Furnace ignites and stays on for 5 sec then shuts off for about 30 sec. Tries again and shuts off again. Does this five times and quits. Unit is a natural gas Carrier 58PAV070-12. Also LED on furnace blinks {short, long, long and then repeats.} Tstat is White Rodgers #1F78 basic, nonprogrammable. AC part of system has run fine. Squirl cage blower and upper exhaust blower run fine before glow plate and gas come on. Any thoughts for me to try? Thanks
Submitted: 8 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 5 minutes by:
12/11/2009
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 8 years ago
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 22,886
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified
Have you sanded the flame sensor yet?
Ask Your Own HVAC Question
Customer reply replied 8 years ago
no where is the flame sensor?
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 8 years ago
in front of the burner at one end is the ignitor, at the other end is a metal rod with a white porcelin base. Sand it off with emery cloth or steel wool, even if it looks clean. A glaze can develope and impede flame sense thus shutting down the system. re start and wait 90 seconds for results.
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 22,886
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified
BillyHvac and 87 other HVAC Specialists are ready to help you
Ask your own question now
Customer reply replied 8 years ago
The flame sensor is cleaned flame is on it, but still kicks out after 5 seconds. What next?
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 8 years ago
Ground issue. Check that control and furnace ground are good..check all the way to breaker. Then we can move to pressure switch
Ask Your Own HVAC Question
Customer reply replied 8 years ago
Grounds appear to be good. One screw was a bit loose but everything looks solid now and function is still the same. Please what's next?
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 8 years ago

now locate pressure switch. It has an rubber tube and 2 wires to it. Remove 2 wires, start furnace, wait for exhaust fan to start and touch the 2 wires together so they make contact and hold them that way and see if unit progresses.

 

I will be off line for a bit but will respond as soon as I get back

Ask Your Own HVAC Question
Customer reply replied 8 years ago
Found the pressure switch. When second or exhaust fan came on I connected the wires that were connected to the switch. (It was round and did have a rubber tube going ditectly to the heat exchanger wall.) Unfortunately function remains unchanged. Still just 5 seconds of heat. What's next?
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 8 years ago

Here is a manual for your unit. - http://www.docs.hvacpartners.com/idc/groups/public/documents/techlit/58pa-1si.pdf

 

Frome here out the test require checking micro amps of flame sensor. If sensor test good replace circuit board. If sensor does not test good replace sensor

Ask Your Own HVAC Question
Customer reply replied 8 years ago
How many microamps should the flame sensor show? Only one wire goes to it so ...read current from what to what and would this be while the flame is on it? Is there anything else to try other than the circuit board if the sensor tests ok?
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 8 years ago

Hello again...

 

the sensor should read at least .5 ua. The meter set for DC micro amps, one meter lead to sensor and other eter lead to where sensor was plugged in. If .5 and above replace ign control. You can also add a wire from the burner to the ground terminal on the control

Ask Your Own HVAC Question
Customer reply replied 8 years ago

We do not have the furnace working yet but Billy went out of his way to help. We still have something to try that he gave us. My husband wants to make sure Billy receives compensation for all his help. I think the last thing he did was getting us the manual for the furnace. Which may still hold the answer to the problem. We are pleased with the service we received and will recommend the site to others, or use it again for any further problems. We were not able to work on it today and will not work on it on Sunday. If there are further questions we will contact the service on Monday.

Thank you for all your help

XXXXX XXXXXs

HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 8 years ago
I thank you very much! Happy Holidays!
Ask Your Own HVAC Question
Ask BillyHvac Your Own Question
BillyHvac
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 22,886
22,886 Satisfied Customers
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics

BillyHvac is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Phil, we have a Carrier Infinity Weathermaer natgas
Phil, we have a Carrier Infinity Weathermaer natgas furnacethis week the limit switch had to reset at lest 4 ties. We replaced the limit switch,ever since then the furnace runs but the top of the plen… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I Have a Carrier gas furnace model PG9MAB060120A. The
I Have a Carrier gas furnace model PG9MAB060120A. The burners blow but the air from the heat exchange at the furnace is luke warm. Is there a problem with the heat exchange? … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,142 satisfied customers
My high efficiency condensing furnace (Carrier) emits a
My high efficiency condensing furnace (Carrier) emits a terrible eye-stinging odor when heating. The furnace runs quiet and otherwise appears to be trouble free, however I see (and smell) a fresh (wet… read more
Appliance Guru
Appliance Guru
17,062 satisfied customers
Have Carrier fan coil unit model FV4CNB003. Have Carrier Fan
Have Carrier Fan Coil unit # FV4CNB003. Seemed to run and change speed during operation. Is this normal? … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I HAVE A CARRIER CNPHP HVAC SYSTEM THAT IS LEAKING WATER
I HAVE A CARRIER CNPHP HVAC SYSTEM THAT IS LEAKING WATER INTO THE SAFETY PAN BELOW. THE TECHNICAIN DIAGNOSED THE PROBLEM AS THE SECONDARY HEAT EXCHANGER HAS A CRACK. THE UNIT IS TEN YEARS OLD. RATHER … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,288 satisfied customers
I have a white Rodgers heat only thermostat, mod.1e78-140.
I have a white Rodgers heat only thermostat, mod.1e78-140. it is not working, does it run on batt. or is the power wired from home. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
58MVP080 model got the heat exchanger issue. I have tech
Hi Pearl,58MVP080 model got the heat exchanger issue … read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
22,886 satisfied customers
I have a White-Rodgers 1 F81-261 Programmable thermostat.I
I have a White-Rodgers 1 F81-261 Programmable thermostat.I want to operate it manually. Please help. It has reset at 62 degrees. … read more
Rick
Rick
Supervisor
22,874 satisfied customers
Need a heat exchanger for model GIN 80bu-1000 14B-3A; ser. #
need a heat exchanger for model GIN 80bu-1000 14B-3A; ser. # 1607K 03798 … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Is it unsafe to have a cracked heat exchange on your
Is it unsafe to have a cracked heat exchange on your furnace? … read more
Rick
Rick
Supervisor
22,874 satisfied customers
I have a White-Rodgers thermostat with the flap that opens
Hi, I have a White-Rodgers thermostat with the flap that opens to the menu. All of a sudden the temp of the room that the display shows on the left is not showing the temperature in Fahrenheit, but it… read more
Rick
Rick
Supervisor
22,874 satisfied customers
My white rodgers 1f78 non-prgm thermostat won't work. The
My white rodgers 1f78 non-prgm thermostat won't work. … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
I have a White Rodgers !F-95-1291 Touch screen thermostat
I have a White Rodgers !F-95-1291 Touch screen thermostat with remote outdoor sensor. The out door reading is off by 10 degr F, too low. What's the prob? … read more
Rick
Rick
Supervisor
22,874 satisfied customers
I have an f8024 white rodgers, i am renting right now but
I have an f8024 white rodgers, i am renting right now but the unit worked last summer, i just replaced the batteries, but when i press the temp down button, nothing happens. … read more
Iohn Keffer
Iohn Keffer
HVAC Tech
Associate Degree
41 satisfied customers
I need a heat exchanger kit for a weil-mclain ultra 105, no
i need a heat exchanger kit for a weil-mclain ultra 105 … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
How do I check heat exchanger for blockage. Today. Sounds
how do I check heat exchanger for blockage JA: I'll do all I can to help. How long have you been dealing with this? Customer: today JA: Do you plan on doing the work yourself? Customer: yes JA: Anythi… read more
Rick
Rick
Supervisor
22,874 satisfied customers
When were stainless steel heat exchangers required for
When were stainless steel heat exchangers required for residential usage and/or what HVAC company was the first to provide them. And are they as effective as touted.… read more
D.E. Anderson
D.E. Anderson
Industrial Refrigeration Service Manager
200 satisfied customers
I have a white/rodgers 8A05A -101 relay that I want to use
I have a white/rodgers 8A05A -101 relay that I want to use for a hot water circulating pump. The thermostat wiring is straight forward but the wiring for the 120 v is not. I have the following wires. … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x