This answer was rated:

Furnace is not working. Giving error code 13.

I have a Payne PG8JAA...
I have a Payne PG8JAA furnace that is sending code 13 and then turning into code 33 after about 5 minutes.
Show More
Show Less
Ask Your Own HVAC Question
Answered in 3 minutes by:
11/20/2009
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 22,767
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified
Did resetting the switches on the burners do anything?
Ask Your Own HVAC Question
Customer reply replied 8 years ago

No, it did not. The main fan just keeps running. In case you didn't already know:
Code 13: Limit Circuit Lockout
Code 33: Limit Circuit Fault
The instructions said that there would be an auto reset after it goes to code 33, so I waited the 3 hours and nothing happened.
I've also checked all the filters and the vents and everything is clean and clear. The unit is only a year old, and as you can tell from the images I've attached, it is very clean.

http://img25.imageshack.us/i/dsc00989f.jpg/
http://img23.imageshack.us/i/dsc00991mv.jpg/
http://img97.imageshack.us/i/dsc00992nr.jpg/

Behind the gas valve on the front wall is a 2"X4" rectangle plate with 2 wires attached to it. Turn power off and remove the 2 screws holding the plate in and remove the switch. Tap on the end a couple times and reinstall. This is a limit that is supposed to reset itself but can get stuck. Try that and get back to me with results

Ask Your Own HVAC Question
Customer reply replied 8 years ago

Okay.... This isn't a switch, unless I removed the wrong thing. Please verify...
http://img39.imageshack.us/img39/7985/dsc00993h.jpg

Ok that is a limit. Is this a down flow?

Ask Your Own HVAC Question
Customer reply replied 8 years ago

Yes it a down flow... Down flow meaning the heated air goes into the slab of the house and the intake is coming from the top...

That means you may have a limit in the blower section
Ask Your Own HVAC Question
Customer reply replied 8 years ago

While I was waiting for your response, I took the cover off of the blower section and was looking for something similar to what the other switches looked like; and could not find anything.
http://img695.imageshack.us/img695/7809/dsc00995o.jpg
http://img36.imageshack.us/img36/14/dsc00994ni.jpg

Ok, lets get going on some elimination. Tape the safety door switch down. The code should start. Remove the 2 wires from the limit you took off earlier, don't let these touch ground or the 3 amp fuse on the circuit board will blow. Touch the metal ends of the 2 wires together and see if code stops. If not, put back on switch and try same thing with roll-outs.

Ask Your Own HVAC Question
Customer reply replied 8 years ago

Okay. I took the wires off the limiter (image I sent you before) and put a paper clip in between them. Powered up the unit and it works now. I have ignition and everything is operating normal (solid red light). So I have a bad limiter. Where would I be able to get a replacement and about how much do they cost?

You can buy the online for around 45-50 dollars. You could probably pick one up at a local heating shop for less than that. That limit is very common in many furnaces and will be a regular stock item. Jut take that one with you. You can try for temporary fix to hold a flame on the switch for 20 seconds and then put it in the freezer for 2-3 minutes. That sometimes un-sticks them, but I still think you should get a new one.

BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 22,767
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified
BillyHvac and 87 other HVAC Specialists are ready to help you
Ask your own question now
Customer reply replied 8 years ago
Excellent. Thank you very much!!

Actually I thank you. You have shown great patience and I appreciate it greatly.

Ask Your Own HVAC Question
Ask BillyHvac Your Own Question
BillyHvac
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 22,767
22,767 Satisfied Customers
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics

BillyHvac is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,730 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Have a tank less hot water heater that will not come on. It
Have a tank less hot water heater that will not come on … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a GE power vent gas water heater that will not stay
I have a GE power vent gas water heater that will not stay on. … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Why do we have warning signal showing on our panel also wot
Why do we have warning signal showing on our panel also wot is w 42 h mean … read more
travis webb
travis webb
tech.
2,159 satisfied customers
I have a 80uhg that when i call for heat the gas burner
I have a 80uhg that when i call for heat the gas burner doesnt light and the blower comes on … read more
travis webb
travis webb
tech.
2,159 satisfied customers
I purchese my Rheem 40 Gal water heater in 2016, now it only
I purchese my Rheem 40 Gal water heater in 2016, now it only gives me warm water for a short time then cold. Can it be repaired or do I need a new unit? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Why is the supply connection at the header 1 1/2” do i have
Why is the supply connection at the header 1 1/2” do i have to run 1 1/2” to the pumps? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a York Diamond 80 and I am getting the 4 flashes code
I have a York Diamond 80 and I am getting the 4 flashes code for open high limit switch. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My recirculation fan does not shut off ony good man natural
My recirculation fan does not shut off ony good man natural gas furnace and the trouble light shows normal operation … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a loga max 142-45 the water relief valve started
I have a loga max 142-45 the water relief valve started leaking water. Replaced the expansion tank and releif valve. Still leaking. now contractor wants to replace the hot water heater. please help wi… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Americian standard freedom 80 single stage natural gas
americian standard freedom 80 single stage natural gas furnace won't light … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Have Philco furnace Model G6RC 100C-16 - furnace runs for 4
Have Philco furnace Model G6RC 100C-16 - furnace runs for 4 minutes, then shuts off for 10 minutes. Red light blinks twice. Checked to make sure drain is operating, which it is. Checked the flame sens… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
22,767 satisfied customers
I have a Carrier Model 58MVP 120 blinking error code. 13.
I have a Carrier Model 58MVP 120 blinking error code … read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
22,767 satisfied customers
Hvac troubleshoot. Airease RPGE13 will not crank up for
Hvac troubleshoot. Airease RPGE13 will not crank up for heating for the first time this season. LED indicator light is blinking a fast steady blink which is supposed to indicate normal operation. I am… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a lennox airhandler cbx32mv-048-230-6-07 I have no
I have a lennox airhandler cbx32mv-048-230-6-07 I have no heat and this unit has heat strips. I have had techs out here and they have changed the 3 relays and today the mother board. lasts week the ma… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a 1989 vintage Vaillant boiler that continues to
Hi, I have a 1989 vintage Vaillant boiler that continues to ignite and then shuts off. What would cause this problem? … read more
Plumbers_Mate
Plumbers_Mate
General Manager
Vocational, Technical or Trade Scho
2 satisfied customers
I have a Nordyne 3.5 Ton heat pump that a acted up and
I have a Nordyne 3.5 Ton heat pump that a acted up and wouldn't heat last week. It has small leak in coil that seems very slight. R 22 imstalled , unit holding 40psi for twenty minutes the repairman (… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Heater not heating. One day. I,m not sure. I have removed
I,m not sure. I have removed the front cover. you can hear the click when the water is turned on but the blower does not come on … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
The red emergency on/off switch was accidentally turned off.
The red emergency on/off switch was accidentally turned off. After turning it back on, checking the breakers, and turning the thermostat off, then on and resetting it, I still have no heat. What else … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x