I had an a/c problem...
I had an a/c problem, the tech came out and found a burned through contact. He also checked the r22 levels....the levels were +100 on the high pressure side. Also high on the low pressure side, but I did not get a number. He believed that a tech had mistakenly added 410a into the system and pushed the pressures up to be at the correct level for that refrigerant. Question 1...does adding 410a to a system made for R22 and with R22 in it hurt the system. Question 2....does having the higher pressure in the system have the potential of damaging it.

The tech removed the refrigerant, vacuumed the system and then added R22 to 75 psi.
Submitted: 8 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 7 minutes by:
6/15/2010
HVAC Technician: Bart Jay, HVAC Technician replied 8 years ago
Bart Jay
Bart Jay, HVAC Technician
Category: HVAC
Satisfied Customers: 655
Experience: 35 years in HVAC. NATE Certified EPA certified
Verified
Chat Conversation Started
Bart Jay :

It would have been worse if it was the other way around. If he evaucted the sytem good and repalce the filter drier you should be okay. There should be no serious problem because of it.

Bart Jay :

Is the unit running and cooling the house?

Customer:

He did not replace any filter...where would that be?

Customer:

It has been running for about 2.5 hours and the temperature has come down 1 degree (83 to 82)

Bart Jay :

That is in the smaller copper line looks like a shell about 3" round

Bart Jay :

how are we doing with this

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Bart Jay Your Own Question
Bart Jay
Bart Jay
Bart Jay, HVAC Technician
Category: HVAC
Satisfied Customers: 655
655 Satisfied Customers
Experience: 35 years in HVAC. NATE Certified EPA certified

Bart Jay is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I recharged R410A to my Goodman. How do I make sure it is
I recharged R410A to my Goodman. How do I make sure it is not overcharged or undercharged? Also, I want to apply EasySeal, they say the low pressure should be 40-50 psi. How can I lower the pressure s… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
I have a Goodman model CKL18-1M HVAC unit. When he HVAC tech
I have a Goodman model CKL18-1M HVAC unit. When he HVAC tech added the old refrigerant, it all leaked out after 2 days. So he sold me an outdoor unit and changed the refrigerant to 427A. That seems to… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
My son has a Goodman 2,5 ton heat pump, it stopped working,
my son has a Goodman 2,5 ton heat pump, it stopped working, then after a few hours it worked again briefly. … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My compressor is running but when its hot outside its
My compressor is running but when its hot outside its running continuesly to reach the set temp of 78 degree Called the tech, he said that the pressure is too low where it is supposed to be 100 psi an… read more
joeydelia
joeydelia
HVAC-R Tech
High School or GED
81 satisfied customers
I have a brand new 2 ton goodman unit that I just installed.
I have a brand new 2 ton goodman unit that I just installed. I don't have any experience with r410a refrigerant. It is the 14 seer model condenser and air handler. I installed the TXV as per instructi… read more
Jason Whatley
Jason Whatley
60 satisfied customers
My rooftop unit has highside pressure and refrigerant in it
My rooftop unit has highside pressure and refrigerant in it the low side just air and very low pressure, I pulled out all refrigerant and pressurized and it held actually it rose any ideas?… read more
Jason Whatley
Jason Whatley
60 satisfied customers
I have a split system that was leaking I pumped the unit
I have a split system that was leaking I pumped the unit down and reflared the pipes as that was the cause of the leak. The pressure while the unit was running was 35 psi so I have now added some r22 … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Hi, My A/C unit I think needs some Freon added to it. We
Hi, My A/C unit I think needs some Freon added to it. We put in a new Lennox compressor unit in November 2001. Does it take r-134a or something else?… read more
Tech Justin
Tech Justin
Master HVAC Technician
66 satisfied customers
I was recently working on a 3 ton Goodman(R22) replacing a
Hello, I was recently working on a 3 ton Goodman(R22) replacing a TXV, due to the high side having head pressures of 600 PSI , and I also changed the bi flo filter on the hide side as well. The custom… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
My condenser will run for 2 to 3 days with no problem and then
My condenser will run for 2 to 3 days with no problem and then stop working. I turn the ac switch off and then on and the condenser starts working. What is up ?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Unfortunately, recently my previous home burned down in a accidental
Unfortunately, recently my previous home burned down in a accidental fire. I was able to salvage my 2008 Lennox 5-Ton Air Conditioning Condenser Unit (Model #14ACX-060) off my home. It uses 410A. We h… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
My coil is clean and the filter is changed. My air flow is
My coil is clean and the filter is changed. My air flow is at 45 degree, and 18 degrees on the suction line 2 foot from the A coil, at the unit outside the liquid line is at 92 degrees. My PSI are 145… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Have a comfortmaker A/C unit that may need recharging. Model
Have a comfortmaker A/C unit that may need recharging. Model number is XXXXX The chart inside the panel that shows ambient outdoor temperature, refrigerant temperatures and pressures, is water damaged… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Hi There! I have a Carrier split room type air conditioner.
Hi There! I have a Carrier split room type air conditioner. I believe it is about a 1 ton unit but not sure of the BTU's... maybe 9,000 to 12,000? Anyway my neighbor wanted a new, more quiet model and… read more
Bart Jay
Bart Jay
HVAC Technician
Vocational, Technical or Trade Scho
655 satisfied customers
What type of pressures would you have if there was a restriction
What type of pressures would you have if there was a restriction at the metering device on a residential air conditioner?… read more
drcool299
drcool299
shop owner
Bachelor\u0027s Degree
22 satisfied customers
When pressurizing a resdebtial air conditioner to check for
When pressurizing a resdebtial air conditioner to check for leaks with Nitrogen which is the bset way to put the nitrogen in the system, through the low side, high side, or both? and how much do u rec… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
Hi, I have a Trane XE1200, split system, unit was built in
Hi, I have a Trane XE1200, split system, unit was built in 04/1996. How can I find what type freon it has and where can I get a table of what the high/low pressures and temperature drop should be vers… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Understand the 410A refrigerant does not work as well as the
Understand the 410A refrigerant does not work as well as the R-22 in a desert environment due to the ambient temperature shutting down the compressor due to overheating. can I get some input. thank yo… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x