Whirlpool Furnace, Model # XXXXX Just lit pilot light=OK. Furnace fires=OK. Turn fan on thermostat to 'ON' fan works=OK. With all covers on and secure, furnace fires, but fan does not come on automatically. Thermostat set to 'FAN-AUTO'. Is there a temp sensor or relay that needs replacement? Is there a schematic available?
Show More
Show Less
Ask Your Own HVAC Question
Answered in 2 minutes by:
10/17/2009
Kenton Guidry
Kenton Guidry, HVAC Technician
Category: HVAC
Satisfied Customers: 966
Experience: 12 years install/service experience.
Verified
Do you have a device that looks like the following picture? I do not have a diagram.
graphic
Ask Your Own HVAC Question
Customer reply replied 8 years ago

Yes, I have a device that looks like the picture.

 

Leon

That device acts as a hi limit, and fan delay.

Two wires are going to be the power to the fan.

The other two will be the control voltage to the switch.

Do you see that?
Ask Your Own HVAC Question
Customer reply replied 8 years ago

Yes, 2 yellow wires, 1 goes to FAN load, and 1 FAN line

and 2 orange wires, 1 goes to LIMIT load, and 1 LIMIT line.

 

OK

When in cooling your fan will run by getting power from another relay.

When in heating your fan will run by getting power from that limit switch.

So to check voltage you will measure from the neutral to the fan load.

This is a way to make the fan run at different speeds.

On a temperature rise the switch will close the fan line and load which will give the low or medium speed to the fan power.

Please respond with any further questions, or concerns.
Ask Your Own HVAC Question
Customer reply replied 8 years ago

Does this sound like a defective FAN/LIMIT switch? What is this switch called and how can I order a replacement?

 

I can see the dial rotate as temp rises, but I'm thinking it doesn't close the contacts to turn on the fan.

 

Just want to make sure I'm understanding what is occurring..

 

Thanks

 

 

You are correct Leon, this does sound like a defective switch.

However you can confirm this by measuring the resistance across the fan load and line, or you can measure voltage.

What is your zip code, I will see if I can find a location for you.
Ask Your Own HVAC Question
Customer reply replied 8 years ago
Zip code is: 30078
The following locations will be able to get you the part you need.

#J4 LAWRENCEVILLE, GA
2105 Newpoint Pl. Ste 300
Lawrenceville, GANNN-NN-NNNNbr />PHONE:(NNN) NNN-NNNNbr />FAX:(NNN) NNN-NNNNbr />Saturday Hours: CLOSED

#H3 CONYERS, GAXXXXXNW
Conyers, GANNN-NN-NNNNbr />PHONE:(NNN) NNN-NNNNbr />FAX:(NNN) NNN-NNNNbr />Saturday Hours: CLOSED
Kenton Guidry
Kenton Guidry, HVAC Technician
Category: HVAC
Satisfied Customers: 966
Experience: 12 years install/service experience.
Verified
Kenton Guidry and 87 other HVAC Specialists are ready to help you
Ask your own question now
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Kenton Guidry Your Own Question
Kenton Guidry
Kenton Guidry
Kenton Guidry, HVAC Technician
Category: HVAC
Satisfied Customers: 966
966 Satisfied Customers
Experience: 12 years install/service experience.

Kenton Guidry is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

966 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
My furnace burner turns off after just a couple minutes. The
my furnace burner turns off after just a couple minutes. The blower motor keeps running so it starts blowing cold air. … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
The belt driven fan on my willaimson furance does not run.
The belt driven fan on my willaimson furance does not run. I hace checked the fan motor and it is fine.… read more
mranswer
mranswer
TECHNICIAN
Bachelor's Degree
481 satisfied customers
I have a Model RCDC10NCBJR Forced Air Unit in my home. REcently
I have a Model RCDC10NCBJR Forced Air Unit in my home. REcently I had a electrical Utility issue where the incoming power 'single phased" so there was only 240volts to all circuits. The Utility Compan… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Goodman model # GU075-3. The pilot will light; it
I have a Goodman model # XXXXX The pilot will light; it will go through the heating cycle until the temp gets up to the thermostat setting (as it should),but when the main burner cuts off the pilot al… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
Hi, I am able to light my pilot light successfully by doing
Hi, I am able to light my pilot light successfully by doing the following (power to the furnace has been off during the summer), but my furnace never fires up: 1. Turn the knob on the furnace from "OF… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
I have Lennox G26 gas heater. The heater did not kick in when
I have Lennox G26 gas heater. The heater did not kick in when the thermostat temperature is reading lower than the setpoint, say even at 67 when the setpoing is 73. Is this due to relay board problem?… read more
Heath
Heath
Vocational, Technical or Trade Scho
1,002 satisfied customers
My heat thermostat is set on automatic heat but the fan does
My heat thermostat is set on automatic heat but the fan does not come on when the temperature in the house is below the set point. Do I need to a new sensor? I have a White-Rodgers thermostat. Type 1F… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have an older amana furnace and the pilot light starts up
I have an older amana furnace and the pilot light starts up fine after the thermostat triggers it but it takes a long time for the burners to light, if they do. Its it an ignitor problem or is it a pr… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
I have a Lennox furnace in my small commercial building that
I have a Lennox furnace in my small commercial building that isn't working. Thermostat is set to heat and fan to auto, pilot light is lit, but won't fire up. If you switch fan selector to on, the fan … read more
Master tech
Master tech
High School or GED
62 satisfied customers
I have an Lennox G12R03E*82-6 auto light furnace. It does
I have an Lennox G12R03E*82-6 auto light furnace. It does not light. I have replaced the filter that was clogged and put in a new thermostat. I followed the auto light instructions which did not work.… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
i have a Rheem furnace model RGDD-08NE-GR and the blower does
i have a Rheem furnace model RGDD-08NE-GR and the blower does not come on when the thermostat creates a demand signal. the pilot comes on and the gas comes on but the blower does not. the fan can be t… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
I have a coleman DES 80 model 2880A766 95K Btu furnace in my
I have a coleman DES 80 model 2880A766 95K Btu furnace in my house, it is probably 15 to 17 years old that won't stay on. The main burner will light, the main fan will come on, but after 1 to 15 minut… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
I have a Coleman auto ignite furnace. It will not work in the
I have a Coleman auto ignite furnace. It will not work in the auto mode, but will work in the on mode?… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
How can I test my Robertshaw 7000BER Natural Gas furnace valve
How can I test my Robertshaw 7000BER Natural Gas furnace valve to see if it is functional or not. Gas won't turn on.I have measured 24VAC from Transformer. Put in a new Thermostat. But no worky.… read more
DanielC
DanielC
Service manager
High School or GED
95 satisfied customers
I just tried to turn on the heat in my house this morning and
I just tried to turn on the heat in my house this morning and I heard an intermittant humming noise comming from the mechanical room. The noise sounded like it was from the furnace and lasted about 15… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
my lennox furnace model #V810A1012 will not start up. I have
my lennox furnace model #V810A1012 will not start up. I have a pilot light, and the thermostat is commanding heat… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Tappan gas furnace model GUF105D30E5 blower fan wont turn
Tappan gas furnace model GUF105D30E5 blower fan won't turn off not even when temperature setting has been achieved. Thermostat fan setting is on auto. Any place I can find users manual, schematics?… read more
coolman1973
coolman1973
AC/Heat Tech
Vocational, Technical or Trade Scho
162 satisfied customers
I have a Hart Crouse Model CP112 with a honewell L80478B10092
I have a Hart Crouse Model CP112 with a honewell L80478B10092 aquastat. Circulator pump is running, water temp has dropped bellow 100° and boiler has not fired. How do I trouble shoot this problem?… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x