I have a TRANE BLU055E936B1 Gas Fired Air Furnace. My heat

Customer Question
stopped blowing last night. The...
I have a TRANE BLU055E936B1 Gas Fired Air Furnace. My heat stopped blowing last night. The Thermostat is working properly. The gas in on and pilot is ignited. I removed the fan blower door and manually pressed the blower door switch. The switch clicks and ignited the furnace once, but once I released it that time, it would not re-ignite. Is this most likely a failure with the door switch or something more? This happened in late fall but I assumed the door switched had slipped under the door frame, once I played with it a couple of times it ignited the furnace and has worked until last night.
Submitted: 7 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 9 minutes by:
1/11/2010
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 7 years ago
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 22,756
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified

You are correct. I also commend you for realizing and recognizing the function of door switch. If it becomes too troublesome you can bypass until you get a new switch.

 

Obviously it is a safety feature for when the bottom door is removed to cut power.

 

I wish you luck

Ask Your Own HVAC Question
Customer reply replied 7 years ago
I have bypassed the blower door switch. Should the furnace ignite imediately? Furnace has not ignited now for well over an hour. What should I do next? Tranformer? Gas Valve 36C03 Type 222? Clean pilot ignition?
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 7 years ago

I apologize...computer troubles...

 

Clean all the rods and metal components of ignitor with steel wool, reset power and see if cycle improves

Ask Your Own HVAC Question
Customer reply replied 7 years ago
I was able to wire brush the thermocouple senser using a small brass brush. I lit the pilot and turned the system on. The pilot is burning just fine. Still no gas released to the burners though. Does this mean I need to replace the gas valve or is there more to check? Is the thermocouple causing the problem? If pilot is lit, thermocouple is working properly, no?
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 7 years ago
Ask Your Own HVAC Question
Customer reply replied 7 years ago
No. Looks like this one and connects directly to the top of the Gas Valve 36C03 type 222.

http://americanhvacparts.com/Merchant2/merchant.mvc?Screen=PROD&Product_Code=PIL2400&Category_Code=P

HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 7 years ago
This valve has 2 terminals under the thermocouple fitting that run to a safety. Follow the 2 wires from under tcouple fitting and tell me what they run to.
Ask Your Own HVAC Question
Customer reply replied 7 years ago
The wires run to what looks like a sensor into the sheet metal. I removed it and it has a copper loop on the end. The plate reads General Electric and 415º with a long part no.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 7 years ago
Remove the wires from it and touch them together
Ask Your Own HVAC Question
Customer reply replied 7 years ago
Do you mean to remove the wires from the terminals and cross connect the terminals with say a screw driver?
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 7 years ago
that works also
Ask Your Own HVAC Question
Customer reply replied 7 years ago
I removed the wires from the terminals. The pilot went out, immediately. I touched a screwdriver to both terminals connecting them and had no reaction.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 7 years ago

 

Good, at least now we know the limit and thermocouple are good. Do you have a meter to check 24v at the gas valve?

Ask Your Own HVAC Question
Customer reply replied 7 years ago
No. no voltage meter. Once I have one what should I do? I will run and buy another, I'm sure my stepson or ex-wife has mine.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 7 years ago

you will check for 24 to the gas valve terminal...one meter lead to ground and the other to th on valve.

 

24v on th with no burner = bad gas valve

Ask Your Own HVAC Question
Customer reply replied 7 years ago
I performed the meter reading. Make sure I did this properly. I placed the black (-) lead to the body of the gas valve and the red (+) lead to the th terminal (left of center terminal). I used ACV setting of 50 on the GB instruments GMT -312. This is a needled meter not digital. Should have purchased digital. The needle moved and held slightly at 2 marks off 0 (zero). I want to say that's definitely less than 24. Note, I did not lite the pilot, nor did I replace the two wires to the terminals removed a step or two ago.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 7 years ago

 

sorry for delay...my regular job needed my attention.

 

Now take the blower door off and tape the switch down again. Find the white wire coming from the thermostat and tell me what it goes to in the furnace.

Ask Your Own HVAC Question
Customer reply replied 7 years ago
I believe I made a mistake when metering the Gas Valve. I changed my placement of the black lead and placed it into the black wire wire-nut connecting the power to the furnace and the red (+) lead to the th terminal (left of center terminal). The meter read 24 when I metered it in those locations. Doing this wrong? When I placed the black on the ground wire coming into the furnace and then the red to the th terminal it read maybe 5-10.

The white wire from thermostat? Is the the white wire running with 4 others green, red, yellow and blue?
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 7 years ago
correct, the white with the colors you described. Does it run through the limit?
Ask Your Own HVAC Question
Customer reply replied 7 years ago
It connects by wire-nut to a heavier wire with inline fuse to the th terminal on the gas valve.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 7 years ago

 

Great, that is what I wanted....now put red lead to TH and black lead to cabinet while thermostat is calling for heat.

Ask Your Own HVAC Question
Customer reply replied 7 years ago
Do I first remove white wire from th? Black wire to cabinet? Cabinet meaning the furnace itself?
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 7 years ago
Leave white to TH and black meter lead to furnace cabinet
Ask Your Own HVAC Question
Customer reply replied 7 years ago
Meter needle is barely moving to 5 - 10
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 7 years ago

lets leave the black lead on the side metal of the gas valve, no paint and conductive.

 

Now move the red lead to the white wire coming from stat. Unhook from wire nut and test the wire direct.

Ask Your Own HVAC Question
Customer reply replied 7 years ago
The meter read maybe 15.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 7 years ago

 

go to thermostat and remove top section. Take R wire and W wire and twist together. Metal to metal.

Ask Your Own HVAC Question
Customer reply replied 7 years ago
Done. So far nothing happening. It's been about 5 minutes
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 7 years ago
Take apart red and white and put a meter lead on each wire
Ask Your Own HVAC Question
Customer reply replied 7 years ago
Done. Almost nothing maybe 5.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 7 years ago

 

we need to bypass the door switch and make sure power is going to furnace. The red wire should have 24 volts at all times. We are missing power somewhere

Ask Your Own HVAC Question
Customer reply replied 7 years ago
Done. Bypassed the door switch. What next? read red and white wire at thermostat again?
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 7 years ago
Correct
Ask Your Own HVAC Question
Customer reply replied 7 years ago
Done. when I place the black meter lead on white and Red on red or vice versa the meter reads barely anything. When I place the black to the black ground and and red to red the meter reads a tad more than 25V. Sorry I do not work with electricity often or even some.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 7 years ago

Now hook all back up.

 

so red wire to ground got us 24v. Pull the TH wire from gas valve and measure it to ground the same way. I know we did this before but it was missing last time

Ask Your Own HVAC Question
Customer reply replied 7 years ago
My apologies. The one step back. It was not a black wire at the thermostat is was a green wire. It's connection on the thermostat is marked with a G and there is black electrical tape close to the end.

I re-connected the thermostat. I took the th wire from the gas valve and touched the black lead to the galvanized metal cabinet and red lead to th, resulting in low meter reading. I then touched the black lead to the incoming ground wire, (black, white, ground - power source) and red to th, resulting in the same. I then touched the same thermostat green wire and red lead to th, resulting in 24V.

Gotta call it a night. How do I resume tomorrow?
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 7 years ago

Ok now that your familiar with the meter a bit more....

 

all the thermostat wires come into the furnace. Do they all just connect to other wires or do any mount on a control board?

Ask Your Own HVAC Question
Customer reply replied 7 years ago
They connect to other wires. I have two groups of wires coming into the unit other than the main power supply wire. One from the thermostat and I don't know about the other.

Once connected by wire-nuts to other wires some connect to post of terminals (see photos)

graphic

1st group
Colors are red, yellow, lt blue, white and green.
yellow not used

2nd group
Colors are dark blue, white and red.
dark blue not used

graphic

some sort cylinder connected to this, hard to see in photo.






HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 7 years ago

 

excellent, the cable with 5 wires comes from thermostat, the cabel with 2 wires goes out to the outdoor ac unit.

 

The white wire in the cable with 2 wires is know as common. The red takes 24v out to the ac unit.

 

The white wire in the 5 wire cable is the one that goes to the gas valve on TH right?



Edited by Billy on 1/12/2010 at 4:18 PM EST
Ask Your Own HVAC Question
Customer reply replied 7 years ago
Yes
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 7 years ago

 

Great, thermosta hooked up, heat turned up, power on. Remove TH wire from gas valve. take wire nut off the white wire in the 2 wire cable but leave twisted together.

 

Red meter lead to TH wire removed from gas valve and black lead to white wire in 2 wire cable.

Ask Your Own HVAC Question
Customer reply replied 7 years ago
Sorry for the delay. I did what you instructed and the needle did not move at all.

HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 7 years ago
that means no power is getting to the valve. Can you see if 24 v is at the red wire in 5 wire cable
Ask Your Own HVAC Question
Customer reply replied 7 years ago
Black lead to Red Wire and Red Lead to th terminal?
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 7 years ago
Sorry, black lead to the 2 wire cable white. Red lead to red wire
Ask Your Own HVAC Question
Customer reply replied 7 years ago
Yes, 24V
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 7 years ago

 

And not to beat a dead horse...but the white wire from the thermostat goes direct to TH on gas valve?

Ask Your Own HVAC Question
Customer reply replied 7 years ago
Yes, however it is connected by wire nut to another white wire connected by wire nut to another white wire with and inline fuse connected to th.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 7 years ago

 

I understand...check the inline fuse

Ask Your Own HVAC Question
Customer reply replied 7 years ago
Looks to be okay when shining light through opposite side, I don't see any breaks, but there is some amber discoloration to one end of the fuse. The fuse looks like this one.

http://americanhvacparts.com/Merchant2/merchant.mvc?Screen=PROD&Product_Code=FUS0283&Category_Code=F
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 7 years ago

 

Take the fuse section out of the equation and have white wire go direct to TH.

Ask Your Own HVAC Question
Customer reply replied 7 years ago
OMG...Burner came on immediately
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 7 years ago
Excellent, gosh I am glad you have patience!
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 22,756
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified
BillyHvac and 87 other HVAC Specialists are ready to help you
Ask your own question now
Customer reply replied 7 years ago
Thanks very much. You know I have a friend that works does this stuff for a living, some 25 years now, but he is always working late and I decided I wanted to learn a little something. Thanks for your patience. Have a great week.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 7 years ago

 

Well done. I thank you

Ask Your Own HVAC Question
Ask BillyHvac Your Own Question
BillyHvac
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 22,756
22,756 Satisfied Customers
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics

BillyHvac is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,730 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have replace the board and the the limit switch and the
i have replace the board and the the limit switch and the flame sensor. now and before the exact thing happens.... exhaust would come on and the igniter would glow orange flame would kick on and then … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Have a Nordyne gas furnace- unit mod#M1MB 077A AW - fails on
Have a Nordyne gas furnace- unit mod#M1MB 077A AW - fails on flame failure. Igniter glows,main flame comes on,goes into failure. When reset it will run for days and again have same problem. Could ther… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
22,756 satisfied customers
I am looking for a gas valve for my Duo Therm Model 708001-2
I am looking for a gas valve for my Duo Therm Model 708001-2 mobile home furnace. The numbers on the valve are TF-555 TM-6 … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,070 satisfied customers
I am trying to figure out why our pilot light won't ignite.
I am trying to figure out why our pilot light won't ignite. Our power went out today and now the furnace is blowing cold. We have reset the breaker and the on/off switch and the gas and the thermostat… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a T.H.E. 90 furnace, model 2970E766. A couple of days
I have a Coleman T.H.E. 90 furnace, model 2970E766. A couple of days ago, the high speed blower wire (black) at the blower relay melted. I replaced it with a new 1/4 female blade terminal. Now the red… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My boiler flashes red on occasion and says hardware fault
my boiler flashes red on occasion and says hardware fault reset control if problem reoccurs replace sage control … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a Honeywell pro 3000 thermostat to install and there
I have a Honeywell pro 3000 thermostat to install and there is only a red and a white wire what wiring diagram do I use? … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I want to buy a heater that is more powerful than what I
I want to buy a heater that is more powerful than what I have: Lasko model 754200Any option?… read more
Paul the Plumber
Paul the Plumber
Vocational, Technical or Trade Scho
21 satisfied customers
I have a 70 pint dehumidifier GL-DEH-70EIP-6 purchased July
I have a 70 pint dehumidifier GL-DEH-70EIP-6 purchased July 2013. 2 years ago the internal pump stopped working and this year it runs but does not dehumidify. I like the unit and have gone through all… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Trying to get my furnace running. Only the blower keeps
Trying to get my furnace running. Only the blower keeps running with no heat. Had the igniter checked and it is ok … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a panaosonic split system heat and air conditioner. -
i have a panaosonic split system heat and air conditioner. - CS MKE 18 NKU … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,070 satisfied customers
I'm reading the issue where blower doesn't come on after
I'm reading the issue where blower doesn't come on after combustion but does work in manual or when heat pump runs. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Where can I buy a temperature sensor for an Amtrol Water
where can I buy a temperature sensor for an Amtrol Water Heater? Part number E1 Type 2B61 … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I can not unlock the day button. Tried the recommended
I can not unlock the day button. Tried the recommended action and still, nothing … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I would like to install a new thermostat with my new hvac
Hi I would like to install a new thermostat with my new hvac and I need some documentation please … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Vitodens 100 boiler with a recurring F5 fault code
I have a Vitodens 100 boiler with a recurring F5 fault code when it turns off or goes into rest mode. Internet search revealed it was the air or pressure-switch problem, "the infamous flap," which is … read more
Elliott Oxton
Elliott Oxton
NVQ Level 2
4 satisfied customers
Have a York D1NP042N09006 DUAL AC/GAS HEAT unit. had blower
have a York D1NP042N09006 DUAL AC/GAS HEAT unit. had blower replaced and since then fan speed is too high(35 40 degree difference in/out) how do adjust? or is ST9120 2002 board bad? … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Honeywell thermostat ct87k. how do i set the anticipator to
honeywell thermostat ct87k. how do i set the anticipator to 0.9amp? … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x