HVAC

Have HVAC Questions? Ask an HVAC Expert for Answers

Ask an Expert,
Get an Answer ASAP!

HVAC
This answer was rated:

I have a Bryant Model 661CJ042-G Air Conditioner that when

I engage the circuit breaker...
I have a Bryant Model 661CJ042-G Air Conditioner that when I engage the circuit breaker, it trips after a few seconds. I have pulled outside fuse connector and breaker stays on, I have also disconnected the fan and the breaker still trips
Show More
Show Less
Ask Your Own HVAC Question
Answered in 4 minutes by:
3/8/2010
John
John, HVAC Technician
Category: HVAC
Satisfied Customers: 27
Experience: Master residential technician. 18 years experience, heat pumps, air conditioners, lp and nat. gas
Verified

Hello,

I would start by checking the wires leading down to the compressor, and all of the high voltage connections in the outdoor unit control box. You want to look for anything that is obviously burnt or shorted to any metal (cabinet or copper tubing)

Ask Your Own HVAC Question
Customer reply replied 7 years ago

Will do this evening inside at the compressor

I took the access panel off that allows me to see the board, capacitor, contactor and all wiring leading into the inside area and everything looks good. Contacts look clean and unburnt - not sure about capacitor - it looks a bit rusted and has some oil on the outside My volt/ohm meter is busted - I will get one tonight after work. But all wires in the control area within the outside access panel look good

Ok sounds good, just take a real close look at the wires leading down to the compressor itself. A little rust on the capacitor is usually not that big a deal. Sound to me like there is a short in the compressor itself. To test compressor, put meter to ohms, put one lead to a compressor terminal and the other to a ground, (any metal will do) to see if it is shorted to ground. Let me know and we can go forward at that point.

Also the full model and serial numbers would be helpful as well to look up the specs. for your specific unit.

 

 



Edited by John on 3/8/2010 at 5:49 PM EST
Ask Your Own HVAC Question
Also, is the unit calling for the compressor to run when the breaker trips?
Ask Your Own HVAC Question
Customer reply replied 7 years ago

Bryant

 

Serial 2404E21644

 

Product 661CJX04200AGAA

 

Model: 661CJ042-G

ok thanks.

 

When is the breaker tripping? Is the heat pump calling for heat or just sitting idle?

Ask Your Own HVAC Question
Customer reply replied 7 years ago

Just sitting idle - yesterday was a nice day in my area - nothing was on - heat set low to 65 and it was a 70 degree day, so nothing came on. When I reset the breaker it takes about 2-3 seconds to hear "rumbling" (my word) in the breaker box and then the breaker trips within another second.

 

My second unit works fine - its a smaller Bryant unit

Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,168
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Thanks for looking at my profile. I hope I can be of service.

 

In those cases its usually a very stuck or partially grounded compressor... a completely shorted to compressor will trip the breaker instantly.

 

If you have an ohm meter and are good with it... do this:

 

Kill the power to the unit, verify its OFF, then pull the three wires off of the compressor, mark them C, S. R same as on the compressor... this is important.

 

then use the ohm meter to check resistance to ground...if you get no resistance to ground from any of those that compressor is toast.

 

then pull a cap off of the refrigerant charging port, depress the schraeder valve core and sniff the gas that comes out...if its acidic/ burnt smelling you are in trouble...time to buy a whole new unit and have it installed to get rid of any contaminants.

 

If it sniffs clean, the compressor can be replaced....but I don't recommend it if the unit is over 5 years old... the new ones are better, cheaper and the utility company will often pay half of the cost of upgrading it.

 

I hope that helps,

 

Good luck

 

Phil

Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,168
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified
Phil and 87 other HVAC Specialists are ready to help you
Ask your own question now

Ok, well there are only 2 parts left in your machine....the compressor and the crankcase heater. By what your symptoms are I would first try to disconnect the crankcase heater and see what it does. If the breaker still trips then the compressor is most likely the cause.

To disconnect the crankcase heater remove the red(or or black) wire from the L1 terminal on the contactor and remove the red (or black) wire from the T1 terminal of the contactor. Note these may be marked 11 and 21 also, but they will lead directly to the crankcase heater at the bottom of the compressor.

Be sure to tape off these wires before trying to restore power. The side of the contactor you are looking for has the plunger on it. Let me know what you find out.

Ask Your Own HVAC Question
Customer reply replied 7 years ago

John

 

Sorry I didnt get back to you yesterday - long work day

 

I didnt get a new meter yet - will do that this evening. I did however have my wife hit the breaker while I stayed close to the unit to see what was transpiring. All wires look good to all parts of the unit. When she reset the breaker the compressor hummed and the fan began to turn, but very slowly. This went on for about 10 seconds this time and then the breaker tripped. We did it again and almost the same thing happened. The compressor felt a bit warm

 

I will use the meter tonight as you suggested testing the wires and get back to you, I will also inspect the refrigant for smell and other.

 

Unit is going on its 4th year, and I believe it sat idle for almost a year from late 08 to late 09 when I bought the house (Dec 09 - it was a short sale and the house had not had occupants for about 1 1/2 years)

Ok, from what you are telling me, the compressor has locked up for some reason and cannot start. That is basically the only thing left that can draw enough power to cause the breaker to trip. If anything was shorted to ground the breaker would trip right away and not wait 10 sec. or so.

That compressor would still be under parts warranty so that will help with the cost.

Sorry about the bad news, but you are most likely going to have to call somebody in to replace the compressor for you.

I also DO NOT recommend smelling the refrigerant for safety and regulatory reasons.

If you should have any more questions, please let me know.

John

John
John, HVAC Technician
Category: HVAC
Satisfied Customers: 27
Experience: Master residential technician. 18 years experience, heat pumps, air conditioners, lp and nat. gas
Verified
John and 87 other HVAC Specialists are ready to help you
Ask your own question now
Ask John Your Own Question
John
John
John, HVAC Technician
Category: HVAC
Satisfied Customers: 27
27 Satisfied Customers
Experience: Master residential technician. 18 years experience, heat pumps, air conditioners, lp and nat. gas

John is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,168 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Turned off circuit breaker while furnace running ... turned
turned off circuit breaker while furnace running ... turned on circuit breaker ... furnace did not come back on ... got message system malfunction outside sensor error on carrier infinity 96. read you… read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
388 satisfied customers
Have central air heat pump trane unit. Have central air
have central air trane unit heat pump. in either the heat mode --compressor running or in the emergency heat mode , the heat circuit breaker trips after about 5 minutes. in the cool mode there is no problem . . a technician checked the system this past .summer when i had this problem sporadicallyin the cool mode . he did not find a problem. suggested that that circuit breaker was bad. The circuit breaker was changed . --it did NOT solve the problem . I removed the cover from the thermostat. --found the 3 batteries badly corroded . cleaned the terminals --replaced the batteries . system worked fine in cool mode . now it appears the problem has shifted to the heat mode - Can it be that the Trane touch thermostat is defective and is causing the heat breaker to trip ????..or there is another possible problem ??? ..I.hate to call the tech folks and spent more dollars if not needed … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I'm replacing board on Lennox 80uhg4-75a-3 and can't find
I'm replacing board on Lennox 80uhg4-75a-3 and can't find e20 on new board (hum-h) … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
MY STOVE HAS C01 DISPLAYED I TURNED OFF CIRCUIT BREAKER AND
MY STOVE HAS C01 DISPLAYED I TURNED OFF CIRCUIT BREAKER AND IT RESET FOR A TIME THEN DISPLAY CAME BACK UP … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a Heil CA5536VKD2, circuit breaker trips when it
i have a Heil CA5536VKD2, circuit breaker trips when it turns on compressor runs for like a second then trips bad compressor? … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I turned the circuit breaker off to my AC to replace a
I turned the circuit breaker off to my AC to replace a thermostat with a NEST thermostat. When finished, I turned the CB back on. No power. I put the old thermostat back on and still no power at therm… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
Will a weak capacitor trip the circuit breaker. Today only
well I can tell you I took off a fan motor that had 3 wires and replaced it with one with 4 wires… read more
Phil
Phil
Mechanical Engineer
9,168 satisfied customers
I woke up this morning to a tripped furnace circuit breaker,
I woke up this morning to a tripped furnace circuit breaker, I reset it and went up to the furnace and also noticed a burning smell and a humming noise.… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My HVAC is not working. The AC circuit breaker trips as soon
my HVAC is not working. The AC circuit breaker trips as soon as the, I guess, the outside unit try to start … read more
WCohn
WCohn
Journeyman Plumber
Journeyman License
1,353 satisfied customers
The circuit breaker keeps shutting off when the Rheem
The circuit breaker keeps shutting off when the Rheem furnance/air conditioner tries to come on. What is our problem? We just had a new capacitor put in about two weeks ago. … read more
D.E. Anderson
D.E. Anderson
Industrial Refrigeration Service Manager
200 satisfied customers
What size amp circuit breakers needed for lennox heat pump
what size amp circuit breakers needed for lennox heat pump 14hpx-036-230-21 and Lennox air handler cby25uh-036-230-10? … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,891 satisfied customers
On my Model 213C A/C, I have: Reset the circuit breaker,
On my Bryant Model 213C A/C, I have: Reset the circuit breaker, Replaced the fuses, Replaced thermostat batteries, Replaced the capacitor, Replaced the circuit board. Our A/C unit is less than five ye… read more
Phil
Phil
Mechanical Engineer
9,168 satisfied customers
The circuit breaker that I plugged my window unit into
The circuit breaker that I plugged my window unit into wasn't labeled so it got too much voltage when I plugged it in and it seems to have blown an internal fuse. I'm trying to figure out which compon… read more
Phil
Phil
Mechanical Engineer
9,168 satisfied customers
Circuit breaker cutting off no ac or ac will not run,
circuit breaker cutting off no ac or ac will not run … read more
HvacmanSean
HvacmanSean
Owner
HVAC
229 satisfied customers
I turned off circuit breaker to cleanup a water problem in
Greetings, I turned off circuit breaker to cleanup a water problem in my house. As I went to turn on the heat it would start up but then turned back off. Please can you send me some pictures or a link… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My thermastat is blank I have reset my circuit breakers
My thermastat is blank I have reset my circuit breakers although they were not tripped , taken it off wall and replaced , still no reading … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Lennox furnace model SLP98UH090XV36C-04 > circuit breaker
Lennox furnace model SLP98UH090XV36C-04 > circuit breaker relay (CB8) keeps tripping off when interlock switch (panel cover switch) is engaged… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I turned off power from circuit breaker and outside
i turned off power from circuit breaker and outside switch,still buzzing where all wires are connected,… read more
D.E. Anderson
D.E. Anderson
Industrial Refrigeration Service Manager
200 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question