I have a 3 zone honeywll control unit and I'm only using 2 zones with a damper on my upstairs unit and it appears to only work at night time.I dont understand it's been working fine until the summer.The upstairs unit have been a problem since i move in this house. Unit is only 2 years old.The damper is wire in a closed positon on the panel. White and green wires should be connected to what wires on the damper.
Submitted: 8 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 day by:
6/15/2010
HVAC Technician: gotoman for ac, HVAC Technician replied 8 years ago
gotoman for ac
gotoman for ac, HVAC Technician
Category: HVAC
Satisfied Customers: 5,358
Experience: 51 years of experience install design and repair of all makes and models of AC
Verified
Dampers are rated spring open power closed or spromg closed power open. Kill power to damper and see what it does. It may just be we have to switch wires. Give me terminals on board damper wires are hooked to. Russ
Ask Your Own HVAC Question
Customer reply replied 8 years ago
The dampers are wire to close,about a year ago I change the damper upstairs to open because it was doing the same thing.I change it back to close this morning and it start working.but the unit wasn,t blowing very hard.
HVAC Technician: gotoman for ac, HVAC Technician replied 8 years ago
You may have to up fan speed to compensate for that zone. You might check your bypass damper and see if it is closing. With all zones open it should be closed. Russ
Ask Your Own HVAC Question
Customer reply replied 8 years ago
How do you up the fan speed, I check the bypass already,it is located over the unit, right.
HVAC Technician: gotoman for ac, HVAC Technician replied 8 years ago
Yes it has a weighted arm. It should be closed when dampers are open to maintain .1 static pressure. What is model number and Make of your air handler. Russ
Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
My house has 2 zones for A/C and 3 zones for Heat. Currently
My house has 2 zones for A/C and 3 zones for Heat. Currently one room upstairs is right over the garage and has no attic (the rest of the house does) so this room gets too hot and with a single zone u… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
On the top floor, cool air is coming from the vents only on
On the top floor, cool air is coming from the vents only on one side of the house. The other side of the top floor is not getting any air from the vents.I have a 2 story house with each floor having i… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
I am running a two zone HVAC in a two story house, my first
I am running a two zone HVAC in a two story house, my first floor gets super cold no mater what the thermostat is set to (currently set at 80, temp reading 60) the upstairs is set at 70 temp reads in … read more
gotoman for ac
gotoman for ac
HVAC Technician
5,358 satisfied customers
Upstairs heat works, blows air. downstairs doesnt. if i turn
Customer: upstairs heat works, blows air. downstairs doesnt. if i turn off the upstairs heat and turn on the downstairs, air blows out of the upstairs vents, even though the upstairs heat is off. I sh… read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
463 satisfied customers
, i have a brivis buffalo 120 ems in a double storey house
hi, i have a brivis buffalo 120 ems in a double storey house i just bought. but the heat is not coming out of any vents upstairs, it is working fine downstairs though. it was installed in 1995 can u s… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have upstairs and downstairs w/ seperate thermostats. Upstairs
I have upstairs and downstairs w/ seperate thermostats. Upstairs works fine. Downstairs thermostat says its working but no air.… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
i have two thermostats one upstairs one down and gas furnace
i have two thermostats one upstairs one down and gas furnace in the attic. it is cold downstairs and unbearably hot upstairs… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
So on the coldest day of the winter, my furnace is no longer
So on the coldest day of the winter, my furnace is no longer heating both zones. The furnace will heat the upstairs zone no problem, but downstairs has no heat. I have a Lennox gas heater with a Honey… read more
Heath.M
Heath.M
Refrigeration Mechanic
Vocational, Technical or Trade School
223 satisfied customers
I am homeowner and have a Lenox pulse21 force hot air furnace
I am homeowner and have a Lenox pulse21 force hot air furnace fueled by natural gas. It was put in when house was built around 1992. We recently turned our heat back on as cold weather set in and I no… read more
Jerry M.
Jerry M.
Senior HVAC Technician
High School or GED
133 satisfied customers
HI! I have a bryant/carrier furnace. We have a honeywell
HI! I have a bryant/carrier furnace. We have a honeywell chronotherm iv plus two-zone system. The 1st zone heats the main level (living room, kitchen, 1 bedroom), the second heats the bedrooms upstair… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
I have a 2-zone hvac; everything was working fine until one
I have a 2-zone hvac; everything was working fine until one of the displays went out on a thermostat. Initially, I bought one new thermostat. When I was lining up the wires in the furnace control pane… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,024 satisfied customers
I have zoned thermostats, one downstairs, one upstairs. Honeywell
I have zoned thermostats, one downstairs, one upstairs. Honeywell T8132C model. Furnace in the attic. Just recently, when I turn on the thermostat downstairs, the air (heat in this case) blows upstair… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Hi. I have a single AC unit on the roof. The house was
Hi. I have a single AC unit on the roof. The house was built in 1990, the AC replaced about 2 years ago. The AC unit works really well blowing cold air. My problem is that the upstairs is not getting … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
I have a Honeywell EMM-3U MiniZone Panel on a heat-pump system
I have a Honeywell EMM-3U MiniZone Panel on a heat-pump system with 2 active zones, downstairs (zone 1) and upstairs (zone 2), and nothing connected to zone 3. Whenever the downstairs (zone 1) thermos… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
i have an Amana heat pump (Goodman manufacturing model 3ASH130601
i have an Amana heat pump (Goodman manufacturing model 3ASH130601 AA). It will not stop running. I have a dual thermostat system and turned the upstairs thermostat off.....it's 93 degree up there and … read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
I have 2 honeywell thermostats, one for upstairs in my house
I have 2 honeywell thermostats, one for upstairs in my house and one for downstairs. Currently the downstairs thermostat turns on the heat for both zones, when previously it only would heat the downst… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Why is my gas furnace working upstairs but not downstairs?
I have a gas furnace that is working upstairs but not downstairs. replaced thermostat..ac works..fan works in ON mode...what would cause it not to come on just downstairs?… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
Open limit device error on my furnace with no heat upstairs
Have gas furnace with Honeywell MiniZone controller. No heat or flow is getting to upstairs. Red light is showing on controller for Zone 1 (upstairs) and system, green light for Zone 2 (downstairs). T… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x