The "heat" on my A/C won't come on. I can hear click on thermostat, but NO fan or heat from the unit kicks on. Circuits haven't tripped. The "cool" on the A/C works. Just the "heat" won't come on?? Can you help?
Submitted: 8 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 52 minutes by:
10/9/2009
HVAC Technician: Kenton Guidry, HVAC Technician replied 8 years ago
Kenton Guidry
Kenton Guidry, HVAC Technician
Category: HVAC
Satisfied Customers: 966
Experience: 12 years install/service experience.
Verified
Please turn your furnace off. Wait one minute. Then turn it back on. After that watch the furnace start up. You will need to remove one of the panels to observe the following.

Gas furnaces have a start sequence they must go through.

The first step is that the furnace will get the signal from the thermostat to turn on.

Then the induced draft fan will come on. Not all systems have this fan.

After that, if you have an induced draft fan, the pressure switch will close because of the induced draft fan running.

Once that happens your ignition will attempt to ignite the flame.

If you have a spark ignition the ignitor will spark. If you have a hot surface ignitor, the ignitor will glow very bright from being so hot.

This is when the gas valve should open.

The gas will not ignite.

Then the flame sensor will sense the flame.

Once the flame is sensed, the heat exchanger will warm up.

After the heat exchanger warms up the indoor blower motor will start.


Let me know how your system runs compared to the above description.
Kenton Guidry
Kenton Guidry, HVAC Technician
Category: HVAC
Satisfied Customers: 966
Experience: 12 years install/service experience.
Verified
Kenton Guidry and 87 other HVAC Specialists are ready to help you
Ask your own question now
Customer reply replied 8 years ago
I don't know that I can remove the "panel" that you suggested me to do as my A/C unit is located on my roof??...
HVAC Technician: Kenton Guidry, HVAC Technician replied 8 years ago
Then you must call out a service company.
Ask Your Own HVAC Question
Customer reply replied 8 years ago
Thank you for your help. I did call out a service tech. And, when he arrived I turned on the heat at the thermostat and it "worked"!! Go figure. He had a few explanations why it would work and then all of a sudden not work. And, things to try before I call next time (should it happen again :-(( ...BotXXXXX XXXXXne... I paid you and a service tech for an H/A unit that started to work all on it's own. ??? But, what's a person to do when you don't know how to "fix" something??? Call a Service Tech. Thanks anyway.
HVAC Technician: Kenton Guidry, HVAC Technician replied 8 years ago
You can try to trouble shoot it but if you cannot get to the system then it was best to call someone out.
Ask Your Own HVAC Question
Customer reply replied 8 years ago
Thanks for the help. It's all fixed. I called a Tech. The system began working all on its own. Go figure. But, thanks anyway. We're all done. Bye.
HVAC Technician: Kenton Guidry, HVAC Technician replied 8 years ago
bye
Ask Your Own HVAC Question
Ask Kenton Guidry Your Own Question
Kenton Guidry
Kenton Guidry
Kenton Guidry, HVAC Technician
Category: HVAC
Satisfied Customers: 966
966 Satisfied Customers
Experience: 12 years install/service experience.

Kenton Guidry is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,730 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

966 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
90% secondary heatexchanger holding a lot of water in it,
Bryant 90% secondary heatexchanger holding a lot of water in it, not allowing the pressure switch to close. I removed the 3 hoses at the top (2 large 1 small) of the plastic trap and drained the water… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Need a heat exchanger for model GIN 80bu-1000 14B-3A; ser. #
need a heat exchanger for model GIN 80bu-1000 14B-3A; ser. # 1607K 03798 … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
In 2003, we had a new high-end Carrier Infinity Weathermaker
In 2003, we had a new high-end Carrier Infinity Weathermaker furnace installed - Model 58MVP-100-20 (run on propane). 8 years later, in 2011 - while still under warranty (parts and labor) the main hea… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Comfortmaker RPJ II furnace. It won't heat. The
I have a Comfortmaker RPJ II furnace. It won't heat. The induction motor runs and runs. I don't see the ignitor light. But, I don't hear the click before the ignitor should light. Does that mean the p… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I have a furnace 17 years old. renters say are experincing
I have a bryant furnace 17 years old. renters say are experincing maybe a co2 leak. any advice.… read more
Kenton Guidry
Kenton Guidry
HVAC Technician
966 satisfied customers
Is it unsafe to have a cracked heat exchange on your
Is it unsafe to have a cracked heat exchange on your furnace? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I need a heat exchanger kit for a weil-mclain ultra 105, no
i need a heat exchanger kit for a weil-mclain ultra 105 … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
How do I check heat exchanger for blockage. Today. Sounds
how do I check heat exchanger for blockage JA: I'll do all I can to help. How long have you been dealing with this? Customer: today JA: Do you plan on doing the work yourself? Customer: yes JA: Anythi… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
When were stainless steel heat exchangers required for
When were stainless steel heat exchangers required for residential usage and/or what HVAC company was the first to provide them. And are they as effective as touted.… read more
D.E. Anderson
D.E. Anderson
Industrial Refrigeration Service Manager
200 satisfied customers
Funky smell coming from heat exchanger outside...... repair
funky smell coming from heat exchanger outside...... repair guy said the gas not m ixing with the air properly..true? said probably just clogged … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Heat exchanger is a month old and heat stopped working.
Heat exchanger is a month old and heat stopped working. Three lights are blinking saying it is a limit or rollout switch … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,090 satisfied customers
I have a property with a Keeprite heat exchanger installed.
I have a property with a Keeprite heat exchanger installed. I believe the filter is clogged but I don't know where it's located. The model is PGF018K040E … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
The condensation water leaks from heat exchanger near the
The condensation water leaks from heat exchanger near the filter and comes on the ground tray. There is no blockage of any sort. What needs to be done for auxiliary condensation tray if it is cracked.… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,090 satisfied customers
How can I clean the inside of the heat exchanger on my
how can I clean the inside of the heat exchanger on my furnace? … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My carrier heating heat exchanger is plugged. I understand
My carrier heating heat exchanger is plugged. I understand it is civered under a recall action. if bI purchase a new systeem 59mn7a080-20 what price drduction do I receive? … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
How much time should be allowed to change a heat exchanger
How much time should be allowed to change a heat exchanger for a 48tjf016 series 580ba and 2 men?… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,090 satisfied customers
I have Yorx High efficiency tubular heat exchanger, im not
Hi, my name is***** have Yorx High efficiency tubular heat exchanger, im not sure wich model though GY9S , GM9S, or GF9S. There is water leaking from the white PVC pipes, can I just cut them out and r… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,090 satisfied customers
I was looking into a trane tud060 heat exchanger and noticed
I was looking into a trane tud060 heat exchanger and noticed a buildup of white powder at one of the factory seams and need to know what is causing this. I attached a pic. Thanks… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x