HVAC

Have HVAC Questions? Ask an HVAC Expert for Answers

Ask an Expert,
Get an Answer ASAP!

HVAC

I have a Comfortmaker RPJ II Model# GNJ150N20A1. Ive been

Customer Question
I have a Comfortmaker RPJ...
I have a Comfortmaker RPJ II Model# XXXXX I've been told the gas valve needs to be replaced, but that it is no longer manufactured by White Rogers. The valve # XXXXX XXXXX Rogers 36E35202. Part # XXXXX I was told I'm SOL and that I have to buy a new furnace. The furnace was manufactured in April 1995. I can't believe that is the only solution for a 15 year old furnace.

Any suggestions?

Many thanks

Glenn [email protected]
Submitted: 7 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 17 minutes by:
3/12/2010
HVAC Technician: Charles, HVAC Contractor replied 7 years ago
Charles
Charles, HVAC Contractor
Category: HVAC
Satisfied Customers: 69
Experience: State Lic. HVAC Contractor. 20 yrs field exp. Repairs and installtions.
Verified

hello

I think a replacement can found to replace it. let me check in the morning. I will get back to you.

 

I think the repairman wanted a commission for a sale . lots of HVAC companies offer bonuses for selling new equipment. to their Techs. makes them prone to condemn and replace for no reason other than to pad their pockets some and empty yours.

 

Had a customer call me that was referred to me by a concerned friend about a elderly couples furnace not working and were told it had to be replaced. wanted me to make sure this was true. I checked the unit unclogged a pressure switch hose. that was the only problem it had. It has worked fine since this was 3 years ago.

 

They then showed me their warranty paper work and it was still under warranty.

 

 

 

thanks

 



Edited by Charles on 3/12/2010 at 8:25 AM EST
Ask Your Own HVAC Question
HVAC Technician: Charles, HVAC Contractor replied 7 years ago

still working on it please be patient

Ask Your Own HVAC Question
HVAC Technician: Charles, HVAC Contractor replied 7 years ago

Comfortmaker no longer makes or supports that model. there are a few parts floating around just not the Gas Valve.

 

The comfortmaker rep I spoke to feels Like I do that a good tech should be able to find a generic gas valve and make it work.

 

On the other hand parts for that unit are no longer made so. It In my opinion would be better for you if you can afford it would be to replace your furnace. and If I were you It wouldn't be a comfortmaker.

 

If it were me I would just replace the whole old system to bring it up to date 13 SEER and 410a refrigerant. With warranties or if you like saving money on power and gas bills a higher seer like 18 to 23 SEER. SEER = Seasonal Energy Efficiency Rating. The larger the number the cheaper it is to run. but the more they cost to buy.

 

the reason being if you try to just replace the furnace the existing coil may not match up/ fit together well but probably could be done, If any other part fails after that you will be facing the same parts replacement problem!! Also the R-22 refrigerant it uses is being phased out. everything is gong to R-410a, And if your coil ever goes bad which they do when they get old they will eventually start to leak. some sooner than others.

 

At that point you will probably not be able to find a R-22 Coil. and have to change to a R-410a one and will have to change your outdoor unit / condenser to a 410 a also.

 

I really hate to have to tell you this but it is the God honest truth. I have tried All day to get you that valve. Its just not available.

 

remember You may still find a good tech that will install a generic valve. but I think you should look for some new equipment that parts are available for and would be under factory warranties.

 

Sorry I could not get the right part and only offer advice but thats the way it goes sometimes.

 

Thanks for giving me the opportunity to help.

 

Do not feel obligated to accept the answer.

 

Have a wonderful Day

 

 

Charles
Charles, HVAC Contractor
Category: HVAC
Satisfied Customers: 69
Experience: State Lic. HVAC Contractor. 20 yrs field exp. Repairs and installtions.
Verified
Charles and 87 other HVAC Specialists are ready to help you
Ask your own question now
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 7 years ago
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 22,893
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified

 

The valve was labeled a few different numbers depending on the company it was made for.

 

Trane bought the same valve for a series of their furnaces.

 

See if this is your valve here - http://www.hvacpartsoutlet.com/gasvalvetraneval04210.aspx

 

the Trane VAL, the 36e35 202 and 201 are all the same valve...just different end retailers.

Ask Your Own HVAC Question
HVAC Technician: Charles, HVAC Contractor replied 7 years ago

FYI I talked to Directly with several Trane dealers/ distributors they Claimed it did not crossover and I spoke Directly to comfortmaker distributor. They agreed that it did not cross!!!!but what do they know right!

 

But As I stated already You may find a generic that will work and a willing Installer.

 

Maybe billy is right. I hope it is the correct one. And you could keep going on the same old less efficient hard to find parts for unit. but save money not changing it out. thats a plus.

 

When I talked to Comfortmaker they said the heat exchanger only had a 10 year warranty.

 

So I would weigh my options carefully. Do what you feel is the right thing for you

 

Good luck

Ask Your Own HVAC Question
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 7 years ago

 

 

It is common for "distributors" to not divulge the information simply because they do not have it in black and white on the paperwork. Trane will not have Comfortmaker and vice versa.

 

Imagine going to a Ford dealer and having them tell you that you can get the same part from Chevy. Even though that part was made by a manufacturer supplying multiple sources. It just doesn't happen. You have to talk to someone with good experience overall.

 

When a manufacturer no longer wants "their" version of the valve, it becomes obsolete.

I really have no preference whether you replace the unit or repair the unit...I just like people knowing their choices.

 

So, yes, as you see, those who don't have the answer always want to replace. Should it be replaced? Maybe....Is the warranty good or not?...I don't know. Can we always just replace things when they break regardless of cost? No.

 

I am simply letting you know that you have an option. Just because a part is harder to find does not mean you have to replace the furnace.

 

I think if you see the link you will have the info you need.

 

http://www.hvacpartsoutlet.com/gasvalvetraneval04210.aspx

 

 

 

Ask Your Own HVAC Question
Ask Charles Your Own Question
Charles
Charles
Charles, HVAC Contractor
Category: HVAC
Satisfied Customers: 69
69 Satisfied Customers
Experience: State Lic. HVAC Contractor. 20 yrs field exp. Repairs and installtions.

Charles is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a GSZ130421AE condensing unit and ARUF486016CA air
I have a GSZ130421AE condensing unit and ARUF486016CA air handler. The heat pump intermittently comes on and may operate a few minutes. When it stops operating, the air handler continues to run until … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I'm installing a condensation pump for a friend, he has dual
I'm installing a condensation pump for a friend, he has dual zones and the condensation pump has a after switch. The thermostat has ABCD connections. I need the common and normally open connections an… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Didn't know this site had chat. I had a plugged condensate
Hi There. Didn't know this site had chat. I had a plugged condensate colector, at least that's what I think it is. The white thing the drain tube comes out of below the blower on a carrier 58MCA080. I… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
All my windows have condensation. Can I turn off the water
All my windows have condensation. Can I turn off the water to my G3203-75-2 to lower the humidity? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Does it make sense that the outside condenser unit for the
Does it make sense that the outside condenser unit for the second story of our split HVAC system is 3.5 ton but the evaporator unit in the attic is 4 ton?… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My high efficiency condensing furnace (Carrier) emits a
My high efficiency condensing furnace (Carrier) emits a terrible eye-stinging odor when heating. The furnace runs quiet and otherwise appears to be trouble free, however I see (and smell) a fresh (wet… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Can I have a condensing furnace in a garage that's only
Can I have a condensing furnace in a garage that's only heated a couple days out of the week? I can install it inside the conditioned space but do I have to keep the garage heated all the time or can … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
58MVP080 model got the heat exchanger issue. I have tech
Hi Pearl,58MVP080 model got the heat exchanger issue … read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
22,893 satisfied customers
I have a condensing furnace, MN G51MP- 48C- 090 -06 this
Hi , i have a condensing furnace, MN G51MP- 48C- 090 -06 this furnace gives trouble every year at some point. flash code says condensation is backed up or not enough combustion air or pressure switch … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Need a heat exchanger for model GIN 80bu-1000 14B-3A; ser. #
need a heat exchanger for model GIN 80bu-1000 14B-3A; ser. # 1607K 03798 … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a replacement condenser from Goodman, the original
i have a replacement condenser from Goodman, the original was a variable speed and they have since discontinued it and as a warranty replacement they sent me a different condenser and the wiring is to… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
Condenser not running checked all breakers and thermostat
condenser not running checked all breakers and thermostat settings … read more
travis webb
travis webb
tech.
2,414 satisfied customers
Is it unsafe to have a cracked heat exchange on your
Is it unsafe to have a cracked heat exchange on your furnace? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Have classic 90 plus Rheem unit leaks Condensation from
Have classic 90 plus Rheem unit leaks Condensation from blower motor cycles 4 minutes times out and repeats … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I need a heat exchanger kit for a weil-mclain ultra 105, no
i need a heat exchanger kit for a weil-mclain ultra 105 … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
How do I check heat exchanger for blockage. Today. Sounds
how do I check heat exchanger for blockage JA: I'll do all I can to help. How long have you been dealing with this? Customer: today JA: Do you plan on doing the work yourself? Customer: yes JA: Anythi… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
When were stainless steel heat exchangers required for
When were stainless steel heat exchangers required for residential usage and/or what HVAC company was the first to provide them. And are they as effective as touted.… read more
D.E. Anderson
D.E. Anderson
Industrial Refrigeration Service Manager
200 satisfied customers
The condensation water leaks from heat exchanger near the
The condensation water leaks from heat exchanger near the filter and comes on the ground tray. There is no blockage of any sort. What needs to be done for auxiliary condensation tray if it is cracked.… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,142 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x