Hi neither my air or heat will come on. the thermostat works…

Customer Question
Hi neither my air or heat...
Hi
neither my air or heat will come on. the thermostat works to make the fan come on, I check out at the compressor and nothing is happening out there could it be the capacitor ?
Submitted: 8 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 3 minutes by:
6/12/2010
HVAC Technician: Tom, HVAC Technician replied 8 years ago
Tom
Tom, HVAC Technician
Category: HVAC
Satisfied Customers: 770
Experience: 16+yrs HVAC/R service. Residential Commerical Industrial
Verified

Does it hum or buzz or do anything?

 

Have you checked the circuit breaker feeding the outside unit? Not the disconnect by the unit, but the breaker in your breaker box?

 

Tom

Ask Your Own HVAC Question
Customer reply replied 8 years ago
I checked the heat pump breakers in the box and nothing happened
HVAC Technician: Tom, HVAC Technician replied 8 years ago

If you've already checked power..you need to pull the disconnect by the a/c unit and pull the side panel off.

 

See if the compressor contactor is pulled in. It should look something like this.

View Full Image
The movable contacts should be in the down or closed position. You don't need the main power on to check this part. The contactor gets it's power through your thermostat and we need to see if it's pulling in. Can you hear it hum or buzz. It's powered by 24 volt from the indoor unit.

 

Also check the small thermostat leads going to the a/c unit. Make sure they haven't been damaged by a rodent or weed trimmer...happens all the time. The small brown lead wire is what supplies 24 volts to your contactor.

 

Check and let me know.

 

Tom

Ask Your Own HVAC Question
Customer reply replied 8 years ago
They are in good shape
HVAC Technician: Tom, HVAC Technician replied 8 years ago

Ok, you need to check and see if the relay is pulled in.

 

Tom

Ask Your Own HVAC Question
Customer reply replied 8 years ago

They are in good shape. It worked just fine yesterday. I realize a anything electrical can work fine and the just stop working

Where do I find the relay ?

HVAC Technician: Tom, HVAC Technician replied 8 years ago

Inside the outdoor compressor unit. You need to pull the disconnect switch by the unit. Take the panel off and you'll see the contactor inside. We just need to know if it's energized or not.

 

It is supplied 24 volts to actuate it by the indoor unit/thermostat.

 

Check and let me know.

 

Thanks! Tom

Ask Your Own HVAC Question
Customer reply replied 8 years ago

HI It will take me a while. I am in a wheel chair and I have no one here right now to run in and out

So I will have to get back to you later when I can get some help to get the tools to open up the unit.

Thanks

Ben

HVAC Technician: Tom, HVAC Technician replied 8 years ago

Tom



Edited by Tom on 6/13/2010 at 1:57 AM EST
Ask Your Own HVAC Question
HVAC Technician: Tom, HVAC Technician replied 8 years ago
No problem Ben, just let me know when you find out something.

Tom
Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Tom Your Own Question
Tom
Tom
Tom, HVAC Technician
Category: HVAC
Satisfied Customers: 770
770 Satisfied Customers
Experience: 16+yrs HVAC/R service. Residential Commerical Industrial

Tom is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Heat pump does not work. Checked them both. Air handler is
checked them both. Air handler is working, and checked the breakers … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a trane xl1200 the fan runs little air coming out of
I have a trane xl1200 the fan runs little air coming out of air ducts. I checked the fuses and replaced them … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,974 satisfied customers
I replaced my capacitor with a new one.and my air unit wont
I replaced my capacitor with a new one.and my air unit wont make any sound fan not working..but it will spin if i use something to move it … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
The outside unit will not turn on. The contact or & run
The outside unit will not turn on. The contact or & run capacitor has been replaced … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Troubleshooting an RV air conditioner. its a ceiling unit
Troubleshooting an RV air conditioner. its a ceiling unit without a thermostat. With any attempt to turn it on on any setting, absolutely nothing happens. The customer said that one minute, it was run… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My RUUD ac condenser fan outside is not turning and the downstairs
My RUUD ac condenser fan outside is not turning and the downstairs won't cool down. My upstairs system works fine and the fan is turning. Is there anything i can do to fix it?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Trane ductless heating and Air Cond. unit in a garage
I have a Trane ductless heating and Air Cond. unit in a garage apartment. Model # XXXXX Serial # XXXXX It has a manual thermostat located on the main control panel board. The unit will come on and hea… read more
DennisMooreAC
DennisMooreAC
Service Engineer
Associate Degree
76 satisfied customers
Lennox central Air conditioner suddenly stopped working, furnace
Lennox central Air conditioner suddenly stopped working, furnace fan is still working but the fan on the top of the Lennox unit outside is not running… read more
hvacguy17
hvacguy17
Mentor Service Technician
Associate Degree
12 satisfied customers
I have a Fredrich airconditioner/heatpump. Model #YM18J34A-2.
I have a Fredrich airconditioner/heatpump. Model #YM18J34A-2. It's an in the wall unit. It just quit running last night. I turned it off. Today I tried turning it on, and nothing. It has never done th… read more
servtech50
servtech50
HVAC/R service tech
216 satisfied customers
model ass25 reverse cycle air conditioner. cooling works ok
model ass25 reverse cycle air conditioner. cooling works ok . heating not working . fan outside working but not inside . every minute or so lights in house dim. seems to be trying to kick in but wont … read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I HAVE A 2 TON GOODMAN CONDENSOR ,UNIT INSIDE COMES ON BUT
I HAVE A 2 TON GOODMAN CONDENSOR ,UNIT INSIDE COMES ON BUT OUTSIDE UNIT DOESNOT I REPLACED CAPACITOR… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
Just went over to my rental which had a new Bryant Heater and
Just went over to my rental which had a new Bryant Heater and A/C installed at the end of April. this was the first time I had a chance to check the A/C syatem. My tenant said she did not used the Hea… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Goodman Hvac-The air handler is running, the outside fan is
Goodman Hvac-The air handler is running, the outside fan is running but the unit is blowing hot air through the vents. The fan outside is blowing cool air. I don't think the compressor is coming on. I… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My compressor and condensor fan do not come on when called
My compressor and condensor fan do not come on when called for but i hear a humming noise. The central air system is 6 years old. What is the most likely cause?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My Lennox heat pump condensing unit is not coming on. Model
My Lennox heat pump condensing unit is not coming on. Model # XXXXX I checked to make sure no breakers are tripped. The indoor fan is blowing air. What else can I check?… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
I have a Luxaire G9T08012UPB13A HVAC system and when turned
I have a Luxaire G9T08012UPB13A HVAC system and when turned on, outside unit fan spins up, some air comes through vents, but system generates neither hot air from heater nor cold air from A/C. What do… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Hi Mark You help me out before I need you again My outdoor
Hi Mark You help me out before I need you again My outdoor ac unit wont come on I checked my fuses all good when i turn it on by themstate the contact does click in . what do I check next… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
Hi. I have a york heat pump. 9yrs old. Heat will not come
Hi. I have a york heat pump. 9yrs old. Heat will not come on when i set it way up. I can hear a click on the thermostat and my little flame picture comes on, but nothing, Sometimes the fan blows,but I… read more
Rick or Nick in Texas
Rick or Nick in Texas
General Manager-Lead Tech
Own and run HVAC business 29yrs
44 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x