4 or 6 Ducts. Which is better I just had Central A/C

4" or 6" Ducts. Which...
4" or 6" Ducts. Which is better?

I just had Central A/C and Heat installed and most of the rooms connected to the end of the Trunk line barely push out any air. There are currently 5 Registers/supply's (Cat Room, Bathroom 1 & 2, Computer Room, Baby Room) connected to the end of the trunk line, all seem to be 6" ducts.

The lines in the beginning of the Trunk (my bedroom) pumps out an enormous amount of airflow, so much that I leave the vent closed.

my question is, When do i use 4" or 6" ducts? I believe the beginning of the Trunks have 6" and 7" and towards the end are all 6".

I need to increase the airflow at the end of the Trunk Line (the 5 registers). I got two different answers when i went to Home Depot and Lowes. One said I need 6" ducts at the end while the other says to use 4" ducts because the airflow is the weakest and I am just moving cold air.

Do I leave the 6" at the front and change all at the end to 4"? Will type more in a sec
Show More
Show Less
Ask Your Own HVAC Question
Answered in 12 minutes by:
1/17/2010
Douglas
Douglas, HVAC Technician
Category: HVAC
Satisfied Customers: 3,089
Experience: Manufacture Rep for Major Brand, Technical Trainer, NATE
Verified
Fortunately....or rather unfortunately (depending on how you look at it) the guys at home depot and lowes have no expertise in HVAC or they would be working for an HVAC contractor making twice the money. No worries, half the jack legs calling themselves HVAC contractors dont know airflow either. Around here all you need is a ballcap and a pickup truck to call yourself a contractor and get a liscence too.

The problem is that the duct was not properly graduated to maintain velocities. Whoever said 4 needs a kick in the shins. The other guy is partially right, but should have elaborated.

Duct systems need to be designed to maintain static pressure in the duct and keep the velocity in check. The air, as you can see will take the path of least resistance. By keeping the static up in the duct system (Static is the outward pressure that keeps a basketball pushed out all the way around). The static will force the air to where you want it to go.

Personally I would drag the installer back and make him do it right. He is supposed to sell solutions, not units. The unit cant do anything by itself.

I know this is not your home but look how the duct is reduced after a run is taken off (Blue Ducts). This is how it's supposed to be. Air is dumb.... you need to tell it where to go. Taking a closer look, the engineer specified how much air he wanted in each room and designed the duct to deliever just that amount. The number on the bottom of his notes show the CFM (amount of air), the number on top tells the contractor what diffuser or register to use and the size of the pipes are spelled out. (Again some schmuck with a ball cap thinks he knows this and in the end has no clue). Your system may be 2 stage which will only exagerate a bad duct system.

graphic

Ask Your Own HVAC Question
Customer reply replied 7 years ago
doh I finished revising my question and it didnt take lol Give me one sec, I am uploading a design and questions. Uno Momento por favor
ok shoot
Ask Your Own HVAC Question
Customer reply replied 7 years ago

4" or 6" Ducts. Which is better? I just had Central A/C and Heat installed and most of the rooms connected to the end of the Trunk line barely push out any air. There are currently 5 Registers/supply's (Cat Room, Bathroom 1 & 2, Computer Room, Baby Room) connected to the end of the trunk line, all seem to be 6" ducts. The lines in the beginning of the Trunk (my bedroom) pump out an enormous amount of airflow, so much that I leave the vent closed.

 

my question is, When do i use 4" or 6" ducts? I believe the beginning of the Trunks have 6" and 7" and towards the end are all 6". I need to increase the airflow at the end of the Trunk Line (the 5 registers).

 

I got two different answers when i went to Home Depot and Lowes. One said I need 6" ducts at the end while the other says to use 4" ducts because the airflow is the weakest and I am just moving cold air.

 

Do I leave the 6" at the front and change all at the end to 4"?

 

Is using a 6" to 4" reducer the same or do i have to replace the actual piece at the trunk.

 

Here is a PPT drawing of my home. Please note that the Trunk/Unit are actually the same but since I have a crawlspace running alongside my home, It was just best to draw it twice. Also, it may look reversed but the 1st page is drawn horizontally and the 2nd vertically. Just picture the crawlspace in your head to line up the direction in your mind.

http://www.mediafire.com/?2mkjgjlltwo

I am not concerned about the bathrooms, primarily the Computer Room (1st floor), Living Room (1st floor), Main Bedroom (2nd floor) and Baby Room (1st floor).

My beams run in the same direction as the arrows for ductwork. If you need size dimensions, I would my house is roughly 35 feet by 60 feet. 35 feet is the direction of the arrows.

 

I would prefer to reduce the Main Bedroom and increase flow to the Living Room (directly below Main Bedroom (2nd Floor) and Computer/Baby room (Below Cat Room on 2nd Floor)

Customer reply replied 7 years ago

Ohh this is my home lol my oil heater went so it was going to cost just as much to replace and move my oil furnance as it was to install Central Air and Heat.

 

At first, I had them come back because i was barely getting anything out of the end of trunk registers. They used so much Flex, We literally cut off about 6 Feet of Flex at each register. I thought that would solve the problem, it did make it better, but not efficient.

 

I didnt draw Returns but there is a huge return in the hallway on the 2nd floor, One in the Cat Room, One in the Main Bedroom, and One in teh Living Room.

 

ok...

As an example of what I was saying... (I cant upload any files, but I took a snapshot of what I was saying after a quick modification.)

The industry should use ACCA manual D as a reference... but here... look at this.

graphic
Ask Your Own HVAC Question
Customer reply replied 7 years ago

If you need to know the model its a 3 Ton Goodman 16 Seer w/ Heat Pump and I believe they did a 4 Ton blower? Not quiet sure.

 

i believe all vents are 12"? and 2 x 10" vents in the Living Room.

 

I already have the ceilings opened cause the electrician cut one of the ducts when he ran wiring for my new electric water heater. I also already removed the flex from the Baby Room and have both 4 and 6" hard ducts ready to install. Plus since Im doing it, I am going to properly insultate each piece as i run them.

 

As for getting the installer to come back... well, thats what i get for going with the cheaper company. Its just one of those things where you say to yourself, i dont want to deal with these people anymore and if you want something done right, gotta do it yourself heh

 

Yah i see what your saying about reducing, Forgot to put that in the drawing but there is one point, about halfway where it looks like they reduced it a 6"? Unsure of amount but it does get a bit smaller and stays that width until the end of the trunk

Customer reply replied 7 years ago

So I guess your saying leave the ones at the end as 6"? I dont mind shrinking the ones in my bedroom to a 4" if that will increase airflow. I was also debating on removing one Register from my bedroom since that room gets VERY hot

 

I bought all the necessary pieces of 4" and 6" I just want to try to make the airflow better at the end heh.

 

Another option is installing one of those in-duct Fan things? Or should i just leave it all as is and just insulate the duct pieces I can get to that run between the joists. the ceiling is already open

in a nutshell a 3 ton machine needs to move 1200 cfm of air. It needs to move this at about 700 feet per minute in the main trunk. (there's more to it).

is you main duct rectangular or round?

I cant answer your last question just yet.... if we are going to do this, we are going to do it right.
Ask Your Own HVAC Question
Customer reply replied 7 years ago

ok, its a 3 Ton Heat Pump and I believe the Blower is set to 4 ton. As for the Main duct, if you mean the Trunk it is Rectangle. and wrapped in some insulation cover.

 

All Lines to registers were mostly Flex Duct but they came and replaced a lot of it with the hard metal duct and removed excess flex at each register. The whole house is only 1700 Sq feet i believe.

 

All are 12" Registers I believe except the two in the living room which are 10"

Customer reply replied 7 years ago

I am going to run upstairs and measure the size of the rectangle trunk and where it shrinks down a size. brb 2 min.

 

GOod thing my walls are still down. Had wood walls upstairs and i tore it down because i was redoing all the drywall & electrical.

Customer reply replied 7 years ago

ok so the Trunk is 9 Inches High and 16.5" wide. Roughly right where the stairs are on the 2nd floor is where it shrinks to 9" high and 12" wide

Are you saying that the first drawing you provided is correct or an example of an incorrectly one? Do you think that the solution really is to just shrink the main trunk line down a bit more? And if so, how easy is that lol

ok rectangluar....

1600 CFM for 4 ton, but I wouldnt know why they would do that unless you have like no humidity in the summer to contend with.... Lets spit the difference for arguments sake to 1400 CFM

1400 CFM to move at 700 FPM would require a main trunk starting at like 10 x 35" or 8 x 50 or 12 x 28.... as a couple runs are taken off at say 110 cfm per run, that leaves us with 1070 cfm.... this would need to be reduced to 10x24 or 8x34 or 12x20...take 3 more off at 110 cfm and we are down to 740 which will be about 10x17 or 8x22 or 12x14...take 3 more off with 110 cfm each for instance and we have to supply the last 3 with the remaining 310 with a 10x7, 8x8 or 12x6

A 6" flex duct will only move about 70 cfm if stretched tight. Hard pipe 6" would get you about 100 cfm. Hard 7" will get you about 140 give or take.

Your 9x16.5 is about half what it should be.
Ask Your Own HVAC Question
Customer reply replied 7 years ago

Just measured the main trunk start and it is 20.5" wide, 9" high. Ill have to go scout to see where it drops to 16" wide and 9" high

So basically your saying the problem isnt necessarily the actual duct work, its the trunk. So leaving them all at 6" should be sufficient?

Right at the start of the trunk there are 3 lines coming off it (2 in Family room + Kitchen)

and it looks like 4 lines coming off the trunk when it is 16.5"

and 5 when it is 12 " wide

Uhh, yes and a little no, but more yes.

Like I said, the air is dumb but you really cant wish it to go where you want it, you have to force it there.
Ask Your Own HVAC Question
Customer reply replied 7 years ago

Give me one sec, I kind of understand where you are going with this. I just want to get the total length of my trunk and the distance between the trunk and register.

 

brb 1 min

I have to eat... I'll be back shortly... wife says so.
Ask Your Own HVAC Question
Customer reply replied 7 years ago

ok.

since I know im taking up a lot of your time. If i was to give you a $40 tip and provide you with the exact length of my trunk (or max space available for the trunk lengthwise) and provide you with the exact distance from the trunk to the registers. Could you provide me with the trunk dimensions and where I need to decrease it? Not sure if you have that book Manual D - Residential Duct System. it doesnt have to be perfect, just your guestimation would probably be better than what i have now lol

Frankly, since my walls are open, me re-doing the trunk would be a lot easier than me trying to redo all the ductwork to each room. I have full access to 85% of the trunk except at the end there is about 4-5 feet I would have to crawl to but is still accessible.

I can just completely remove the trunk and make adjustments to it and just reconnect the registers/supplies since those pieces will be there already waiting to be connected

I can always run a trunk within the beams horizontally if you think that is better . My house isnt that big and with the way the crawlspace is, Ideally it would be nicer to just keep 1 trunk and leave the register/supply ductwork that is already in place.

As you can see by the drawing, that one trunk locations basically directly hits 8 (Main Bedroom x 2, Living Room x 2, Family room x 2, Computer room, Cat Room) of the 12 registers without running a lot of ductwork.

The only ones with more than roughly 4-5 feet of duct are the Kitchen, Both Bathrooms and Baby Room.

 

Ill go measure while you are eating.

so how do the ducts get to the second floor?


How does the duct connect to the unit? Is this a packaged unit or a split system?

Edited by Douglas on 1/18/2010 at 12:12 AM EST
Ask Your Own HVAC Question
heres what I need....

Do another powerpoint single page

Do the downstairs in one color and overlay the second floor in another color Lets say brown for first and green for second. Put the registers in the rooms using the same colors as the walls.

I dont get the crawl space on the side thing...how does that work, is this a space between row houses or somthing or what am I missing?
Ask Your Own HVAC Question
Customer reply replied 7 years ago

Whoops Sorry, was doing the PPT. http://www.mediafire.com/?ammd0gidord

 

Basically the crawlspace runs alongside my house and is roughly 3 feet wide by 3 feet high. Some people use it for extra storage space but its pretty much unfinished and kind of like an attic crawlspace but running alongside my house on the 2nd floor. Why its there, is beyond me lol I actually have the crawlspace running along both sides but I removed the irrelevant one because it is hard to get to if we were going to run ductwork.

 

The Indoor part of A/C Heater Unit is in my attic which is directly above the Family room. The Trunk is connected to that unit and runs into the crawlspace. Both pieces are located on the 2nd floor. So that one trunk line does both 1st and 2nd Floor.

 

On the 2nd floor, all the registers and supplies come out of the top of the trunk to feed the upstairs registers. All of the ones downstairs come out of the bottom/underneath the trunk and in my Joists to get the the rooms like the Baby room, 1st floor bathroom, and Kitchen. All other registers - Computer Room, Cat Room, Main Bedroom, Living Room are literally either 2 feet above or below the Trunk Line. The 2nd Flr bathroom Basically shoots across from the trunk to the bathroom by utilizing the attic. And the Family room (1st flr) is literally below th attic so they just ran 6" ducts in the attic and just cut holes to install the register.

 

I think the confusion is coming in because the 2nd floor was drawn Horizontally and the 1st floor the other way but if u use the Trunk as your point of reference just turn one page so that they are literally on top of each other.

 

 

ok let me digest this for a while....
Ask Your Own HVAC Question
Customer reply replied 7 years ago

hopefully this one makes a little more sense. I rotated the second page so you can basically see how they line up

http://www.mediafire.com/?m5zjdjdyqoz or

http://www.mediafire.com/file/m5zjdjdyqoz/Rotated AC_and_heat_design_Revised[1].ppt

Ok, I overlaid it.... Dont worry about where the rooms are, you can visualize the rooms

On this picture the upstairs registers are in purple and the downstairs are in yellow... Does this look right?

graphic
Ask Your Own HVAC Question
Customer reply replied 7 years ago
Yup looks about right
ok I'll work on the sizing... it may be a little while.
Ask Your Own HVAC Question
Customer reply replied 7 years ago

Sure, thanks again. XXXXX mistaken, i thought they said my blower can go up to a 5.5 ton blower but im not 100% on that. You would think this house should be easy to heat since 80% of the vents are right above and below the trunk. There are really only 4 vents that have to travel any distance (Bathrooms, Kitchen, Baby Room)

 

the Family room ones I was probably going to move to the other side of the wall to eliminate the extra 10 Feet of duct they put down so those will only be about 5 feet directly to the left of the start of the trunk.

 

I have to run to walgreens to get baby detergent. If you answer while im gone or need any additional info, I can text that from my phone since it sends me a message.

 

Hopefully its just the trunk that is causing the problem cause it would be nice to return the $400 worth of duct stuff i bought and just get a newer, bigger trunk plus materials to reconnect each supply back to the trunk

 

 

graphic


Because of some of the real short runs, you will have to put balancing dampers in the take offs to the runs so you can balance it. You dont want to depend on the registers as the air has already started down the pipe...
graphic
Ask Your Own HVAC Question
you'll laugh at this, but it works when you dont have the fancy tools those of us spend thousands on....

When you have it all piped in, you can use the balancing dampers to get the airflow set.

Read and bookmark this article.... You can set the airflow on each run. It takes a little math but it works....

http://www.kqed.org/quest/blog/2007/04/20/energy-efficiency-get-your-ducts-in-a-row/
Douglas
Douglas, HVAC Technician
Category: HVAC
Satisfied Customers: 3,089
Experience: Manufacture Rep for Major Brand, Technical Trainer, NATE
Verified
Douglas and 87 other HVAC Specialists are ready to help you
Ask your own question now
Customer reply replied 7 years ago
Okey dokey. I'll be home in 15-20 min won't let me open any attachments or pics on my phone. At the cash register now, be home soon
lol you sound like me... driving around with GPS, Laptop, blackberry.
Ask Your Own HVAC Question
Customer reply replied 7 years ago

Gotcha. Thanks a bunch but I just want to make sure i understand this diagram.

 

So where you indicate 6" or 7", I know that is pretty straight forward for the actual duct work but when it comes to the actual connection between the end of hte duct and the register, do i need to specifically look for a 7" register or at that point, can i use a 7" to 6" converter etc.

 

For the trunk, is the 1200, 790 and 410 the CFM that is remaining at that point? or does it mean something else. Does how long each section is matter? Or can i pretty much just wing it from the point indicated on teh design or after it passes the last register for that group.

 

Im assuming the 10x24, 10x15, and 10x9 are the sizes in Inches. Dumb question but, is there a specific name for Trunk so when i go look for it in Lowes or Homedepot do i need to call it something else?

 

And the 120, 110, 100 etc I assume that is the umm Feet per Minute or CFM each register should be pumping out?

 

When you mention dampers, I briefly read through that link you posted, so basically im putting in Dampers not so i can change them around freely whenever i want but to balance out the airflow throughout the entire system? And basically I can close the wall up cause i wont need to mess around with the dampers once it is set?

 

And the last dumb question, does it really make a difference if I have all the supplies coming out of hte side or top or should i really have it come out of the bottom for all the 1st floor registers?

Customer reply replied 7 years ago
not sure if i need to post so it allows you to respond or not. I dont know if justanswer closes the topic once i accept heh
you can use an increaser at the end if you need to for the register boot.

The ducts are in square inches. Just make sure the volume is the same give or take a very small amount. So if you were converting 10x24 thats a cross section of 240 square inches. If they only have 8" duct then you would need 8x30.

The 100, 110 are cfm measurements.

Yes the dampers will allow you to fine tune it. Because some runs are longer than others, there will be variables. Start with them all open and adjust accordingly.

It doesnt matter where they come from, just try to keep the nubmer of elbows to a minimum.
Ask Your Own HVAC Question
Customer reply replied 7 years ago

Thanks again for all your help and advice, now I just need to go return two truck fulls of duct and go get the correct stuff. I hope When i disconnect the trunk from the A/C unit that it isnt that hard to go from the 20"x9" to a a bigger 24"x10" or whatever combo makes it 240 square inches. So it doesnt matter how tall or long it is, as long as it comes out to the same Square inches per section?

 

What are the common sizes available to people at local hardware stores?

Dont know, I never bought any duct at a hardware store... Always made my own. (better made and less expensive).

You can make your transitions out of spare metal. Just make sure it's sealed. You will want to apply mastic to the seams to prevent leakage.

graphic
Ask Your Own HVAC Question
Customer reply replied 7 years ago

hmmm do you need any special tools to make your own? I recall Home depot selling like sheets of the metal, wasnt quiet sure how to turn that into a trunk.

 

Is the tool similar to this http://www.homedepot.com/webapp/wc s/stores/servlet/ProductDisplay?storeId=10051&productId=100648037&langId=-1&catalogId=10053&ci_sku=100648037&ci_src=14110944&cm_mmc=shopping-_-googlebase-_-D27X-_-100648037&locStoreNum=4163&marketID=34

 

Along with like umm S Cleats or something like that?

Haha that's one tool the others looks like this....
graphic

graphic

graphic
Ask Your Own HVAC Question
Customer reply replied 7 years ago

LOL well I dont think ill be picking one of those up anytime soon LOL

 

Ok, last question, When you say 10" high x 24" wide, how long does that particular trunk need to be or does the length not matter cause a 10"x24" by 5 foot piece will have a higher square inch than a 3foot etc

same thing.. just more joints.... As long as you get past the take offs that are supposed to be on that run.
Ask Your Own HVAC Question
Customer reply replied 7 years ago

ok, that makes sense. Ill just pretty much follow the design. Its pretty much like how it is now except I will be making the trunk a bit bigger. Thanks again, ill leave you be now heh.. plus i have to clean the mess before my wife comes home :P

 

Ill let you know how it turns out.

Customer reply replied 7 years ago
unless you live near PA then come drop those machines off :P
uhhh no....
Ask Your Own HVAC Question
Ask Douglas Your Own Question
Douglas
Douglas
Douglas, HVAC Technician
Category: HVAC
Satisfied Customers: 3,089
3,089 Satisfied Customers
Experience: Manufacture Rep for Major Brand, Technical Trainer, NATE

Douglas is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,730 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
We installed a bradford water heater 1 week ago, it has a
good morning we installed a bradford white water heater 1 week ago, it has a honeywell control, and the issue: two flashes on the LED status, the pilot goes on the unit fires for 20 seconds and then g… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a 19.9 Rheem 120 volt water heater it does not have a
I have a 19.9 Rheem 120 volt water heater it does not have a drain valve . how do I drain it ? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
If a gas water heater with an FVIR is installed in a room
If a gas water heater with an FVIR is installed in a room with a washing machine, can cleaning products such as liquid laundry detergent and chlorine bleach trip the FVIR? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Question about basement insulation... It's not a problem -
It's not a problem - it's a question...we live in the Atlanta area. 3 years ago, we purchased an existing home that has a full, unfinished walk-out basement, which means that the entire north and west side of the basement is above grade. The south and east walls are poured concrete and are below grade. When we bought the home, it had zero insulation in the stud walls on the north and west sides. The concrete walls also were not insulated. However, there was faced fiberglass insulation stuffed between the floor joists in the basement ceiliing … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My water heater won't light. Yesterday. Trying. Is there a
my water heater won't light JA: How long has this been going on? And how severe is the problem? Customer: yesterday JA: Do you plan on doing the work yourself? Customer: trying JA: Anything else we sh… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
The yellow wire on the blower motor through insulation. It
The yellow wire on the blower motor burnt through insulation. It appears to be 15 years old. Would it be safe to repair the yellow wire and continue to run the motor? The ground wite is hanging loose … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My honeywell hot water heater is flashing a code of upper
My honeywell hot water heater is flashing a code of upper sensor failure, what should i do? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a takagi tankless water heater that is used for in
i have a takagi tankless water heater that is used for in floor heat. it makes a really loud noise when it starts up. no always, but often. originally it did it all the time, but we reset some dip swi… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I HAVE A WHIRLPOOL HOT WATER HEATER WITH A HONEYWELL
I HAVE A WHIRLPOOL HOT WATER HEATER WITH A HONEYWELL FLAMABLE VAPOR SENSOR LOCKOUT. MY BASEMENT GOT 2 TO 4 INCHES OF WATER DUE TO RECENT HEAVY RAINS AND APPEARS TO HAVE TRIGGERED THE LOCKOUT. MY QUEST… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Bradford defender power vent hot water heater. One flash
Bradford white defender power vent hot water heater. One flash every 4 seconds or so.WV4460E 2014 pilot is working but no increase in temperature as I move temperature control up.… read more
WCohn
WCohn
Journeyman Plumber
Journeyman License
1,199 satisfied customers
I have a tankless water heater and it is not warming the
I have a tankless water heater and it is not warming the water and coming up with a C7 error. I have turned it on and off a couple of times and it will warm the water for a little and then goes off ag… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
Where on the water heater is the optimal position to install
Where on the water heater is the optimal position to install the Taco recirc. timer? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Our water heater was leaking and now are heating and cooling
Our water heater was leaking and now are heating and cooling isn't working. The fan doesn't cone on at all; Are these things related? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Draining a Richmond model 54P50E-1 water heater but it will
Draining a Richmond model 54P50E-1 water heater but it will only drain slowly … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
Our water heater will not ignite. The flame goes on for very
Our water heater will not ignite. The flame goes on for very short periods of time We changed flammable vapor sensor today SP20172 … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I'm looking for the best method and type of insulation to
I'm looking for the best method and type of insulation to use in an 1890's home that has non-uniform stud and rafter spacing that ranges from 28"- 34" on center. In this process should I use a vapor b… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I need service on my water heater. Water heater still under
I need service on my water heater. Water heater still under warranty. Who do I contact for service asap? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
What is the use of insulating suction pipe of compressor? I
What is the use of insulating suction pipe of compressor ? I mean is it useful in package units also ?… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
953 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x