I have an Amana Furnace/AC with White Rogers 50A55-288 control

This answer was rated:

I have an Amana Furnace/AC with White Rogers 50A55-288 control unit. I was using the AC which seemed to be working fine but then later the Furnace Main Fan stopped running. Condenser unit fan still runs but not sure about the compressor (I believe it is running). I tried running the fan with just the thermostat fan run function ....no go. Also attempted to do so by running on the heat cycle ...no go. Swapped thermostats with identical unit from my main floor furnace/AC....no go. Jumpered 120 volt directly to the fan motor Hi speed winding and the fan runs no problem. (Obviously, I also had the fan cabinet interlock jumpered out when I was trying all these different things.
One of the two 24 volt control transformers doesn't have any voltage coming to it in any flavor of the above tests and it appears to get it's power out of the control module. Is the control module the problem (no diagnostic lamp codes...led is dark at all times)?
Chat Conversation Started
Matthew :

Not sure why you have 2 transformers unless you have a humidifier or U.V tied into the system using the other transformer, but these transformers are fed 120v from the board high voltage terminals and then in turn the 24v from the transformer goes back to the board to power all of the 24v circiuts. If you have 120v going to the transformer but no 24v coming out of the transformer then it is bad. If you have 24v coming out of the transformer but no 24v on any of the functions coming out of the board using 24v like the thermostat (should have 24v between R and C at all times) then the board is bad or the 3 or 5 amp fuse on the control board is blown.

Customer:

Matthew,


 

Matthew :

yes?

Customer:

I think you're correct the one transformer powers the humidifier valve/control.

Customer:

I'll verify that.

Customer:

What can keep the fan from running when I use the "run" over-ride on the thermostat?

Matthew :

No power to the motor because of a bad control board, bad transformer, or the 3 or 5 amp fuse on the board is blown

Matthew :

You said that you can manually jump 120v to the motor and it runs so we know that it simply is not getting the call to run from the board

Customer:

Fuse is good. Transformer is good so based on your input it must be the board...right?

Matthew :

One final test will tell us

Customer:

and that is?

Matthew :

take a jumper wire and connect the G terminal on the control board to the R terminal on the control board and then press the door saftey switch in

Matthew :

If the motor doesn't come on bad board. If the motor does come on bad thermostat (or thermostat wire)

Customer:

OK, I'll try that and let you know in a few minutes....It's hot in the attic so I'll try to be quick.

Customer:

Looks like bad board....no joy on the motor running jumpering G to R.

Matthew :

yeah if you hot wire and the motor runs with direct power then there is no problem with the motor or the capacitor. Jumping G and R bypasses the thermostat so if there is 24v at the R and C terminal and the motor doesn't run then it is the board.

Customer:

OK, thanks. Any recommendations on where to get a good price on board relatively quickly?

Matthew :

If you buy it online your going to have to wait for shipping. Best bet is to call a Tech most of the good ones carry a universal board for these 50A55 boards.

Customer:

OK, thank you...have a great (remainder of) day!

Matthew :

ttp://www.emersonclimate.com/Documents/White-Rodgers/instruction_sheets/0037-6265.pdf

Matthew :

that is the board that shows up as the replacement for the 288

Customer:

Thanks again.

Matthew and 2 other HVAC Specialists are ready to help you