I have a Lennox G43UF Series furnace. It is not blowing hot air to the house. The LED#1 light is off and LED #2 is Slow Flash, which I understand to mean the combustion Air pressure switch is not open. What do I do?
Show More
Show Less
Ask Your Own HVAC Question
Answered in 24 minutes by:
10/1/2009
KenCan
KenCan, HVAC Technician
Category: HVAC
Satisfied Customers: 111
Experience: 20+ years experience, Nate certified, EPA certified, TX state license
Verified

Hello,

Do you know where the pressure switch is located on this furnace?

 

Thanks,

Ken

Ask Your Own HVAC Question
Customer reply replied 8 years ago
Thank you for offering to help me. Yes, and I have my installation guide and manual to follow along. That is how I was able to provide this information. I found it on the trouble shooting section under the "Heating Sequence of Opertation" section.

Thank you for responding back.

 

Ken

Ask Your Own HVAC Question
Customer reply replied 8 years ago
OK I have the pressure swith located.

Ok. What you will do not is find the rubber hose and remove off of the pressure switch and the other end where it connects to the ports on the long black box. You will want to look inside these ports for any debris. You will want to also see if you can blow into once you put hose back in. Make sure you do not blow into the pressure switch. After you do this you can put hoses back on and give a call for heat and see if unit will run.

 

Thanks,

Ken

Ask Your Own HVAC Question
Customer reply replied 8 years ago
No luck. I have two rubber hoses. ONe red and one black. Both were clear of debris. The Combustion Air Inducer sounds like it has a hum coming it and the cylinder that connectis into it with copper wiring inside is extremely hot!

Ok. Have you ever seen your igniter glow yet?

 

Ken

Ask Your Own HVAC Question
Customer reply replied 8 years ago
Is that the silver box that is on the top on the inside with a small glass opening? If yes, then the answer is no, there is no igniter glow. I have a honeywellVR8205 Gas Valve with on/off lever. I followed the directions to try to light the unit before but again, with no luck.

Yes this is where your igniter is. Are you ready for some more hands on?

 

Ken

Ask Your Own HVAC Question
Customer reply replied 8 years ago
Yes I am

Ok. You will need to find the two wires that go to the pressure switch that you found earlier. Once you find these you will first need to shut the furnace off at the thermostat. Then you will remove these two wires. Next give a call for heat from the thermostat and be ready to jump these two wires together when your small inducer motor (just below your burner box) comes on. After these two wires are joined together you will look for the igniter to come on and the unit to fire off. After your furnace fires off shut down at the thermostat you will not need to let it run for more than a couple of seconds. We just want to see if it will fire off.

 

Thanks,

Ken

Ask Your Own HVAC Question

You can use a metal paper clip to join the two steak ons together. Both wires will need to make contact after the inducer motor starts up.

 

Ken

Ask Your Own HVAC Question
Customer reply replied 8 years ago

I'm sorry, I don't fully understand. I turned off the thermostat and removed the two wires. I'm not sure what you mean by jump the wires together. They have white plastic caps on them. Should I try to touch them together, or do you mean place them back on the switch when the motor comes on? should I remove the white caps from the wires? OK I just got your post about the paper clip. I'll try that

 

Customer reply replied 8 years ago
I'm sorry, I don't fully understand. I turned off the thermostat and removed the two wires. I'm not sure what you mean by jump the wires together. They have white plastic caps on them. Should I try to touch them together, or do you mean place them back on the switch when the motor comes on? should I remove the white caps from the wires?
Customer reply replied 8 years ago

The inducer motor is not starting up. It only hums, unless that is what it is suppose to do. I did use a paper clips to join the two wires and nothing happened.

 

If your indcuer motor is not starting up this is going to be your problem. What is the serial number of this furnace?

 

Thanks,

Ken

Ask Your Own HVAC Question
Customer reply replied 8 years ago
S/N is 5906H43089. What should the inducer motor sound like when it is on? Does this have anything to do with the AC, as that was working fine a week ago?

Inducer motor has nothing to do with the AC. The purpose of the inducer motor is to pull the air through your heat exchanger and close the pressure switch. It should sound like a small fan and should be the first thing that comes on when you call for heat. The good news is this furnace has a 5 year on the parts and the inducer motor is one of those parts.Smile Don't forget to put both of your wires back on the pressure switch.

 

Thanks,

Ken

 

Positive Feedback is appreciated!!

Ask Your Own HVAC Question
Customer reply replied 8 years ago
Thanks for your help! I'll have to call to have someone come out. I know I have to cover labor cost. About how many hours on average to replace an Inducer motor? I don't want to get ripped off.

SmileIf the technician has done this before it should not take more than 30 minutes to do. He is removing five 1/4 inch screws and putting a new gasket behind the inducer motor. You can call a couple of different contractors and tell them what you need and let them know that the furnace is under warranty and ask each one what they would charge for the installation of an inducer motor. This could save you some $$$

 

Thanks,

Ken

 

 

Ask Your Own HVAC Question

You can put your zip code in this link for some contractors in your area.

 

http://www.lennox.com/residential/#

 

 

KenCan
KenCan, HVAC Technician
Category: HVAC
Satisfied Customers: 111
Experience: 20+ years experience, Nate certified, EPA certified, TX state license
Verified
KenCan and 87 other HVAC Specialists are ready to help you
Ask your own question now
Ask KenCan Your Own Question
KenCan
KenCan
KenCan, HVAC Technician
Category: HVAC
Satisfied Customers: 111
111 Satisfied Customers
Experience: 20+ years experience, Nate certified, EPA certified, TX state license

KenCan is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,730 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
90% secondary heatexchanger holding a lot of water in it,
Bryant 90% secondary heatexchanger holding a lot of water in it, not allowing the pressure switch to close. I removed the 3 hoses at the top (2 large 1 small) of the plastic trap and drained the water… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Need a heat exchanger for model GIN 80bu-1000 14B-3A; ser. #
need a heat exchanger for model GIN 80bu-1000 14B-3A; ser. # 1607K 03798 … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
In 2003, we had a new high-end Carrier Infinity Weathermaker
In 2003, we had a new high-end Carrier Infinity Weathermaker furnace installed - Model 58MVP-100-20 (run on propane). 8 years later, in 2011 - while still under warranty (parts and labor) the main hea… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Comfortmaker RPJ II furnace. It won't heat. The
I have a Comfortmaker RPJ II furnace. It won't heat. The induction motor runs and runs. I don't see the ignitor light. But, I don't hear the click before the ignitor should light. Does that mean the p… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I have a furnace 17 years old. renters say are experincing
I have a bryant furnace 17 years old. renters say are experincing maybe a co2 leak. any advice.… read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
Is it unsafe to have a cracked heat exchange on your
Is it unsafe to have a cracked heat exchange on your furnace? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I need a heat exchanger kit for a weil-mclain ultra 105, no
i need a heat exchanger kit for a weil-mclain ultra 105 … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
How do I check heat exchanger for blockage. Today. Sounds
how do I check heat exchanger for blockage JA: I'll do all I can to help. How long have you been dealing with this? Customer: today JA: Do you plan on doing the work yourself? Customer: yes JA: Anythi… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
When were stainless steel heat exchangers required for
When were stainless steel heat exchangers required for residential usage and/or what HVAC company was the first to provide them. And are they as effective as touted.… read more
D.E. Anderson
D.E. Anderson
Industrial Refrigeration Service Manager
198 satisfied customers
Funky smell coming from heat exchanger outside...... repair
funky smell coming from heat exchanger outside...... repair guy said the gas not m ixing with the air properly..true? said probably just clogged … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Heat exchanger is a month old and heat stopped working.
Heat exchanger is a month old and heat stopped working. Three lights are blinking saying it is a limit or rollout switch … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,086 satisfied customers
I have a property with a Keeprite heat exchanger installed.
I have a property with a Keeprite heat exchanger installed. I believe the filter is clogged but I don't know where it's located. The model is PGF018K040E … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
The condensation water leaks from heat exchanger near the
The condensation water leaks from heat exchanger near the filter and comes on the ground tray. There is no blockage of any sort. What needs to be done for auxiliary condensation tray if it is cracked.… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,086 satisfied customers
How can I clean the inside of the heat exchanger on my
how can I clean the inside of the heat exchanger on my furnace? … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My carrier heating heat exchanger is plugged. I understand
My carrier heating heat exchanger is plugged. I understand it is civered under a recall action. if bI purchase a new systeem 59mn7a080-20 what price drduction do I receive? … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
How much time should be allowed to change a heat exchanger
How much time should be allowed to change a heat exchanger for a 48tjf016 series 580ba and 2 men?… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,086 satisfied customers
I have Yorx High efficiency tubular heat exchanger, im not
Hi, my name is***** have Yorx High efficiency tubular heat exchanger, im not sure wich model though GY9S , GM9S, or GF9S. There is water leaking from the white PVC pipes, can I just cut them out and r… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,086 satisfied customers
I was looking into a trane tud060 heat exchanger and noticed
I was looking into a trane tud060 heat exchanger and noticed a buildup of white powder at one of the factory seams and need to know what is causing this. I attached a pic. Thanks… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x