I believe is a 2.5 ton unit. The compressor kicks on but I hear liquid flowing through the high side line and the liquid line. Do I have a blown compressor? … read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
Carrier heat pump model 38YRA030300 outside unit pressure problem The
Carrier heat pump model 38YRA030300 outside unit pressure problem The system can start and seems it works normally at the beginning(cold air comes out from inside vents), then the pressure (low side) … read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
I have a rheem AC with scroll compressor. Compressor was replaced
I have a rheem AC with scroll compressor. Compressor was replaced last year. What is the temperature it should run on the low pressure side. AC guy was just out here and said that it was overcharged w… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
Outdoor Unit is Goodman Model# VSH130361AA and Serial XXXXXXXXXX
Outdoor Unit is: Goodman Model#: VSH130361AA and Serial: XXXXXXXXXX installed April 2009 and a compressor replacement in Sept 2009 Indoor Unit is: Payne Model#: PF1MNCO37 and Serial: 4407A88033 instal… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a goodman 5ton ac unit, that is 3 years old, someone
I have a goodman 5ton ac unit, that is 3 years old, someone stole the copper line set and it ruined the compressor. I had the compressor replaced and now the unit still is not working. The compressor … read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
my house a/c outside unit is working but is not blowing any
my house a/c outside unit is working but is not blowing any air at all inside, what could be wrong?… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
State Licensed Mechanical Contractor
23,151 satisfied customers
Complaint AC not cooling keeps shutting off. Unit has a new
Complaint – AC not cooling keeps shutting off. Unit has a new five ton compressor. Pressures are at 120+ and 450+ when I get there. Recover 2 pounds and now at 72 and 310 and continues to run. At thre… read more
Josh
Josh
Service Technician
High School or GED
30 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x