I have a Trane XL-80 with White Rogers control board 50a51-405,

Customer Question
these are original since the...
I have a Trane XL-80 with White Rogers control board 50a51-405, these are original since the house was built in 1993. last week, the furnace could not get ignited, the light on the board shows one slower single flashing first, I think it means requestin heat, then it goes to a fast double blinks after failing in ignition, I think it means system lock-out, then the fan kicks on, the light is static on. The fan seems never shuts off.

I check the vent, it is all clean. I had a guy came in from "First Call" a service company, he measured the voltage coming out the board to "R" terminal is only 13v. it is supposed to be around 24v. he also verified that the transformer works fine, it does generates the 24v going into the board, then board should take the 24v from transformer and sending a 24v signal to "R" terminal which in my case it is only 13v. So he suggested to change the whole board which will cost me $500. Is this the root cause? I made it ignited after turn off/on thermometer.
Submitted: 7 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 10 minutes by:
1/4/2010
HVAC Technician: Douglas, HVAC Technician replied 7 years ago
Douglas
Douglas, HVAC Technician
Category: HVAC
Satisfied Customers: 3,089
Experience: Manufacture Rep for Major Brand, Technical Trainer, NATE
Verified
without actually using the meter, it's difficult to say but I will say this..

IF the volatge was measured without a load, the reading may be incorrect because solid state will allow voltage through but no current. The way to test the 24v in solid state is to have a known load such as a relay. Measure the voltgage with the relay.

If the measurement was made while the furnace was locked out, the current to the R terminal may have been interupted by the control.. This is how it stops the unit from running.

IF I were there, I would test the circuit by removing the thermostat and thermostat wiring from the equasion and simply jump R-W. If it fired, I would repeat the process several times. If there is a safety locking it out such as flame failure, I could go from there to determine if the flame actually came on, and then back off or could begin troublshooting from there.

My bet, is it would work with a jumper, the flame would ignite and go back out telling me that the flame sensor simply needs cleaned.

Now, I said all that because I dont know what his steps were. I am not saying he is wrong because there is no way from here to tell, but 13v sounds like an unloaded solid state type reading.
Douglas
Douglas, HVAC Technician
Category: HVAC
Satisfied Customers: 3,089
Experience: Manufacture Rep for Major Brand, Technical Trainer, NATE
Verified
Douglas and 87 other HVAC Specialists are ready to help you
Ask your own question now
Customer reply replied 7 years ago

 

Doug,

 

Thanks for your info, I saw the service guy removed the wire connection at R terminal during the measurement, and he acutally tried to feed the output from the transformer into "R" terminal directly, but no flame, maybe the thermostat is off at the time, because he wants me to have thermostat is off for safety. I guess try to approve the voltage problem which is too low.

HVAC Technician: Douglas, HVAC Technician replied 7 years ago
Certaily there is room for being skeptical on a bill that large but my hope is he backs up his claim and when the board doesnt do the job, he doesnt bill you for it. It's not for me to question his ability, he may very well have nailed it.
Ask Your Own HVAC Question
Ask Douglas Your Own Question
Douglas
Douglas
Douglas, HVAC Technician
Category: HVAC
Satisfied Customers: 3,089
3,089 Satisfied Customers
Experience: Manufacture Rep for Major Brand, Technical Trainer, NATE

Douglas is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,730 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have central AC sysyem - Spacepak airhandler, York
I have central AC sysyem - Spacepak airhandler, York affinity 3s outside unit and a Honeywell TH8100U1003 thermostat. The outdoor unit has been intermittently cooling but seemed to start working again… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
My unit is not operating correctly. I have it set at a temp,
my unit is not operating correctly. I have it set at a temp, and it doesn't come on when the temp goes below the set heating temp. I have to manually hit the set button and it comes on, but then it do… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a Weil-McLain CGa boiler. The pilot is lit and it
I have a Weil-McLain CGa boiler. The pilot is lit and it sounds like it is switching on and off (when the thermostat is on) but we're getting no heat. Is there something I should be checking? Thanks. … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My Trane TUE080A936K2 furnace isn't heating the ignitor
my Trane TUE080A936K2 furnace isn't heating the ignitor never glows, but the fan spins up … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Looking for replacement blower motor for an old RUUD gas
Looking for replacement blower motor for an old RUUD gas furnace model HN-175JD blower # RL10-9DUH … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a York central heat unit. The problem is it wants to
I have a York central heat unit. The problem is it wants to turn on to give heat but shuts off after about 2 seconds and keeps on doing the same thing. Had this problem 3 weeks ago. Unplugged limit sw… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,082 satisfied customers
I am replacing a RUUD 3aat86b9a1 with a Honeywell
I am replacing a RUUD 3aat86b9a1 with a Honeywell RTH2510/RTH2410v series. … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Just inherited my grandparents house. Built in 1972. They
Just inherited my grandparents house. Built in 1972. They have a closet that is 50 by 70 inches that used to house a gas water heater and a gas furnace, below the closet is the intake air. The gas fur… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have the same problem with my code 33 I followed your
I have the same problem with my Bryant code 33 I followed your instructions as described here and it worked so I need a new limit switch, with one caveat, I let the wires touch metal and now I get not… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
90% secondary heatexchanger holding a lot of water in it,
Bryant 90% secondary heatexchanger holding a lot of water in it, not allowing the pressure switch to close. I removed the 3 hoses at the top (2 large 1 small) of the plastic trap and drained the water… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
How are you? I have a Breckwell P-2700 FSA Pellet stove and
I have a Breckwell P-2700 FSA Pellet stove and when the stove is on the auger continues to feed pellets into the pot. … read more
Jerry
Jerry
Plumber
High School or GED
1,456 satisfied customers
I have a Trane XE90. When the cover, covering the chamber
I have a Trane XE90. When the cover, covering the chamber containing the gas tubes, igniter, heat sensor, flame sensor rod, etc. is off the system runs perfect. If I put the cover on the system will i… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a Heat-N- Glo gas fireplace. Fire starts, when I turn
I have a Heat-N- Glo gas fireplace. Fire starts, when I turn switch on, burns for a few minutes, then go out & in a few minutes start burning again … read more
Jerry
Jerry
Plumber
High School or GED
1,456 satisfied customers
I have a leak in the water supply pipe right at the
I have a leak in the water supply pipe right at the connection where the pipes are welded together … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
My temperature gage is stuck on Hold 67. How do I clear the
how do I clear the program so I can regulate the temp… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I want to know if I can on a F 45 Greenville jotul
I want to know if I can cook on a F 45 Greenville jotul woodstove. … read more
Webb-Guy
Webb-Guy
tech.
77 satisfied customers
Our furnace is no heating. I just changed the filter. It
I just changed the filter. It doesn't seem to be lighting. The red LED is flashing 1 + 3 which indicates "Flame Sense out of sequence". … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Heater blowing cold air, Just replaced the filter, and I
Just replaced the filter, and I think that was the problem, but it still won't heat … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x