I have an Amana Furnace/AC with White Rogers 50A55-288 control unit. I was using the AC which seemed to be working fine but then later the Furnace Main Fan stopped running. Condenser unit fan still runs but not sure about the compressor (I believe it is running). I tried running the fan with just the thermostat fan run function ....no go. Also attempted to do so by running on the heat cycle ...no go. Swapped thermostats with identical unit from my main floor furnace/AC....no go. Jumpered 120 volt directly to the fan motor Hi speed winding and the fan runs no problem. (Obviously, I also had the fan cabinet interlock jumpered out when I was trying all these different things.
One of the two 24 volt control transformers doesn't have any voltage coming to it in any flavor of the above tests and it appears to get it's power out of the control module. Is the control module the problem (no diagnostic lamp codes...led is dark at all times)?
Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 hour by:
6/13/2010
Matthew
Matthew, HVAC Technician
Category: HVAC
Satisfied Customers: 2,014
Experience: 14 years experience in the HVAC field of service, installation, Manual J & D calculations
Verified
Chat Conversation Started
Matthew :

Not sure why you have 2 transformers unless you have a humidifier or U.V tied into the system using the other transformer, but these transformers are fed 120v from the board high voltage terminals and then in turn the 24v from the transformer goes back to the board to power all of the 24v circiuts. If you have 120v going to the transformer but no 24v coming out of the transformer then it is bad. If you have 24v coming out of the transformer but no 24v on any of the functions coming out of the board using 24v like the thermostat (should have 24v between R and C at all times) then the board is bad or the 3 or 5 amp fuse on the control board is blown.

Customer:

Matthew,


 

Matthew :

yes?

Customer:

I think you're correct the one transformer powers the humidifier valve/control.

Customer:

I'll verify that.

Customer:

What can keep the fan from running when I use the "run" over-ride on the thermostat?

Matthew :

No power to the motor because of a bad control board, bad transformer, or the 3 or 5 amp fuse on the board is blown

Matthew :

You said that you can manually jump 120v to the motor and it runs so we know that it simply is not getting the call to run from the board

Customer:

Fuse is good. Transformer is good so based on your input it must be the board...right?

Matthew :

One final test will tell us

Customer:

and that is?

Matthew :

take a jumper wire and connect the G terminal on the control board to the R terminal on the control board and then press the door saftey switch in

Matthew :

If the motor doesn't come on bad board. If the motor does come on bad thermostat (or thermostat wire)

Customer:

OK, I'll try that and let you know in a few minutes....It's hot in the attic so I'll try to be quick.

Customer:

Looks like bad board....no joy on the motor running jumpering G to R.

Matthew :

yeah if you hot wire and the motor runs with direct power then there is no problem with the motor or the capacitor. Jumping G and R bypasses the thermostat so if there is 24v at the R and C terminal and the motor doesn't run then it is the board.

Customer:

OK, thanks. Any recommendations on where to get a good price on board relatively quickly?

Matthew :

If you buy it online your going to have to wait for shipping. Best bet is to call a Tech most of the good ones carry a universal board for these 50A55 boards.

Customer:

OK, thank you...have a great (remainder of) day!

Matthew :

ttp://www.emersonclimate.com/Documents/White-Rodgers/instruction_sheets/0037-6265.pdf

Matthew :

that is the board that shows up as the replacement for the 288

Customer:

Thanks again.

Matthew
Matthew, HVAC Technician
Category: HVAC
Satisfied Customers: 2,014
Experience: 14 years experience in the HVAC field of service, installation, Manual J & D calculations
Verified
Matthew and 87 other HVAC Specialists are ready to help you
Ask your own question now
Ask Matthew Your Own Question
Matthew
Matthew
Matthew, HVAC Technician
Category: HVAC
Satisfied Customers: 2,014
2,014 Satisfied Customers
Experience: 14 years experience in the HVAC field of service, installation, Manual J & D calculations

Matthew is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
It doesn't seem like my newly installed Aprilaire humidifier
It doesn't seem like my newly installed Aprilaire humidifier is working. Shouldn't I hear water draining out the condensation drain? … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,142 satisfied customers
I'm installing a HM700A1000 steam humidifier and the steam
I'm installing a HM700A1000 steam humidifier and the steam distributor has 2 condensate legs. One comes out horizontal directly underneath or in line with the steam hose and the other comes out vertic… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,142 satisfied customers
I have a beckett oil burner in a floor furnace. It is A-AF.
I have a beckett oil burner in a floor furnace. It is A-AF . I installed it in Oct. 2017 . It got low of oil in the tank and sucked air. I bled it and put a new nozzle in it . I also washed up the ele… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Gooman furnace i was replacing the humidifier the fabn on
gooman furnace i was replacing the humidifier the fabn on furnace was running then stopped, and now now power … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
How do I wire a Generalaire 1042 humidifier to my Payne PG9
How do I wire a Generalaire 1042 humidifier to my Payne PG9 circuit board so the humidifer only runs when the blower is on. … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,142 satisfied customers
I need to know how to fan powered humidifier to my furnace.
I need to know how to fan powered humidifier to my furnace.The furnace is a Bryant 355CAV. It has a HUM terminal.An isolation relay is required to separate the power from the humidifier from the furnn… read more
Steve Peck
Steve Peck
NC
16 satisfied customers
I have a Honeywell hwm-330 humidifier. Is there a manual
I have a Honeywell hwm-330 humidifier. Is there a manual available? … read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
383 satisfied customers
My Aprilaire 700 humidifier is not working properly. The
My Aprilaire 700 humidifier is not working properly. The humidistat on the side of the furnace reads 50% while the actual humidity throughout the house is only 30%. Is this something I can fix myself,… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I need a manual for my Honeywell furnace humidifier
I need a manual for my Honeywell furnace humidifier #HM506A2000, purchased 1/12/15. Couldn't find one for that # product on the Honeywell home page. Can you tell me how to find one? --Thanks. … read more
David Bowden
David Bowden
Owner
467 satisfied customers
The flashing light on control says humidifier is running but
The green flashing light on control says humidifier is running but is not the screen that says the amount of humidity is blank … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
I don't think our humidifier works on our gas furnace. The
I don't think our humidifier works on our gas furnace. The humidifier is a Chippewa 224. I didn't feel any water at the end of the water line that is going into the humidifier. Didn't know if it's the… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
How can I adjust the water flow on the humidifier? The
how can I adjust the water flow on the humidifier? The saddle valve will not shut off and I replaced it twice. … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,142 satisfied customers
I have a Aprilaire Humidifier on my burner.I'am wondering if
Hi I have a Aprilaire Humidifier on my burner.I'am wondering if the unit should come on when the burner starts a cycle?When I use the test mode on the control panel the water starts going in but when … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My Carrier Furnace Model CNPVP4324ATAACAA says humidifier
My Carrier Furnace Model CNPVP4324ATAACAA says humidifier pad needs to be changed. Is that something easy to do? … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,142 satisfied customers
My Lennox humidifier HCWP18 Healthy Climate is not putting
My Lennox humidifier HCWP18 Healthy Climate is not putting moisture in the air. The pad has been changed and water is running through it, but it's not doing the job. Usually I can get the windows a li… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,142 satisfied customers
A quick question on a humidifier: The humidifier goes on at
A quick question on a humidifier: The humidifier goes on at 20 {manual on} but does not shut off when the flame goes off (cool). Where can I find manuals for these humidifiers and what is the problem?… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
My amana furnace is not igniting. Hopefully. The red light
My amana furnace is not igniting JA: Did you check the furnace's filters? Customer: Yes JA: Do you plan on doing the work yourself? Customer: Hopefully JA: Anything else we should know to help you bes… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Bypass Humidifier, MODEL 445, and this season it is
I have a Bypass Humidifier, MODEL 445, and this season it is leaking water from the water tray. I went to remove the finger nut that secures the tray and it just split in half. could the finger nut be… read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
383 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x